mzezman reacted to a post in a topic:
Pitfalls when connecting a Generator to a Sunsynk or other Inverter
-
Thunderdolt reacted to a post in a topic:
Pitfalls when connecting a Generator to a Sunsynk or other Inverter
-
Pitfalls when connecting a Generator to a Sunsynk or other Inverter
Hi I want add some more input to this topic. I recently found a question in my mailbox from a member with the same problem, and would like to sort it out. The generator link does not work when it is tied to the inverter. This was my reply. Hi xxxxxxx I see your problem. The biggest problem with a small generator is this. Firstly, the generator needs to be adjusted to just under 50Hz under load. The biggest problem is that when the load changes, the frequency also changes. This effect stops the generator connection and is not ideal. The problem is also that you will charge the batteries and run the house. My best suggestion is that you have a changeover switch that runs the house only from the generator and allows the batteries to charge for the PV panels at the same time. The way to stop the problem is to put the changeover switch in series with the output of inverter. Now you can switch the changeover to either run the house from the generator or inverter while still charging the batteries from the PV panels. This configuration does not have a frequency issue with the inverter. It is difficult if not impossible to set a small generator to have the correct frequency under different loads. I have both generator connections and only use the changeover that directly powers the house, as I suggested. I am most sure most installers do not understand this problem, or they would have tested the configuration or warned you. Lastly, any installer or electrician can do my suggested installation of the changeover switch. Just make sure the earth is connected correctly for the suggested configuration so that your earth leakage works. I hope this will help you overcome the problem. I did this modification for a family member with a small coffee shop with the same problem, and now they are happy. I am not an electrician or installer, just retired with 45 years of electronics, instrumentation experience.
-
Borehole Filter advice
Hi Oelof Going through this exercise myself, I agree with James 1 to wait before getting your water tested, and that you will need at least one big blue filter and other filters. I wasted a lot of filter material because my water ph had changed after some time. I would like to know what area you are from. I use mainly Clinobrite media, as it removes iron and other substances in a FRP vessel. It is better than sand or glass. You can read my posts and see what I have done to get acceptable drinking water under Sustainable Landscaping. It has been working well for about 8 years. The filtering depends on the test results showing the contaminants and the quantity of contamination. Replacing media in an FRP vessel is not as easy as it is heavy because it is filled with water and media, and the opening is small.
-
-
-
Geyserwise enquiry
Hi Vish999 Is the bill only for electricity, or is it the whole bill? There is a way to check your electricity usage. You would need to install a CT (current transformer) on the live wire of the 60A isolation switch in your DB or a Meter fitted in your DB. Many devices come with a CT, and that can be connected to the web. With this, you can monitor your electricity usage. compared to your bill. Just remember, the bill might not cover the entire month from the 1st to the end. If you leave the element off for most of the day and at night, it can take up to 3 hours to heat a geyser in Winter to 65 degrees in the morning. The cost would be about 3KW X 3HR X 30 Days X R4/Unit = R1080.00 a month, including VAT, only for the geyser element if you only heat for 3 hours a day. It will cost you about R80.00 a month if you boil your kettle (5 minutes) 4 times a day. 0.083 X 4 X 30 X 2KW X R4/unit If you have an electric oven and use it, it will also contribute to the electricity usage. The 12VDC 60W solar pump. If on for 8 hours a day. 8 X .06Kw X 30 days X R4/unit=R57.60 a month.
-
Charging 10kwh Freedom Won batteries with 7500w generator via 8kw Sunsynck inverter
Hi I had the same problems. The solution is in my post "Connecting a 5KW Generator to an 8KW Sunsynk inverter".
