Yesterday the street whatsapp group lit up with complaints about very low incoming grid voltage. Like > 190 V low. People were saying that their lights wouldn't work properly, that anything that heated via an element was taking longer. More generally they were worried about damage to their appliances.

City Power actually reacted quite quickly and went to inspect the substation feeding our street. They said (and I'm quoting 2nd hand here) that it was only the even numbered properties affected, and that the problem was a bent feeder cable.

I wasn't sure about the bit about the bent cable, but the voltage came up to about 215V.

Until later that evening when it got down into the 180s again. Then came up about 23:00 (+200).

This morning we sit at about 205 - 208 V AC, but I have reason to think that the voltage dropped a bit earlier this morning. I say this because it looks like my inverter disconnected from the grid for a while. The usual little "sips" of grid power that it usually takes throughout the night were greatly reduced, and battery SOC at 7:00 was lower than usual.

OK... so it seems to me that if voltage goes DOWN, then current must go UP if the load remains the same. This means that for keeping the same devices running, our circuit breakers are getting closer to tripping.

But some questions
1) I know that voltage IS important, but not why. Is it because of transformers that precede rectifiers, and expect a certain incoming voltage so that they can deliver the correct output DC. OK... that's for televisions and such. What about AC stuff like motors in appliances?

2) What can cause the voltage to drop? (I suspect I might regret asking this). It seems to me - on a small sample so far - that the voltage gets lower during Eskom's period of highest demand. Also I have repeatedly seen that when power is restored after a load shed, then voltage is initially low and climbs to something approaching 230 over 45 minutes or so. 

This is really about gathering information so that we can help City Power to help us.

TIA

Posted

OK.... So City Power have been out twice to look at this. Yesterday they cut our street off for a couple of minutes whilst they did some work.

The situation persists, and it may be out of their control. We generally get 205 to 215 V during the day, but every evening it dips and then recovers. The timing seems to correspond with Eskom's reported time of heaviest usage.

I am going to monitor the voltage in another suburb (where my mother lives, and where she has an inverter box that displays the incoming voltage). That will be another clue, though I sense that City Power are now filing this under "first world problems".

Posted

Possible to much load been pulled out of that circuit. The transformer in that minisub cannot handle the load.

They could possibly change the tap settings on the transformer, if they are not already at maximum.

Cable bend will never have such an effect. That is a big joke, lol

 

 

Posted
10 minutes ago, Antonio de Sa said:

Possible to much load been pulled out of that circuit. The transformer in that minisub cannot handle the load.

They could possibly change the tap settings on the transformer, if they are not already at maximum.

Cable bend will never have such an effect. That is a big joke, lol

 

 

I raised an eyebrow at the bent cable explantion, but I did not hear it from City Power but from somebody who was quoting what they understood City Power to have done (and who assumed that they were actually addressing the low voltage problem), and so it has to be taken with a pinch of salt.

I have long suspected that there is something up on our little hoekie of the grid, with one or more properties demanding a lot of power. Often after a load shed our street is left in darkness whilst everybody else's power is restored. Or so it seems. Since I got my solar system, and since a couple of folks bought inverters, what we see is that the power is back on but the voltage is very low. Voltage slowly climbs after restoration.

This is why Eskom recommend that people turn off everything except light circuits on the DB during a load shed, and then turn them back on once power is restored. It's an inconvenience (especially if the load shed is 2am - but then who is awake to have a moan?), and we should not be happy with it, but it will reduce the problem of sub stations tripping because of a huge surge in demand, so it's a lesser of evils. This is a constant problem not far away from our street, but try to get those folks to turn off their geysers...

Two things
1) City Power have ripple switches installed (this is mandated) but I guess these are easily bypassed, or ignored when people add extra geysers.
2) Attitudes aren't always sensible. I know folks whose response to a load shed is to turn on EVERYTHING in their house when power is restored, just to demonstrate to Eskom that nobody is going to tell them when they can use power and how much.

Posted
51 minutes ago, WannabeSolarSparky said:

That is code for "we have no e@@ing clue what we are doing"

Low voltages are fridge killers :(

Well they did respond, and even knocked on somebody's door to say they would be looking into the matter. But when there are suburbs with no power for days, one street complaining about low voltage is probably not what they are most concerned with.

