Pylontech battery Mix

Featured Replies

Good day, does anyone have experience in connecting different series Pylontech batteries? I was selling my existing 3 x US3000 batteries then found out that it is okay to mix different series batteries as per other posts and advice from a supplier. So I am going to buy two UP5000 or possibly two US3000C (which may be better idea, not sure).

However I am still not convinced as the advice given was that I should put the one UP5000 as master (fine, happy with that) then the 3 x US3000, and last in the string the second UP5000 (which I am skeptical about).  (And update firmware on all three US3000). I would have thought UP5000, UP5000, US3000, US3000, US3000 would have been correct. Does anyone know for sure?

Secondly, I have a Goodwe GW5048D-ES inverter. When I originally set it up, it recognised the 3 x US3000 batteries quite fine and has worked perfectly for two years. Will it recognise a mix of batteries?

Thanks in advance for advice.

14 minutes ago, Barry8355 said:

However I am still not convinced as the advice given was that I should put the one UP5000 as master (fine, happy with that) then the 3 x US3000, and last in the string the second UP5000 (which I am skeptical about).

This is not bad advice at all seeing as though the top and bottom battery of the stack will usually be taking the most of the current. this will sandwich your older batteries and possibly provide a better distribution of current between them. This will also "baby" your older batteries better i suspect.  

 

19 minutes ago, Barry8355 said:

Will it recognise a mix of batteries?

Yes if the batteries are all connected correctly to each other.

2 minutes ago, Nexuss said:

This is not bad advice at all seeing as though the top and bottom battery of the stack will usually be taking the most of the current. this will sandwich your older batteries and possibly provide a better distribution of current between them. This will also "baby" your older batteries better i suspect.  

 

Yes if the batteries are all connected correctly to each other.

Why would the last (bottom) of the 5 supply more current than those in between? 

The 1st one I agree. 

The Pylons are great for this backward and forwards compatibility. The newer battery - UP5000 for example in this case - would be the master battery and have comms cables between all other batteries in the bank. The inverter will comm with this master and betold that the size of the bank is X. This works 100% ad i know there is a user on MyBBwho has a system like this

image.thumb.png.fe311e03643eb69cae35603300bc5874.png

image.thumb.png.ced9ecd6d8993b2b24bfdf2dd428f906.png

I have a mix of US3000C and US3000 batteries. Always make the newest battery the master. It usually has the latest firmware. The new firmware is backward compatible (to a degree, there are always exceptions). The older pylons link up and continue going as normal. No need to upgrade the firmware on the older units. Its a risky operation in my opinion and there aren't a lot of installers that even know how to upgrade pylon firmware.

4 minutes ago, Scorp007 said:

Why would the last (bottom) of the 5 supply more current than those in between? 

The 1st one I agree. 

Well thats where your main wires from the inverter go to ... I observed my stack in batteryview and noticed that .

Yes, it is the recommendation to 'sandwich' the old batteries with the new.

It probably stems from the fact that old batteries can only occupy positions 2 to 8 so don't use these positions for new batteries. (Unless you have less than 9 batteries as then you can't not use them!)

Edited by Tinbum

4 hours ago, Nexuss said:

Well thats where your main wires from the inverter go to ... I observed my stack in batteryview and noticed that .

If you have connected them as per the manual then the batteries should be equally used as the connection length to each battery is the same.

7 hours ago, Barry8355 said:

Many thanks for the comments and advice. Question - better for me to buy US3000C's or UP5000's? Cant seem to find US5000's.  

One difference I can see is that US3000C has 6000 cycle life (like US3000) whereas UP5000 has 4500 cycle life. US3000C has 37A discharge current whereas UP5000 has 50A. I have US3000C and would rather go for something with a longer cycle life if I was you.

  • 1 month later...
  • Author

Update on this topic:

I bought 2 x US3000C's

Charged the bank of 3 old  US3000's to 100%

Whilst the US3000's were charging I connected the two US3000C's together to balance them.

Disconnected the 3 x US3000's, connected the 2 x US3000C's. Turned system on and programmed the Goodwe to accept 2 x US3000C's

Whilst the 2 x US3000C's were charging (they arrived at 52% SOC) I contacted Goodwe support and they updated the firmware on the inverter online.

Once the 2 x US3000C's were at 100% SOC I joined all five batteries - US3000C master, US3000C, US3000, US3000, US3000

Turned the system on and programmed the Goodwe to accept US3000Cx4+

All well and system running 100%. I did not update the firmware on the old 3 x US3000's

Hope this is helpful. 

  • 1 year later...

Greetings

My previous setup used to be 8 x us3000a batteries connected in parallel. One of the batteries failed, the supplier replaced the failed battery with UP5000 model. How do I got about connecting this battery to the remaining 7 US3000a batteries?

I believe the firmware on the us3000a need to be updated, currently it is on B67.13.0.0 (21-08-07).

Since the battery is much bigger and could not fit into my rack, I had to buy longer + and - cables with communication cable.

I changed the dip swich position 1 to on

What at my missing? The inverter is only seeing the UP5000 and not the rest of the battery bank

12 minutes ago, Riaz Moolla said:

Greetings

My previous setup used to be 8 x us3000a batteries connected in parallel. One of the batteries failed, the supplier replaced the failed battery with UP5000 model. How do I got about connecting this battery to the remaining 7 US3000a batteries?

I believe the firmware on the us3000a need to be updated, currently it is on B67.13.0.0 (21-08-07).

Since the battery is much bigger and could not fit into my rack, I had to buy longer + and - cables with communication cable.

I changed the dip swich position 1 to on

What at my missing? The inverter is only seeing the UP5000 and not the rest of the battery bank

New is master and read the manual with it, including how the dip switches should be set. They normally only have to be changed in rare cases.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.