-
Geyserwise enquiry
Hi Vish999 You asked if the solar pump could cause the high power usage. The 12VDC solar pump uses less than 100W of power, so it is not the culprit. I can tell you what the problem is with the high power usage. Three weeks ago, I had my 150L geyser with twenty brand-new retrofitted solar tubes replaced as my old geyser leaked, and some of my old tubes were cracked. I also replaced the 3KW element with a 2KW. I did this for four reasons. My house has a granny flat that also has a 150L geyser. With two geysers, the power usage at one time, with all the other appliances, can be a problem for me. I also have one geyser coupled to my inverter as my whole house (not the flat) is on the inverter. The Geyserwise controller uses a relay to switch the element on. Lower current will help the relay to last longer with constant switching. The most important reason is that I have the solar tubes. The 2KW element will take longer to heat the geyser, and it gives more time for the collector to heat up and to circulate the water when both the element and the solar pump are on. I always knew that my old solar tubes did not help at all in Winter. With your post, I had a closer look at my system efficiency. This is my conclusion. When I woke up this morning at 5:45 am, the geyser water was 50 degrees, and the collector was at 8 degrees, heated by the element. My wife had a long shower at 8:30 am. The readings before the shower were geyser 47 degrees and collector 9 degrees. After the shower, the geyser read 19 degrees, and the collector stayed at 9 degrees. I checked intermittently, and the solar pump never switched again the whole day as the delta was never above 7 degrees for the pump to switch on. The maximum the collector reached was 46 degrees, which is well below the set temperature of 50 degrees. If I had switched off my element, I would only have cool water at any time, never reaching the geyser's set point of 50 degrees. My conclusion is that in Winter, the solar tubes do not help much if you are using a fair amount of hot water during the day, as the element will always do most of the heating. I have seen the pump and collector keeping the geyser temperature at the set temperature, but not today. I know that in Summer the solar tubes work much better. I am sure this is the same problem I have. How the Solar geysers are advertised, and reality is quite different. Fortunately, I do have a gas geyser backup if all else fails. I also added an extra 4KW of solar panels so that I run my geyser on mains through the inverter. I hope this explanation gives you and others a better insight into why your power bill is high, even though you have a solar geyser.
-
Geyserwise enquiry
Hi Vish999 The pump will start running if the collector falls below 5 degrees to stop the collector from freezing. It will run the hot water from the geyser to warm the collector. The heating of the geyser is done in small increments, as the collector is significantly smaller than the geyser. In winter, it also takes longer to heat the collector. If you are using the hot water all the time, the element will also switch on at the same time as the pump, which will heat the water faster, but at the same time also affect the collector's effectiveness. You could switch off the element, but it will take much longer to heat the water and not keep the set temperature if you are using a lot of hot water. I was looking at the same problem, and now I understand how it functions. I hope this will help.
-
Faulty Readings on Unit, App and PC from a 8KW Sunsynk when connected to a 5KW Generator.
Update to all faults on the 8 KW Sunsynk Inverter app. Sunsynk did contact me, and after a firmware update, all faults on the app were rectified. The Firmware update COMM:E440 - MCU:6027-0717
-
Faulty Readings on Unit, App and PC from a 8KW Sunsynk when connected to a 5KW Generator.
Update on faults on App when connecting a 5KW inverter to an 8KW Sunsynk inverter. Atter spending 3 weeks spelling out the faults and sending pictures of the errors on the Sunsynk app the only solution from Sunsynk was to update the firmware. Sunsynk has now stopped communicating with me without a solution to the app problem. I am disappointed in the way they have handled this error, as I have over 40 years of experience as an instrument technician and have expressed my disappointment to them. I will again show the faults, and if anyone has any suggestions on how to resolve the problems, it would be appreciated. The fault only lies in the app in the photos. The inverter works and is displayed correctly. "Hi After updating as suggested, the firmware was updated to COMM: E43D, but nothing has changed to resolve the problem. So, I will have to start from scratch again. When the generator is not used and the inverter is connected to the grid, PV, and batteries, the inverter works correctly and shows the correct readings on the inverter screen, as shown in photo A. When the generator is not used and the inverter is connected to the grid, PV, and batteries, the inverter works correctly, and the APP is in normal view; it shows correctly, as shown in photo B. When the generator is not used and the inverter is connected to the grid, PV, and batteries, the inverter works correctly. However, when the APP is in detail view, it shows incorrectly. It shows the generator producing 1850W of power when no power is generated by the generator, as shown in photo C. When the generator is used and connected to the AUX input, PV and batteries are used, and the inverter is not connected to the grid, the inverter works correctly and shows the correct readings on the inverter screen, as shown in photo D. When the generator is used and connected to the AUX input, PV and batteries are used, and the inverter is not connected to the grid, the inverter works correctly and shows the wrong readings on the APP in normal view. It shows 2019w generated from the generator when only about 200w is generated, and the totals do not match up, as shown in photo E. When the generator is used and connected to the AUX input, PV and batteries are used, and the inverter is not connected to the grid, the inverter works correctly and shows the wrong readings on the APP in detail. It shows 2019w generated from the generator when only about 200w is generated, and the totals do not match up, as shown in photo F. I hope you can see the problems now, as I have highlighted this all before. Please give me some meaningful feedback, as I am now frustrated at the way these problems have been handled. I am surprised at the response I was given previously, as it has achieved nothing fruitful. I am eagerly waiting for a meaningful response to the highlighted problems that persist. Regards Peter Topp" Photo B. Photo C. Photo E. Photo F. Photo D. Photo A.
