September 19, 20223 yr Hi, Can someone please help me with settings for an RCT-AXKING-5K48V inverter connected to a Dyness 4.8kWh. I believe my setting is correct as per the manual from Dyness but my problem is that on the Inverter screen the battery shows 100% but as soon as the utility drops my battery capacity drops to below 50% (Attached file 20220919.xls shows the data) On the Battery indicators it shows that it is full and does not go lower that 3 lights out of 5. Product Information Model Type: Stand alone Topology: Transformerless Main CPU Version: 00071.90 Secondary CPU Version: 00001.10 Parameter Set to Charger source priority: Utility and Solar Output source priority: Solar AC input range: UPS Battery type: User Max. Charging Current: 50 A Max. AC Charging current: 40A Back to charge voltage: 49.0V Back to discharge voltage: 54 Bulk charging voltage(C.V. voltage): 53.5V Float charging voltage: 52.5V Battery cut-off voltage: 47.5V I have attached the battery parameters from the manual. Assistance will be greatly appreciated. 20220919.xls
September 19, 20223 yr Under battery type - what other options do you have? Is the battery connected to the inverter through the comms port?
September 19, 20223 yr Author @mzezmanThe other options I have there is AGM, Flooded and PYLON. It is connected through the coms port with network cable that was supplied with battery.
September 19, 20223 yr Only if the Dyness makes use of Pylontech RS485 communication protocol will it be compatible with the inverter. Otherwise USE settings will work but the appropriate other settings like Bulk, float, cut off & charge amps will need to be set in the inverter.
September 19, 20223 yr Author @mzezmanThe dip switches are set to 0100. Here is a short video clip as well. 20220917_095856.mp4
September 19, 20223 yr 10 minutes ago, MarkP said: @mzezmanThe dip switches are set to 0100. Here is a short video clip as well. 20220917_095856.mp4 That's the correct dipswitch setting - @Steve87 might be better placed here
September 19, 20223 yr 29 minutes ago, MarkP said: @mzezmanThe dip switches are set to 0100. Here is a short video clip as well. 20220917_095856.mp4 This battery looks alot like the Mecer M3000 ESS......... wonder if they operate the same way. Trying to get proper settings for older Axpert type inverters.
September 19, 20223 yr 12 hours ago, MarkP said: @mzezmanThe other options I have there is AGM, Flooded and PYLON. It is connected through the coms port with network cable that was supplied with battery. The network cable won't be doing anything unless the inverter is set to PYL. The cable that came with the battery won't work either (it's for battery to battery comms), you may have been provided a battery cable with the inverter? If not you need to make up a custom cable with the dyness pinout. I think the dyness works just like a pylontech with the axpert, but I'm not 100% sure, there should be other posts about this on the forum. 13 hours ago, MarkP said: the battery shows 100% but as soon as the utility drops my battery capacity drops to below 50% The reason for this is that the axpert uses the battery cutoff and charge voltage settings to calculate the range of charge (0-100%). The problem is that the battery settles to a lower voltage than the charging voltages, so it appears to drop dramatically when the charging source is disconnected as the inverter works with voltage. The other reason it drops so dramatically is because it takes the cutoff voltage (47.5V) as 0%, but in actuality that is more than 20% SOC, so the range become smaller. If you change the cutoff setting to the same voltage that represents 0% SOC on the battery it would bring the two more in line with each other, but they will never be the same as the battery counts the current (A) going into the battery, but the inverter uses the voltage. The lights on the battery will always be the correct one though.
September 20, 20223 yr Author @jumperThank you for the explanation. Helps a lot. Will play around with some settings. Just don't want to change settings that would effect the life expectancy of the battery.
December 2, 20223 yr Author I got the problem resolved working with the supplier. The problem was the firmware on the inverter. I had to update the firmware and select LIC under battery type. Now the Dyness battery and inverter is communicating.
December 3, 20223 yr The "secondary CPU version" actually shows the version of SCC firmware, not display firmware. And it was display (including BMS) firmware that you needed updated. I do wish they'd fix that one. It's fixed with the phone app. Edited December 3, 20223 yr by Coulomb
May 10, 20233 yr my battery seems to have the same issue, despite my supposered 'newer' inverter, have the axpert 11KW, with a 4.8kw dyness battery, and have the comms cable installed. what would be the lowest cut-off voltage? have myne currently set on 47.0, yet the default setting is 45, which seems really low. I honestly don't mind the current setting, but just want to test the actual battery capacity out hence for one time i want to take it to like 10% of charge left. btw my CPU version's 57.04 and secondary CPU version's at 12.21, is this the latest?
May 11, 20233 yr 10 hours ago, ebrahim said: btw my CPU version's 57.04 and secondary CPU version's at 12.21, is this the latest? Your display (secondary) firmware is up to date, but there is a slightly later main firmware, 57.05: I'm still not totally convinced which is later, 57.05 or 57.61, but so far it looks like 57.61 was experimental, and some of the changes that they tried out there are gone again in 57.05. But that's just a slightly educated guess.
May 11, 20233 yr thanks so very much!:) do you think its worth updating or should i wait for a larger set of changes? also, what's the update process like?
May 11, 20233 yr 4 hours ago, ebrahim said: do you think its worth updating or should i wait for a larger set of changes? I think I would, since this version seemingly was sent to a forum reader specifically to address a known problem. Quote also, what's the update process like? As described in the firmware upgrade instructions.