PylonTech US3000C Battery Produces No Output , Accepts No Charge

Featured Replies

Hi @PurePower, @Youda and PylonTech experts , I have a problem with US3000C remaining in 'Idle' mode. I have no experience or knowledge of Pylon batteries. The site it belongs to has 3 of these in parallel . A couple of days ago one of 2 Axpert Kings connected to this pack had an MPPT failure. The owner  informed me that the battery pack went dormant after that , but without an error (alarm). When I visited the site the batteries had no problem to switch on and reset , and all of them had the green led flashing  once every 4 seconds or so .  No red alarm . However ,  the packs gave no voltage output on battery terminals. I isolated batteries and also tested them as standalone (no link port connections) , but still nothing.

I revisited the site today , this time armed with a console RS232 cable and BatteryView version 3.0.28 , and a 60V variable power supply .  Fortunately my homebrewed cable connected successfully and I was able to extract info from the individual batteries .

image.thumb.png.b0d009c094d68d36cdf592c5ae6a6bd8.png

The state  is "IDLE" (not shown in the image")  , but as you can see there is no protection alarms . The batteries are brand new.

image.thumb.png.9e324c8128f170a6afab5c7efb61c785.png

 

below is additional info , which indicates no error code , cycle count only 2.

image.thumb.png.4f7d851c5ca092b467c8601b198e3731.png

 

I went so far as to connect a 51V power supply to the terminals , to see if it would accept charge , but nothing.

So as you can see everything looks pretty normal , the cells are well balanced. But I get no output from any of these 3 packs.

Any help or pointers to what I can attempt next would be highly appreciated.

Kind Regards

 

  • Replies 112
  • Views 19.1k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • BritishRacingGreen
    BritishRacingGreen

    Ah, vultures circling very early already😁😁

  • This is spot on! The module experienced a high voltage as it reached 100%. Looks like the MPPT charge controller did not manage to drop the voltage to the pack and this more than likely popped the fus

  • Hi @BritishRacingGreen 1) First of all - if the US3000C is running and the RUN led is slowly blinking, then the battery should be supplying 48V to the output terminals. There's no need to connect

Posted Images

Hi @BritishRacingGreen

1) First of all - if the US3000C is running and the RUN led is slowly blinking, then the battery should be supplying 48V to the output terminals. There's no need to connect the communication cables etc.

2) Just grab a voltmeter and check the terminals. Beware that the SurLok terminals have plastic-insulated pins. Therefore you have to touch the side of the pin, not the tip. Like this:

image.thumb.png.66fdadf2250bb98ef98124ae58611e04.png

3) Test each battery, one by one.

4) The screenshots that you've provided in the first post show that all the usual suspects are okay:
- BMS OK
- Cells OK
- Temperature OK

 

So, if there's no voltage on the terminals then the internal fuse (or precharge circuit) has blown.

Even the manual is clear on this:

image.png.94167e3d77b44973910cbef614af5973.png

 

BTW:
Reliable Pylontech distributors have some spare BMS boards on stock and are experienced with flashing firmware or swapping the boards as these batteries are being sold in thousands. So the repair should not take ages. And in this particular case it really might be just the fuse.

  • Author
11 hours ago, Youda said:

Hi @BritishRacingGreen

1) First of all - if the US3000C is running and the RUN led is slowly blinking, then the battery should be supplying 48V to the output terminals. There's no need to connect the communication cables etc.

2) Just grab a voltmeter and check the terminals. Beware that the SurLok terminals have plastic-insulated pins. Therefore you have to touch the side of the pin, not the tip. Like this:

image.thumb.png.66fdadf2250bb98ef98124ae58611e04.png

3) Test each battery, one by one.

4) The screenshots that you've provided in the first post show that all the usual suspects are okay:
- BMS OK
- Cells OK
- Temperature OK

 

So, if there's no voltage on the terminals then the internal fuse (or precharge circuit) has blown.

Even the manual is clear on this:

image.png.94167e3d77b44973910cbef614af5973.png

 

BTW:
Reliable Pylontech distributors have some spare BMS boards on stock and are experienced with flashing firmware or swapping the boards as these batteries are being sold in thousands. So the repair should not take ages. And in this particular case it really might be just the fuse.

Hi @Youda, thanks, I have focused on proper connection. I have, example set a 50V supply on one set of terminals, and check meter output one the other terminals, in order to verify.

So far, with you and others feedback, it looks indeed like a blown intetnal fuse. I have brought this to the attention of owner, and he will negotiate with supplier/agent to what extent we can verify this on site. 

 

  • Author

Hi @John, @PurePower, @Youda  , I had a third visit to site and managed to non-intrusively gain access to the inside the battery box . The image below of BMS refers.

image.png.29024552c27973ffed9b014d0ba59bb7.png

I measured negative 50V at points 1,2.3,5 and 6. Nothing at 7.    I deducted the following simplified schematic as seen below :

EDIT : please note that the orientation of my CFET is wrong , it should be mirrored horizontally:

image.png.178f96ab5ae353ef0004906be95c9720.png

The readings inferred that both  CFET (ChargeMOSfet) and DFET (DischargeMOSfet)  had been turned on (there was no forward voltage drops from the body diodes inside the mosfets). Please note that the components are actually duplicated in parallel , eg. there are 8 cfets,8dfets,8 sets of fuses.

There was no reading on 7 , which inferred the second fuse array had blown. This is an interesting fuse in that it has 4 pins instead of 2. You can note that in the image as well. Turns out  this is a very interesting fuse  , some of you might be familiar with it , but me , never knew it even existed. Following is a link from a helpful guy that identified the fuse type and explained the working and meaning of it.

