November 12, 20196 yr 4 minutes ago, Wilfred said: In your situation as mentioned above by @Coulomb and @Dex_ set these two at 1V higher than the settings I used. 12 48V 13 53V I would also go for: 26 53,5V 27 53,2V 29 45,5V In this situation
November 12, 20196 yr Author Right now the moment I adjusted the setting the Axpert is beeping like crazy showing battery low, so I just went to bypass and it seems to be charging the battery. When out of bypass ie normal, I see the AC icon, but it doesn't seem to be charging. The UPS's are small 300w items. They were there to keep air flowing so I could wheel out the generator (prior to this install), run some extension cables and start the gennie. Hope the pic makes sense...
November 12, 20196 yr Currently that picture show that the grid is available and it is running off the battery check pm Edited November 12, 20196 yr by Wilfred Pm
November 12, 20196 yr Author Ok, after nearly an hour on the phone with Wilfred I think we found the problem. The inverter was configured to run in PAL, with HS displaying.. It's a single inverter, it should not be in parallel. Thanks for the call, I'll come visit with biltong to say thanks!
November 12, 20196 yr 5 minutes ago, pblaauw said: Ok, after nearly an hour on the phone with Wilfred I think we found the problem. The inverter was configured to run in PAL, with HS displaying.. It's a single inverter, it should not be in parallel. Thanks for the call, I'll come visit with biltong to say thanks! I really hope it resolves your issue, was strange that the batteries charged in bypass mode but not when the inverter was on and in USB mode. Really hope your issue is resolved :). Was an absolute pleasure meeting/speaking with you over the phone.
November 13, 20196 yr Author Problem solved it seems! It's raining, there's no sun and the entire system is charging from Eskom through the night. Happiness is!
November 13, 20196 yr 10 hours ago, pblaauw said: Problem solved it seems! It's raining, there's no sun and the entire system is charging from Eskom through the night. Happiness is! How does it look now? All good?
November 13, 20196 yr Author 4 hours ago, Wilfred said: How does it look now? All good? Not a single issue today so far, hoping tonight goes well, but pretty sure it's all good
November 14, 20196 yr Author System has now run through the night two nights in a row without shutting down. I'm comfortable to say it's sorted! Thanks again Wilfred and everyone that commented.
March 29, 20206 yr We are from Namibia. Is there an possibility that we can call you regarding our Mecer SOL-I-AX-5P inverter. 0V input 230V output. Philip 0812419907