CFE-5100 S 5.12kWh Lithium battery wifi connection with CF energy app

Featured Replies

On 2023/01/09 at 3:13 PM, isie said:

Let me try these voltage numbers. Thanks

I've set my inverter with the following voltages:

Float: 53.6 V
Absorption: 53.8 V
Equalization charge: 53.8 V

This seems to have stabilised that erratic discharge and charge process. Thanks @Rosh for the suggestions. Really appreciate it

  • Replies 211
  • Views 49.6k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • Hello, I'm calling from Italy, I have a problem with the storage batteries. I have a growatt sfh 5000 inverter and CFE 5100 batteries. The batteries cannot hold the voltage and therefore shut down.

  • hehe me too - i've even offered to re-translate everything for them

  • Its not our inverters. Its the CFE Batteries. How is it possible that we all have the same problem with CFE Batteries but different inveters. 

Posted Images

On 2023/01/09 at 2:15 PM, isie said:

Hi @Paul.Ve, spot on what I'm experiencing. I've read some other forum that stated the BMS is what guides the inverter on what and how to handle the battery. So not really sure if there is a solution to be honest.

Hi, I have the same issue. The batteries charge to 100% by 11AM, and then discharges to 90% without using PV power. Cycles like this until the sun goes down. Time of use settings have no effect at all.

I am busy with CFE to resolve - they are apparently working on new firmware that will only let the batteries discharge to 95% (Apparently the current charge/discharge setup is to protect the battery life....)

15 minutes ago, DeonB1003 said:

Hi, I have the same issue. The batteries charge to 100% by 11AM, and then discharges to 90% without using PV power. Cycles like this until the sun goes down. Time of use settings have no effect at all.

I am busy with CFE to resolve - they are apparently working on new firmware that will only let the batteries discharge to 95% (Apparently the current charge/discharge setup is to protect the battery life....)

Interesting, I would like to know how will they update the firmware.🤔

15 minutes ago, isie said:

Interesting, I would like to know how will they update the firmware.🤔

They do it through your wifi connection - must be online on the cellphone app "Smart BESS"

44 minutes ago, DeonB1003 said:

They do it through your wifi connection - must be online on the cellphone app "Smart BESS"

Yup, my installer can't get that working. I think we all just gave up to be honest 😁

Hello, I'm calling from Italy, I have a problem with the storage batteries. I have a growatt sfh 5000 inverter and CFE 5100 batteries.
The batteries cannot hold the voltage and therefore shut down. ever happened to anyone? The system is new, everything went well for a month and then it's under the problem.

On 2023/01/09 at 3:13 PM, isie said:

Let me try these voltage numbers. Thanks

How is this going folks? I'm using a DEYE inverter and it charges to 100% a few times during the day, but in the afternoon it charges to 100% and I guess there isn't much load and the batteries go into a fault mode and make a clicking noise.

 

I've tried downloading the apk and registering - i scan the barcode and it takes me to the add inverter and details page, which i fill out but then it throws a profile creation error when submitting... sigh...

On 2023/01/12 at 1:55 PM, DeonB1003 said:

Hi, I have the same issue. The batteries charge to 100% by 11AM, and then discharges to 90% without using PV power. Cycles like this until the sun goes down. Time of use settings have no effect at all.

I am busy with CFE to resolve - they are apparently working on new firmware that will only let the batteries discharge to 95% (Apparently the current charge/discharge setup is to protect the battery life....)

Hey Deon, have you been able to successfully install the CF Energy app on android and register? If so what link/version did you use - can't get the blinking thing working...

Just now, GrantCPT said:

How is this going folks? I'm using a DEYE inverter and it charges to 100% a few times during the day, but in the afternoon it charges to 100% and I guess there isn't much load and the batteries go into a fault mode and make a clicking noise.

 

I've tried downloading the apk and registering - i scan the barcode and it takes me to the add inverter and details page, which i fill out but then it throws a profile creation error when submitting... sigh...

I updated the voltages but still having that issue where the battery drops from 100% to 94% and then starts charging again. From the sounds of it, it's the BMS and it's not anything that we can configure on the inverter.

With regards to the battery going to fault mode when reaching 100%, I had the same issue when I first got the batteries. I solved it by discharging the battery to very close to 10% and then recharging it back to 100%. Ever since then I've never experienced that again

Hi all. I can't see BMS info on inverter. it's just blank. Deye 8kw inverter and 3 x CFE 5.12kwh. Also should the - pole of last slave battery run to inverter - and + from master to inverter +? I am under the impression this is only for series connection? currently + and - go to inverter from master battery. 

My 2 x CFE-5100s keep discharging to 90% then charging again. Its not a train smash but I'd prefer if they just stayed at 100%


I installed the BESS app off google play store on an android device I have and I managed to connect my 2 batteries. However I dont see a firmware update available for the batteries

Edited by Zkrige

On 2023/01/17 at 10:45 AM, Zkrige said:

My 2 x CFE-5100s keep discharging to 90% then charging again. Its not a train smash but I'd prefer if they just stayed at 100%


I installed the BESS app off google play store on an android device I have and I managed to connect my 2 batteries. However I dont see a firmware update available for the batteries

I for the life of me just cannot get the battery connected to the app. My Installer is trying to get assistance from CFE but we are getting nowhere to be honest 😞

On 2023/01/16 at 6:28 PM, isie said:

I updated the voltages but still having that issue where the battery drops from 100% to 94% and then starts charging again. From the sounds of it, it's the BMS and it's not anything that we can configure on the inverter.