 

http://www.karosium.com/2016/09/the-weird-fuses-in-laptop-batteries.html?m=1

 

I will continue this post in a next post. 

Edited by BritishRacingGreen

  • Author


... continued from previous post .

Ah , beautiful , Pylontech ! I am supposed to be an experienced engineer that can at least change a fuse in an appliance , but no , apparently not !

Can you imagine what the owner thinks of me now !!! 

So the thermal fuse  has a square of solder alloy which acts as the fusing element . So when the current approaches the critical  region  , it get hot and melts away into the cavity. In addition there is a mechanism for the BMS MCU to also trigger a meltdown. This is actually very powerful and adds an additional level of defense when things go wrong. So the MCU will switch on the heater resistor , which sits below the alloy , and concentrates about 10 watts to heat it.

So the jackpot question is whether the fuse blew because of over current or did it blow via the heater resistor activated by the MCU. My opinion is the latter. Firstly, the first fuse array did not blow . Secondly , if there was an overcurrent then the first defense is the MCU turns of both DFET and CFET. Now we know the fets are still working so I assume that it would have cut off the surge current by this means. My take on this is that the battery had been confronted with an over voltage condition from outside. Under this circumstance it is not enough to turn off the fets as the over voltage would still sit on the outboard fets and there could have been a risk that it would kill that fet array . So the MCU blew the thermal fuse . This is the only logical explanation I have and would invite any other explanation from you.

Pylontech fuses are NOT  serviceable for various reasons . Firstly its an inseparable part of a very large BMS control board . Secondly its SMD devices directly soladered onto the cb pads , and there are no less than 8 of them in parallel to make up for the high current rating.
And to get the SMD code of the devices is very difficult. On the Teardown thread of  @PurePower there is a nice view of the US2000 fuse array and at least when can clearly see the 'Z' marking , which is 20A Fast Blow at 65Volts.


Then the 4 pin fuses are probably very hard to get by , and I think if you don't match them correctly , you doing your BMS no good.

So i am basically stepping down , the owner will attempt to get it fixed via warranty or void repair. I will be a watchdog for him to ensure that he does not  pay exorbitant price for a battery that is otherwise working.

Thank you so much for all your valuable inputs.

NOTE : PylonTech looks quality . The only downside for me is the fact that all BMS subsystems are on one large pcb. I would have liked to see a controller pxb , a power train pcb (fets)  and a fuse pcb with surge protection. 
 

Edited by BritishRacingGreen

Pwr OV Times    :        4
Pwr HV Times    :       30

Definitely looks like it experienced some kind of high voltage. 

469   23-01-31 16:44:30  52973  870    33800   27600   28100   3507     3535     Charge    Normal    Normal    Normal  100%        
470   23-01-31 17:14:30  53768  0      34400   27700   28200   3558     3588     Idle      High      Normal    Normal   99% IDLE PHV 

You can see there something happens on line 469, Pack high voltage and then after that it never moved current again .

  • Author
14 hours ago, Nexuss said:

Pwr OV Times    :        4
Pwr HV Times    :       30

Definitely looks like it experienced some kind of high voltage. 

469   23-01-31 16:44:30  52973  870    33800   27600   28100   3507     3535     Charge    Normal    Normal    Normal  100%        
470   23-01-31 17:14:30  53768  0      34400   27700   28200   3558     3588     Idle      High      Normal    Normal   99% IDLE PHV 

You can see there something happens on line 469, Pack high voltage and then after that it never moved current again .

@Nexuss thank you for  the analysis , it does align with my suspicion that the cause of the thermal fuses blown is due to high voltage.

On 2023/02/18 at 5:08 PM, Nexuss said:

Pwr OV Times    :        4
Pwr HV Times    :       30

Definitely looks like it experienced some kind of high voltage. 

469   23-01-31 16:44:30  52973  870    33800   27600   28100   3507     3535     Charge    Normal    Normal    Normal  100%        
470   23-01-31 17:14:30  53768  0      34400   27700   28200   3558     3588     Idle      High      Normal    Normal   99% IDLE PHV 

You can see there something happens on line 469, Pack high voltage and then after that it never moved current again .

This is spot on! The module experienced a high voltage as it reached 100%. Looks like the MPPT charge controller did not manage to drop the voltage to the pack and this more than likely popped the fuses. 

Command "datalist event 0" returned the following:

