Everything posted by Dyness
-
Dyness Paralell connection
Good day. 4.8kwh battery is 15-strings battery,and the nominal voltage is 48V,5.12kwh battery is 16-strings battery,the nominal voltage is 51.2V. Obviously,These 2 type of batteries have different platform,But the inverter only can output one volatge platform.It will cause one battery overcharge. Thanks Tour Shen After-sales manger of DYNESS South Africa
-
Dyness battery setup --> Deye 8K inverter
Hi Please add my account Whatsapp +86 17625812876 Thanks
-
Dyness battery setup --> Deye 8K inverter
Hi I have checked your connection Settings and found that they are all normal. Could you please show me the information of Li-BMS? Thanks
-
Possible Dyness battery failure?
Hi This is Tour from after-sales department of Dyness. 1.What is the SN of the battery? 2.Are there any alarms after the battery is turned on? 3.How long does it take for the battery to turn itself off after it is turned on? You can add my Whatsapp:+86 176 2581 2876 Best regards Tour Shen
-
Dyness 4.8: "Sudden Death" - SOC instantly from 40% to 0% with no load
Hello,Sir/Madam This is Tour from after-sales department of Dyness. Can you add my account of Whatsapp :+86 17625812876 If you have another contact information,Please provide to me. Best regards
-
Growatt inverter spf 5000ES with dyness 2.4kw battery setup
According to my judgment, if your current battery has no other problems, you just need to increase the capacity of the battery to get more power output and the problem can be solved.
-
Growatt inverter spf 5000ES with dyness 2.4kw battery setup
Now the reason for your battery alarm is that the load power is too large and exceeds the energy that the battery can output.
-
Growatt inverter spf 5000ES with dyness 2.4kw battery setup
The maximum output power of a battery is about 1200W, how much power is your load? Because the battery makes a bibi sound, it indicates that the battery is over-discharged or over-current. According to the voltage and SOC of your battery, it is normal. So I judge that the fault of your battery is an over-current alarm. You should consider adding one more battery or multiple battery packs. , to ensure that the output of the battery can fully guarantee the normal operation of the load.
-
Dyness B3 3.6 Battery discharge setting
46V minimum.
-
Dyness RS232 Protocol for A48100
Hi You can contact me first,I will communicate your request to our technical director.. whatsapp:+8617625812876 e-mail:[email protected] Thank you
-
Can a Dyness 48Volt 2.4kva be used in parallel Dyness 48volt 3.5kva
No, this is prohibited, the same model can only be used in parallel with the same model.
-
Growatt inverter spf 5000ES with dyness 2.4kw battery setup
Please contact me: Whatsapp:+8617625812876 e-mail:[email protected] 1. What is your battery model? How many batteries are used in parallel? 2. Does it communicate with the inverter? What are the parameters for charging and discharging settings? What is the cutoff value? 3. What is the voltage and SOC of the battery when the fault occurs?
-
Dyness B3 3.6 Battery discharge setting
Hi there.The cut-off value of the battery is recommended to be set to 20%, and the minimum can be set to 15%.Thank you.
-
Growatt SPF5000ES BMS communication error
Hi ,You can give me your battery SN.If you've never done a firmware upgrade, I'll let you know if you need an upgrade based on the information you provided.
-
Dyness: Dry Contact Terminal
-
Growatt SPF5000ES BMS communication error
Hi If the communication between your battery and the inverter is normal, the high voltage alarm is normal. You can also send your battery to Rectron, and update the firmware to solve the problem.(Updating firmware is free) Thanks
-
Simple Sunsynk + Dyness
Hi Please see the below information: 1.The comms cable between the battery and inverter use standard cables.Connect the comm cable from inverter CAN port(ComSyncIn). 2.The battery dip-switch set to 0010 3.Inverter setting select LI CAN and protocol set to 00. If you have another question please contact us: Whatsapp:+8617625812876 email:[email protected]
-
Growatt BMS Issues - Faulty BMS?
Hi, 1. The comms cable between the A48100 battery and the inverter is a standard cable sequence(Ordinary RJ45 network cable). 2. The battery dip-switch is set to 0110. 3. Inverter setting 05 option choose LI and 36 option choose 01. 4. The inverter sets the cut-off SOC of 20 items to 20%(When you see that the cut-off of the inverter can be set to a percentage, it proves that the battery has successfully communicated with the inverter.) If you have any other questions please contact me: e-mail:[email protected] Whatsapp:+8617625812876 Thanks
-
Growatt Inverter + Pylontech Batteries : BMS Comms Guide
Hi Mike Please contact us use e-mail or whatsapp. email:[email protected] Whatsapp:+8617625812876 Thanks
-
Battery Terminals for Parallel Wiring
You can take a closer look, one is the quick-connect plug and the other is the terminal. Multiple terminals can be used in parallel. But the quick-connect plug can only be connected to one power cable at one position.
-
Growatt SPF ES5000 inverter + Dyness BX51100 lithium battery + 10 x 380 Watt perc mono solar panels
Hello,GarthW. When you correctly install the inverter to communicate with the battery according to our manual, whether the inverter is alarm 04 or alarm 04&20?