September 5, 20223 yr https://www.exicom-ps.com/backup-solutions.html?id=divTab230 https://www.tempestns.com/products/vestwoods-vt48100b-lithium-battery-module/ this is my battery 48npfc100-y model; this is same as narada battery 48npfc100 https://www.vestwoods.com/product/standard_telecom_backup_battery_vt48100 Please identify bms of it Edited September 6, 20223 yr by junkes
September 6, 20223 yr Author I have some good progress with the RS485/CAN translation. The Battery Voltage, Current and SOC are read from the BMS via RS485 and sent to the inverter via the CAN port every second. The rest, such as Battery Temp, Alarms, Charge Voltage and Charge/Discharge limits are currently hard-coded until I get them mapped from the BMS info. No pack information yet either. Documentation and examples are very scarce, which adds to the difficulty.
September 6, 20223 yr 5 minutes ago, SolarConvert said: I have some good progress with the RS485/CAN translation. The Battery Voltage, Current and SOC are read from the BMS via RS485 and sent to the inverter via the CAN port every second. The rest, such as Battery Temp, Alarms, Charge Voltage and Charge/Discharge limits are currently hard-coded until I get them mapped from the BMS info. No pack information yet either. Documentation and examples are very scarce, which adds to the difficulty. Now this is exciting news!!! Now the trick is to get you to do it for both types of Narada batteries 🙏
September 6, 20223 yr Not sure if this will help: https://github.com/justinschoeman/dalybms In can.h I have a bunch of different attempts to generate working CAN messages (all disabled with #if 0, except the last one). There are also a bunch of samples and other projects referenced in the comments, which may be of some help. (This code has been running for 2 years now on my Sunsynk/Daly BMS combo.) I was actually following this thread as I was planning on adding a variant for the Narada at some point.
September 6, 20223 yr Author 14 hours ago, JustinSchoeman said: Not sure if this will help: https://github.com/justinschoeman/dalybms In can.h I have a bunch of different attempts to generate working CAN messages (all disabled with #if 0, except the last one). There are also a bunch of samples and other projects referenced in the comments, which may be of some help. (This code has been running for 2 years now on my Sunsynk/Daly BMS combo.) I was actually following this thread as I was planning on adding a variant for the Narada at some point. Thanks for the link @JustinSchoeman. I managed to get CAN IDs 0x351, 0x355 and 0x356, but 0x359 is the tricky one which I don't find examples of, especially when the alarm/warning bits are set. By far the best set of docs for the CAN IDs I have found is the SMA CAN protocol one SMA CAN protocol.pdf, but I attach the Sunsynk Sunsynk Battery Compatibility v4.pdf and Pylontech CAN-Bus-protocol-PYLON-low-voltage-V1.2-20180408.pdf docs too. Whilst 0x351, 0x355 and 0x356 are a huge upgrade for me since I never had BMS comms, I do think that 0x359 is very important because the inverter must know about any fault conditions of the battery. Those who already had proper BMS comms working via RS485 and choose to go with this RS485/CAN translation route (like @Jay-Dee ) should get no less than what they had before when there was direct BMS comms between the inverter and the battery. Pages 3 of the Pylon CAN protocol doc is what I'm going to tackle next. The hard part for me is figuring out the Tian Power BMS protocol and mapping it to CAN ID 0x359, including the alarm / warning bits, as well as cherry picking the correct values from an unknown dictionary of data. For example, the following response from my BMS contains a lot of useful information, but deciphering it is hard: 7e01439400020e10010203e802020dac03020af0040203e805020c1c0602154a070203e8080214c8090211940a0203e80b0213880c021f400d0203e80e021b580f021f40100203e811021b581202006913020fa01402005f1502003216020fa01702003c1802006919020fa01a02005f1b0200321c020fa01d02003c1e02008c1f020fa0200200872102000a2202000f23020320240201f4de0d Here it is translated: {0: (3600,), 1: (1000,), 2: (3500,), 3: (2800,), 4: (1000,), 5: (3100,), 6: (5450,), 7: (1000,), 8: (5320,), 9: (4500,), 10: (1000,), 11: (5000,), 12: (8000,), 13: (1000,), 14: (7000,), 15: (8000,), 16: (1000,), 17: (7000,), 18: (105,), 19: (4000,), 20: (95,), 21: (50,), 22: (4000,), 23: (60,), 24: (105,), 25: (4000,), 26: (95,), 27: (50,), 28: (4000,), 29: (60,), 30: (140,), 31: (4000,), 