pylon_debug>
datalist event 0
@
Item  Time                      Vo(mV) Cu(mA) Tempr   Tlow    Thigh   Vlowest  Vhighest Base.St   Volt.St   Curr.St   Temp.St Per% Events SysErrCode
0     23-01-31 16:31:04  52541  752    33100   27700   28200   3480     3506     Charge    Normal    SC        Normal  100% SC        
1     23-01-31 16:59:44  53867  9525   33600   27600   28100   3561     3596     Charge    High      Normal    Normal  100% PHV        
2     23-01-31 17:00:08  53880  9203   33600   27600   28100   3562     3596     Charge    High      Normal    Normal  100% PHV        
3     23-01-31 17:00:30  53749  9167   33700   27600   28100   3555     3587     Charge    High      Normal    Normal  100% PHV        
4     23-01-31 17:00:54  53898  9568   33700   27600   28100   3564     3598     Charge    High      Normal    Normal  100% PHV        
5     23-01-31 17:01:16  53793  9718   33700   27600   28100   3559     3590     Charge    High      Normal    Normal  100% PHV        
6     23-01-31 17:01:40  53940  9963   33800   27600   28100   3568     3600     Charge    High      Normal    Normal  100% PHV BHV        
7     23-01-31 17:02:02  53790  9546   33900   27600   28100   3559     3590     Charge    High      Normal    Normal  100% PHV        
8     23-01-31 17:02:04  53930  9596   33900   27600   28100   3566     3600     Charge    High      Normal    Normal  100% BHV        
9     23-01-31 17:02:26  53817  8969   34000   27600   28100   3561     3592     Charge    High      Normal    Normal  100% PHV        
10    23-01-31 17:02:50  53893  8749   34100   27600   28100   3566     3597     Charge    High      Normal    Normal  100% PHV        
11    23-01-31 17:03:12  53762  9124   34200   27600   28100   3558     3588     Charge    High      Normal    Normal  100% PHV        
12    23-01-31 17:03:34  53767  10035  34300   27600   28100   3559     3589     Charge    High      Normal    Normal  100% PHV        
13    23-01-31 17:03:36  54016  10030  34300   27600   28100   3573     3605     Charge    OV        Normal    Normal  100% POV BHV        
14    23-01-31 17:03:58  53778  8507   34400   27600   28100   3559     3589     Charge    High      Normal    Normal  100% PHV        
15    23-01-31 17:04:20  53722  9732   34400   27600   28100   3556     3585     Charge    High      Normal    Normal  100% PHV        
16    23-01-31 17:04:22  53968  9706   34400   27600   28100   3571     3602     Charge    High      Normal    Normal  100% BHV        
17    23-01-31 17:04:44  53777  9056   34500   27600   28100   3559     3589     Charge    High      Normal    Normal  100% PHV        
18    23-01-31 17:07:04  53758  9852   34700   27600   28100   3558     3588     Charge    High      Normal    Normal   99% PHV        
19    23-01-31 17:08:36  53741  8325   34600   27600   28100   3557     3586     Charge    High      Normal    Normal   99% PHV        
20    23-01-31 17:09:20  53711  10368  34500   27600   28100   3555     3584     Charge    High      Normal    Normal   99% PHV        
21    23-01-31 17:09:22  54008  10204  34500   27600   28100   3573     3604     Charge    OV        Normal    Normal   99% POV BHV        
22    23-01-31 17:09:44  53893  10149  34500   27600   28100   3567     3597     Charge    High      Normal    Normal   99% PHV        
23    23-01-31 17:10:06  53715  9602   34500   27600   28200   3556     3584     Charge    High      Normal    Normal   99% PHV        
24    23-01-31 17:10:30  53818  9454   34500   27600   28200   3562     3591     Charge    High      Normal    Normal   99% PHV        
25    23-01-31 17:10:54  53881  9393   34400   27600   28200   3566     3596     Charge    High      Normal    Normal   99% PHV        
26    23-01-31 17:11:16  53809  9688   34400   27600   28200   3562     3591     Charge    High      Normal    Normal   99% PHV        
27    23-01-31 17:11:38  53714  9973   34400   27700   28200   3557     3584     Charge    High      Normal    Normal   99% PHV        
28    23-01-31 17:11:40  53961  9852   34400   27700   28200   3571     3601     Charge    High      Normal    Normal   99% BHV        
29    23-01-31 17:12:02  53839  9812   34400   27700   28200   3564     3593     Charge    High      Normal    Normal   99% PHV        
30    23-01-31 17:12:26  53923  9939   34400   27700   28200   3569     3598     Charge    High      Normal    Normal   99% PHV        
31    23-01-31 17:12:48  53820  9861   34400   27700   28200   3563     3591     Charge    High      Normal    Normal   99% PHV        
32    23-01-31 17:13:34  53740  9767   34400   27700   28200   3558     3586     Charge    High      Normal    Normal   99% PHV        
33    23-01-31 17:13:36  54015  9888   34400   27700   28200   3575     3605     Charge    OV        Normal    Normal   99% POV BHV        
34    23-01-31 17:13:58  53978  10446  34400   27700   28200   3573     3602     Charge    High      Normal    Normal   99% PHV BHV        
35    23-01-31 17:14:20  53781  9961   34400   27700   28200   3561     3589     Charge    High      Normal    Normal   99% PHV        
36    23-01-31 17:14:22  54251  10137  34400   27700   28200   3590     3621     Charge    OV        Normal    Normal   99% POV BHV        
37    23-01-31 17:14:30  53768  0      34400   27700   28200   3558     3588     Idle      High      Normal    Normal   99% IDLE PHV        
38    23-02-01 01:03:55  50756  0      28600   26900   27300   3375     3386     SysError  Normal    Normal    Normal  100% SYSERR  0x200   

 

A "SC" event is a Short Circuit, occurring at 23-01-31 16:31:04, this is more than likely when the MPPT failed. You can also see that the current was not tapering down even though the battery was at 100% SOC.

Thereafter "PHV" (Pack High Voltage) events occurred several times. This event gets logged when the pack voltage reached 53.7v. 

Then also some cells hit a "BHV" (Battery cell High Voltage). This event gets logged when a cell voltage reached 3.6v.

There are also "POV" (Pack Over Voltage) events. This get logged when the pack voltage reached 54v. 

Then around 23-01-31 17:14:30, which is 45 minutes later, there was no current sent to the pack. There after System errors are logged and the Battery more than likely went into an alarm state.

From the logs, there doesn't seem to be any over current events logged but rather an over voltage event several times!

The BMS board will need replacing but then you need to ensure that the cells are still in good condition as well. 

 

This is not for the first time I have seen Pylontechs do this. A BMS should be able to protect itself from a high voltage event. How a high voltage event can fry a BMS is beyond me. If thats the case then they need to apply a Voltage & amperage fuse to prevent this. How can a global company send out a battery that renders it in need of repair for a high voltage event. Even the cheapest BMSs sold in the DIY market will voltage protect without damage. 

Pylontech needs to improve their product. It's well below expectation at the moment. 

