DC fuses or DC breaker between solar panels and inverter?


RocketBoy

Recommended Posts

I was chatting to a mate who does installations and he was saying that he is planning on replacing his DC fuses between his panels and inverter with DC breakers instead.

He had heard that fuses were a fire risk and breakers are safer. That is the exact opposite of what I have heard and there are numerous reports from the Aussies about breakers/isolaters catching fire.

If I look at commercially available combiner boxes they normally just have breakers.

I watched a video where an installer was explaining that breakers cant always handle the load when they get turned off while the sun is shining and the panels are producing. The sparky in the vid explained that the contacts in a DC breaker are too small to stop that power safely. Just like he said, when he turned the breaker off under power it melted down and caught fire.

I have fuses rated according to my panel manufacturer and no breakers - the Sunsynk has a contactor for disconnecting PV. 

So to all of the clever people who have experience in these matters, which is the correct one to use? should it be fuses into breakers?

Link to comment
Share on other sites

On 2023/04/11 at 10:02 AM, Superfly said:

Can you post the link to that? DC breakers are safe if sized correctly, same for fuses - never heard of them catching fire other that due to arc-ing which happens when an AC breaker is used on DC.

There are quite a lot of recorded cases in Australia, here is one vid I watched on the topic:

I agree that there shouldnt be a reason if there is a arc diffuser like in DC breakers, but the argument that the contacts being disconnected under load can fuse and melt down is a little scary.

Is the solution to have DC breakers *and* fuses? seems a bit overkill to me.

Link to comment
Share on other sites

23 minutes ago, RocketBoy said:

There are quite a lot of recorded cases in Australia, here is one vid I watched on the topic:

I would have loved to see a multi-meter indicating correct polarity before he did that test. If I recall, there were no instances of fires attributed to breakers wired with the correct polarity - only when they were installed backwards.

Link to comment
Share on other sites

Be careful with certain fuses. This is what happened to a friend less than 24hrs after installation and at about 16h30 far from peak power. Fuse holder melted that one could not even get it to open around the pivot point. Now this is a 1000V DC fuse but what about the holder? 

IMG_20230412_174349.thumb.jpg.b01af6491c18859930a974575945f027.jpg

Link to comment
Share on other sites

6 minutes ago, Superfly said:

Those din isolators are useless. I'm pretty sure a fuse would have blown with that short circuit current anyway always use a DC breaker with Short-Circuit and Overload protection.

Without seeing the fuse myself the rating was higher than the panel Isc. Further if blown it would have been during peak full sunshine day not 16h30. My take is just a hot connection in the fuse holder. 

Link to comment
Share on other sites

On 2023/04/11 at 9:18 AM, RocketBoy said:

I was chatting to a mate who does installations and he was saying that he is planning on replacing his DC fuses between his panels and inverter with DC breakers instead.

He had heard that fuses were a fire risk and breakers are safer. That is the exact opposite of what I have heard and there are numerous reports from the Aussies about breakers/isolaters catching fire.

If I look at commercially available combiner boxes they normally just have breakers.

I watched a video where an installer was explaining that breakers cant always handle the load when they get turned off while the sun is shining and the panels are producing. The sparky in the vid explained that the contacts in a DC breaker are too small to stop that power safely. Just like he said, when he turned the breaker off under power it melted down and caught fire.

I have fuses rated according to my panel manufacturer and no breakers - the Sunsynk has a contactor for disconnecting PV. 

So to all of the clever people who have experience in these matters, which is the correct one to use? should it be fuses into breakers?

Sorry but, why will any one break the circuit under load? shouldn't you first switch off all the loads before isolating the panels? In MHO, it doesn't matter whether you use fuses or isolator or both. I prefer using both 

Link to comment
Share on other sites

1 hour ago, hoohloc said:

Sorry but, why will any one break the circuit under load? shouldn't you first switch off all the loads before isolating the panels? In MHO, it doesn't matter whether you use fuses or isolator or both. I prefer using both 

All your loads could be off. Also the inverter can be off as well but charging will still take place based on the PV input and charge setting thus under load. 