32: (135,), 33: (10,), 34: (15,), 35: (800,), 36: (500,)} I assume item 6 is charge voltage (54.5V), which plugs into CAN ID 0x351, but I'm not quite sure which one is max charge and discharge current, so I have them hard-coded for now. 17 hours ago, Jay-Dee said: Now this is exciting news!!! Now the trick is to get you to do it for both types of Narada batteries 🙏 I don't see why not. If the Shinwa BMS software works for you, it should be fairly easy to get the required protocol. But it will take some time to get this stable enough for you to be able to run it and forget that it's running. I also think that if SolarAssistant supports this down the line, it would be better to use that since it is a supported product, but until they have this feature, an interim solution would work. Edited September 6, 20223 yr by SolarConvert
September 7, 20223 yr Author 11 hours ago, SolarConvert said: The hard part for me is figuring out the Tian Power BMS protocol and mapping it to CAN ID 0x359, including the alarm / warning bits, as well as cherry picking the correct values from an unknown dictionary of data. For example, the following response from my BMS contains a lot of useful information, but deciphering it is hard: 7e01439400020e10010203e802020dac03020af0040203e805020c1c0602154a070203e8080214c8090211940a0203e80b0213880c021f400d0203e80e021b580f021f40100203e811021b581202006913020fa01402005f1502003216020fa01702003c1802006919020fa01a02005f1b0200321c020fa01d02003c1e02008c1f020fa0200200872102000a2202000f23020320240201f4de0d Here it is translated: {0: (3600,), 1: (1000,), 2: (3500,), 3: (2800,), 4: (1000,), 5: (3100,), 6: (5450,), 7: (1000,), 8: (5320,), 9: (4500,), 10: (1000,), 11: (5000,), 12: (8000,), 13: (1000,), 14: (7000,), 15: (8000,), 16: (1000,), 17: (7000,), 18: (105,), 19: (4000,), 20: (95,), 21: (50,), 22: (4000,), 23: (60,), 24: (105,), 25: (4000,), 26: (95,), 27: (50,), 28: (4000,), 29: (60,), 30: (140,), 31: (4000,), 32: (135,), 33: (10,), 34: (15,), 35: (800,), 36: (500,)} I assume item 6 is charge voltage (54.5V), which plugs into CAN ID 0x351, but I'm not quite sure which one is max charge and discharge current, so I have them hard-coded for now. Ok progress made on this. I now know what each of the numbered items mean above and I know the meaning of the alarm bits on the BMS side. What is left to do is to map the BMS alarm bits to CAN 0x359, as well as to get pack info to the inverter - currently the inverter does not allow me to go into the details of each individual battery (even though I have just one), so it's just the summary screen that is available as per my previous screenshot (though the values are now all real values from the BMS). Will post more info tonight.
September 7, 20223 yr 2 minutes ago, SolarConvert said: Ok progress made on this. I now know what each of the numbered items mean above and I know the meaning of the alarm bits on the BMS side. What is left to do is to map the BMS alarm bits to CAN 0x359, as well as to get pack info to the inverter - currently the inverter does not allow me to go into the details of each individual battery (even though I have just one), so it's just the summary screen that is available as per my previous screenshot (though the values are now all real values from the BMS). Will post more info tonight. This is some seriously exciting news... When you have it working on your end and want to test with my BMS... Let me know... I just need to get a Windows machine to the batteries with TeamViewer or the likes of for you... You can then see the other BMS as well as multiple battery backs if that changes anything. I run ICM on my Pi... This will make it easier down the line as I still have full control over the Pi and therefor can run the emulation on the same Pi as the reporting. The only think that I will need to get is the CAN bus to USB module as I already have the RS485 to USB for the battery
September 7, 20223 yr 13 hours ago, SolarConvert said: The hard part for me is figuring out the Tian Power BMS protocol and mapping it to CAN ID 0x359, including the alarm / warning bits, as well as cherry picking the correct values from an unknown dictionary of data. The inverter pretty much ignores the alarm bits anyway. The important thing is to set the charge/discharge (as appropriate) current to 0 under alarm conditions. For me the trickiest part was the charge derating (which has a lot of hand tuned heuristics) to slow rate of charge as individual cells approach maximum voltage).
