Posted September 10, 20186 yr Hey guys. It's been a life dream for me to be powered by the sun... Finally got my A into G and setup my system.. Expecting my first kid to arrive anytime soon so no time like now... At the moment I have a single axpert 5kva and 4 X 100 ah raylight flooded bat's along with 6 panels. Works like a charm. Runs my whole house. Although I need some advise please. 1. Without blowing the bank, what battery bank should I aim at? 2. Prog 1 - I want to be most aggressive against using utility. So I presume SOL. Problem is, when the sun goes down, the system almost hunts and the lights tend to quick flash when's its trying to use solar and/or batteries. Any idea? 3. Is there a list of ideal or best system settings to optimism or minimalise as the case my be, ultility usage? 4. The system runs my whole house hold. I have gas geyser and gas stove top. While running on utility and only on AC, when the system is overloaded running elec oven, heating etc, the axpert eventually trips - pulling 7-8kw..I then have to use the manual bypass to keep everything going. Is there not a setting to do this automatically? 5. Can you have the beeping off for button pushing but have the alarms on? Ie when the power fails... 6. I gather the lights flicker when eksdom trips and the invertor runs off batteries? If you miss it and carry on as per normal, you risk running flat without knowing you actually running off DC. Basically is there any way to be notified? 7. Is there a Bluetooth module that I can install to use my phone to see what's happening with the system? Will send a pic of my installation when I can.. Im sure there are many questions to come but will appreciate any help. Thanks
September 10, 20186 yr Hi Petum Let me be the first to welcome you to the forum.. I am only going to answer one of your questions, 30 minutes ago, Petum said: I gather the lights flicker when eksdom trips and the invertor runs off batteries? The lights flicker when the inverter switches between PV and grid for example. Every Changeover will be seen as a flicker. The settings part I will leave to the local Axpert Expert , @Chris Hobson . He is running similar units and knows the settings well.
September 10, 20186 yr 1 hour ago, Petum said: 4 X 100 ah raylight flooded bat's This bank will be happiest below 1KW. 1 hour ago, Petum said: 1. Without blowing the bank, what battery bank should I aim at? Remember the old Rolls Royce joke about having to ask the price? Lithium Iron Phosphate has reduced significantly in price and is now similar in price to lead acid banks for a similar capacity (usually at slightly deeper discharge levels). If you're going to save up for something, save up for a nice Pylontech rack. Your 4 x 100Ah bank stores 2.4kwh at a 50% DoD, if you aim for 2 x Pylontech racks you can extend that to around 4kwh for around 30k.
September 11, 20186 yr Author My setup... Excuse the celebratory beer... Including my 12v system for garden lights that runs independently. Still not sure if I'm going to add lightning protection to the panels...
September 11, 20186 yr 1 hour ago, Petum said: Still not sure if I'm going to add lightning protection to the panels... Hey Petum! Like your install man! Beer helps! Do you need lightning protection for the PV's? I did some proper earthing and linked it to my main earth. What do the other power users recommend?
September 11, 20186 yr 2 hours ago, Petum said: Excuse the celebratory beer... Reminds me of the day I have such prematurely (it was a hot day in my defense) ... and promptly burned out a panels connection box. I like the use of a ventilation tile to pass wires through!
September 11, 20186 yr 1 minute ago, The Terrible Triplett said: I like the use of a ventilation tile to pass wires through! Not quite as well ventilated as your old setup, but close!
September 11, 20186 yr 1 minute ago, plonkster said: Not quite as well ventilated as your old setup, but close! Who said it was the "old" setup? Ventilation is important, no? Still wrangling with the Sparky ... new setup is a wee bit heavy ... but I do have a plan.
September 11, 20186 yr Hi Petum Welcome to the solar club. With the first kid on the way surge protection is mandatory. I would also earth your panel frames. Can you give us a list of your settings and we will try optimise your system.
November 20, 20186 yr Author hi there. after experiencing a major failure - error 09 .. i made the big decision to get a new unit. my thoughts are if im successful in getting anyone to fix the stuffed unit, i can put them in parallel. anyway... i still have my 4 x fld 100ah batts as per original setup... and my little kiddo is well and kicking and the wife wants backup power for beeps and bobs... so more as a ups than a power saver for now... but whatever you think is best. i have 6 x panels. im currently running the unit on utility mode as im too scared that the same error will occur with the incorrect settings. could my batteries not have been the reason for error 09?? please give me your advise on settings: 01 - awaiting advise 02 - 30 A - (this is where i guess error 09 ??? but no idea) 03 - APL 04 - SDS 05 - FLD 06 - LTD 07 - ETD? 09 - 50HZ 11 - 30A 12 - 46V 13 - 54V 16 - SNU 18 - OFF 19 - ESP 20 - ON 22 - ON 23 - BYD 25 - FDS 26 - 58.4V 27 - 54V 28 - PAL 29 - 42V 30 - ONE 31 - SBE 32 - AGt 33 - EdS 34 - 58.4 35 - 60 36 - 120 37 - 3OD 38 - d15 39 - AdS EXCUSE THE WRONG CODES ETC,,,, thanks soo much Pete
November 21, 20186 yr Hi Petum Your should be charging your lead acid batteries at about 10-13% of their Amp hour rating so you have a 100Ah bank therefore you should be charging at 10A. Gel and AGMs can handle higher charging currents but you have flooded batteries. 10A is a good starting place. I think your 30 A is too high.(program 2 and 11).
