Help Needed - 2 x Deye 8kw Inverters in Parallel

Featured Replies

Hi

I've got an issue with my inverters not prioritizing battery and solar. Instead, the grid is being used even when I've set the time of use to draw solar and battery. The result being that my batteries are always at 100% and municipal power is being used even though there's ample battery power.

This problem only started after I added an inverter to my original one. Any suggestions would be highly appreciated.

39 minutes ago, Bobster. said:

@JK84 please tell us more about the inverters and the battery. Make, model, capacity.

Hi

It’s 2x Deye 8kw Inverters in parallel connected to 5 x 4.8kwh Pylontech batteries.

It might be unrelated but I have had issues of late with enabling/disabling the time of use remotely, specifically on the new model Deye 8kWs. Has it been set on the inverters manually?

  • Author
7 hours ago, Shadders said:

It might be unrelated but I have had issues of late with enabling/disabling the time of use remotely, specifically on the new model Deye 8kWs. Has it been set on the inverters manually?

Yes, I've set the time of use on the inverter manually.

When you installed the 2nd inverter did you do firmware update?

What are the settings for:

Battery 1
Battery 3
System work mode 1
System work mode 2
Advanced Function 1

1 hour ago, Shadders said:

It might be unrelated but I have had issues of late with enabling/disabling the time of use remotely, specifically on the new model Deye 8kWs. Has it been set on the inverters manually?

Hi

Yes, I’ve set the time of use on the inverter manually.

13 minutes ago, Shadders said:

When you installed the 2nd inverter did you do firmware update?

What are the settings for:

Battery 1
Battery 3
System work mode 1
System work mode 2
Advanced Function 1

Yes, the installer confirmed that the firmware was updated on both inverters.

I’m attaching pictures of inverter settings and also of the setting from the Solarman app d4a586e6-a0dd-48ad-9286-2b8793778e90.jpeg

4172d92c-7585-48be-ae8a-a6fadeb6eb99.jpega2c7f424-493e-42ea-9654-2fcd3527cc39.jpeg4f5f0c95-40bf-42d7-8702-4e2f9ba484af.jpeg9abe2bfa-e3f2-4a43-851c-558c1cffb3a8.jpeg340c3e55-4954-4e55-9f87-bba5998853c1.jpegc3007191-5d3c-4715-9a67-8f31ac22cb11.jpege888813f-4f26-48bb-a91a-89df2739d0ae.jpeg

A couple of comments:
- I would normally set zero-export power to 20-40W to prevent prepaid meters from tripping. If you haven't had problems don't worry about it

Check battery %.

You've instructed that it would use the battery only in slots 2 and 3, and then only to 70% DOD. For the rest, it should stay at 100%.

PF 2025-11-28 150528.png

Sorry I had a meeting and did not get a chance to complete my post, following on from earlier:
- Personally I would drop SOC earlier in the morning so there is battery capacity for the panels to work closer to their maximum capacity rather than just matching load. You will save more electricity and make better use of your investment. It's nearly impossible in most applications to reach the warranty number of cycles so use the batteries more i.e. in the early morning hours before the sun comes up. Typically I go as low as 40% and as high as 60%
- time slot 1, 2 (and maybe 3) I would untick grid charge. If you hit the stated % it will hold at that value but not charge from grid. You only really need to charge to 100% in the evening to give backup for the evening

  • 2 months later...
  • Author
On 2025/11/29 at 10:19 AM, Shadders said:

Sorry I had a meeting and did not get a chance to complete my post, following on from earlier:
- Personally I would drop SOC earlier in the morning so there is battery capacity for the panels to work closer to their maximum capacity rather than just matching load. You will save more electricity and make better use of your investment. It's nearly impossible in most applications to reach the warranty number of cycles so use the batteries more i.e. in the early morning hours before the sun comes up. Typically I go as low as 40% and as high as 60%
- time slot 1, 2 (and maybe 3) I would untick grid charge. If you hit the stated % it will hold at that value but not charge from grid. You only really need to charge to 100% in the evening to give backup for the evening

Hi

Thanks for this. The system is still:

- Keeping batteries at 100% throughout the day and night.

  • Drawing from grid when the house requires more than the solar being produced as opposed to covering the shortfall from the batteries.

Edited by JK84
Clarifying the issue

silly question but under system work mode are all days are ticked? try lowering your tou battery percentages and then also run a test by unticking grid charge under tou settings. bit of trial and error

11 hours ago, Mattyboy said:

silly question but under system work mode are all days are ticked? try lowering your tou battery percentages and then also run a test by unticking grid charge under tou settings. bit of trial and error

Hi

Yes, all days are ticked and grid charge is unticked for all time slots.

Two issues bugging me.

  1. If you have 5 x 0.5C batteries installed, why are you seeing a 200A discharge limit and not 250A Is the Pylontech spec? Are all the batteries communicating to the inverter? What happens when you run with the battery settings in Voltage mode?

  2. On one of the screens above the power inflow and out from from the inverter doesn't match. Around 2.05kW PV, but almost nothing from battery, but then 0.98kW going to loads and 2.68kW exported to grid. Was this transient? Any chance there's a problem with the CT coil fitment?

On 2026/02/01 at 1:18 PM, JK84 said:

Thanks for this. The system is still:

- Keeping batteries at 100% throughout the day and night.

  • Drawing from grid when the house requires more than the solar being produced as opposed to covering the shortfall from the batteries.

Post the current settings on Main Inverter 'SYSTEM WORK MODE' 2 (2nd Menu)

This menu

image.png

Edited by CobusK
Add image of SWM 2

40 minutes ago, GreenFields said:

Is this your master or slave inverter? Please post all system work mode and battery settings screens for the master inverter.

Posting setting from the master.

image.jpeg

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.