Using Pylontech US3000 batteries efficiently


Recommended Posts

I have two US3000 Pylontechs (3.5kw each).  My Deye 8kw inverter was default programmed to run down to 80% DOD then moves to grid power.  I get maybe 2/3 hours of battery use after sunset before switching to grid.  Questions:

- What DoD can I safely set the system to without damaging the Pylontech batteries - would like it to last 10 years!

- Lowest DOD that is recommended for these batteries?

- The Deye BMS is configured for Pylon Li batteries - does it automatically choose the rate of charge at the optimum level - the inverter settings only ask for the max charging amps

 

 

Link to post
Share on other sites
11 minutes ago, Pren said:

Lowest DOD that is recommended for these batteries

I would say never go below 20% for LiFePO4

But keep it above that if you can. The less you test the limits the longer the battery will last. It's like brake disks: They can last a long time if you are an easy driver, or fail fast if you are a race driver. :) 

Link to post
Share on other sites

Yes, the alarm is set to scream if it goes below 20%, but this only happens when no grid power.  On a normal evening, it goes to grid at 80% DOD which is probably wasting the very expensive battery capacity and potential.  Correct?

 

Link to post
Share on other sites
2 hours ago, Pren said:

The Deye BMS is configured for Pylon Li batteries - does it automatically choose the rate of charge at the optimum level - the inverter settings only ask for the max charging amps

Not sure what settings the Deye automatically chooses, but I would recommend checking against / adjusting to the settings recommended here

2 hours ago, Pren said:

On a normal evening, it goes to grid at 80% DOD which is probably wasting the very expensive battery capacity and potential.  Correct?

Agreed. I am running my Pylons down to around 23% every night

Link to post
Share on other sites
3 hours ago, Pren said:

it goes to grid at 80% DOD which is probably wasting the very expensive battery capacity and potential.  Correct?

Are you sure that you are not confusing DoD with the SoC?

80%DoD means that there's roughly just 20% of energy left in the battery. Such a deep everyday cycling cannot be called "wasting of a potential" as consuming that last remaining 1.4kWh won't make any change but it will kill the batteries for sure.

In the US3000 BMS the 9%SoC is hardcoded as a lower limit. Once you discharge US3000 to this limit it will auto-shutdown and log an error to its NVRAM.

Edited by Youda
Link to post
Share on other sites
7 hours ago, Youda said:

Are you sure that you are not confusing DoD with the SoC?

YES, my bad.  SoC is at 80% when the inverter switches to grid.

Guess what I am trying to understand is what is a level to take SoC down to and keep battery life to ten years +.  Someone mentioned that if I draw power to SoC of 50% then the life of the battery drops exponentially!  

Link to post
Share on other sites

Personally, I'm cycling my US3000 stack between 100% SoC and 40%SoC. Once discharged to 40% SoC, my system automatically switches to the grid. Since manufacturer's specs allow cycling between 100% and 10%, I have a lot of margin here.

BTW:
Technically, it would be better to cycle these between 40% SoC and 90% SoC daily, while allowing a full charge (100%SoC) only once a week, to let BMS reset amphours counter and balance the cells. But as far as I know, no inverter on the market has ability to set such a complex rule.

Link to post
Share on other sites
11 hours ago, Pren said:

I have two US3000 Pylontechs (3.5kw each).  My Deye 8kw inverter was default programmed to run down to 80% DOD then moves to grid power.  I get maybe 2/3 hours of battery use after sunset before switching to grid.  Qs

What sort of loads are you running to have such a short period out of two Pylons? My single pylon does 2-3hrs. But loads are under 1kw constant. 

My pylon gets discharged to roughly 35% SoC as I only start discharging them from 5am when I switch from grid to Solar / Battery. But 7:30 the solar has picked up enough to carry the loads and the battery is at 35%  

Link to post
Share on other sites
1 minute ago, Youda said:

@Rclegg

just check the whole thread you will notice the reason for that short period:
@Pren mismatched DoD and SoC in his description. In reality, he's using just 1.4kWh out of 2xUS3000 and then he's switching to grid. Basically treating 7kWh of lithium like 7kWh of lead-acid :lol:

Ooooooh yeah okay that makes more sense! 😅

Link to post
Share on other sites
59 minutes ago, Youda said:

@Rclegg

just check the whole thread you will notice the reason for that short period:
@Pren mismatched DoD and SoC in his description. In reality, he's using just 1.4kWh out of 2xUS3000 and then he's switching to grid. Basically treating 7kWh of lithium like 7kWh of lead-acid :lol:

Too many acronyms for a noobie....

Going to reset the SoC limit to 50% before going to grid today... that should balance using the batteries more efficiently, allowing some leeway if there is power outage, and preserving the battery life!

Link to post
Share on other sites
1 hour ago, Pren said:

Going to reset the SoC limit to 50% before going to grid today... that should balance using the batteries more efficiently, allowing some leeway if there is power outage, and preserving the battery life!

