RCT AXKING 5K48V with Dyness A48100 Battery

Featured Replies

Hi,

Can someone please help me with settings for an RCT-AXKING-5K48V inverter connected to a Dyness 4.8kWh. I believe my setting is correct as per the manual from Dyness but my problem is that on the Inverter screen the battery shows 100% but as soon as the utility drops my battery capacity drops to below 50% (Attached file 20220919.xls shows the data) On the Battery indicators it shows that it is full and does not go lower that 3 lights out of 5.

Product Information

Model Type: Stand alone

Topology: Transformerless

Main CPU Version: 00071.90

Secondary CPU Version: 00001.10

 

Parameter Set to

Charger source priority: Utility and Solar

Output source priority: Solar

AC input range: UPS

Battery type: User

Max. Charging Current: 50 A

Max. AC Charging current: 40A

Back to charge voltage: 49.0V

Back to discharge voltage: 54

Bulk charging voltage(C.V. voltage): 53.5V

Float charging voltage: 52.5V

Battery cut-off voltage: 47.5V

I have attached the battery parameters from the manual.

 

Assistance will be greatly appreciated.

image.png

image.png

image.png

20220919.xls

  • Author

@mzezmanThe other options I have there is AGM, Flooded and PYLON. It is connected through the coms port with network cable that was supplied with battery.

Only if the Dyness makes use of Pylontech RS485 communication protocol will it be compatible with the inverter. Otherwise USE settings will work but the appropriate other settings like Bulk, float, cut off & charge amps will need to be set in the inverter. 

29 minutes ago, MarkP said:

@mzezmanThe dip switches are set to 0100. Here is a short video clip  as well.

This battery looks alot like the Mecer M3000 ESS......... wonder if they operate the same way. Trying to get proper settings for older Axpert type inverters.

 

12 hours ago, MarkP said:

@mzezmanThe other options I have there is AGM, Flooded and PYLON. It is connected through the coms port with network cable that was supplied with battery.

The network cable won't be doing anything unless the inverter is set to PYL. The cable that came with the battery won't work either (it's for battery to battery comms), you may have been provided a battery cable with the inverter? If not you need to make up a custom cable with the dyness pinout. I think the dyness works just like a pylontech with the axpert, but I'm not 100% sure, there should be other posts about this on the forum.

13 hours ago, MarkP said:

the battery shows 100% but as soon as the utility drops my battery capacity drops to below 50%

The reason for this is that the axpert uses the battery cutoff and charge voltage settings to calculate the range of charge (0-100%). The problem is that the battery settles to a lower voltage than the charging voltages, so it appears to drop dramatically when the charging source is disconnected as the inverter works with voltage. The other reason it drops so dramatically is because it takes the cutoff voltage (47.5V) as 0%, but in actuality that is more than 20% SOC, so the range become smaller. If you change the cutoff setting to the same voltage that represents 0% SOC on the battery it would bring the two more in line with each other, but they will never be the same as the battery counts the current (A) going into the battery, but the inverter uses the voltage. The lights on the battery will always be the correct one though.

  • Author

@jumperThank you for the explanation. Helps a lot. Will play around with some settings. Just don't want to change settings that would effect the life expectancy of the battery.

  • 2 months later...
  • Author

I got the problem resolved working with the supplier. The problem was the firmware on the inverter. I had to update the firmware and select LIC under battery type. Now the Dyness battery and inverter is communicating.

The "secondary CPU version" actually shows the version of SCC firmware, not display firmware. And it was display (including BMS) firmware that you needed updated.

I do wish they'd fix that one. It's fixed with the phone app.

Edited by Coulomb

  • 3 months later...
  • 1 month later...

my battery seems to have the same issue, despite my supposered 'newer' inverter, have the axpert 11KW, with a 4.8kw dyness battery, and have the comms cable installed. what would be the lowest cut-off voltage? have myne currently set on 47.0, yet the default setting is 45, which seems really low. I honestly don't mind the current setting, but just want to test the actual battery capacity out hence for one time i want to take it to like 10% of charge left. btw my CPU version's 57.04 and secondary CPU version's at 12.21, is this the latest?

10 hours ago, ebrahim said:

btw my CPU version's 57.04 and secondary CPU version's at 12.21, is this the latest?

Your display (secondary) firmware is up to date, but there is a slightly later main firmware, 57.05:

I'm still not totally convinced which is later, 57.05 or 57.61, but so far it looks like 57.61 was experimental, and some of the changes that they tried out there are gone again in 57.05. But that's just a slightly educated guess.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.