September 9, 20223 yr hi can u confirm this is shinwa bms used here https://www.youtube.com/watch?v=eqU8wNfyaDg Edited September 9, 20223 yr by junkes
September 9, 20223 yr hi can any one confirm this is shinwa bms board any one having tian bms can u share the internal hardware here is my bms similar model inside
September 9, 20223 yr i think mine is also shinwa bms used inside,can any one reconfirm this here are some other snaps of similar bms board
September 9, 20223 yr does any one have any /or have any contact with shinwa bms pc software tool/company, if any one having narada bms tool kindly reply, for rs232 com port for firmware change or to add or change bms protocol. this is the snap of the tool narada uses to rewrite firmware to support different vendors Edited September 9, 20223 yr by junkes
September 9, 20223 yr why dont you use the following bms, super configurable with all softwares supplied with it seplos / eel bms meritsun bms
September 9, 20223 yr Author So I didn't make much progress in the meantime, but let me post some more detail as promised. Firstly, the Tian Power output that I was trying to understand: 7e01439400020e10010203e802020dac03020af0040203e805020c1c0602154a070203e8080214c8090211940a0203e80b0213880c021f400d0203e80e021b580f021f40100203e811021b581202006913020fa01402005f1502003216020fa01702003c1802006919020fa01a02005f1b0200321c020fa01d02003c1e02008c1f020fa0200200872102000a2202000f23020320240201f4de0d Means the following: { "cell_ov_start": 3.6, "cell_ov_delay": 1000, "cell_ov_stop": 3.5, "cell_uv_start": 2.8, "cell_uv_delay": 1000, "cell_uv_stop": 3.1, "pack_ov_start": 54.5, "pack_ov_delay": 1000, "pack_ov_stop": 53.2, "pack_uv_start": 45.0, "pack_uv_delay": 1000, "pack_uv_stop": 50.0, "charge_oc_start": 80.0, "charge_oc_delay": 1000, "charge_oc_stop": 70.0, "discharge_oc_start": 80.0, "discharge_oc_delay": 1000, "discharge_oc_stop": 70.0, "cell_ot_start": 55, "cell_ot_delay": 4000, "cell_ot_stop": 45, "cell_ut_start": 0, "cell_ut_delay": 4000, "cell_ut_stop": 10, "env_ot_start": 55, "env_ot_delay": 4000, "env_ot_stop": 45, "env_ut_start": 0, "env_ut_delay": 4000, "env_ut_stop": 10, "mos_ot_start": 90, "mos_ot_delay": 4000, "mos_ot_stop": 85, "capacity_low_start": 10, "capacity_low_stop": 15, "volt_diff_start": 800, "volt_diff_stop": 500 } These are the protection parameters that the BMS returns for command 7e 01 43 00 fe 0d. This allowed me to get the charge and discharge current limits (80A for both) as well as the charge and discharge voltages from the BMS and send them to the inverter. I compared all of the values to my attempt of using Lithium mode 7 a few months back and the results were very similar. Here is a photo from a few months back: If you recall, Lithium mode 7, which is meant for Revov batteries, didn't work for me at the time because not all of the values interpreted from the BMS by the inverter were correct, for example, the mean temp was wrong and I almost immediately got an error condition on the inverter, likely because it interpreted the alarm bits incorrectly. Nevertheless, the above photo at least gave me a point of comparison and I felt more comfortable with the charging/discharging voltages and currents that i am sending to the inverter now via the CAN port. Here is what the screen looks like with my current script running on my PI which queries the BMS via the battery RS485 port and sends the results to the CAN port of the inverter. The script has been running well, I made it start automatically when the PI is rebooted. For me, this is a much needed upgrade since I never had BMS comms working before. However, I cannot figure out in what format I should send the PACK information to the inverter, so you will see above that the Sum Data and Details Data buttons are missing, because the inverter does not know about the individual batteries, just the battery "system" as a whole. This is not a problem for me since I only have one battery anyway, but for those that would like to use this script, you would lose the ability to see the details of the individual battery packs, unless there is some way I can send the pack info to the inverter too. I cannot find any documentation or examples online where pack info is sent on the CAN bus. On 2022/09/07 at 9:52 AM, JustinSchoeman said: For me the trickiest part was the charge derating (which has a lot of hand tuned heuristics) to slow rate of charge as individual cells approach maximum voltage). This is very interesting and I actually didn't know what the derating file was for, but now that you explained it, it makes a lot of sense. I ran my script without any derating functionality and the inverter appeared to do the right thing as per the graph below - note that at the time I took the screenshot I had not even implemented any alarm bits either. The charge current did decrease as soon as the voltage went past 54.5V. I am actually thinking of using pack_ov_stop instead of pack_ov_start for the voltage limit because pack_ov_start means that 54.5V is already "over voltage" so using the lower value (53.2V) should prevent the pack_ov_start value from being reached. As an aside, if you're wondering why the spike to 100% SOC just before 12:00 and then back down - it is because I switched the inverter from Lithium mode 0 back to