I have a 4kWh battery. My SOC limit is set at 40% and when we had load shedding the other day it went down to 30% using about 400W during that time. If you don't have mega loads (resistive loads) then 50% might be too conservative still for a 7kWh battery. 

But look at your loads that you plan to use and check the values during the next loadshedding and then adjust accordingly for your setup.

Link to post
Share on other sites

What I would like to see is the option to limit charging to 90% of capacity..

The DoD one can manage, its the charging that is the problem.

3 hours ago, Youda said:

BTW:
Technically, it would be better to cycle these between 40% SoC and 90% SoC daily, while allowing a full charge (100%SoC) only once a week, to let BMS reset amphours counter and balance the cells. But as far as I know, no inverter on the market has ability to set such a complex rule.

 

Link to post
Share on other sites
3 hours ago, Youda said:

Technically, it would be better to cycle these between 40% SoC and 90% SoC daily, while allowing a full charge (100%SoC) only once a week, to let BMS reset amphours counter and balance the cells. But as far as I know, no inverter on the market has ability to set such a complex rule.

Well I guess an option would be to have a big bank that won't be able to charge from 20% SoC to 100% SoC with the PV available in which case Victron's BatteryLife (if enabled) will kick in. The way I understand it (pretty much pasting from there) is that it will raise the Low SOC limit by 5% each day until it reaches a 85% SoC. It will then stay on that level, but if it reaches 95% then it will lower the Low SOC limit by 5% again.

It's not exactly the "ensure 100% once a week" state, but it ensures that it reaches 85% to 100% each day.

Link to post
Share on other sites
1 hour ago, FixAMess said:

What I would like to see is the option to limit charging to 90% of capacity..

The DoD one can manage, its the charging that is the problem.

 

@FixAMess the Deye seems to hover around 99% SoC most of the time, going to 100% but not staying there for long.  wonder if this helps??

Link to post
Share on other sites
2 hours ago, Pren said:

@Youda The Deye inverter uses the Solarman app to monitor the system - can you recommend a better app?  for some reason I do not see the Pylons on the App so cannot monitor this

 

I use both the solarman app as well as solarman smart. Smart gives you a lot more stats if you go into the inverter section. 
 

 Click the 3 dots on top right and select device details, then go to inverter and stats. 
 

anyway, both apps should give you the soc info. Have you set the grid type to storage system 

95F00F6C-2B7B-4AE8-BBDE-CC4A4451EAA0.jpeg

FCDAE33A-8D06-4378-B8E1-F21093A73AD7.jpeg

Link to post
Share on other sites
1 hour ago, FixAMess said:

What I would like to see is the option to limit charging to 90% of capacity..

The DoD one can manage, its the charging that is the problem.

 

You can set the desired soc that you want but if you have excess generation then batteries will still charge 

Link to post
Share on other sites

ck the 3 dots on top right and select device details, then go to inverter and stats. 

12 minutes ago, Vassen said:

anyway, both apps should give you the soc info. Have you set the grid type to storage system 

 

Have set it to storage and see the batteries now - thanks this was very useful

Do you know how to reduce the SoC limit on the Deye - not obvious on the menus I went through

Link to post
Share on other sites
2 minutes ago, Pren said:

Do you know how to reduce the SoC limit on the Deye - not obvious on the menus I went through

Not sure what the deye interface looks like but on the sunsynk I have the following where I can Choose how much to charge batteries from either generator input or grid. 
 

but as I said, excess solar will still charge batteries to 100%. 

F9C4E435-5AD7-48BE-9EAB-893744EF063E.jpeg

Link to post
Share on other sites
14 minutes ago, Pren said:

the 3 dots on top right and select device details, then go to inverter and stats. 

Oh. This was when using the solarman smart app.  
 

there’s a ton of useful info there, like pv voltage and current. Energy generated / used per period... etc 

Link to post
Share on other sites
17 minutes ago, Vassen said:

Not sure what the deye interface looks like but on the sunsynk I have the following where I can Choose how much to charge batteries from either generator input or grid. 
 

but as I said, excess solar will still charge batteries to 100%. 

 

Deye has a similar page setup except it just shows "Batt" and not SoC %

Link to post
Share on other sites
5 hours ago, Pren said:

Deye has a similar page setup except it just shows "Batt" and not SoC %

Can you post a picture of what it looks like. 
 

im pretty sure it should be configured the same way. Sunsynk has been releasing lots of updates recently and with some of the updates, they change the descriptions from  bad chinglish to not-so-bad chinglish.  😂

Link to post
Share on other sites
20 hours ago, FixAMess said:

What I would like to see is the option to limit charging to 90% of capacity..

The DoD one can manage, its the charging that is the problem.

 

Would it not be possible to just check what voltage your battery has at 90% SoC and then just set that as the voltage to which it should be charged?

Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...