With regards to the battery going to fault mode when reaching 100%, I had the same issue when I first got the batteries. I solved it by discharging the battery to very close to 10% and then recharging it back to 100%. Ever since then I've never experienced that again

Apologies thought i'd get an email notification on a reply to the post. First timers!

 

I had that same issue with my Deye->CFE's. It would charge to 100% then pv would drop off and load would pull from battery till it got to 90% then it would kick back in again charging... Was resolved by a Deye inverter firmware update (from the installer).

 

So my issue isn't that it goes to fault mode when it hits 100% - when it charges to 100% in the PM and I don't have any load and the pv still able to generate, then the batteries throw a fault after about 30 minutes or so (typically if i leave it between 4pm and 5pm never in the morning charge and usage) - if i generate some load between 4pm and 5pm then it is fine and stays around 100% gets used a little then back to 100% etc... Apparently the installer doing a round of CFE firmware updates on saturday so hopefully that resolves it...

On 2023/01/17 at 12:27 AM, Danie Schoeman said:

Hi all. I can't see BMS info on inverter. it's just blank. Deye 8kw inverter and 3 x CFE 5.12kwh. Also should the - pole of last slave battery run to inverter - and + from master to inverter +? I am under the impression this is only for series connection? currently + and - go to inverter from master battery. 

take a pic of your battery setup including pins and cables and i'll try assist

11 hours ago, isie said:

I for the life of me just cannot get the battery connected to the app. My Installer is trying to get assistance from CFE but we are getting nowhere to be honest 😞

that BMS app is rubbish - i connected both batteries which is fine but the warnings don't actually show the warning codes when it fires. Need the CFE Energy app which seems much better but only on android (although i can't get that working either lol)

On 2023/01/17 at 10:45 AM, Zkrige said:

My 2 x CFE-5100s keep discharging to 90% then charging again. Its not a train smash but I'd prefer if they just stayed at 100%


I installed the BESS app off google play store on an android device I have and I managed to connect my 2 batteries. However I dont see a firmware update available for the batteries

Does your PV follow the load when this happens, or does it drop off and the batteries serve the load until they hit 90% then the pv kicks back in? If so, that's an inverter issue I had as well with my Deye, an upgrade of firmware resolved it.

38 minutes ago, GrantCPT said:

Apologies thought i'd get an email notification on a reply to the post. First timers!

 

I had that same issue with my Deye->CFE's. It would charge to 100% then pv would drop off and load would pull from battery till it got to 90% then it would kick back in again charging... Was resolved by a Deye inverter firmware update (from the installer).

 

So my issue isn't that it goes to fault mode when it hits 100% - when it charges to 100% in the PM and I don't have any load and the pv still able to generate, then the batteries throw a fault after about 30 minutes or so (typically if i leave it between 4pm and 5pm never in the morning charge and usage) - if i generate some load between 4pm and 5pm then it is fine and stays around 100% gets used a little then back to 100% etc... Apparently the installer doing a round of CFE firmware updates on saturday so hopefully that resolves it...

The CFE support guys said the inverter needs a firmware update. Lets see if that solves the issue 😃

 

Edited by isie

34 minutes ago, GrantCPT said:

that BMS app is rubbish - i connected both batteries which is fine but the warnings don't actually show the warning codes when it fires. Need the CFE Energy app which seems much better but only on android (although i can't get that working either lol)

In conversation with CFE Support, let's see what happens

Did you folks have any joy here? I have 4 x cfe5100s batteries linked up, and 2 x deye 8kw inverters in parallel. home assistant + solar man plugin shows that every day i'm charging the batteries more than what im pulling out of them. That makes no sense at all - surely what's put into the batteries should be more or less what's pulled out (excl inefficiencies)

 

I'm curious to know if an inverter and battery firmware update is going to solve this (and the fact that my batteries seem to vaccilate between 90% and 100% all day)

image.png.4ce2c56e0c21b69177616095a5bef742.png103907881_image(3).png.9c4c115a2ff4ccc2154a421251356e71.png932044018_image(2).png.72caac6b746dfe73bd73f404f6918cb7.png1990996724_image(1).png.36ff0ee8d56233f4dce9f2185ce38bd1.png

Edited by Zkrige

On 2023/01/19 at 5:31 PM, GrantCPT said:

Does your PV follow the load when this happens, or does it drop off and the batteries serve the load until they hit 90% then the pv kicks back in? If so, that's an inverter issue I had as well with my Deye, an upgrade of firmware resolved it.

How did you get your inverter firmware upgraded?

19 minutes ago, Zkrige said:

How did you get your inverter firmware upgraded?

The installer did it remotely - I had to send my logger qr code and stuff to him and he initiated it.

Hi

Does anyone know if there is a fault on the smart bess app. From yesterday its failing to show my battery. Wifi is on and battery added but thats it. Did reset and reinstalled and everything i can think of.

On 2023/01/10 at 4:43 PM, isie said:

I've set my inverter with the following voltages:

Float: 53.6 V
Absorption: 53.8 V
Equalization charge: 53.8 V

This seems to have stabilised that erratic discharge and charge process. Thanks @Rosh for the suggestions. Really appreciate it

is all running still running well 2 weeks later?

 

 

Edited by nam-hunt

6 minutes ago, nam-hunt said:

is all running still running well 2 weeks later?

 

 

Nah, I thought this would've helped but it looks like it didn't. Still goes back and forth after being charged full. The CFE support guys said the Deye Inverter Firmware needs to be updated and this might solve the problem. So waiting for the update and will see if that solves the problem. Will keep you guys updated

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.