Svolt 106AH Battery Review (5.43kWh / 16 cells)

Featured Replies

  • Author
On 2023/12/12 at 4:03 PM, Vos001 said:

I have purchased 2 x 48v the problem I have is that the manual says 80% discharge is at 42v my batteries switch of at 48v can anyone tell me what I am doing wrong

except for that very impressed

@Vos001Are they the 5.09kWh or 5.42kWh batteries? What does it say on the front of the battery.

 

Which inverter are you using them with and do you have them working in Lithium mode with communication or have you set the voltages manually?

  • 2 weeks later...
  • Replies 71
  • Views 49.1k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • There is a diffrence between batt voltage ans Soc. Your battery is not been used i presume as the inverter is in bypass. Switch the utility in that feeds the inverter off at the breaker and discharge

  • Very good price.   One thing for everyone to keep in mind is that Svolt offer these batteries in a 15 cell version & a 16 cell version. When expanding to your battery bank, you alwa

  • What is the brand of your batteries? The connectors are all from China and they would vary a bit, however majority of batteries are assembled in China so it makes sense that the connectors would be sh

Posted Images

@PsyCLown Hi, Hope that you had good Christmas. I have 2x Svolt batteries that I purchased and a 5 Kw ECCO inverter.

I am using it as a standalone UPS and it is working great. I have been unable to get the BMS to work and currently using voltage setting. I do have the dipswitch 1 set for master on one battery.

Inverter Option 05 - battery type LI 2 supports PYLON US2000 but BMS does not connect so I would like to connect to the battery using RS232 and verify the protocol settings on the battery.

May I ask where you purchased the RS232 cable so I can give it a try with PBMStools.

Much appreciated

  • Author
On 2023/12/30 at 1:37 PM, MarkHoskings said:

@PsyCLown Hi, Hope that you had good Christmas. I have 2x Svolt batteries that I purchased and a 5 Kw ECCO inverter.

I am using it as a standalone UPS and it is working great. I have been unable to get the BMS to work and currently using voltage setting. I do have the dipswitch 1 set for master on one battery.

Inverter Option 05 - battery type LI 2 supports PYLON US2000 but BMS does not connect so I would like to connect to the battery using RS232 and verify the protocol settings on the battery.

May I ask where you purchased the RS232 cable so I can give it a try with PBMStools.

Much appreciated

By default it should be on Pylon, however settings for your inverter might be different.

 

The cable was gifted to me, it is a RS232 cable with a USB adapter.

  • 2 months later...

Hi,
Thanks for the information. I also have two of the 51.2 V LiFePO4 batteries. Lets call it Battery ONE and Battery TWO. Its a 48V system, I have connected this in parallel and is working fine.
I have a question. 

How to connect the network cable to the BMS panel of the inverter. Also there are RS485A, CAN, RS232, RS458B ports for SVOLT battery.

1) Where does the inverter to the Battery ONE connect to for Inverter to Battery communication?
 
2) Where does the  Battery ONE connect to Battery TWO for Battery to Battery communication?
 
May you please assist....🙏🏻🙏🏻🙏🏻

 

image.png

  • Author
22 hours ago, aju said:

Hi,
Thanks for the information. I also have two of the 51.2 V LiFePO4 batteries. Lets call it Battery ONE and Battery TWO. Its a 48V system, I have connected this in parallel and is working fine.
I have a question. 

How to connect the network cable to the BMS panel of the inverter. Also there are RS485A, CAN, RS232, RS458B ports for SVOLT battery.

1) Where does the inverter to the Battery ONE connect to for Inverter to Battery communication?
 
2) Where does the  Battery ONE connect to Battery TWO for Battery to Battery communication?
 
May you please assist....🙏🏻🙏🏻🙏🏻

 

image.png

@aju Which inverter are you connecting the Svolt batteries to?

 

For #2, it does show this info in the manual which comes with the batteries.

Otherwise I can take some photos tonight showing you with my batteries how to connect the batteries in parallel for BMS comms.

  • 3 weeks later...

@PsyCLownThanks for the write up. I also intend to purchase an S Volt battery though i am not in SA. My interest is in remote monitoring. Is the raspberry PI reporting reasonable SoC for the S Volt batteries?

  • Author
On 2024/04/03 at 8:08 AM, Mo Sali said:

Hi Payclown

What is the address & tel no for Svolt Johannesburg office?

I cannot seem to find this information anywhere 

thanks

Best would be to reach out to them via email, don't want to provide details which may be outdated.