 

 

 

 

Edited by Steve87

Anyone know what a SysError is?

In a pack of 8 batteries I had one go into fault. Buzzer sounding and red led.  I shut it down and restarted and it's been fine ever since. It was discharging at the time.

 

610   23-01-26  05:32:29  49167  -1000    8100     6500     6800     3276     3280     Dischg    Normal    Normal    Normal    0x0          Normal      68% 74000      1  3278   6700    Normal    Normal      68% 2  3278   6700    Normal    Normal      68% 3  3277   6700    Normal    Normal      68% 4  3280   6700    Normal    Normal      68% 5  3278   6700    Normal    Normal      68% 6  3277   6800    Normal    Normal      68% 7  3278   6800    Normal    Normal      68% 8  3278   6800    Normal    Normal      68% 9  3279   6800    Normal    Normal      68% 10 3279   6800    Normal    Normal      68% 11 3277   6500    Normal    Normal      68% 12 3278   6500    Normal    Normal      68% 13 3277   6500    Normal    Normal      68% 14 3277   6500    Normal    Normal      68% 15 3276   6500    Normal    Normal      68%

611   23-01-26  06:02:32  49281  0        9400     6300     6700     3284     3287     SysError  Normal    Normal    Normal    0x8          Normal      67% 74000      1  3285   6600    Normal    Normal      67% 2  3286   6600    Normal    Normal      67% 3  3285   6600    Normal    Normal      67% 4  3287   6600    Normal    Normal      67% 5  3286   6600    Normal    Normal      67% 6  3285   6700    Normal    Normal      67% 7  3286   6700    Normal    Normal      67% 8  3286   6700    Normal    Normal      67% 9  3286   6700    Normal    Normal      67% 10 3286   6700    Normal    Normal      67% 11 3285   6300    Normal    Normal      67% 12 3285   6300    Normal    Normal      67% 13 3285   6300    Normal    Normal      67% 14 3284   6300    Normal    Normal      67% 15 3284   6300    Normal    Normal      67%

640   23-01-26  20:34:15  49419  0        10100    5900     6100     3294     3296     SysError  Normal    Normal    Normal    0x8          Normal      67% 74000      1  3294   6100    Normal    Normal      67% 2  3295   6100    Normal    Normal      67% 3  3294   6100    Normal    Normal      67% 4  3296   6100    Normal    Normal      67% 5  3295   6100    Normal    Normal      67% 6  3294   6100    Normal    Normal      67% 7  3295   6100    Normal    Normal      67% 8  3295   6100    Normal    Normal      67% 9  3295   6100    Normal    Normal      67% 10 3295   6100    Normal    Normal      67% 11 3294   5900    Normal    Normal      67% 12 3295   5900    Normal    Normal      67% 13 3294   5900    Normal    Normal      67% 14 3294   5900    Normal    Normal      67% 15 3294   5900    Normal    Normal      67%

Restart

641   23-01-26  20:59:20  49419  0        10200    5900     6100     3294     3296     Idle      Normal    Normal    Normal    0x0          Normal      66% 74000      1  3294   6100    Normal    Normal      66% 2  3295   6100    Normal    Normal      66% 3  3294   6100    Normal    Normal      66% 4  3296   6100    Normal    Normal      66% 5  3295   6100    Normal    Normal      66% 6  3294   6100    Normal    Normal      66% 7  3295   6100    Normal    Normal      66% 8  3295   6100    Normal    Normal      66% 9  3295   6100    Normal    Normal      66% 10 3295   6100    Normal    Normal      66% 11 3294   5900    Normal    Normal      66% 12 3295   5900    Normal    Normal      66% 13 3294   5900    Normal    Normal      66% 14 3294   5900    Normal    Normal      66% 15 3294   5900    Normal    Normal      66%

642   23-01-26  21:01:03  49976  5113     9700     5900     6200     3331     3334     Charge    Normal    Normal    Normal    0x80000      Normal      67% 74000      1  3332   6100    Normal    Normal      67% 2  3332   6100    Normal    Normal      67% 3  3331   6100    Normal    Normal      67% 4  3334   6100    Normal    Normal      67% 5  3332   6100    Normal    Normal      67% 6  3331   6200    Normal    Normal      67% 7  3332   6200    Normal    Normal      67% 8  3332   6200    Normal    Normal      67% 9  3332   6200    Normal    Normal      67% 10 3332   6200    Normal    Normal      67% 11 3331   5900    Normal    Normal      67% 12 3332   5900    Normal    Normal      67% 13 3331   5900    Normal    Normal      67% 14 3331   5900    Normal    Normal      67% 15 3331   5900    Normal    Normal      67%

 

Edit found it- seems very strange though when the battery is discharging;

3     23-01-26  05:52:55  49965  -1015    8000     6400     6800     3275     4095     SysError  Normal    Normal    Normal    0x8          Normal      67% 74000      1  4095   6600    High      Normal      67% 2  3277   6600    Normal    Normal      67% 3  3276   6600    Normal    Normal      67% 4  3278   6600    Normal    Normal      67% 5  3277   6600    Normal    Normal      67% 6  3276   6800    Normal    Normal      67% 7  3277   6800    Normal    Normal      67% 8  3277   6800    Normal    Normal      67% 9  3277   6800    Normal    Normal      67% 10 3277   6800    Normal    Normal      67% 11 3276   6400    Normal    Normal      67% 12 3276   6400    Normal    Normal      67% 13 3276   6400    Normal    Normal      67% 14 3275   6400    Normal    Normal      67% 15 3275   6400    Normal    Normal      67%

I see it's done it once more since but it didn't shut down, same cell.