-
-
Deye inverter 8k setting
Hi I see the pictures show only one with grid use at 5:21 in the afternoon, which I failed to see. I find it interesting about the lag of the MPPT response, which makes complete sense. The PV panel won't produce more than is needed. The excess power produced can't be stored anywhere other than the batteries, which show they are fully charged. The PV panels will give more power if fed back into the grid. There is most probably no problem at all, as KM has indicated. To get the most out of the PV panels installed (8880w) is to do all the heavy-duty work and use the power-hungry appliances (electric geyser, electric hotplates, electric kettle, iron, aircon, etc) during the day if you can't feed back to the grid. Be sure to switch a geyser and aircon off at night, as it will be expensive, or they will drain the battery quickly if not tied to the grid.
-
-
Deye inverter 8k setting
Hi Bachir To me, it looks like a PV panel problem, as you say, you do not produce enough PV power. According to the pictures shown for the time of day, except if it is overcast. I would check the setting that limits the PV power first, and then check the PV panels. How have you connected the 16 PV panels(serial, parallel), and are the panels facing South at about 35 degrees, as the pictures show in Lebanon? It could also be the MPPTs in the Dye.
-
-
Mr
Hi I suppose it depends how tall you are. I think eye level would be best with the specified clearances given in the manual.
-
TaliaB reacted to a post in a topic:
Faulty Readings on Unit, App and PC from a 8KW Sunsynk when connected to a 5KW Generator.
-
Faulty Readings on Unit, App and PC from a 8KW Sunsynk when connected to a 5KW Generator.
Hi TaliaB I have checked all the settings and found one wrong setting. I had AC coupled on the load side in Aux, ticked. This correction fixed the current flow arrows on the unit to show correctly. The inverter readings and function all work correctly. The readings in the app are still all wrong. I first thought it was the CT, as when I test the generator, I switch off the mains power in the inverter DB, which isolates the CT. It was not the problem, as I changed this by switching off in the main Municipal DB box.
-
Peter Topp reacted to a post in a topic:
Faulty Readings on Unit, App and PC from a 8KW Sunsynk when connected to a 5KW Generator.
-
Faulty Readings on Unit, App and PC from a 8KW Sunsynk when connected to a 5KW Generator.
Hi, The arrows only point in the wrong direction only when the generator is on. The current flow arrows point correctly when there is no generator power, and the grid and solar are present. The arrows also show correctly when I export power to the grid. If the ct is wrong, the grid power would show in the wrong direction. The grid arrows show correctly, so I am relatively sure the ct is correct. The first picture shows generator power when there is none. If there is no ct, no current flow arrows are shown from the grid.
-
Faulty Readings on Unit, App and PC from a 8KW Sunsynk when connected to a 5KW Generator.
Hi I redid the tests and removed possible earth loops, but I got the same results. I have now put in a ticket with Sunsynk. I'm looking forward to their explanation.
-
Faulty Readings on Unit, App and PC from a 8KW Sunsynk when connected to a 5KW Generator.
Hi After fixing my problems connecting a 5 KW generator to my 8 kW Sunsynk inverter, I was quite happy, it seemed to perform well. Today, I decided to do some load tests with the generator with solar. To my dismay, this is what I saw and experienced. The inverter and generator work well together, however, the readings are completely haywire. I have added the photos with an explanation. 1. 2. In pictures 1 & 2, the generator is off. The first photo shows power only from solar. The second photo from detail shows the solar and the generator, but as a total does not add up. When the grid is present and the generator is off, the same result. This is also the same on PC. 4. 5. Pictures 3,4 & 5 are with the generator running. The actual power from the generator is about 200W. The app and PC show the wrong generator power. This shows correctly on the unit only however, the UPS load shows it is exporting power. This is a puzzle to me. This is my unit update done on 14/11/2024. Model No: SUNSYNK-8K-SG01LP1 ID:2006204203F COMM:E439 - MCU:6026-0717 I do not know if it is a hardware or software fault. I would much appreciate some help to sort this out. Please Help!!!!!