Recommend approach to expand solar input power on Deye 8.8.
What is your peak current draw from the battery? If you are hitting close to 7 or 8kW during peak periods you could set the power limit to for argument's sake 4-5kW at night. This might help to compensate for a deeper discharge, if you treat it more like a 0.25C battery. Basically, you're going to run out of power overnight anyway, may as well do it slowly and go easy on your batteries.
-
Victron and Lithium
If it's a choice between the AM-5 and AM-2, then the AM5. Out of the other batteries that are on the Victron inverter compatibility list, the Dyness seems to be a good value option to investigate if the intention is to buy multiple batteries to build up a bigger bank. Not saying it's the best or that others are not compatible, just that Dyness is listed by Victron as compatible (according to their website), and that prices seem to be among the best currently for 5kWh and 10kWh lithium batteries of a "recognized" brand name.
-
No of strings MPP Tracker 2+1
The strings should have the same Voltage (or very close) to place them in parallel, ie. you could do two strings of 8 in parallel on the 1st MPPT with 2 inputs, and put the other 7 panels on the single-input MPPT. But not mix a string of 8 and 7 in parallel. If the panels are facing generally in the same direction it should be fine, and a 2-degree difference in angle will not make a significant difference to the panel Voltage. Otherwise drop a panel and put 7+7 in parallel on the roof if in doubt.
-
Battery vs grid storage
I just don't know where in SA this is still permitted, assuming you are locally-based. More common around here is some fixed portion, asymmetrical crediting, and/or TOU. But technically the export to grid is more efficient than storage, if you just ensure to still run your batteries down regularly, don't keep it at 100% permanently.
-
Battery vs grid storage
Not enough info I think to give a definitive answer. Pushing back to the grid is not storage, it's trading with the power utility. Whether it makes financial sense depends on the terms and conditions in your location, but energy efficiency is good. Battery storage efficiency depends on your batteries and inverter, and number of conversion stages before the battery.
-
Deye vs Victron + Fronius
Maybe bear the specs in mind. I think the Victron is 5kVA as opposed to 5kW, with only 4kW real power rating. On the other hand the pass-through of 50A is quite good compared to the Deye's 32A or thereabouts. Also with the low-frequency vs high-frequency design, also the AC-coupling vs DC coupling conversion to storage, it's not a straight 1-to-1 comparison. Your application could be a deciding factor.
-
When do you think loadshedding will come back?
I would have expected to see a shift in the marketing approach, ie. fewer ads promoting the product, technical specs, price and the loadshedding benefits, and more ads evaluating the investment case, electricity per-unit savings, payback period, projected Eskom increases, etc. Perhaps some attractive finance options to make the decision easier? Am I just looking in the wrong places?
-
Solar Geyser Problems (Thermosyphon system) Advice would be greatly appreciated.
Do you have non-return valves installed that could prevent a reverse-flow thermosiphon from being set up? Can't make it out on the images.
-
New SOLAR adopter
Something else is happening here. You're showing in 2022 you were averaging 44.6kWh per day, and now 12.313kWh per day. This drop in consumption cannot be explained by 4x550w panels, especially in Winter. Those panels would generate approx 10-12kWh per day on average during the year, and less this time of the year. Could it be that you just became more frugal?
-
Sunsynk Setting Intepretation Input
I think you have the gist of it, though you might struggle to do solar charging at midnight.
-
5Kw Sunsynk Hybrid - Geyser
Repeating a bit of the above. Okay, so this is looks to be the main source of your issues, that your battery is the limiting factor of your power output. You could double up with a second battery so that you can make better use of the total 5kW power capacity of your inverter during loadshedding. It's very easy to exceed the 2.5kW limit of one battery, the geyser alone will do it, but it could be as simple as a kettle and a toaster together to trip your house. It's still not a good idea though to let your geyser chow through your battery capacity. It is better to connect your geyser as a non-essential load, so that when power goes off, that the geyser also switches off. The other alternative is to put your geyser on as a Smart Load, so that you could run the geyser as long as there is sufficient sunlight/solar power, but if that drops away, and the battery gets too low, the geyser will then again switch off. To find an installer, maybe ask directly to @Powerforum Store for the guys that usually work in your area. Some usernames come to mind, but I'm not sure who works where. Might also be a fair choice to use your first installer. Doesn't look like he's done anything obviously technically wrong except fit a system in a configuration that doesn't meet your needs or expectations.
-
5Kw Sunsynk Hybrid - Geyser
Can you confirm what battery(s) and battery settings you're using? The graph doesn't show the geyser or any loads exceeding the inverter's rated capacity of 5kW, and it also doesn't show the battery ever exceeding around 3kW output. Could still be anything else, but I just want to eliminate one of the obvious possibilities like a 0.5C discharge rate.
