5Kw System setup

Featured Replies

We recently installed the following system:

Axpert 5Kw Inverter

6 x Canadian 335w Solar panels

1 x Huawei 100ah 48v Battery

Settings on inverter is as follows:

01: SOL

02: 30A

03: UPS

11: 30A

12: 49V (reason for 49V is that we don't use to much Battery power during the day) - Does it make sense to you guys  ???

13: 51V (Same as floating V) - is it fine like this??

16: OSO - Should I add utility also?

26: 53.5V - (As per attached pic taken from the Huawei battery user manual ) - do you guys agree??

27: 51V - (As per attached pic taken from the Huawei battery user manual ) - do you guys agree??

29: 47V - Will 47V be about 70% DOD ??

Extra Questions:

1. For some reason the inverter is on "SL" status (Slave) and I don't know why?

2. When the Battery reaches 49.4v I get error "04" (Battery voltage to low) and the Battery Icon on the inverter screen is indicating 1 bar only??

3. We can run the pool pump (750w) inc. the Fridge etc. total load of about 850 to 900w ......but as soon as the load is to much it struggles to go over to Utility immediately and basically cuts the power supply to the house (not tripping any earth leakages) and after about a minute it will switch over to Utility and start everything up again..... this only happens when the pool pump is on. Is it something to do with the pool pump trying to re-start again?? 

Guys your input will be much appreciated

Please keep in mind that I'm not an Electrician or Solar expert and are new to this so please can we keep the inputs "Simple" ? 

Thanks

 

 

 

2019-05-18 11-12-55 AM.jpg

esm_jpeg_9e361454623fd7cb02fc0e6bcc659cd8.jpg

22 hours ago, GrahamS said:

01: SOL

That means the inverter will switch the loads to the grid at sundown. This is good if you want to preserve maximum battery energy for load shedding, but to get maximum use of the battery, you would use SBU.

Quote

02: 30A

You could go to 50 A.

Quote

12: 49V (reason for 49V is that we don't use to much Battery power during the day) - Does it make sense to you guys  ???

Yes. You might even want to bump it up to 50 V.

Quote

13: 51V (Same as floating V) - is it fine like this??

See how it goes. This is the voltage at which the battery starts discharging again, after having the loads supplied by the grid.

Quote

16: OSO - Should I add utility also?

I like to put this on a timer; setting OSO at 7am and SNU at 10pm. But you'd want a computer to do that automatically. I use Node Red running on a BeagleBone (similar to a Raspbeyy Pi).

Quote

26: 53.5V - (As per attached pic taken from the Huawei battery user manual ) - do you guys agree??

27: 51V - (As per attached pic taken from the Huawei battery user manual ) - do you guys agree??

Yes, that seems to be the received wisdom for 15S batteries, such as yours.

Quote

29: 47V - Will 47V be about 70% DOD ??

No, that's dead empty. 30% SOC would be about 48.7 V, rested, no load.

Quote

1. For some reason the inverter is on "SL" status (Slave) and I don't know why?

Presumably, setting 28 is something other than SnG. Turn off the "power" switch to be able to change this setting.

Quote

2. When the Battery reaches 49.4v I get error "04" (Battery voltage to low) and the Battery Icon on the inverter screen is indicating 1 bar only??

The inverter considers 2.0V more than the low cutoff voltage (setting 29) to be "low battery" and will issue the warning. At 49.4 V, presumably there will be small dips due to heavy loads going off (even a fridge starting could be 1 kW briefly). If you are able to run a patched firmware, this will be changed to 0.5 V above the low voltage cutoff. You didn't say your exact inverter model (there are about 4 models that are "Axpert 5 kW"), so I can't say if yours is eligible for patched firmware. See Can I Update my Firmware, and if so to what?

Quote

3. We can run the pool pump (750w) inc. the Fridge etc. total load of about 850 to 900w ......but as soon as the load is to much it struggles to go over to Utility immediately and basically cuts the power supply to the house (not tripping any earth leakages) and after about a minute it will switch over to Utility and start everything up again..... this only happens when the pool pump is on. Is it something to do with the pool pump trying to re-start again?? 