[email protected] is the email I have for them

 

19 hours ago, CM21 said:

@PsyCLownThanks for the write up. I also intend to purchase an S Volt battery though i am not in SA. My interest is in remote monitoring. Is the raspberry PI reporting reasonable SoC for the S Volt batteries?

I monitor the SoC via my inverter in Home Assistant - so inverter integrates with Home Assistant (running on a RPI 4) and I can monitor SoC via the inverter.

I am sure there are other ways, but for me that is the easiest and its good enough.

On 2024/04/09 at 6:04 PM, CM21 said:

@PsyCLownThanks for the write up. I also intend to purchase an S Volt battery though i am not in SA. My interest is in remote monitoring. Is the raspberry PI reporting reasonable SoC for the S Volt batteries?

I have 2 setups with a Pi monitoring the batteries via the RS232 port (I just use a MAX2232 module to do the TTL<->RS232 level conversion, but the USB<->RS232 devices work great too), using https://github.com/Tertiush/bmspace. Works great, and goes into home assistant.

I've also gotten PBMSTools to work remotely with ser2net to read out the logs which was helpful. They're standard PACE BMS's though, so anything that talks to Hubble/Revov/SVolt (and many, many others) etc will work.

  • 2 weeks later...
On 2023/12/30 at 1:37 PM, MarkHoskings said:

@PsyCLown Hi, Hope that you had good Christmas. I have 2x Svolt batteries that I purchased and a 5 Kw ECCO inverter.

I am using it as a standalone UPS and it is working great. I have been unable to get the BMS to work and currently using voltage setting. I do have the dipswitch 1 set for master on one battery.

Inverter Option 05 - battery type LI 2 supports PYLON US2000 but BMS does not connect so I would like to connect to the battery using RS232 and verify the protocol settings on the battery.

May I ask where you purchased the RS232 cable so I can give it a try with PBMStools.

Much appreciated

@MarkHoskings what app are you using with the with the Ecco WiFi dongle? And is it only for monitoring or also can change some parameters (settings on the inverter)?

4 hours ago, MarkHoskings said:

 

Hi Rou

I used the app SmartESS and you can access it on the Web or your phone.

Both Web and APP allow you to make changes but I have not tried.

Too scared lol :).

image.thumb.png.fc9c3289aae3ee1ac3d3e64b92817036.pngimage.thumb.png.3177266ca34c62e63b9eb4ee4c03018e.png 
 

Thank you @MarkHoskings! And are you happy with your Ecco inverter, any issues or it works as you expected without issues. And how is the support if you have tried to use any.  I am considering buying the same and would appreciate some advice.

By the way, do you know of any WhatsApp (or Telegram; Viber etc.) support user group for Ecco?
Thanks!

 

Edited by Rou

Thank you @MarkHoskings! And are you happy with your Ecco inverter, any issues or it works as you expected without issues. And how is the support if you have tried to use any.  I am considering buying the same and would appreciate some advice. 

By the way, do you know of any WhatsApp (or Telegram; Viber etc.) support user group for Ecco?
Thanks!

@Rou I have had my ECCO inverter since September last year with no operational issues. The only issue I have is that I can't get the BMS to work to my SVolt batteries  no matter what I do. I have given up and stuck to voltage settings and all works well. I do find a drift with SOC on batteries but don't think that is related to the inverter. I just run batteries down every second month to get SOC back to normal on batteries. If I could go back in time I think I would have chosen the LuxPower as it is similar in pricing (a little more) and has a generator input which becomes a shlep with ECCO in that every time you want to charge the batteries with Generator, you need to go into setting and change the input. LuxPower seems to support more batteries and has better support from what I can find. ECCO is difficult to find much, just my opinion. Hope this helps in your choice.

@MarkHoskingsas a matter of interest, have you been in contact with the SVolt rep to ascertain if they have a CAN or RS485 protocol suggestion to get their BMS to communicate with the Ecco?  I suppose one would need to establish from the Ecco distributers what protocol they use.

1 hour ago, MarkHoskings said:

@Rou I have had my ECCO inverter since September last year with no operational issues. The only issue I have is that I can't get the BMS to work to my SVolt batteries  no matter what I do. I have given up and stuck to voltage settings and all works well. I do find a drift with SOC on batteries but don't think that is related to the inverter. I just run batteries down every second month to get SOC back to normal on batteries. If I could go back in time I think I would have chosen the LuxPower as it is similar in pricing (a little more) and has a generator input which becomes a shlep with ECCO in that every time you want to charge the batteries with Generator, you need to go into setting and change the input. LuxPower seems to support more batteries and has better support from what I can find. ECCO is difficult to find much, just my opinion. Hope this helps in your choice.