-
SunSynk Batteries: Cable and Fuse Sizing
Thanks @TaliaB, was not aware, and I humbly stand corrected/educated.
-
SunSynk Batteries: Cable and Fuse Sizing
My 2c' worth. I'm going to see it the other way around, and start with the maximum charge and discharge currents on the inverter. For the 5kW inverter it's I think 115A, and on the 8kW inverter it's 190A, so it's based on the power ratings of the inverter at approx 48V. So under normal operation except for transient surges you should not be exceeding that Amp value significantly, and accordingly they've specified the fuse rating at 150A and 250A respectively, with wiring sizes to match. No matter how much battery capacity you install, for me it's the inverter and its rated power that should dictate the maximum discharge limit in the event of a fault, even if the batteries could comfortably push out more current. The magnetic ring you're referring to - if you mean the CT coil - is not intended to be fitted to a battery cable. It must go onto the incoming AC mains wiring. I think you need to re-read that section of the manual carefully.
-
Bypass mode always on (connected to grid)
What is your battery Voltage at the time of testing? Possibly below the value in Setting 12, ie. 24V "back to utility" Voltage? Considering you may have discharged to 21V cut-of Voltage overnight.
-
Sunsynk 16kw single phase inverter running hot.
Agreement, as above, to create clearance on the sides and behind the inverter for airflow. Battery cables away, maybe against the side walls, and the inverter better centralised in the cabinet. Is the airflow upwards? I'm assuming the inverter's cooling fans move air upwards. If so, I would add, to move the surface-mount DB's away also, ie. possibly against the side walls of the cabinet also, else maybe on the other side of the wall? Regarding the vents, to have two, the lower vent to allow cooler air INTO the cabinet, and an upper vent to remove warm air FROM the cabinet back into the next room. Don't create suction below the inverter. Keep cables from obstructing the space just before the vents. No guarantee this will work to keep the inverter inside the cabinet. Best maybe just to move it after all.
-
30 panel installation ideas
Tending to like the idea of a hybrid as well. From the point of view, for the amount of power, 30 panels, so let's call it 15kW-16kW, I'm struggling to find a suitably-sized Solis inverter that's single-phase. By the time one's bought three of the 4.6kW grid-tieds to connect in parallel, you're virtually in the price territory to start looking for bargains on the 16kW Deye or maybe an over-panelled 12kW.
-
Recommend approach to expand solar input power on Deye 8.8.
See if you can get this panel from Herholdts: JAM72S20 445-470 MR 35边框 (herholdts.co.za) JA Solar (herholdts.co.za) The specs are much closer to your original panel, and I think the pricing is reasonable. Pmax=460W, Vmp=42.13V. Imp=10.92A, Voc=50.01V, Isc=11.45A That gives you some better confidence to be able to mix strings if you must, but still try to keep one type of panel on one MPPT in a balanced number of panels in parallel pointed in one direction if you can. It's not a problem if Isc exceeds your maximum operating current. The Isc limit is much higher for that inverter.
-
Temperature Effect on MPPT Voltage
Thanks. If I may ask, what's the nominal Voc and Vmp based on the panel spec sheet for your string? I guess the values at 25 degrees, and based on STC and/or NOCT, before doing temperature adjustments? Trying to get a sense whether the temperature issue is overblown for our SA conditions. I mean, will you ever get a case where the daytime temperatures hover around freezing, and the sun then emerges behind a cloud at noon? Sutherland's looking promising for the week, but I don't expect a massive wave of inverters failing coming from that area.
-
Temperature Effect on MPPT Voltage
One of the recurring solar topics here is what the impact is of temperature on MPPT Voltage, and choosing your panels' Voc with some spare gap in theory to the inverter's maximum input limit. I'm just wondering whether the current cold snap could bring a surge of failures in some parts of SA. For example, Johannesburg's forecast for Tuesday morning is showing freezing temperatures overnight, with early morning sunshine around 7am-9am. Are there any folks around those areas with longer strings of around 450Voc that could share their real Voltage measurements and/or experience in these conditions?
-
Deye - "Zero Export To CT" Reduces Power & Load Values
Put in the CT coil, even if you think you won't need it now. It will allow the inverter to send battery power to the non-essential loads as long as the grid is present. So if you can buy cheaply at night and reduce dependence on the grid even if it is there. Zero Export to Load is all you need for now, but that might change. Energy pattern generally set to "battery priority" but actually doesn't really matter until you get solar panels. Grid peak shaving doesn't make sense to use. Your problem is not that you have a low-power rated supply line, your problem is that you sometimes don't have any power at all. Don't use this function, or set it to a high value, so that as long as the grid is available you will draw as much as you need and not let the inverter place a limit on what it will take from grid. It might still make sense to use the timer if you set all time slots day and night to 100%, but only tick the grid-charge boxes against the cheaper time slots at night. That way you will reduce the amount of cycles from the battery, discharge it deeper during the day before recharging at night. To be weighed up against the risk of running out of power before night falls, and depends on your usage. Which is to say, it will only discharge during grid outages, but not discharge any further once the grid comes on again.