 

Edited by Tinbum

  • Author
3 hours ago, PurePower said:

This is spot on! The module experienced a high voltage as it reached 100%. Looks like the MPPT charge controller did not manage to drop the voltage to the pack and this more than likely popped the fuses. 

Command "datalist event 0" returned the following:

pylon_debug>
datalist event 0
@
Item  Time                      Vo(mV) Cu(mA) Tempr   Tlow    Thigh   Vlowest  Vhighest Base.St   Volt.St   Curr.St   Temp.St Per% Events SysErrCode
0     23-01-31 16:31:04  52541  752    33100   27700   28200   3480     3506     Charge    Normal    SC        Normal  100% SC        
1     23-01-31 16:59:44  53867  9525   33600   27600   28100   3561     3596     Charge    High      Normal    Normal  100% PHV        
2     23-01-31 17:00:08  53880  9203   33600   27600   28100   3562     3596     Charge    High      Normal    Normal  100% PHV        
3     23-01-31 17:00:30  53749  9167   33700   27600   28100   3555     3587     Charge    High      Normal    Normal  100% PHV        
4     23-01-31 17:00:54  53898  9568   33700   27600   28100   3564     3598     Charge    High      Normal    Normal  100% PHV        
5     23-01-31 17:01:16  53793  9718   33700   27600   28100   3559     3590     Charge    High      Normal    Normal  100% PHV        
6     23-01-31 17:01:40  53940  9963   33800   27600   28100   3568     3600     Charge    High      Normal    Normal  100% PHV BHV        
7     23-01-31 17:02:02  53790  9546   33900   27600   28100   3559     3590     Charge    High      Normal    Normal  100% PHV        
8     23-01-31 17:02:04  53930  9596   33900   27600   28100   3566     3600     Charge    High      Normal    Normal  100% BHV        
9     23-01-31 17:02:26  53817  8969   34000   27600   28100   3561     3592     Charge    High      Normal    Normal  100% PHV        
10    23-01-31 17:02:50  53893  8749   34100   27600   28100   3566     3597     Charge    High      Normal    Normal  100% PHV        
11    23-01-31 17:03:12  53762  9124   34200   27600   28100   3558     3588     Charge    High      Normal    Normal  100% PHV        
12    23-01-31 17:03:34  53767  10035  34300   27600   28100   3559     3589     Charge    High      Normal    Normal  100% PHV        
13    23-01-31 17:03:36  54016  10030  34300   27600   28100   3573     3605     Charge    OV        Normal    Normal  100% POV BHV        
14    23-01-31 17:03:58  53778  8507   34400   27600   28100   3559     3589     Charge    High      Normal    Normal  100% PHV        
15    23-01-31 17:04:20  53722  9732   34400   27600   28100   3556     3585     Charge    High      Normal    Normal  100% PHV        
16    23-01-31 17:04:22  53968  9706   34400   27600   28100   3571     3602     Charge    High      Normal    Normal  100% BHV        
17    23-01-31 17:04:44  53777  9056   34500   27600   28100   3559     3589     Charge    High      Normal    Normal  100% PHV        
18    23-01-31 17:07:04  53758  9852   34700   27600   28100   3558     3588     Charge    High      Normal    Normal   99% PHV        
19    23-01-31 17:08:36  53741  8325   34600   27600   28100   3557     3586     Charge    High      Normal    Normal   99% PHV        
20    23-01-31 17:09:20  53711  10368  34500   27600   28100   3555     3584     Charge    High      Normal    Normal   99% PHV        
21    23-01-31 17:09:22  54008  10204  34500   27600   28100   3573     3604     Charge    OV        Normal    Normal   99% POV BHV        
22    23-01-31 17:09:44  53893  10149  34500   27600   28100   3567     3597     Charge    High      Normal    Normal   99% PHV        
23    23-01-31 17:10:06  53715  9602   34500   27600   28200   3556     3584     Charge    High      Normal    Normal   99% PHV        
24    23-01-31 17:10:30  53818  9454   34500   27600   28200   3562     3591     Charge    High      Normal    Normal   99% PHV        
25    23-01-31 17:10:54  53881  9393   34400   27600   28200   3566     3596     Charge    High      Normal    Normal   99% PHV        
26    23-01-31 17:11:16  53809  9688   34400   27600   28200   3562     3591     Charge    High      Normal    Normal   99% PHV        
27    23-01-31 17:11:38  53714  9973   34400   27700   28200   3557     3584     Charge    High      Normal    Normal   99% PHV        
28    23-01-31 17:11:40  53961  9852   34400   27700   28200   3571     3601     Charge    High      Normal    Normal   99% BHV        
29    23-01-31 17:12:02  53839  9812   34400   27700   28200   3564     3593     Charge    High      Normal    Normal   99% PHV        
30    23-01-31 17:12:26  53923  9939   34400   27700   28200   3569     3598     Charge    High      Normal    Normal   99% PHV        
31    23-01-31 17:12:48  53820  9861   34400   27700   28200   3563     3591     Charge    High      Normal    Normal   99% PHV        
32    23-01-31 17:13:34  53740  9767   34400   27700   28200   3558     3586     Charge    High      Normal    Normal   99% PHV        
33    23-01-31 17:13:36  54015  9888   34400   27700   28200   3575     3605     Charge    OV        Normal    Normal   99% POV BHV        
34    23-01-31 17:13:58  53978  10446  34400   27700   28200   3573     3602     Charge    High      Normal    Normal   99% PHV BHV        
35    23-01-31 17:14:20  53781  9961   34400   27700   28200   3561     3589     Charge    High      Normal    Normal   99% PHV        
36    23-01-31 17:14:22  54251  10137  34400   27700   28200   3590     3621     Charge    OV        Normal    Normal   99% POV BHV        
37    23-01-31 17:14:30  53768  0      34400   27700   28200   3558     3588     Idle      High      Normal    Normal   99% IDLE PHV        
38    23-02-01 01:03:55  50756  0      28600   26900   27300   3375     3386     SysError  Normal    Normal    Normal  100% SYSERR  0x200   

 

A "SC" event is a Short Circuit, occurring at 23-01-31 16:31:04, this is more than likely when the MPPT failed. You can also see that the current was not tapering down even though the battery was at 100% SOC.