Posted

PS: The larger than usual drop in my battery's SOC over night may have been due to a person who decided to use "free electricity" to run an electric blanket. The problem is confusing "from the sun" with "unlimited". This is a battle I find myself fighting over and over again. The concept of "finity" seems very hard for some to grasp.

Posted

Their are actually a few reasons this can happen.

Load to high for Transformer/Minisub to handle.

Cable not able to handle the load.

Phase loss on the 11KV side.

Internal winding fault on transformer(Doubt there protection will pick it up if any is still working.)

Tap changer fault inside transformer.

Loose connection on HT or LV side.

Posted

That makes sense, but a burned cable would possibly have a dead shorth circuit, that would trip the breaker at the minisub, in my humble opinion low voltage means that there is not enough " Juice" to supply the load.  the transformer at the minisub for that specific suburb cannot cope. 

Posted

Many reasons given but due to ageing network this low voltage could come all the way from the 88/132kV network. All the transformers will have their own tap changers.

Further due to the state of the network the voltage could also be lowered in order to draw lower amps from all the equipment in use. I am not indicating it is done but can be used as a tool in peak times when more heating=resistive loads are connected while preparing meals and heating of water.

I would also take a flyer and say that about all the ripple controllers are no longer in use. This is the case in Tshwane. We all paid to have them fitted and they out of order.

These ripple relays can easy save Eskom about 2 stages if all Munics that have them fitted were to do the repairs and have them actively used during LS. Yes most are bypassed or just set to be off(permanent on for geyser) and will stay off unless a carrier is sent to put them back in use. This is one of the 10 plans to lower LS if there was a will to improve the supply of power. Not rocket science.

 

Posted

Just thinking out loud. Since everyone and his neighbour seems to have installed an inverter, I wonder what's the demand for battery charging directly after a round of loadshedding. One or two or more x 1C batteries at 5kW charge rate each, times by how many houses in the street?

Posted (edited)
6 minutes ago, GreenFields said:

Just thinking out loud. Since everyone and his neighbour seems to have installed an inverter, I wonder what's the demand for battery charging directly after a round of loadshedding. One or two or more x 1C batteries at 5kW charge rate each, times by how many houses in the street?

Not sure in your area but the penetration of PV systems is still very low. May be less than 5%. Yes a lot of batteries are charged but also some might only be charged from PV the next day. 5kw inverters do not use more power than say a oven and geyser. Items that might be on if LS ends during meal preparing times in the evening.

Edited by Scorp007
  • 5 weeks later...
Posted

The end of this tale is that we eventually had a major outage when a cable and substation got fried by inrush after a load shed. City Power replaced some components in the substation and since then our voltage, whilst still fluctuating, is higher overall. Yesterday I saw 234. We used to max out at near but just below 230. Maybe when they did all the replacements they used a different tap on the transformer - or maybe it was losses in the old infrastructure. Me no engineer.
 

Posted
On 2022/07/28 at 8:36 PM, Scorp007 said:

Not sure in your area but the penetration of PV systems is still very low. May be less than 5%. Yes a lot of batteries are charged but also some might only be charged from PV the next day. 5kw inverters do not use more power than say a oven and geyser. Items that might be on if LS ends during meal preparing times in the evening.

I think the reference here is to these little boxes on wheels that have an inverter and some (usually) lead-acid batteries. I think it's plausible that they will contribute to the in-rush by starting to recharge once there is incoming juice.

I understand people's anger at load shedding, but it seems to me to be sawing at the branch we are sitting on to not heed the request made to use to isolate heavy drawing items (geysers being a good example) during load shedding, because we KNOW there's going to be a huge demand when the power comes back on. And I would bet that our local grids are designed for an average load when everybody's geyser is on at some time, but not everybody's is on at the same time. Plus I know of people who put supper in the oven and leave it on so that supper starts cooking when the power comes back on. This all adds up to a big surge when power is resumed. I won't even mention my friends whose practice is to turn on EVERYTHING in their house when power comes back on, just to show Eskom who is who in the zoo.

The sort of inverter I think is meant here will work just as well during a load shed if you unplug it. There is a growing understanding in my street (not stemming from me, because I have solar, so nobody takes me seriously on power issues) that we should isolate stoves and geysers during load shed.

  • 1 year later...
Posted

Maybe one of the first signs that loadshedding is about to return after the elections? Reduction in power quality due to insufficient generation capacity to meet the winter demand?