Battery % mode (so no more BMS comms via the PI) and the inverter thought that the battery SOC was 100%, then I quickly switched back to Lithium mode. That being said, do you think derating is needed? On the one hand I think that the derating feature is great since it does a similar thing as the expensive + intelligent BMSes, but on the other hand, does one actually need to worry about derating whether using RS485 or CAN for BMS comms? On 2022/09/07 at 7:37 AM, Jay-Dee said: This is some seriously exciting news... When you have it working on your end and want to test with my BMS... Let me know... I just need to get a Windows machine to the batteries with TeamViewer or the likes of for you... You can then see the other BMS as well as multiple battery backs if that changes anything. I run ICM on my Pi... This will make it easier down the line as I still have full control over the Pi and therefor can run the emulation on the same Pi as the reporting. The only think that I will need to get is the CAN bus to USB module as I already have the RS485 to USB for the battery I am happy to take a stab at getting the Shinwa protocol to work, I'd probably send you a script to test out on the PI to see if the output values make sense. However, please note above that i cannot get the pack information to work at this stage, so you would lose the ability to monitor individual batteries. That may be a deal breaker for you. Regarding the CAN bus module, I use this the Waveshare RS485 CAN HAT which does both RS486 and CAN, plus it connects directly to the ports, no need for USB. There are many other options for CAN interfaces though, for example on this page. I am going to keep searching for how to get pack information to the inverter via CAN. Surely it must have been done before. I cannot imagine that if you use the CAN port directly on the inverter with a supported BMS that you cannot monitor the individual batteries irrespective of the BMS manufacturer?
September 10, 20223 yr On 2022/05/02 at 7:54 AM, zivva said: You will need to contact Narada with the serial number of your battery. They use different BMS for different batteries & the software is specific for each of them ... Alternatively you can open the rack and look for the brand & model of the BMS but by opening the rack you loose the warranty. Let me know if you have a Shinwa LM-M01A BMS, then I could post the software ... i am aslo having same bms but old version ,but cant get bms sync with deye, what pinout worked for you, is shinwa using pin 1,2 for rs 485 b,a ??
September 10, 20223 yr On 2022/09/06 at 10:52 AM, Jay-Dee said: Now this is exciting news!!! Now the trick is to get you to do it for both types of Narada batteries 🙏 what pinout u got for rs485 to work??
September 10, 20223 yr On 2022/06/04 at 9:44 PM, zivva said: Here is the software for Narada equipped with a Shinwa LM-M01A BMS. You will need : - battery dip switch set to ID 0 (all down) or first battery ID 0, second battery ID 1, etc if you have multiple batteries : - RS485 communication cable : standard RJ45 connected to the RS485 port of the battery, pins 2 & 3 connected to the USB converter. I'm using successfully an RS485 to USB converter with an FTDI chip (see picture) for both using the Windows software or connecting a PI to use Solar Assistant LM-M01A-ND574_200805.zip 1.28 MB · 30 downloads will this work on my same model mine is lm-m01a,but no nd574 tag,only nd 1576 written
September 10, 20223 yr 6 hours ago, junkes said: what pinout u got for rs485 to work?? Page 3... First post from me on 12 June
September 12, 20223 yr Author Ok after a lot of searching and asking for some expert advice, I believe this is as good as the RS485 to CAN translation is going to get - CAN bus works in such a way that the inverter only ever sees one battery, even if that is made up of multiple modules. This would then be the tradeoff if switching from RS485 to CAN using a PI as the translator - you would not be able to see the individual module details anymore on the inverter. To me this is perfectly fine because I never had BMS comms via the RS485 port to begin with, but for others this may not be and you may prefer to stick with the inverter RS485 port for BMS comms rather than monitoring the inverter. @Jay-Dee your thoughts? I would still like to tweak the script to use 0x35A instead of 0x359 for the alarm/warning bits. Edited September 12, 20223 yr by SolarConvert
September 12, 20223 yr On 2022/09/10 at 1:03 AM, SolarConvert said: That being said, do you think derating is needed? On the one hand I think that the derating feature is great since it does a similar thing as the expensive + intelligent BMSes, but on the other hand, does one actually need to worry about derating whether using RS485 or CAN for BMS comms? I certainly needed it - but then I have a DIY 2nd life pack. After about 3.5V/cell the imbalance grew quickly until cell protection kicked in and opened the BMS while still under charge, which resulted in quite a voltage spike on the output. So I added derating to decrease charge current and voltage when any one cell starts approaching full, and this solved the issue. After a few months, the cells balanced nicely, and it might not even be needed anymore, but I feel it is a healthy bit of paranoia to keep.