Thereafter "PHV" (Pack High Voltage) events occurred several times. This event gets logged when the pack voltage reached 53.7v. 

Then also some cells hit a "BHV" (Battery cell High Voltage). This event gets logged when a cell voltage reached 3.6v.

There are also "POV" (Pack Over Voltage) events. This get logged when the pack voltage reached 54v. 

Then around 23-01-31 17:14:30, which is 45 minutes later, there was no current sent to the pack. There after System errors are logged and the Battery more than likely went into an alarm state.

From the logs, there doesn't seem to be any over current events logged but rather an over voltage event several times!

The BMS board will need replacing but then you need to ensure that the cells are still in good condition as well. 

 

Thank you so much for your input , and confirming  . One thing is for sure , you know your Pylontech 👌

  • Author
2 hours ago, Steve87 said:

This is not for the first time I have seen Pylontechs do this. A BMS should be able to protect itself from a high voltage event. How a high voltage event can fry a BMS is beyond me. If thats the case then they need to apply a Voltage & amperage fuse to prevent this. How can a global company send out a battery that renders it in need of repair for a high voltage event. Even the cheapest BMSs sold in the DIY market will voltage protect without damage. 

Pylontech needs to improve their product. It's well below expectation at the moment. 

 

 

 

 

Hi Steve , in PylonTech's defense , the battery did  negate the high voltage / short circuit condition and passivated the pack . However , I do agree that the replacement of the fuses is a delicate SMT rework exercise only to be undertaken by very skilled personnel.  If your local support agent   is not equipped to do so , we in for a complete BMS replacement ,  because the fuse arrays are part of the BMS PCB .  That does not go well down by me. Imagine the owner of a Pylontech in Pofadder!

  • Author
2 hours ago, Tinbum said:

Anyone know what a SysError is?

In a pack of 8 batteries I had one go into fault. Buzzer sounding and red led.  I shut it down and restarted and it's been fine ever since. It was discharging at the time.

 

610   23-01-26  05:32:29  49167  -1000    8100     6500     6800     3276     3280     Dischg    Normal    Normal    Normal    0x0          Normal      68% 74000      1  3278   6700    Normal    Normal      68% 2  3278   6700    Normal    Normal      68% 3  3277   6700    Normal    Normal      68% 4  3280   6700    Normal    Normal      68% 5  3278   6700    Normal    Normal      68% 6  3277   6800    Normal    Normal      68% 7  3278   6800    Normal    Normal      68% 8  3278   6800    Normal    Normal      68% 9  3279   6800    Normal    Normal      68% 10 3279   6800    Normal    Normal      68% 11 3277   6500    Normal    Normal      68% 12 3278   6500    Normal    Normal      68% 13 3277   6500    Normal    Normal      68% 14 3277   6500    Normal    Normal      68% 15 3276   6500    Normal    Normal      68%

611   23-01-26  06:02:32  49281  0        9400     6300     6700     3284     3287     SysError  Normal    Normal    Normal    0x8          Normal      67% 74000      1  3285   6600    Normal    Normal      67% 2  3286   6600    Normal    Normal      67% 3  3285   6600    Normal    Normal      67% 4  3287   6600    Normal    Normal      67% 5  3286   6600    Normal    Normal      67% 6  3285   6700    Normal    Normal      67% 7  3286   6700    Normal    Normal      67% 8  3286   6700    Normal    Normal      67% 9  3286   6700    Normal    Normal      67% 10 3286   6700    Normal    Normal      67% 11 3285   6300    Normal    Normal      67% 12 3285   6300    Normal    Normal      67% 13 3285   6300    Normal    Normal      67% 14 3284   6300    Normal    Normal      67% 15 3284   6300    Normal    Normal      67%

640   23-01-26  20:34:15  49419  0        10100    5900     6100     3294     3296     SysError  Normal    Normal    Normal    0x8          Normal      67% 74000      1  3294   6100    Normal    Normal      67% 2  3295   6100    Normal    Normal      67% 3  3294   6100    Normal    Normal      67% 4  3296   6100    Normal    Normal      67% 5  3295   6100    Normal    Normal      67% 6  3294   6100    Normal    Normal      67% 7  3295   6100    Normal    Normal      67% 8  3295   6100    Normal    Normal      67% 9  3295   6100    Normal    Normal      67% 10 3295   6100    Normal    Normal      67% 11 3294   5900    Normal    Normal      67% 12 3295   5900    Normal    Normal      67% 13 3294   5900    Normal    Normal      67% 14 3294   5900    Normal    Normal      67% 15 3294   5900    Normal    Normal      67%

Restart

641   23-01-26  20:59:20  49419  0        10200    5900     6100     3294     3296     Idle      Normal    Normal    Normal    0x0          Normal      66% 74000      1  3294   6100    Normal    Normal      66% 2  3295   6100    Normal    Normal      66% 3  3294   6100    Normal    Normal      66% 4  3296   6100    Normal    Normal      66% 5  3295   6100    Normal    Normal      66% 6  3294   6100    Normal    Normal      66% 7  3295   6100    Normal    Normal      66% 8  3295   6100    Normal    Normal      66% 9  3295   6100    Normal    Normal      66% 10 3295   6100    Normal    Normal      66% 11 3294   5900    Normal    Normal      66% 12 3295   5900    Normal    Normal      66% 13 3294   5900    Normal    Normal      66% 14 3294   5900    Normal    Normal      66% 15 3294   5900    Normal    Normal      66%