November 22, 20186 yr Author Thanks Chris. Besides that, everything OK? My setup... Excuse the celebratory beer... Including my 12v system for garden lights that runs independently. Still not sure if I'm going to add lightning protection to the panels...
November 22, 20186 yr 2 hours ago, Petum said: Thanks Chris. Besides that, everything OK? My setup... Excuse the celebratory beer... Including my 12v system for garden lights that runs independently. Still not sure if I'm going to add lightning protection to the panels... The fifth battery? The box on the right is designed to under your Axpert so that it is virtually plug and play. The two cables running to your batteries do not need to be the same length. I don't like what looks like a separate SCC nestled under wiring. Cabling should be within conduit - not sure how to achieve that through the air brick perhaps chisel one or two segments out.
November 22, 20186 yr Author The fifth battery is for my 12V system and the SCC for couple garden lights etc. (runs totally separate from the axpert system) I will get round to the hardware and hiding all the wires correctly. I still need to earth the panels. but most importantly, i need to know if the settings for the voltages is correct. namely: 12 - 46V 13 - 54V 26 - 58.4V 34 - 58.4 thanks again
November 22, 20186 yr 12 and 13 look good. 26 looks good if you have flooded batteries (they look like VRLA batteries do you have a datasheet?) 34 does not matter as you have equalising disabled.
November 22, 20186 yr 16 minutes ago, Chris Hobson said: Cabling should be within conduit - not sure how to achieve that through the air brick perhaps chisel one or two segments out. I recently invested in a nice Makita hammer drill, and some SDS+ bits. My only regret is that I didn't do this years ago. If I just think of the many hours working with an impact drill. Just put a nice 22mm hole through the middle of the brick and put in some proper conduit. Of course it helps that prices came down quite a bit. Bosch makes a nice entry-level SDS+ drill that you can buy for under 2k on Takealot now. I got the Makita for 2k. The other thing I got was this pipe/electrical detector. This thing is more accurate than some more expensive alternatives I've used. I got this one more for plumbing work (Western Cape, big drought... you know :-) ). Perhaps a bit off topic, but having good tools is just so satisfying.
November 22, 20186 yr Author thanks so much chaps. will send pictures of the finished product. providing the new mom lets me do anything! ;-P
November 22, 20186 yr 3 hours ago, plonkster said: I recently invested in a nice Makita hammer drill, and some SDS+ bits ... now you just need to go cordless. Man it makes life easy. Come to a off-grid place and you need to do an install - but there is no power yet because they waiting for you.
November 22, 20186 yr 23 minutes ago, Chris Hobson said: ... now you just need to go cordless. Man it makes life easy. Come to a off-grid place and you need to do an install - but there is no power yet because they waiting for you. If it was my day job (or even just a regular thing), I'd do it in a heartbeat! The guys who fitted some cupboards recently had a cordless Makita hammer drill, so I can attest to the utility thereof. The thing(s) that finally tipped me towards this was that I had to install blinds, and then I killed two drill bits and ran out of time (had to board a plane to Europe the next day), and I had to pay someone to finish the job. That was strike 1. Then some health mishaps in the family (two old people with replaced joints hanging around) made the bucket-filling nature of the toilets in this house (due to aforementioned drought) a big problem, and suddenly I yet again needed to drill through a wall to put a pipe in. I finally got tired of all this nonsense and bought the tool!
November 22, 20186 yr Author Someone please explain with the settings above as I select solar first, even in the evening, the system starts using my batteries rather than just using ac until it fails? I just want it to use much solar as possible and not use batteries until ac fails IMy setup... Excuse the celebratory beer... Including my 12v system for garden lights that runs independently. Still not sure if I'm going to add lightning protection to the panels...
November 22, 20186 yr Hi Pete, Hope I am not standing on anyone's toes but I have blown 5 or maybe 6 Axpert inverters in the last 2 months . The installation was done by a reputable installer who was pulling his hair out trying to find a reason. It turned out that the manufacturers of the inverters had installed a sub-standard capacitor? or whatever which was causing the problem. i would suggest that you check out this route before you just buy another inverter.
November 23, 20186 yr Author 8 hours ago, Chris Buckley said: Hi Pete, Hope I am not standing on anyone's toes but I have blown 5 or maybe 6 Axpert inverters in the last 2 months . The installation was done by a reputable installer who was pulling his hair out trying to find a reason. It turned out that the manufacturers of the inverters had installed a sub-standard capacitor? or whatever which was causing the problem. i would suggest that you check out this route before you just buy another inverter. No toes to stand on but mine Chris! I didnt have the luxury of time to choose as my wife and the baby need power... I actually got it at ACDC who can give me a year warranty on account. so far so good... but i havnt pushed the unit yet... mostly running on Utility for now... I have tested the unit and it easily handles the load of my house. Still cant understand why when i select Solar in the evening, the unit starts using the battery? I just want it to use much solar as possible during the day and not use batteries until ac fails...
November 23, 20186 yr On 2018/11/22 at 9:14 AM, Chris Hobson said: Cabling should be within conduit - not sure how to achieve that through the air brick perhaps chisel one or two segments out. Excuse the newbie question, but why, except it being neat, or that regulations require it?
November 24, 20186 yr On 2018/11/23 at 3:24 PM, Herman said: Excuse the newbie question, but why, except it being neat, or that regulations require it? Regulations require it. Surfix cable get around this requirement because it is "mineral insulated metal sheathed conductor" - and for the same reason it does not need to be stranded but can be a solid conductor.