Essential loads not stable sunsynk SUN-5K-SG01LP1-EU inverter

Featured Replies

When the grid loadshed them my essentials load output dips just enough to reset my servers. I have a sunsynk SUN-5K-SG01LP1-EU inverter.

 

Is there away to keep the essentials load output on regardless if its getting power from the grid, solar or batteries? 

My load is constant 4.8kwh and I have 4 pylontech 3000c. 

If I add the ups back on the servers then my load is more than 5kwh so the inverter throws an AC overload and shutdown. 

I suspect the dip is as the grid disappears the voltage dips until the relay opens. There will probably always be a very short dip. It will be interesting to note if others have been able to elimiate or reduce this dip. I notice it on the LED lights every time load shedding kicks in.

There's the rub, the Sunsynk does not switch to mains, and then switch to batteries / solar. It seemlessly blends to lot. The downside is when the grid goes down, it needs to open the relay that connects the UPS to the grid. In that moment it seems to dip for a short while. The dip is visible on my lights that run on the UPS output but we're fortunate that none of our appliances seem to care.

image.png.ba6bc00869273ce7174ff439bcc53370.png

My thinking is that the grid goes down and pulls the AC voltage down throughput the entire inverter until it detects and opens the AC relay that goes to grid. Looking at this block diagram I don't see how it can open fast enough to not have a short dip on all outputs. Notice there is no changover relay. Perhaps the grid voltage low (brownout voltage) can be set more aggressively so it cuts out sooner. Mine is set to 185V from the factory. Worth a try perhaps. 

  • Author
2 hours ago, Speedster said:

Why not move it load?

Where? It's on the essentials output. Where should I move it? 

I noticed that if I reduced the load to 2.5kwh then the servers don't resets. But obviously I can do this when I have running work. 

  • Author

I ment I can't reduce the load all the time 

And ssh in to the servers at 4am is also not very conducive to long term parter relationships 

2 hours ago, HannesZ said:

Where? It's on the essentials output. Where should I move it? 

I noticed that if I reduced the load to 2.5kwh then the servers don't resets. But obviously I can do this when I have running work. 

Apologies. I somehow read non-essential 🙈

  • Author

Yes. I was tols that to run the multi they need to be the same model. I was planning to do this next year or closer to the end of winter but seems like they forced my hand

  • Author

sunsynk updated the firmware of the inverter. Im hoping this solves the dip issue. 

If not Im thinking i can run a 750w Single phase AC motor driving a flywheel to store power for the switch over. Im just not sure if it will damage the inverter essential output. 

47 minutes ago, HannesZ said:

sunsynk updated the firmware of the inverter. Im hoping this solves the dip issue. 

If not Im thinking i can run a 750w Single phase AC motor driving a flywheel to store power for the switch over. Im just not sure if it will damage the inverter essential output. 

what version number did they update it to?

  • Author

well i don't know if its better but my servers still reboots. Talking to the tech it seems it is due to the soft start of the DC to AC converter. in retrospect I should most likely not have gone for this type of inverter.

Edited by HannesZ

  • Author

I added back the UPS on each which expect 230v so they don't bypass when the sunsynk runs. Resulting in a 5%-10% loss. Add the charging and I am over the output of the sunsynk. 

Edited by HannesZ

5 hours ago, HannesZ said:

I added back the UPS on each which expect 230v so they don't bypass when the sunsynk runs. Resulting in a 5%-10% loss. Add the charging and I am over the output of the sunsynk. 

What do you mean by over the output?

8 hours ago, HannesZ said:

well i don't know if its better but my servers still reboots. Talking to the tech it seems it is due to the soft start of the DC to AC converter. in retrospect I should most likely not have gone for this type of inverter.

 

I'm pretty sure you've undersized your inverter for your use case.

 

In addition to my whole houses load, I have four computers, two of which could be classified as a "server", on the essential load side of my 8kW Deye inverter and I don't experience any "turn offs" or "restarts" when Eskom power disappears.

Edited by excitedphoton

32 minutes ago, excitedphoton said:

 

I'm pretty sure you've undersized your inverter for your use case.

 

In addition to my whole houses load, I have four computers, two of which could be classified as a "server", on the essential load side of my 8kW Deye inverter and I don't experience any "turn offs" or "restarts" when Eskom power disappears.

Yeah, this makes the most sense. Parallel another 5kW Sunsynk onto the existing one.

  • Author

I can't really fualt sunsynk. It's operating as designed. Just sad as I measured the load without the ups and at 4.8kw it was comfortably under the constant limit. I did not take in to consideration the effect of the soft start after change over. Obviously the inverter is not fit for this usecase but I'm now so deep down the rabbit hole there is no return. 

Adding a second sunsynk would also give me the option to expand my solar array. 

 

1 minute ago, HannesZ said:

I can't really fualt sunsynk. It's operating as designed. Just sad as I measured the load without the ups and at 4.8kw it was comfortably under the constant limit. I did not take in to consideration the effect of the soft start after change over. Obviously the inverter is not fit for this usecase but I'm now so deep down the rabbit hole there is no return. 

Adding a second sunsynk would also give me the option to expand my solar array. 

 

Good luck, keep us posted.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.