Coulomb Posted January 10, 2020 Share Posted January 10, 2020 44 minutes ago, Chris Louw said: Am I correct to say this Axpert is fitted with a PWM charge controller . The 36Vdc min volt and 105 Vdc max volts . Yes. Other clues: the 50 A current limit (MPPT versions have 60 A, and since late 2015, 80 A), and the unusual main and secondary firmware version numbers. Chris Louw 1 Quote Link to comment Share on other sites More sharing options...
Rod Posted January 10, 2020 Share Posted January 10, 2020 Thanks Coulomb! Quote Link to comment Share on other sites More sharing options...
Rod Posted January 10, 2020 Share Posted January 10, 2020 I've started looking at the external and presume the PV must then be connected to the charger. If that's the case, then I lose the ability for solar energy running my house when there is excess power? Or can it still be configured to operate more or less like it does now with the built-in charging? Quote Link to comment Share on other sites More sharing options...
Coulomb Posted January 10, 2020 Share Posted January 10, 2020 1 hour ago, Rod said: presume the PV must then be connected to the charger. Yes. Quote If that's the case, then I lose the ability for solar energy running my house when there is excess power? No, there is really no major difference having the solar charger inside the same box or outside the box. When there is excess PV power available and you have a house load, it just takes the power from PV as before. When the battery is full and the solar charger is in float mode, a little energy may come out of the battery briefly, which reduces the battery voltage, which causes the solar charger to replenish it. This holds whether the solar charger is internal or external. You lose minor things. For example, when utility and solar charging at the same time, when using the internal charger, you can limit the total charge current to a value that is good for your battery life. With the external solar charger, the total charge current may exceed that value. But it's pretty rare to be utility and solar charging at the same time. Quote Link to comment Share on other sites More sharing options...
Rod Posted January 10, 2020 Share Posted January 10, 2020 great, thanks once again Coulomb! I'm off-grid, so excess charge current not an issue . Quote Link to comment Share on other sites More sharing options...
Unintentional Posted January 14, 2020 Share Posted January 14, 2020 On 2019/12/30 at 6:23 AM, Coulomb said: One factory firmware is available (74.40), and a patched version of this is in progress. Hi sir, We really appreciate your work on this. I'm on a PF1.0 with 145V SCC and no 64V option and would love to use your patched firmware. I'd be happy to help test where possible if you need a test subject. Thanks, Gareth Quote Link to comment Share on other sites More sharing options...
Calvin Posted June 30, 2020 Share Posted June 30, 2020 On 2019/12/30 at 6:23 AM, Coulomb said: One factory firmware is available (74.40), and a patched version of this is in progress. Hi @Coulomb, any progress on this? I am looking at buying an Axpert to use as a mains charger and really want to use your Dynamic Charge Control. If there is no patch yet for this model, is there another model (available in South Africa) that you would recommend? (Thanks for all the great work) Quote Link to comment Share on other sites More sharing options...
Coulomb Posted July 1, 2020 Share Posted July 1, 2020 10 hours ago, Calvin said: any progress on this? Yes, it was done weeks ago; I'm pretty sure I posted about it, but you must have missed it. Details here: patched firmware version 74.40e. Calvin 1 Quote Link to comment Share on other sites More sharing options...
Ibzampere Posted September 21, 2020 Share Posted September 21, 2020 Hi 2 years ago, I've buyed 2 axpert pf1, now I suspect there are two Chinese clones, I use the 2 inverters in paralel, but sometimes I have the problem that they switch to float to early, and the batteries are not full charged. Attached the sticker of the one inverter, do you recognise as an Axpert PF1? Can I upgrade it? Thanks a lot. Quote Link to comment Share on other sites More sharing options...
Bloubul7 Posted September 22, 2020 Share Posted September 22, 2020 16 hours ago, Ibzampere said: Hi 2 years ago, I've buyed 2 axpert pf1, now I suspect there are two Chinese clones, I use the 2 inverters in paralel, but sometimes I have the problem that they switch to float to early, and the batteries are not full charged. Attached the sticker of the one inverter, do you recognise as an Axpert PF1? Can I upgrade it? Thanks a lot. Based on your photo it looks like a genuine version. The problem with the premature float is a firmware related issue. You can use to the patched firmware from Coulomb and Webber to fix the premature float issue as well as to add some additional patches Quote Link to comment Share on other sites More sharing options...
Ibzampere Posted September 22, 2020 Share Posted September 22, 2020 1 hour ago, Bloubul7 said: Based on your photo it looks like a genuine version. The problem with the premature float is a firmware related issue. You can use to the patched firmware from Coulomb and Webber to fix the premature float issue as well as to add some additional patches Thanks a lot for your information. Now I'm using 2 weco 5,3k lifepo4 batteries, I'm a bit lost with diferents models and versions of firmware, I want to be sure abaut the firmware I need to use, I don't want brick the inversors, wich firmware must I use? Thanks a lot for your colaboration. Quote Link to comment Share on other sites More sharing options...
