Sunsynk 12kw 3phase
Apparently it can do up to 6kW per phase, but only 12 in total.
Edit: don't quote me on that, I cannot find a source. The datasheet says AC Output Rated Current: 17.4A. 17.4x230=4002W. And max current 19.1A (x230 = 4412W)
Edited by P1000
On 2021/12/07 at 7:26 AM, Dirkie said:
Do the Sunsynk 12kw 3 phase inverter give 4kw per phase or 12kw per phase
Hie, the power rating for 3 phase equipment is given as the summation of all the phases. So in other words 12kW is the total output of all the phases combined. So each phase will be 4kW
I am planing a three phase installation and am also trying to find out if it can supply say 6KW on one phase and 2KW on the other two phases. Is their any documentation to support this?
Hi Gerrie,
I have the 12kw 3 Phase Sunsynk installed.  It can do 6 kw on a phase but is limited to 12 Kw in total.
Before I re-balanced the phases, I happily did 6 kw on a single phase and 3-4 kw on the second phase and a bit on the third phase.  I have since rebalanced the load and each phase rarely will go past 5 kW.
Happy to answer any questions you may have.