Link to comment
Share on other sites

11 hours ago, Scorp007 said:

All your loads could be off. Also the inverter can be off as well but charging will still take place based on the PV input and charge setting thus under load. 

how will charging take place when the batteries are off and isolated? Again, it is always best and safe to remove all the load before switching off. The load includes batteries as well. Think safety first and you will not go wrong 

Link to comment
Share on other sites

It is a legal requirement that there be a 'switch-disconnector' on each supply into a device.

So it is required that at least one of the disconnection devices (be it a circuit breaker or fuse) be rated to disconnect under load.

So this symbol (line with circle - either on its own, or in combination with others) should appear on one of the devices:

image.png.6cb04455cea0d852433e4ee14b000e58.png

These disconnectors serve 2 purposes:

1) safely isolate all power sources when working on a device, and

2) emergency disconnect of power to a device when something goes wrong.

The second case requires something that can switch under load.

Link to comment
Share on other sites

5 hours ago, hoohloc said:

how will charging take place when the batteries are off and isolated? Again, it is always best and safe to remove all the load before switching off. The load includes batteries as well. Think safety first and you will not go wrong 

The advice was to switch off loads but not battery. In such a case the battery is still connected and the panels should then not be isolated under load while charging the battery. 

Link to comment
Share on other sites

3 minutes ago, Scorp007 said:

The advice was to switch off loads but not battery. In such a case the battery is still connected and the panels should then not be isolated under load while charging the battery. 

The advice is to switch off all the loads. When all loads are off, that include batteries, you will not have current flowing from the PV panels and it will be safe to switch them off. Always work safe 😉

Link to comment
Share on other sites

  • 2 weeks later...
On 2023/04/13 at 7:19 AM, Scorp007 said:

All your loads could be off. Also the inverter can be off as well but charging will still take place based on the PV input and charge setting thus under load. 

^This.

DC doesnt play games like AC does in terms of waveform so there are no dips which makes it difficult to break. In theory you should never turn any of that DC off under load but what happens if there is a fault and you have no choice?

The inverter will limit the use of solar if there is nothing to do with it, but the full DC current is still reaching right through to the MPPT controller.

Link to comment
Share on other sites

18 minutes ago, RocketBoy said:

^This. In theory you should never turn any of that DC off under load but what happens if there is a fault and you have no choice. 

It is an abnormal condition so no time to think I should not switch off. Use any means to switch off-even if it means cutting a wire/cable and risk another flame. 

This is what I will do. 

Link to comment
Share on other sites

  • 4 months later...

You cannot use a breaker as a switch on pv dc due to arcing. You use a fuse, with a dc breaker and surge protection device tgat needs to be earthed for lighting protection 

If there is a fault, the fuse will blow to protect the breaker. 

 

 

Link to comment
Share on other sites

 

You cannot use a breaker as a switch on pv dc due to arcing. You use a fuse, with a dc breaker and surge protection device tgat needs to be earthed for lighting protection 

If there is a fault, the fuse will blow to protect the breaker. 

 

 

Interesting reason for the fuse. 

Just a question. If a panel with a Isc current 11.68A as in 1 has a 20A fuse as in 2 per the manufacturer how will the panel be able to blow the 20A fuse? 

 

 

IMG_20230919_151313.jpg

Edited by Scorp007
Link to comment
Share on other sites

 

If a panel with a Isc current 11.68A as in 1 has a 20A fuse as in 2 per the manufacturer how will the panel be able to blow the 20A fuse?

The fuse is primarily to protect a single string when multiple strings are in parallel (i.e. in a combiner box), where the sum of the currents from other strings can exceed the current limits of the bypass diodes in a bad string.

This is also why fuses are recommended, as the fault current could be a reverse current. So you would need non-polarised breakers in a combiner.

AFAIK only Australia has a regulation requiring fuses instead of breakers.  I can't see any local regulation requiring a fuse instead of a breaker.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...