It may well be that the start-up current for your pool pump (often 7 x the running power, so 750 x 7 = 5 250 W) is too much for your battery to handle. Your battery is rated at 50 A max discharge (or charge), so that's less than 2500 W AC load (less because the inverter isn't 100% efficient). It may be possible to find some sort of soft start gizmo for the pool pump. But once the pump is on, it's just a 750 W load (perhaps 950 VA due to the power factor of motors), and should not be much of a problem for your inverter or your battery, if your other loads are light.

Edited by Coulomb
White space forum bug.

  • Author

Hi

Thanks for the reply its much appreciated.

Yesterday as well as this morning the inverter had issues going over to utility on a 2kw load and error "20" which is not in the manual occurred.

Should we rather set the Inverter to Utility as first priority when running the Dishwasher or Tumble dryer?

I have attached photos of the error as well as the inverter Model.

 

thanks guys

 

IMG_20190503_135724.jpg

IMG_20190518_150711.jpg

25 minutes ago, GrahamS said:

Yesterday as well as this morning the inverter had issues going over to utility on a 2kw load and error "20" which is not in the manual occurred.

Ah. Well, your machine is a clone, so it's hard to say what that's about. I can't find reference to fault code 20 in the Voltronic Power 73.00 firmware. I think some clones have been reported as having weird problems switching to and from utility.

25 minutes ago, GrahamS said:

Should we rather set the Inverter to Utility as first priority when running the Dishwasher or Tumble dryer?

Either that, or purchase another battery to parallel with the first.

  • Author
3 hours ago, Coulomb said:

Ah. Well, your machine is a clone, so it's hard to say what that's about. I can't find reference to fault code 20 in the Voltronic Power 73.00 firmware. I think some clones have been reported as having weird problems switching to and from utility.

Either that, or purchase another battery to parallel with the first.

Here is a photo of the software version

IMG_20190519_144110.jpg

1 hour ago, GrahamS said:

Here is a photo of the software version

Ah, a familiar version number. 😉  I've just checked, and I can't see how fault code 20 gets generated. My first guess is that it arrives by CAN packet, but I assume you don't have paralleled machines, so there would be no source of CAN packets. So: a mystery, unless they patched our patched firmware! 😮

  • Author

SO I have monitored the Battery yesterday from 17h30 up until this morning 05h43...

17h30 - Inverter running on Utility, Battery on 49.5v

19h20 - 49.2v ..., I decided to charge with utility power

20h00 - fully charged and on 51v float, at this stage I did switch the Utility charge off and the volts dropped to 50.3v

20h10 - 50.1v

21h30 - 49.2v

05h43 - 49..1v

The discharge indicator on the battery itself was on during this 12 hour period

We were on Utility the whole time.

Does all it of this make sense.....I clearly do not understand Battery Chemistry ???

 

 

3 hours ago, GrahamS said:

Does all it of this make sense

Sure. With the utility charger off, even with the utility powering the loads, something has to power the electronics in the inverter-charger: the processor, lighting the display, relays, other electronics, comes to a non-trivial 35 W or so. So that's why the discharge LED is on, and a small part of the reason for the battery voltage to be falling. But batteries of all kinds will fall in voltage after a charge, till they reach a resting voltage, often around 3.33 V per cell for the LFP chemistry. That's just under 50 V for a 15S battery.

So any voltage above about 51 V is a sort of fluffy region where there isn't real energy behind it. The same happens with lead acid. A typical 12 V battery will float at 13.8V or 13.5 V with very little current, but will fall back to a resting voltage of about 12.8 V, even when fully charged.

All battery voltages are also affected by temperature. There is also a self discharge effect (much worse with lead acid) that gets worse with age.

So the takeaway message is: voltage is not a good indicator of state of charge, especially for LFP at middling SOC.

Edited by Coulomb

1 hour ago, GrahamS said:

I thought that maybe the inverter BMS and the BMS of the Battery itself is not communicating with one another.

The inverter firmware doesn't communicate with the battery BMS, and that's a pity. A few very recent models can with a special cable, but they have an RS-485 interface built in. The Axperts don't.

