Solar panels connection

Featured Replies

If possible I would split it into 2 strings of 7, then connect them in parallel at the combiner box.

Also, if one panel in the series is shaded, it influences the output of the entire string.

You have to however see what the max current on the MPPT is, make sure your string of 10 does not exceed this, cause it will most likely limit the output of the 10 panels, or even worse, cave in.

9 hours ago, stoic said:

If possible I would split it into 2 strings of 7, then connect them in parallel at the combiner box.

Also, if one panel in the series is shaded, it influences the output of the entire string.

You have to however see what the max current on the MPPT is, make sure your string of 10 does not exceed this, cause it will most likely limit the output of the 10 panels, or even worse, cave in.

The number of panels in a string does not change the current. 

A two panel  string will deliver the same current as a ten panel string.

2 hours ago, Jaws said:

The number of panels in a string does not change the current. 

A two panel  string will deliver the same current as a ten panel string.

The 2 strings of 7 will produce double the current at half the voltage than if the 14 were in series.

Yes as indicated the 4 inseries will reduce the voltage in the 10 in series to their voltage. It would be like wasting 6 panels.

Most of the older inverters that could take up to 500V were max of 11A to the single MPPT.

15 hours ago, KobusK said:

Is it possible to connect 10 panels in series and then 4 in series, take these two strings and connect them in paralel?  

Physically it is possible, but not a good idea. The VOC of the one string would be 390V (assuming you have an average sized panel putting out around 39V as a random example) and the other string would have a VOC of 156V. The one string would severely affect the other one if in parallel. 

If by chance you have an inverter with two MPPT’s (like a Sunsynk or Deye) then you could do it without paralleling the two strings. 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.