Or maybe just a localised issue with a "bent" cable?

Either way, thanks, I'm going to re-set the Voltage parameters on my inverter. Found out last time that it reverted to default values when a new firmware was installed.

Posted
On 2024/06/07 at 7:53 AM, GreenFields said:

Maybe one of the first signs that loadshedding is about to return after the elections? Reduction in power quality due to insufficient generation capacity to meet the winter demand?

Or maybe just a localised issue with a "bent" cable?

Either way, thanks, I'm going to re-set the Voltage parameters on my inverter. Found out last time that it reverted to default values when a new firmware was installed.

Just wanna say, I called it. Were there any prizes up for grabs?

https://www.news24.com/news24/southafrica/news/joburgs-city-power-to-implement-load-reduction-to-protect-grid-from-total-collapse-20240608

Posted
2 hours ago, GreenFields said:

The article is pay walled. Can you give us some detail?

AIUI load reduction is an Eskom practice used in areas where the infrastructure is badly compromised (IE there are lots of illegal connections) and usually involves disconnecting during times of high demand. 

If that's the case, they are protecting against sub stations getting overloaded. 

Posted
7 hours ago, Bobster. said:

The article is pay walled. Can you give us some detail?

AIUI load reduction is an Eskom practice used in areas where the infrastructure is badly compromised (IE there are lots of illegal connections) and usually involves disconnecting during times of high demand. 

If that's the case, they are protecting against sub stations getting overloaded. 

You are right. I guess no prizes then.

Posted
1 hour ago, GreenFields said:

You are right. I guess no prizes then.

Certainly CP are issuing warnings that their system is constrained and asking people to be frugal. No surprise there, Eskom announced a while back that we might get to stage 2 in the winter. 

Eskom have been doing load reduction for years. They regard it as not shedding, say it is to protect infrastructure, and it mostly happens in townships. 

 

Posted (edited)
On 2024/06/07 at 6:17 AM, SJB said:

apologies for reviving this thread, did you managed to get it sorted out, we have the same problem

We had at least two further cases. First one was very wide spread, but as usual people moaned on social media but didn't do much else. Councillor and residents association got involved, asked everybody to log. They then built up a spreadsheet of addresses and ref numbers. This helped CP identify the area affected and thus the most likely point of failure. 

Then one afternoon the power went down at a time not indicated in LS schedules. It came up about 5 minutes later at a much better number. 

Some time later we had a local problem in my street. AFAIK only three properties were affected. Sparky came out and measured voltages at two properties (third would not grant him access). He then disconnected the other two and measured at mine. Voltage still low. He repeated this process, testing to see if one property was pulling the voltage down. He then traced the fault up the street, round a corner, to the substation, said there was a fuse in there that was not properly in place. At this point the voltage came back up for two properties*. He then did load tests. Asked us to turn on everything we could to check that the properties could handle a high load with no degradation. In my case he asked me to bypass the inverter. This test was passed, and the voltage has been within spec ever since. 

*the owner of the property who wouldn't grant access messaged me to ask if City Power had fixed my problem because his voltage was still low. I said well if you won't let them in, there's only so much they can do. 

Edited by Bobster.
sppeling
Posted
On 2024/06/07 at 7:53 AM, GreenFields said:

Maybe one of the first signs that loadshedding is about to return after the elections? Reduction in power quality due to insufficient generation capacity to meet the winter demand?

 

On 2024/06/09 at 8:01 AM, GreenFields said:

You are right. I guess no prizes then.

Don't be so sure: we're flying awfully close to the sun today with tonight estimated to be truly borderline at around 6PM:

DemandEstimation_20240610.thumb.jpg.d39c2eed0e6d258b1625a3f919fe0f62.jpg

 

That prize of yours may very well still be on the way...

 

  • 1 month later...
Posted
On 2024/06/10 at 10:58 AM, JayMardern said:

 

Don't be so sure: we're flying awfully close to the sun today with tonight estimated to be truly borderline at around 6PM:

DemandEstimation_20240610.thumb.jpg.d39c2eed0e6d258b1625a3f919fe0f62.jpg

 

That prize of yours may very well still be on the way...

 

Any chance we can get a updated Graph for today?
or is this available on the internet?

 

 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...