RCT 5KVA and Lithium battery settings
-
RCT 5KVA and Lithium battery settings
@Ockie OlivierThis is what my battery voltages is for the last 3 hours.This should give you a idea of what you can expect.You can see the voltage drop when the sun goes down. It is nearly 8pm and the batteries is 97% and 49.8v.
-
RCT 5KVA and Lithium battery settings
@Ockie OlivierThe Best is to measure the battery with a multimeter when the error starts. With setting 29 set to 46v the error 4 will start when the battery reaches 48v . This is to check if the Inverter or battery is faulty. Even if your battery is at 49v and should you boil a kettle and a fridge starts up the battery would be pulled down to 48v for a second and the error will start. The error will then stay until the battery gets to 50v before it will reset . I run 3 x Pylontech 3000 for nearly 5 years and this does happen to me sometimes as well. There is 2 ways to get rid of this . Set 29 a bit lower 45.5v or get @ Coulomb kettle comp software . The software alows for more voltage drop before error 4 starts . I believe set at 46v the error will then start at 47v . I will recommend that you adjust setting 13 to 51v and leave 12 at 48v .
-
RCT 5KVA and Lithium battery settings
@Ockie Olivier If you run the batteries on User setting 5 you must change setting no 26 to 52.5v and no 27 to 52.0 v. This is what most of us use . Charging the battery at 56.4v will damage your batteries
-
Trying to better understand the premature float bug and possible solutions
@Coulomb Thank you for your time to explain how the premature float bug affects charging of batteries. There is still something I wonder about. Pylontech batteries do not use a float setting in their Standard operating practice for Axpert inverters. Only bulk/absorb is selected. Will it affect the battery life if 26 and 27 is set the same voltage.
-
Svolt 48v 106Ah 5.09kWh LiFePO4 battery
-
Svolt 48v 106Ah 5.09kWh LiFePO4 battery
You can get the info from the battery display . Select analog info enter -Packv -press down until cell voltage . Pres enter -pres down 3 times see if it is 15 or 16 .
-
Svolt 48v 106Ah 5.09kWh LiFePO4 battery
The resting voltage should be 3.4v per cell . 15 cell 51v . The inverter load can pull it down to 50v .
-
Svolt 106AH Battery Review (5.43kWh / 16 cells)
- SVOLT 48V 106AH 5.09 KWH Low Voltage
No firmware update is needed. Just change the charge settings on the inverter. How many OVP dit you have. My OVP warnings stop after I lowered the battery charging. I lowered the charge voltage just after installation because of OPV warning. The new recomendated voltages only came later .The battery cells stay within 10mv from 40 % SOC to 100% SOC.- SVOLT 48V 106AH 5.09 KWH Low Voltage
@TaliaB the SVolt BMS stops charging when the fullpack settings is reached. This does affects the SOC.- SVOLT 48V 106AH 5.09 KWH Low Voltage
@WannabeSolarSparky I have a 24v so 8cell. The balacing start at 3.45v that is why I assumed 3.5V would be OK. Thank you for the details.- SVOLT 48V 106AH 5.09 KWH Low Voltage
A good top balance will it be 3.5 V per cell.- Using square mm on Android
Thanks @TaliaB and @Scorp007 now I can also do ½ , 10⁰C and 18²- S-Volt lifepo4 battery
- AXPERT 5KVA ERROR CODES
Code 13 is a Warning indicator. Solar charger stops due to high PV voltage. Maximum voltage should be on the sticker on the side of the inverter. What PV voltage is displayed on the display panel.- Over voltage problem with Voltronic Axpert IV (5600W) inverter
- Over voltage problem with Voltronic Axpert IV (5600W) inverter
The installation specifications : Max. PV Array voltage Open Circuit Voltage should never not be exceeded. If the voltage does exceed the max voltage your inverter is not safe. I would remove a panel as was suggested .I dont have the knowledge of the components of the inverter to give advise. If it was my installation and the voltage was within specifications I would swop the wires of the arrays to check if the inverter is faulty.- Over voltage problem with Voltronic Axpert IV (5600W) inverter
Measures the voltage at the circuitbreaker supplying the MPPT. If the reading is to high the MPPT cannot bring it down. This overvoltage will damage the MPPT. It is normal for the voltage to rise to Open circuit voltage of the panels if the battery is full. No current is taken from the panels If the battery is full. When battery is charging current is draw and the voltage go down.- Axpert Max II 11kW with second battery charger
- Astute Smart Controller (ASC) combined with ACDC contactor to control 200L geyser
The device does have a Device Restart Status that can be set.- Do I change or add on?
What do you have to do if the inverter is changed from a low voltage MPPT to the new high one voltage. Can the strings be changed from parallel to series at the combinerbox or do you rewire the lot.- Mercer Axpert Max 8kw inverter issue 69
@Danie834 The BMS has a config page where you must select the Inverter brand connected to the S-volt battery. Was this done. You can also contact S-volt South Africa.- Mercer Axpert Max 8kw inverter issue 69
Hi Danie I dont know the Max 8kW. I am using a old 5kW inverter. There is no Rs 485 cable to the battery. The battery settings of the Axpert is set on User. The charging settings is done on the inverter. I have set the Pack full charge voltage and pack fullcharge current setting on the BMS using the PbmsTools HS1.0.6 download. The battery charges normal and Amps taper off when full and stop charging. All this is controlled by the BMS .The display on the battery - BMS will display - Full. I have a 24v battery so use the specs I sent.The BMS will stop charging a minute or 2 after reaching the settings. Use the interface Definition for the Rs485 cable.- EASUN inverter adding a separate MPPT
- SVOLT 48V 106AH 5.09 KWH Low Voltage