Coulomb Posted September 22, 2020 Share Posted September 22, 2020 3 hours ago, Ibzampere said: I'm a bit lost with diferents models and versions of firmware, I want to be sure abaut the firmware I need to use It depends on whether you have a 64 V model of a 58.4 V model. Check the range of e.g. setting 26. Fortunately, 64 V models have a different command to initiate flash updating, compared to 58.4 V models. If yours is 64 V, you will need patched firmware version 72.20e. If yours is a 58.4 V model, you will need patched firmware version 74.40e. Quote Link to comment Share on other sites More sharing options...
Ibzampere Posted September 22, 2020 Share Posted September 22, 2020 18 minutes ago, Coulomb said: It depends on whether you have a 64 V model of a 58.4 V model. Check the range of e.g. setting 26. Fortunately, 64 V models have a different command to initiate flash updating, compared to 58.4 V models. If yours is 64 V, you will need patched firmware version 72.20e. If yours is a 58.4 V model, you will need patched firmware version 74.40e. Thanks a lot, the 26 setting is up to 64v then I need the 72.20e... Quote Link to comment Share on other sites More sharing options...
viden82 Posted February 2, 2021 Share Posted February 2, 2021 Hello , i have 5048MS PF1 with firmware 74.10 and other 5048MS 64V with 72.40 . Are MPP SOLAR INVERTER firmware 72.40 and 74.10 compatible? Thanks with advance . Quote Link to comment Share on other sites More sharing options...
Coulomb Posted February 4, 2021 Share Posted February 4, 2021 On 2021/02/03 at 4:40 AM, viden82 said: I have 5048MS PF1 with firmware 74.10 and other 5048MS 64V with 72.40 . Are MPP SOLAR INVERTER firmware 72.40 and 74.10 compatible? Thanks with advance . No, 74.10 is a 58.4 V firmware, and that 72.40 (there are two, the other one much older) is a 64 V firmware. You can't parallel 64 V and non-64 V machines. The CAN packet data format is incompatible. With all the different models, it's difficult to parallel machines unless you plan for it up front, and preferably buy the machines at the same time. Unfortunately, life doesn't always work that way. Quote Link to comment Share on other sites More sharing options...
Salazah263 Posted August 11, 2021 Share Posted August 11, 2021 On 2019/12/30 at 6:23 AM, Coulomb said: One factory firmware is available (74.40), and a patched version of this is in progress. Was the 74.40 released and if so. May i have the link Quote Link to comment Share on other sites More sharing options...
Coulomb Posted August 12, 2021 Share Posted August 12, 2021 10 hours ago, Salazah263 said: Was the 74.40 released and if so. May i have the link As usual, it's available from the AEVA topic index, which leads to https://forums.aeva.asn.au/viewtopic.php?p=77943#p77943 That's for the patched firmware. If you want the factory firmware, it's probably in the file section of this forum, or alternatively after unzipping the patched firmware, delete dsp.hex and copy dsp_original.hex as dsp.hex. Salazah263 1 Quote Link to comment Share on other sites More sharing options...
Salazah263 Posted August 13, 2021 Share Posted August 13, 2021 Is the 74.40e compatible with this model. I have attached my unit. Sorry m new Quote Link to comment Share on other sites More sharing options...
Coulomb Posted August 13, 2021 Share Posted August 13, 2021 8 hours ago, Salazah263 said: Is the 74.40e compatible with this model. I have attached my unit. No, that's a 64 V model. But it's compatible with Patched Firmware version 72.20e, which has all the same features as 74.40e. Quote Link to comment Share on other sites More sharing options...
Otto2 Posted January 28, 2022 Share Posted January 28, 2022 Hi. What firmware should I update on this inverter. It still runs on 52.30 and where would I be able to find it. Quote Link to comment Share on other sites More sharing options...
Coulomb Posted January 29, 2022 Share Posted January 29, 2022 Have I replied to this before? Yours is a clone; you may not be able to update the firmware at all, and if you can, it might not work with original Voltronic firmware. They might have patched it to suit their copied design. You may be able to run factory firmware version 73.00 or patched firmware version 73.00e. Which flavour (LFP or lead-acid/other) of patched firmware depends on your battery. Both available from the links in this post: PIP-4048MS and PIP-5048MS inverters. Good luck. Quote Link to comment Share on other sites More sharing options...
wawiel Posted April 26, 2022 Share Posted April 26, 2022 It seams the current firmware version is LC1 72 70C What is the latest firmware version available? Where do I get it? How to I upgrade the firmware? (Instructions for dummies please) Quote Link to comment Share on other sites More sharing options...
Coulomb Posted April 27, 2022 Share Posted April 27, 2022 That's actually patched firmware copied by the clone manufacturer. The latest is 73.00 or 73.00e for patched (LFP or LC flavours). But note that many of the clones that come with 73.00e don't have a bootloader, so they can't be updated at all. One of the patches allows operation without a bootloader (as an unintended side effect, we don't encourage clones at all). Quote Link to comment Share on other sites More sharing options...