Solar Charging

Featured Replies

Hi All, I need help please. I bought a Axpert 5kva inverter, with 2 Pylon tech 2,4kwh batteries and run 6 panels on my farm. 

The solar starts charging in the morning and then disconnects the PV panels the moment  the batteries are charged, sometimes as early as 11am.

From there the farm runs on battery power for the day, meaning the system runs out of power in the night somewhere and shuts down because the batteries were not fully charged going into the evening. 

Why does it do this? How can I fix this? 

2nd question, with the Pylontechs, can I link the 2,4 kw batteries with the newer 3kw versions in the same stack? 

I would appreciate all advice. 

 

Edited by JohanO
Finger problems, was not finished yet.

  • Replies 53
  • Views 11k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • It would be really helpful if people would give the real power of their inverter, since there are two different models with a 5 kVA rating: the older models are rated at 4 kW (PF0.8), and newer ones a

  • Jaco De Jongh
    Jaco De Jongh

    Yes you can, some suppliers sell the two as a combination.  

  • @Chris Louw and @JohanO, I have written a post about Can I update my firmware. In both of your cases, you can update to patched firmware version 72.20c (or later versions of 72.20x if they come o

Posted Images

  • Author

Sure

01 sbu

02   60a

03. apl

04  sds

05 agn

06 ltd

07 tfd

09 50hz

11 30a

12 51v

13 ful

16 snu

18 bon

19 hep

20 lon

22 aof

23 bye

25 fds

26 56,4v

27 54v

28 51g

29 42v

30 one

31 sbe

32 aut

32 eds

34 58.4

35 60

36 120

37 30d

38 dls

39 ads

21 minutes ago, JohanO said:

Sure

01 sbu

02   60a

03. apl

04  sds

05 agn

06 ltd

07 tfd

09 50hz

11 30a

12 51v

13 ful

16 snu

18 bon

19 hep

20 lon

22 aof

23 bye

25 fds

26 56,4v

27 54v

28 51g

29 42v

30 one

31 sbe

32 aut

32 eds

34 58.4

35 60

36 120

37 30d

38 dls

39 ads

It seems it is out of range. These are Pylon specs:

Item No. Setting Value Program

02 Set to N*25A, N=battery amount Program

05 Set to USE Program

12 Set to 48V Program

13 Set to 51V Program

26 Set to 53.2V Program

29 Set to 47.5V

  • Author

Thank You for the feedback , I have entered those settings. Only question I have, on setting 2 it only gives options for 10, 20, 30 A etc.... It will only run in increments of 10a? 

3 minutes ago, JohanO said:

Thank You for the feedback , I have entered those settings. Only question I have, on setting 2 it only gives options for 10, 20, 30 A etc.... It will only run in increments of 10a? 

Parameter 2, in your case, 50 A, because you have 2 pylon.

15 minutes ago, JohanO said:

It now gives an error code 04, battery voltage too low, however batteries are at 5 lights, almost fully charged? 

What´s the voltage that appears for battery in axpert monitor? 

And, what about the size of wires?

Edited by Javi Martínez

  • Author
6 minutes ago, Javi Martínez said:

What´s the voltage that appears for battery in axpert monitor? 

And, what about the size of wires?

Wires are 6mm from the panels

It says 49.7v

 

 

 

Well, it is only a warning, when battery voltage is lower than what is set in 29 parameter + 2 V. I wouldn´t worry for the warning, but if it is a sunny day, you should have more charged batteries. 

14 hours ago, Javi Martínez said:

If parameter 29 is set to 47.5 V, it shouldnt beep till 49.5 V. @Chris Hobson, what´s happening??

If I remember correctly setting 12 also is used to trigger the alarm. I don't have vanilla firmware so I cannot check. @Coulomb you have those facts at you fingertips.

 

19 hours ago, JohanO said:

The solar starts charging in the morning and then disconnects the PV panels the moment  the batteries are charged, sometimes as early as 11am

If you  are using vanilla firmware you may have charging stop prematurely. @Coulomband @weber have collaborated and produced Aussie firmware that eliminates the charging bug.

I do not know if they have firmware for your model of inverter.

On 2018/12/30 at 9:21 PM, JohanO said:

I bought a Axpert 5kva inverter

It would be really helpful if people would give the real power of their inverter, since there are two different models with a 5 kVA rating: the older models are rated at 4 kW (PF0.8), and newer ones at 5 kW (PF1). Especially in South Africa, where people don't tend to buy through MPP Solar and hence often don't get the 64 V option, it's important to know this, since it's now possible to brick a new inverter when attempting to update the firmware.

[ Edit: while that's good for identifying the most important parameter, I now recommend posting the main firmware revision, when asking whether or to what version it can be updated to; see this post. ]

So please: is it 4 kW (PF 0.8) or 5 kW (PF1)?

If 5 kW, does it have the 64 V option?

The 5 kW model without the 64 V option is becoming common, and these are the ones for which there is no firmware available, patched or official/factory, and these are the ones that it's possible to brick.

Edited by Coulomb

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.