-
Deye - "Zero Export To CT" Reduces Power & Load Values
In South African terms, that's something like Stage 8 loadshedding or worse, which is tough, but the inverter will make a massive difference. It's going to be tricky to find one timer setting that works for all days of the week but you'll figure something out with experience. The other thing is that there's an app for push notifications of changes in the loadshedding slots. In South Africa one of the more popular loadshedding schedule apps is called "Eskom Se Push." Maybe they could extend into your country, or someone could come up with something similar that is tailored to your situation. Something like "Pushkin se Push"
-
Deye - "Zero Export To CT" Reduces Power & Load Values
Honestly in this type of scenario I wouldn't even use the timer. Just turn it off, then the system will run as a normal UPS. If you are not generating solar power to store in the batteries, if your only source of power is the grid itself, there is really no point to keep cycling the battery when the grid is available. That just wastes energy and uses up your battery cycles unnecessarily. You want to keep the energy on-hand for when the grid goes down, so just put your essential devices on the backup load port, and operate in Zero Export to Load mode. When the grid is on, the pass-through limit is the maximum that can be supplied to the backup loads, and when the grid goes down, the inverter's rated power is the maximum power that can be supplied from battery. Also, if you keep it in UPS mode without the timer, you don't need to think about setting a time slot when to charge from grid, it will simply re-charge automatically once the grid returns. I would suggest to limit the charge rate to maybe 40A-50A so you don't contribute to overloading the grid once power is restored.
-
DEYE Hybrid installation/mode advice! SUN-12k-SG04LP3-EU
First point, your inverter can be set up to do almost anything you'd need, so no need to think you made a mistake. Just looks like some info has gone lost in communication, or your needs and knowledge not fully understood. But I don't think that in principle your situation is truly unique. Second point, it's noted that you already understand the importance of placing the CT coils correctly, you can follow the manual, you know how to set up the 3 x 3-phase inverters in parallel, with incoming grid power onto the grid port of the inverters. Third point, you NEVER want to export any power to your grid, so you will NOT select the "Selling First" work mode, and you will NEVER tick either of the "Solar Sell" boxes. If you are very determined on this requirement, you should set the "Zero Export Power" function to a reasonably high value. The manual suggests 20-100W for normal operation, but if your utility is extremely strict, you should try the highest value or higher if needs be. This is the minimum amount of Watts you will always draw from the grid, thereby reducing the chance that a fluctuating power demand/supply balance could send a small burst of power back to the grid. Fourth point I don't fully understand, is whether your intention is to back up the entire house and distillery by the battery, or just one or the other? Basically, is your grid stable, or are you worried about your national grid failing in the middle of a heating/brewing process? Is it okay if the distillery is considered a non-essential load that shuts down during a power outage, so that you only supply your house with power? I think you are putting just the house on the backup load port, and the distillery on the non-essential grid output, but I'm not sure. If this is correct, you should use the "Zero Export to CT" function. In the event of a power outage, you do not need a mechanical switch. The Load Port remains automatically backed up by battery, and can use solar power as first option when available. The question that remains - and here's a pep talk for you to do a bit more reading - is how precisely you want to control the usage of solar and battery power to supply the loads. If you do nothing else, your inverter will run as a UPS, basically keeping the batteries charged, using solar power, then utility, and then battery backup. You need to read more on the Time-of-Use function, and then if you have any more detailed questions from that, feel free.
-
Need more panels no MPPT's
As above, panel specs and MPPT specs to be confirmed. But I think another avenue to investigate is to transfer your 4x450W panels onto the Hoymiles micro-inverter on the AUX input. Then get 4 more of your exact 550W panels, such that you connect two strings of 6 of them onto MPPT1 and MPPT2, either both to the East, which would be easier to connect, or else transfer two of the panels to the West.. That's just taken from a quick search on the Voltage and current specs for the inverter, as well as for some 450W panels. Bottom line, I think you'll find the input current of 4x11.5A to be a motivation to rather use smaller panels on the Hoymiles. Whether it's a good idea to go East/West depends on when you mostly run your loads, but in general spreading power generation through the day is sensible. eg. Battery recharge in the morning, and Geyser in the afternoon makes sense to produce hot water just shortly before evening sets in. Also spreads risk of losing generation through cloud cover throughout the day. And it means you are less likely to see a time when your total generation from MPPT1 and MPPT2 exceeds 5000W at once, since if you don't have batteries to charge at that time, the output will be cut to just the rated 5000W anyway.