September 20, 20223 yr Hello everyone, I have searched high and low for a solution to my problem but I cannot seem to find any real solution. I have a Kodak OG Plus 5.48 inverter, 9 solar panels and a Pylontech US3000 5kw battery. The inverter switches off randomly all the time (especially when the grid is off during loadshedding). The inverter never has a high load, it doesn't heat up or crank up in any way. It just switches off and never comes back on until I press the button on the battery. The most common error message is F56, which is apparently a problem with voltage. As I said, it's very random - sometimes there is 3 days without any issues, other days it switches off every 3mins. Any assistance will be greatly appreciated.
September 21, 20223 yr It sounds like the battery is shutting down, and not the inverter. Have you checked your power levels against the battery limits? Continuous Discharge Rate (Normal Use):1776 W Maximum Discharge Rate (5 Minutes):3552 W
September 21, 20223 yr Author 51 minutes ago, JustinSchoeman said: It sounds like the battery is shutting down, and not the inverter. Have you checked your power levels against the battery limits? Continuous Discharge Rate (Normal Use):1776 W Maximum Discharge Rate (5 Minutes):3552 W Hey Justin, thank you - that might be it. I am a complete newbie - how would I be able to test this?
September 21, 20223 yr Well, you could just try turning on loads while watching the battery current on the inverter. If the inverter 'switches off' with around 3.5kW of load, then that is probably your issue.
September 21, 20223 yr I don't know how well the pylontech maximum discharge rate is implemented. From anecdotes, I suspect that the BMS will shut down as soon as you exceed 37A. This event is possible with some base load and the fridge cycling on (due to the induction motor inrush current).
September 21, 20223 yr You need atleast 3 of those batteries to properly satisfy the inverters needs if there is no sunshine.
September 21, 20223 yr 20 hours ago, Rcab said: Pylontech US3000 5kw I'm not sure you will get that 5kw, I see they advertise it, but with an asterisk: "Deliver up to 5KW* with a single module (2.4KWh) – * please note this value is inverter/charger dependent, typically the maximum achieved value is 1.2kW per battery" They also don't specify which inverter that can be achieved with.
September 21, 20223 yr Might be totally unrelated, but I had a similar problem with a different inverter and battery. Turned out to be a problem with the BMS cable between the battery and inverter, such that the battery SOC reading on the inverter was different to the SOC level indicated on the LED's on the front panel of the battery. Maybe worth a sanity check to confirm that your battery is in fact going into load shedding with the charge level you think it's got.
September 21, 20223 yr 9 hours ago, P1000 said: I don't know how well the pylontech maximum discharge rate is implemented. From anecdotes, I suspect that the BMS will shut down as soon as you exceed 37A. This event is possible with some base load and the fridge cycling on (due to the induction motor inrush current). If one does not check what the base load is when a fridge cycles on there is a big chance that the 37A @ 48V will be exceeded as you mentioned even if just for 3 seconds. I would explore this area 1st when trying. If more than 1 fridge then this should be the reason.