15 hours ago, Coulomb said:

One follows the steps in this post: Do I Own a Clone?

Hi Coulomb

We are very newbies and wonder if you could assist (all your posts show a magnitude of knowledge!). We have the following set-up:

4 string of 2@300W panels

Axpert 5 kVA inverter

2 x Huawei lithium batteries.

The problems we are having is following:

·         Panels seem to be picked up during early (South African time) low intensity light by inverter. When intensity increases, e.g.  09h30, the panels are switched off and system runs on batteries (thus no charging).

·         Pool is scheduled to start at 11h00 which then causes system to trip and bypass to UTI. This eventually switches to panels, where input is ~1.6 kV and output is ~1.3 kV, so pool runs solely from solar which also charges batteries.

·         When pool goes off at 14h00, system immediately goes to batteries only, without using any more solar power for charging.

·         When we get home, system runs on batteries registering about 49V, and thereafter quickly goes to UTI. This continues rest of evening, cycling between UTI and batteries

·         Currently system registers load between 400-500 W when pool is not running.

·         Biggest issue is it seems the system is not charging the batteries from solar, or does not recognize solar during day unless a heavy load (e.g. pool) kicks in. So instead of running off grid, we are running mostly one grid.

Our current program settings are as follows:

01     Sbu

02     40A

03     APL

04     SdS

05     USE

06     Lrd

07     Trd

09     50Hz

11     40A

12     48V

13     51V

16   SNU

18   bOF

19   rEP

20   LON

22   AON

23   bYE

25   FdS

26   53.5V

27   53.5V

28   SNG

30   OnE

31   SbE

 

Your advice would be highly appreciated!

6 hours ago, Liz said:

Axpert 5 kVA inverter ...

·         Biggest issue is it seems the system is not charging the batteries from solar, or does not recognize solar during day unless a heavy load (e.g. pool) kicks in. So instead of running off grid, we are running mostly one grid.

You didn't give the exact inverter model. Is it perhaps a King? Others are having problems with the solar power going to zero for 30 seconds, and later going to zero until the PV is turned off and on again (or next day). If unsure, a photo of the sticker on the side with the bar-code will tell us.

6 hours ago, Liz said:

Our current program settings are as follows:

Your settings seem reasonable, except perhaps setting 02. You didn't say the capacity of your Huawei battery, but from other posts, they seem to be a bit larger than the Pylontech US2000s, so perhaps this setting can be increased. What is your exact battery model?

4 hours ago, Coulomb said:

You didn't give the exact inverter model. Is it perhaps a King? Others are having problems with the solar power going to zero for 30 seconds, and later going to zero until the PV is turned off and on again (or next day). If unsure, a photo of the sticker on the side with the bar-code will tell us.

Hi Coulomb

Here is photo of the sticker as well as the firmware. I read the clone forum, but we are told ours is a custom build unit.

20190519_202043.jpg

20190521_072746.jpg

4 hours ago, Coulomb said:

You didn't give the exact inverter model. Is it perhaps a King? Others are having problems with the solar power going to zero for 30 seconds, and later going to zero until the PV is turned off and on again (or next day). If unsure, a photo of the sticker on the side with the bar-code will tell us.

Your settings seem reasonable, except perhaps setting 02. You didn't say the capacity of your Huawei battery, but from other posts, they seem to be a bit larger than the Pylontech US2000s, so perhaps this setting can be increased. What is your exact battery model?

 

4 hours ago, Coulomb said:

Your settings seem reasonable, except perhaps setting 02. You didn't say the capacity of your Huawei battery, but from other posts, they seem to be a bit larger than the Pylontech US2000s, so perhaps this setting can be increased. What is your exact battery model?

We have two of these: 48V, 100 amp, 4.8 kwh

Previously we had 8X100 amp lead acid and then system run perfectly, just the batteries did last through the night.

Thank you for your assistance

IMG-20190521-WA0002.jpg

2 hours ago, Liz said:

I read the clone forum, but we are told ours is a custom build unit.

Sorry, many details nail this as a clone. Alas, it's also one that can't have the firmware updated, though if you complain enough, you might be able to get a replacement control board that fixes that problem.

