Taggy Posted October 12, 2018 Share Posted October 12, 2018 I have got 4 Pylontech batteries currently going into my Solax 3.7kw Hybrid inverter. I would like some info on recommended charge/discharge parameters, the manual only gives a general guide. Its currently set to Lithium Min Capactity 20% Charge Cut Voltage 53.5 Discharge cut voltage 47 Max charge current 50A Max Discharge current 50A Are these parameters ok or do you recommend i adjust them? Quote Link to comment Share on other sites More sharing options...
Chris Hobson Posted October 12, 2018 Share Posted October 12, 2018 The Pylon tech settings for the Axpert is charge cut off 53.2V discharge cutoff 47.5V Max charge rate for 4 Pylontechs 100A max discharge 100A. I have noticed that the Goodwe also charges at 0.4C (your current charge/discharge rate) so I would go with the Solax - Pylontech recommendations. Quote Link to comment Share on other sites More sharing options...
AndewJ Posted December 2, 2018 Share Posted December 2, 2018 On 2018/10/12 at 2:57 PM, Chris Hobson said: The Pylon tech settings for the Axpert is charge cut off 53.2V discharge cutoff 47.5V Max charge rate for 4 Pylontechs 100A max discharge 100A. I have noticed that the Goodwe also charges at 0.4C (your current charge/discharge rate) so I would go with the Solax - Pylontech recommendations. If you don't mind me asking. What settings would you recommend for a Infinisolar 4KW super inverter? I have 16x 325W solar panels and 3x Pylontech batteries and use Eskom during the night. Quote Link to comment Share on other sites More sharing options...
___ Posted December 2, 2018 Share Posted December 2, 2018 1 hour ago, AndewJ said: If you don't mind me asking. What settings would you recommend for a Infinisolar 4KW super inverter? I have 16x 325W solar panels and 3x Pylontech batteries and use Eskom during the night. I'd assume you'd use the same settings? 25A per rack (that's roughly C/2), and you have three of them, so 75A total. Voltages remain the same, the battery wants to be charged to 53.2V. Quote Link to comment Share on other sites More sharing options...
AndewJ Posted December 2, 2018 Share Posted December 2, 2018 13 minutes ago, plonkster said: I'd assume you'd use the same settings? 25A per rack (that's roughly C/2), and you have three of them, so 75A total. Voltages remain the same, the battery wants to be charged to 53.2V. I am looking for the recommended voltage settings since mine seems to not work correctly. Quote Link to comment Share on other sites More sharing options...
___ Posted December 2, 2018 Share Posted December 2, 2018 45 minutes ago, AndewJ said: I am looking for the recommended voltage settings since mine seems to not work correctly. The charge voltage is 53.2V. This is also what it publishes on canbus (for those inverters that support it), but for those that don't, that is what you should set up. LFP batteries don't have a "float" voltage, you simply keep it at that voltage indefinitely, so set absorb and float to the same (or close) value (I think the Axpert documentation incorrectly calls it the "bulk" voltage instead of the absorption voltage). Quote Link to comment Share on other sites More sharing options...
Elbow Posted December 19, 2018 Share Posted December 19, 2018 HI, Can I throw a followup on this thread - working hard to climb the practical learning curve and don't want my batteries to suffer in the process. My inverter I set to 53.2V float and absorb per the recommended figures. What I find is that my Pylon batteries go to "idle" - i.e. no lights except the single one that blinks. But the inverter keeps about 0.4-0.6A charging current flowing; it reports the battery voltage at 53.2v and says it is "floating" the batteries. Like here for instance: "InverterTime":"20181219082748", "GridVolts":221.8, "GridWatts":-62, "GridHz":50.0, "BatteryVolts":53.2, "BatteryPercent":100, "BatteryChargeMode":"F", "BatteryChargeAmps":0.5, Should it run like this continuously - its only 25W or so, but it does cause the fans to turn on and off all the time as the inverter gets warm. I guess its called "float" so it will just stay on continuously? Based on the lack of SOC lights on the batteries I don't think that power is actually going into the cells. (Remember I don't have PV so I'm paying for all the power I use) There is a setting in the software to turn off the charger once the current has been stably low for a period. Is it a bad idea to use this to turn off the charger and then only turn it on again when the battery voltage goes below a threshold? The power goes down in the battery slowly so it might be enough just to top them up once a week if they aren't being used? Does this count as a "cycle"? My guess is that it would depend on the battery BMS actually charging cells. If I turn off the charger in the inverter then the battery voltage gradually drifts down so it doesn't seem like batteries make 53.2 by themselves. (There's no load on the batteries so it can't be cable resistance). Thanks, Elbow Quote Link to comment Share on other sites More sharing options...
Solarsmit Posted May 24, 2020 Share Posted May 24, 2020 (edited) Good day,I have 2 x Pylontech US2000 in parallel.The "Master add dip switch 1 is on and the other 3 is off",The "Slave add dip switch is all off".Is that correct, then the Master has a alarm LED.What and how can I check what is wrong and how can I correct it? Sorry I forgot the inverter is AXPERT 5kW Edited May 24, 2020 by Solarsmit Quote Link to comment Share on other sites More sharing options...
Andries Taljaard Posted February 14, 2021 Share Posted February 14, 2021 I'm a "eppie' in solar systems...Solar:- 6x365 Canadian coupled 3 in series and the 2 rows in parallel. I begin with a us2000b pylontech battery and a 5 kWh Mecer Inverter. My inverter settings according to Mustek Cape Town were not correct although the system worked for +- 5 months. I switch off Escom power before switching on inverter in morning when sufficient energy was obtained from the panels. The panels give enough energy for the house usage but I could not use the geyser - 3 kW element. I heat up water after I switched back to Escom. I was not sure if I could use Escom and Solar simultaneously - reason for switching. I worked outside and by entering the house the Inverter alarm was on and battery at only one LED emmiting + the Alarm. Question:- battery still under quarentee and to whom can I send it for check-up - DO NOT CHARGE.https://powerforum.co.za/topic/2439-pylontech-us2000b-recommended-chargedischarge-parameters/ Quote Link to comment Share on other sites More sharing options...
Boerseun Posted February 14, 2021 Share Posted February 14, 2021 Please post pictures of your installation. Quote Link to comment Share on other sites More sharing options...