Everything posted by P1000
-
Sunsynk 5kW continually consumes 250W of Eskom power but reports 0W import - Please help!
You should not be billed for anything other than real power, unless you are a commercial user.
-
Sunsynk 5kW continually consumes 250W of Eskom power but reports 0W import - Please help!
That will probably all be reactive power. The inverter may only generate unity power factor when connected to the grid, so the reactive load is offloaded to the grid. You cannot measure real power with only a clamp.
-
Deye 12kw 3-Phase inverter MPPT question
-
Can you run a 7.5 kW induction motor on a 12kW inverter?
This
-
Solis 3 phase inverter max pwoer per phase
You can configure it to either export without limit, limit to the lowest phase (like your example), or limit to the sum of power imported in your example case (assuming all phases power factor of 1): L1 = 6.33A L2 = 6.33A L3 = 6.33A Usually the config selected will be determined by how your utility supplier billing works.
-
Solis 3 phase inverter max pwoer per phase
No. These inverters will require 100% load balancing. Typically this is done by exporting the same on all phases, but importing what you need - ie the unbalancing is offloaded to the grid.
-
24v 3kW Inverter recommendation
IIRC, they were 48V and cost just about the same as the 5kW...
-
AC circuit breakers on DC strings of PV
I fixed it for you. Remove the AC breakers to make it compliant. To disconnect, make sure the inverter is not generating power, use the DC disconnect on the inverter to disconnect all the PV, open the fuse of the string you want to work on, and then you can work on that string.
-
Can you run a 7.5 kW induction motor on a 12kW inverter?
VFD usually converts to DC and then generates 3 phase SPWM with IGBTs switching in the 6-16kHz range (typically). Soft starters usually use Triacs (or Triacs made with 2 discrete SCRs each, depending on power level). This means the switching is done at 50Hz, with the peak currents still very high for an inverter. You also have a much wider range of control with a VSD, which allows you to more easily tune it within the limits of the inverter. Thinking about that a bit, the 3 phase Sunsynk would probably be better; matched to 3 phase VSDs.
-
AC circuit breakers on DC strings of PV
Yeah, the fuses are also a legal requirement for battery inverters. If you don't have a battery, you can do without fuses, as long as the wires are oversized to greater than 1.56x Isc. Not installing fuses with a battery inverter should mean no CoC. But even if you have a CoC, in the event of a fire, the insurance might not pay out.
-
AC circuit breakers on DC strings of PV
The fuse is to protect the wires from making flames. In some inverters there are fault conditions that can connect your battery directly to the PV in. You also want a second way to make sure the panels are disconnected and not loaded when doing maintenance.
-
AC circuit breakers on DC strings of PV
Well, if you have a fire at your home, and the insurance investigators figure it out, that DC breaker will look like a real bargain! On inverters with a DC breaker (like the popular SunSynk/Deye/GoodWe models), you only need to fuse the panels, the breaker on the inverter is sufficient if mounted at the correct height.
-
AC circuit breakers on DC strings of PV
You will make fire every time you open the AC breaker under load, not just after 3 years. I think all the other times you were just lucky and the string was not under load.
-
Can you run a 7.5 kW induction motor on a 12kW inverter?
The inverter overload protection should prevent it from getting fried, but I don't think there is a way that you could start a 7.5kW induction motor with 2x12kW Sunsynks. Induction motors are not forgiving, and the (5 to 7)x rule will still apply, and the batteries also need to be able to cater for the surge. VSD is by far the best solution, soft starters are not very kind to inverters.
-
Can you run a 7.5 kW induction motor on a 12kW inverter?
This is the way. You could even go for a single phase inverter like the Sunsynk 16kW then.
-
Joburg regulations for solar
And every single one (in SA) is configured to count both export and import as "use" - that is if it's not configured to go into tamper mode on export.
-
Sunsynk, and the earth neutral bond, again!
None of your issues are the earth/neutral bond's fault. That said, it still has to be fixed to meet code.
-
Inverter Fire
Looks like the burgundy cap to me.
-
Maximum PV input current for Sunsynk 8kW inverter
https://www.solarpowerworldonline.com/2014/02/dual-mppt-defined-understanding-mppt/
-
Goodwe GW5048D-ES Best Settings for Severe Load Shedding
Of course there is. It's the limit set by the BMS. If that limit is so high that it shortens your battery life - then that is a battery design flaw.
-
Goodwe GW5048ES variable PV production?
Don't do that. The newer firmware does not have the high DC injection issue (aside from the fact that it is only an issue when connected to the grid). If you change to 50Hz grid default, you disable some of the safety features, and your inverter is not NRS-097 compliant anymore.
-
Goodwe GW5048ES variable PV production?
It's probably a cloud, which causes production to drop below load, causing a battery mode switch from charging to discharging, which will cause it to stay in that mode for a while. The best policy is not to worry about it.
-
Goodwe GW5048ES variable PV production?
Have you tried shouting at the clouds?
-
Repair of Axpert Inverters : A Journey Started
Well, then I can inform you of the next trick - swapping out one of the soldering irons for hot air works even better...
-
Central aircon advice /KW usage? Aircon guru may be needed ;)
Units like these don't have ways to limit it to a single room, apart from getting a ladder and adjusting all the vents.