642   23-01-26  21:01:03  49976  5113     9700     5900     6200     3331     3334     Charge    Normal    Normal    Normal    0x80000      Normal      67% 74000      1  3332   6100    Normal    Normal      67% 2  3332   6100    Normal    Normal      67% 3  3331   6100    Normal    Normal      67% 4  3334   6100    Normal    Normal      67% 5  3332   6100    Normal    Normal      67% 6  3331   6200    Normal    Normal      67% 7  3332   6200    Normal    Normal      67% 8  3332   6200    Normal    Normal      67% 9  3332   6200    Normal    Normal      67% 10 3332   6200    Normal    Normal      67% 11 3331   5900    Normal    Normal      67% 12 3332   5900    Normal    Normal      67% 13 3331   5900    Normal    Normal      67% 14 3331   5900    Normal    Normal      67% 15 3331   5900    Normal    Normal      67%

 

Edit found it- seems very strange though when the battery is discharging;

3     23-01-26  05:52:55  49965  -1015    8000     6400     6800     3275     4095     SysError  Normal    Normal    Normal    0x8          Normal      67% 74000      1  4095   6600    High      Normal      67% 2  3277   6600    Normal    Normal      67% 3  3276   6600    Normal    Normal      67% 4  3278   6600    Normal    Normal      67% 5  3277   6600    Normal    Normal      67% 6  3276   6800    Normal    Normal      67% 7  3277   6800    Normal    Normal      67% 8  3277   6800    Normal    Normal      67% 9  3277   6800    Normal    Normal      67% 10 3277   6800    Normal    Normal      67% 11 3276   6400    Normal    Normal      67% 12 3276   6400    Normal    Normal      67% 13 3276   6400    Normal    Normal      67% 14 3275   6400    Normal    Normal      67% 15 3275   6400    Normal    Normal      67%

I see it's done it once more since but it didn't shut down, same cell.

 

Turns out you might be assisted by @Nexussand/or @PurePower, as they helped me with my logs.

13 hours ago, Tinbum said:

Anyone know what a SysError is?

In a pack of 8 batteries I had one go into fault. Buzzer sounding and red led.  I shut it down and restarted and it's been fine ever since. It was discharging at the time.

 

610   23-01-26  05:32:29  49167  -1000    8100     6500     6800     3276     3280     Dischg    Normal    Normal    Normal    0x0          Normal      68% 74000      1  3278   6700    Normal    Normal      68% 2  3278   6700    Normal    Normal      68% 3  3277   6700    Normal    Normal      68% 4  3280   6700    Normal    Normal      68% 5  3278   6700    Normal    Normal      68% 6  3277   6800    Normal    Normal      68% 7  3278   6800    Normal    Normal      68% 8  3278   6800    Normal    Normal      68% 9  3279   6800    Normal    Normal      68% 10 3279   6800    Normal    Normal      68% 11 3277   6500    Normal    Normal      68% 12 3278   6500    Normal    Normal      68% 13 3277   6500    Normal    Normal      68% 14 3277   6500    Normal    Normal      68% 15 3276   6500    Normal    Normal      68%

611   23-01-26  06:02:32  49281  0        9400     6300     6700     3284     3287     SysError  Normal    Normal    Normal    0x8          Normal      67% 74000      1  3285   6600    Normal    Normal      67% 2  3286   6600    Normal    Normal      67% 3  3285   6600    Normal    Normal      67% 4  3287   6600    Normal    Normal      67% 5  3286   6600    Normal    Normal      67% 6  3285   6700    Normal    Normal      67% 7  3286   6700    Normal    Normal      67% 8  3286   6700    Normal    Normal      67% 9  3286   6700    Normal    Normal      67% 10 3286   6700    Normal    Normal      67% 11 3285   6300    Normal    Normal      67% 12 3285   6300    Normal    Normal      67% 13 3285   6300    Normal    Normal      67% 14 3284   6300    Normal    Normal      67% 15 3284   6300    Normal    Normal      67%

640   23-01-26  20:34:15  49419  0        10100    5900     6100     3294     3296     SysError  Normal    Normal    Normal    0x8          Normal      67% 74000      1  3294   6100    Normal    Normal      67% 2  3295   6100    Normal    Normal      67% 3  3294   6100    Normal    Normal      67% 4  3296   6100    Normal    Normal      67% 5  3295   6100    Normal    Normal      67% 6  3294   6100    Normal    Normal      67% 7  3295   6100    Normal    Normal      67% 8  3295   6100    Normal    Normal      67% 9  3295   6100    Normal    Normal      67% 10 3295   6100    Normal    Normal      67% 11 3294   5900    Normal    Normal      67% 12 3295   5900    Normal    Normal      67% 13 3294   5900    Normal    Normal      67% 14 3294   5900    Normal    Normal      67% 15 3294   5900    Normal    Normal      67%

Restart

641   23-01-26  20:59:20  49419  0        10200    5900     6100     3294     3296     Idle      Normal    Normal    Normal    0x0          Normal      66% 74000      1  3294   6100    Normal    Normal      66% 2  3295   6100    Normal    Normal      66% 3  3294   6100    Normal    Normal      66% 4  3296   6100    Normal    Normal      66% 5  3295   6100    Normal    Normal      66% 6  3294   6100    Normal    Normal      66% 7  3295   6100    Normal    Normal      66% 8  3295   6100    Normal    Normal      66% 9  3295   6100    Normal    Normal      66% 10 3295   6100    Normal    Normal      66% 11 3294   5900    Normal    Normal      66% 12 3295   5900    Normal    Normal      66% 13 3294   5900    Normal    Normal      66% 14 3294   5900    Normal    Normal      66% 15 3294   5900    Normal    Normal      66%