Several clone owners have reported problems with the solar charge controller (the MPPT if you like). It likely isn't a firmware issue, since it's well known patched firmware, which as it happens yours truly had a hand in writing. There is a small chance that they patched the patched firmware and introduced a bug.

You seem to have been promised a genuine Voltronic Power machine, and plainly didn't receive that, so I think you need to complain to your supplier. Maybe they will replace it for you. It's entirely possible that they were tricked themselves.

In case you need to convince them that it's a clone:

* Only clones come with patched firmware, the letter C in 72.70c means it is patched 

* The barcode is applied over the main sticker, and has 16 digits, and is in the wrong format 

* the cent symbol instead of the Greek letter phi

* the lack of the small sticker with the manufacturing date

Edit: by "custom unit" they may be referring to the patched firmware, which is custom in a sense. Ironically, you would now like to customise it to suit your battery, meaning you'd want the LF (for LFP, lithium iron phosphate) flavour of patched firmware, and can't because of the firmware update issue. 

Edited by Coulomb

39 minutes ago, Coulomb said:

Sorry, many details nail this as a clone. Alas, it's also one that can't have the firmware updated, though if you complain enough, you might be able to get a replacement control board that fixes that problem.

Several clone owners have reported problems with the solar charge controller (the MPPT if you like). It likely isn't a firmware issue, since it's well known patched firmware, which as it happens yours truly had a hand in writing. There is a small chance that they patched the patched firmware and introduced a bug.

You seem to have been promised a genuine Voltronic Power machine, and plainly didn't receive that, so I think you need to complain to your supplier. Maybe they will replace it for you. It's entirely possible that they were tricked themselves.

In case you need to convince them that it's a clone:

* Only clones come with patched firmware, the letter C in 72.70c means it is patched 

* The barcode is applied over the main sticker, and has 16 digits, and is in the wrong format 

* the cent symbol instead of the Greek letter phi

* the lack of the small sticker with the manufacturing date

Edit: by "custom unit" they may be referring to the patched firmware, which is custom in a sense. Ironically, you would now like to customise it to suit your battery, meaning you'd want the LF (for LFP, lithium iron phosphate) flavour of patched firmware, and can't because of the firmware update issue. 

Thank  you so much! All your feedback and advice is highly appreciated!

7 hours ago, Coulomb said:

Sorry, many details nail this as a clone. Alas, it's also one that can't have the firmware updated, though if you complain enough, you might be able to get a replacement control board that fixes that problem.

Several clone owners have reported problems with the solar charge controller (the MPPT if you like). It likely isn't a firmware issue, since it's well known patched firmware, which as it happens yours truly had a hand in writing. There is a small chance that they patched the patched firmware and introduced a bug.

You seem to have been promised a genuine Voltronic Power machine, and plainly didn't receive that, so I think you need to complain to your supplier. Maybe they will replace it for you. It's entirely possible that they were tricked themselves.

In case you need to convince them that it's a clone:

* Only clones come with patched firmware, the letter C in 72.70c means it is patched 

* The barcode is applied over the main sticker, and has 16 digits, and is in the wrong format 

* the cent symbol instead of the Greek letter phi

* the lack of the small sticker with the manufacturing date

Edit: by "custom unit" they may be referring to the patched firmware, which is custom in a sense. Ironically, you would now like to customise it to suit your battery, meaning you'd want the LF (for LFP, lithium iron phosphate) flavour of patched firmware, and can't because of the firmware update issue. 

Sorry to bug again. In your opinion, if we had an original and with our set-up, it would run perfectly and no glitches with pool? Or would you recommend another inverter? Advice much appreciated again.

40 minutes ago, Liz said:

Or would you recommend another inverter?

My 2 cents, unless you are DIY'er and want to keep a hand on an inverter, get a Victron kit for example. Plug and Forget. 🙂 

And if you want to follow SA's NRS and SANS regulations, use one that is NRS approved, one that fits your DB board's main breaker i.e. if it is 63amp breaker, don't get a inverter bigger than 3.5kva if you are grid tied.

Because when you do go grid tied, that is where the most savings are ito 1) solar panel generation and 2) can use less batteries.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.