September 12, 20223 yr 1 hour ago, SolarConvert said: Ok after a lot of searching and asking for some expert advice, I believe this is as good as the RS485 to CAN translation is going to get - CAN bus works in such a way that the inverter only ever sees one battery, even if that is made up of multiple modules. This would then be the tradeoff if switching from RS485 to CAN using a PI as the translator - you would not be able to see the individual module details anymore on the inverter. To me this is perfectly fine because I never had BMS comms via the RS485 port to begin with, but for others this may not be and you may prefer to stick with the inverter RS485 port for BMS comms rather than monitoring the inverter. @Jay-Dee your thoughts? I would still like to tweak the script to use 0x35A instead of 0x359 for the alarm/warning bits. For me this is not an issue... While I can see the individual batteries on the inverter currently there has never been an in-balance between the batteries themselves... Just between the SOC vs voltage but then the issue was the same between the batteries. I have no issue in only reading the first battery and the batteries BMS talk to each other.. This is how the Hubbles work on my other install, I just never realised until now. The only "issue" would be that one needs to manually set the battery charge/discharge currents as well as size when working with multiple packs as the inverter wont know about them. Once again, I had to do this currently anyway so issue. Should I order the CAN to USB in the meanwhile? I am getting excited here!!
September 12, 20223 yr Author 6 minutes ago, Jay-Dee said: I have no issue in only reading the first battery and the batteries BMS talk to each other.. This is how the Hubbles work on my other install, I just never realised until now. So the script would still read both batteries (or more if there were) but would combine the the values from the batteries. For example, it would report the average voltage across them and it would sum up the current. But comms would be through the master battery (the one currently connected to the inverter). The caveat I mentioned in my previous post was that currently your inverter knows about both batteries and combines their values on the main LiBMS screen, whereas with the script it would no longer know about them and the combining would be done on the PI. 11 minutes ago, Jay-Dee said: Should I order the CAN to USB in the meanwhile? I am getting excited here!! I just want to send you a script to run to ensure that the proper values are read from the batteries. If it works, then yes. But I first need to decode the Shinwa protocol, just like the Tian Power one.