642   23-01-26  21:01:03  49976  5113     9700     5900     6200     3331     3334     Charge    Normal    Normal    Normal    0x80000      Normal      67% 74000      1  3332   6100    Normal    Normal      67% 2  3332   6100    Normal    Normal      67% 3  3331   6100    Normal    Normal      67% 4  3334   6100    Normal    Normal      67% 5  3332   6100    Normal    Normal      67% 6  3331   6200    Normal    Normal      67% 7  3332   6200    Normal    Normal      67% 8  3332   6200    Normal    Normal      67% 9  3332   6200    Normal    Normal      67% 10 3332   6200    Normal    Normal      67% 11 3331   5900    Normal    Normal      67% 12 3332   5900    Normal    Normal      67% 13 3331   5900    Normal    Normal      67% 14 3331   5900    Normal    Normal      67% 15 3331   5900    Normal    Normal      67%

 

Edit found it- seems very strange though when the battery is discharging;

3     23-01-26  05:52:55  49965  -1015    8000     6400     6800     3275     4095     SysError  Normal    Normal    Normal    0x8          Normal      67% 74000      1  4095   6600    High      Normal      67% 2  3277   6600    Normal    Normal      67% 3  3276   6600    Normal    Normal      67% 4  3278   6600    Normal    Normal      67% 5  3277   6600    Normal    Normal      67% 6  3276   6800    Normal    Normal      67% 7  3277   6800    Normal    Normal      67% 8  3277   6800    Normal    Normal      67% 9  3277   6800    Normal    Normal      67% 10 3277   6800    Normal    Normal      67% 11 3276   6400    Normal    Normal      67% 12 3276   6400    Normal    Normal      67% 13 3276   6400    Normal    Normal      67% 14 3275   6400    Normal    Normal      67% 15 3275   6400    Normal    Normal      67%

I see it's done it once more since but it didn't shut down, same cell.

 

What model is this? and is it the master battery?

4 hours ago, PurePower said:

What model is this? and is it the master battery?

It's a US3000C and no it's the 7th. I'm going to look at the log for the 8th and see what voltage that shows at the same time, if its logged at that time.

EDIT this is the log for the 8th battery which shows them discharging and also shows the voltages. It's not at the specific time of the error on the 7th. (The way the inverter is set up was to do a constant discharge at a set current during the hours of darkness).

How is the battery pack voltage measured or is it calculated from the sum of all the cell readings?

 

594   23-01-26  05:02:26  49212  -1312    8200     6200     6400     3280     3282     Dischg    Normal    Normal    Normal    0x0          Normal      70% 74000      1  3281   6400    Normal    Normal      70% 2  3282   6400    Normal    Normal      70% 3  3281   6400    Normal    Normal      70% 4  3281   6400    Normal    Normal      70% 5  3281   6400    Normal    Normal      70% 6  3281   6200    Normal    Normal      70% 7  3280   6200    Normal    Normal      70% 8  3281   6200    Normal    Normal      70% 9  3281   6200    Normal    Normal      70% 10 3280   6200    Normal    Normal      70% 11 3281   6400    Normal    Normal      70% 12 3280   6400    Normal    Normal      70% 13 3282   6400    Normal    Normal      70% 14 3280   6400    Normal    Normal      70% 15 3280   6400    Normal    Normal      70%

595   23-01-26  05:32:29  49171  -1252    8000     6200     6300     3277     3279     Dischg    Normal    Normal    Normal    0x0          Normal      69% 74000      1  3279   6300    Normal    Normal      69% 2  3279   6300    Normal    Normal      69% 3  3278   6300    Normal    Normal      69% 4  3278   6300    Normal    Normal      69% 5  3278   6300    Normal    Normal      69% 6  3279   6200    Normal    Normal      69% 7  3277   6200    Normal    Normal      69% 8  3278   6200    Normal    Normal      69% 9  3278   6200    Normal    Normal      69% 10 3277   6200    Normal    Normal      69% 11 3278   6300    Normal    Normal      69% 12 3278   6300    Normal    Normal      69% 13 3279   6300    Normal    Normal      69% 14 3278   6300    Normal    Normal      69% 15 3277   6300    Normal    Normal      69%

596   23-01-26  06:02:33  49112  -1346    7800     6000     6200     3273     3275     Dischg    Normal    Normal    Normal    0x0          Normal      68% 74000      1  3275   6200    Normal    Normal      68% 2  3275   6200    Normal    Normal      68% 3  3274   6200    Normal    Normal      68% 4  3274   6200    Normal    Normal      68% 5  3274   6200    Normal    Normal      68% 6  3275   6000    Normal    Normal      68% 7  3273   6000    Normal    Normal      68% 8  3274   6000    Normal    Normal      68% 9  3274   6000    Normal    Normal      68% 10 3274   6000    Normal    Normal      68% 11 3274   6100    Normal    Normal      68% 12 3274   6100    Normal    Normal      68% 13 3275   6100    Normal    Normal      68% 14 3274   6100    Normal    Normal      68% 15 3273   6100    Normal    Normal      68%

 

 

Edited by Tinbum

SysError is a general error the BMS throws and usually shuts the pack down to protect it. It doesn't really give an explanation but that high voltage cell could very well be the reason in your case. 

I have seen SysError's on my US3000C when i mixed it with older US2000 plus modules. Only a firmware update to the US3000C's corrected that for me. 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.