Thank you very much @MarkHoskings! I made 2 days ago the mistake already- bought the Ecco 5.5kw with SVolt 5.43KWH. But I have a communication with the BMS of the battery- one good thing :) Managed to set up the SmartESS to work and so far looks OK. Will see how it goes..

Edited by Rou
spelling

  • 2 weeks later...

Hello, I need some help please! I have a backup system ECCO 5.5KW with a SVOLT 5.43KWH battery just for only 2 weeks. The BMS is communicating with the inverter (under LI2 - Pylontech). All seems to be working well - the battery was staying at SOC= 99% until 3-4 days ago when I noticed that the battery went to 98%. Then after a day went to 97% and now it is at 96%. Yet it is permanently connected to the grid. One other thing I noticed is that despite the SOC goes down as percentage, the battery voltage stays at 56v.
What could cause the SOC percentage to drop like that while the battery voltage stays at 56v- could it be that the bms is doing some equalizing of the voltage cells and some recalibration.. Or is it the worst- faulty cell? Thank you!

Screenshot 2024-05-15 110754.png

Screenshot 2024-05-15 163401.png

Edited by Rou
add pics

52 minutes ago, Rou said:

Hello, I need some help please! I have a backup system ECCO 5.5KW with a SVOLT 5.43KWH battery just for only 2 weeks. The BMS is communicating with the inverter (under LI2 - Pylontech). All seems to be working well - the battery was staying at SOC= 99% until 3-4 days ago when I noticed that the battery went to 98%. Then after a day went to 97% and now it is at 96%. Yet it is permanently connected to the grid. One other thing I noticed is that despite the SOC goes down as percentage, the battery voltage stays at 56v.
What could cause the SOC percentage to drop like that while the battery voltage stays at 56v- could it be that the bms is doing some equalizing of the voltage cells and some recalibration.. Or is it the worst- faulty cell? Thank you!

Screenshot 2024-05-15 110754.png

Screenshot 2024-05-15 163401.png

There is a diffrence between batt voltage ans Soc. Your battery is not been used i presume as the inverter is in bypass. Switch the utility in that feeds the inverter off at the breaker and discharge the battery to 50% soc switch the breaker on and let the battery charge. That should reset the soc back to 100% or 99%.

Edited by TaliaB

@TaliaB thank you! I actually discharged yesterday the battery but to 75% and then switched the feed on again and it charged it to 97% and that's whare it stopped. Today around lunchtime it dropped to 96%, yet it was all the time connected to the grid to charge..
I will follow your advise to discharge it to 50% and then will switch On to charge it. Hope that will make difference. 

  • 5 weeks later...
  • 2 weeks later...
  • Author
On 2024/06/15 at 1:41 PM, CM21 said:

@PsyCLown I wanted to find out something before i buy. There are units currently being sold which dont have BMS communication with inverters. Any work around such?

I think you are referring to some of the 24v Svolt batteries, they have a BMS but there is no BMS communication.


I am not aware of any work around, other than possibly trying to replace that BMS with a different BMS - I do not think it is worth the effort and cost though. You'd also void your warranty if you were to do this.

On 2024/05/15 at 4:38 PM, Rou said:

 All seems to be working well - the battery was staying at SOC= 99% until 3-4 days ago when I noticed that the battery went to 98%. Then after a day went to 97% and now it is at 96%. Yet it is permanently connected to the grid. One other thing I noticed is that despite the SOC goes down as percentage, the battery voltage stays at 56v.
What could cause the SOC percentage to drop like that while the battery voltage stays at 56v- 

 

 

As it affects the durability of a battery sitting at 100% and not used many BMS will discharge as soon as it hits 100%. Not saying it is in your case. 

As per the reply from @TaliaB discharge to 50% and check again.

1% is only 150Wh of over 5400.

Don't worry to much about it. My own view. 

On 2024/05/15 at 4:38 PM, Rou said:

ECCO 5.5KW

What is strange on the display next to the battery icon it states"Li"for lithuim as far as i know in program 5 there is only 3 battery type settings Agm Flooded and Use, what is program 5 set to? There is no bms comms so  the inverter should be set to "Use"( program 5) then you can set bulk charging voltage to 56v. ( Program  26) and float charging 54.4v(program 27).

Because you do not have bms comms to the inverter it could be the inverter is interpreting the Soc incorrectly. 56v is a full battery i won't worry to much about the Soc displayed by the inverter. If you want an accurate Soc you can fit a Victron Smart Shunt.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.