September 12, 20223 yr 59 minutes ago, SolarConvert said: So the script would still read both batteries (or more if there were) but would combine the the values from the batteries. For example, it would report the average voltage across them and it would sum up the current. But comms would be through the master battery (the one currently connected to the inverter). The caveat I mentioned in my previous post was that currently your inverter knows about both batteries and combines their values on the main LiBMS screen, whereas with the script it would no longer know about them and the combining would be done on the PI. That is perfect... Even better than expected. 1 hour ago, SolarConvert said: I just want to send you a script to run to ensure that the proper values are read from the batteries. If it works, then yes. But I first need to decode the Shinwa protocol, just like the Tian Power one. Send when you ready.. Will DM you with details
October 24, 20223 yr Author I had some queries on how I send the data to the inverter via the CAN port, so I thought I'd share it here. Firstly you'd obviously need to connect your CAN HAT or module to the inverter and PI with the correct pins which are available in earlier posts. Then, there were 3 PDF documents which contained some very useful information on the CAN frames that I needed to map the BMS data to. These I posted in one of my previous posts here: On 2022/09/06 at 8:19 PM, SolarConvert said: Thanks for the link @JustinSchoeman. I managed to get CAN IDs 0x351, 0x355 and 0x356, but 0x359 is the tricky one which I don't find examples of, especially when the alarm/warning bits are set. By far the best set of docs for the CAN IDs I have found is the SMA CAN protocol one SMA CAN protocol.pdf, but I attach the Sunsynk Sunsynk Battery Compatibility v4.pdf and Pylontech CAN-Bus-protocol-PYLON-low-voltage-V1.2-20180408.pdf docs too. Whilst 0x351, 0x355 and 0x356 are a huge upgrade for me since I never had BMS comms, I do think that 0x359 is very important because the inverter must know about any fault conditions of the battery. Those who already had proper BMS comms working via RS485 and choose to go with this RS485/CAN translation route (like @Jay-Dee ) should get no less than what they had before when there was direct BMS comms between the inverter and the battery. Pages 3 of the Pylon CAN protocol doc is what I'm going to tackle next. As for the PI configuration, you'd need to enable the CAN module as per your HAT or adapter's instructions. In my case I consulted this manual for my Waveshare RS485 CAN HAT. Once the module is enabled, you'd bring up the interface, something like the following; sudo ip link set can0 up type can bitrate 500000 I then use python-can in my Python script to send things to the CAN module. Here is an excerpt from the script which shows how to send the CAN frames: import logging import struct from time import sleep import can import battery_tian_power import serial logger = logging.getLogger(__name__) logging.basicConfig( format="%(asctime)s %(levelname)-7s %(message)s", level=logging.INFO ) with serial.Serial( "/dev/ttyS0", baudrate=9600, parity=serial.PARITY_NONE, stopbits=serial.STOPBITS_ONE, bytesize=serial.EIGHTBITS, timeout=1, ) as ser, can.interface.Bus(channel="can0", bustype="socketcan") as bus: logger.info("Reading protection parameters") bms = battery_tian_power.TianPowerBattery() protection_params = bms.read_protection_params(ser, 1) logger.info("Reading battery info") while True: info = bms.read_info(ser, 1) charge_voltage = int(protection_params.pack_ov_start * 10) discharge_voltage = int(protection_params.pack_uv_start * 10) charge_current_limit = int(protection_params.charge_oc_start * 10) discharge_current_limit = int(protection_params.discharge_oc_start * 10) data = struct.pack( "<HhhH", charge_voltage, charge_current_limit, discharge_current_limit, discharge_voltage, ) msg = can.Message(arbitration_id=0x351, data=data, is_extended_id=False) bus.send(msg) soc = int(info.soc) soc_hires = int(info.soc * 100) soh = int(info.soh) data = struct.pack("<HHH", soc, soh, soc_hires) msg = can.Message(arbitration_id=0x355, data=data, is_extended_id=False) bus.send(msg) voltage = int(info.voltage * 100) total_current = int(info.current * 10) avg_cell_temperature = info.temperatures[-1] * 10 data = struct.pack("<hhh", voltage, total_current, avg_cell_temperature) msg = can.Message(arbitration_id=0x356, data=data, is_extended_id=False) bus.send(msg) protection1 = 0 # mapping ommitted in this example protection2 = 0 # mapping ommitted in this example alarm1 = 0 # mapping ommitted in this example alarm2 = 0 # mapping ommitted in this example module_count = 1 data = struct.pack( "<bbbbbbbb", protection1, protection2, alarm1, alarm2, module_count, ord("P"), # careful that we don't act like a Pylon BMS here, maybe omit sending this ord("N"), # careful that we don't act like a Pylon BMS here, maybe omit sending this 0, ) msg = can.Message(arbitration_id=0x359, data=data, is_extended_id=False) bus.send(msg) # data = "PYLON".encode("ascii") # the Deye inverter does behave differently when the manufacturer is PYLON vs something else data = "Narada".encode("ascii") msg = can.Message(arbitration_id=0x35E, data=data, is_extended_id=False) bus.send(msg) sleep(1) I've enabled the above interface command and Python script to run on startup on the PI. Also a neat feature of the PI is to enable the watchdog to reboot the PI in case anything goes wrong as outlined here. There are obviously many ways to do the above things, so what I did is merely one of the ways. I hope the above is useful to anyone who might be attempting the same thing.