September 14, 20205 yr I also have the 2015 model and it does not have the feature settings for lithium batteries. I run mine on "User" settings through a BMV702 which works great. Fault code 57 indicates a "Current Sensor Failure".
September 14, 20205 yr I also set it to User, in fact it has always been set to User. What is a BMV702 which works great and is it a requirement?
September 14, 20205 yr Okay the BMV702 is a battery monitor device, as I found out by googling it. Now what can the problem be with my Inverter? Another question is, can these units be tested as I would hate to buy another one only to find out there is nothing wrong with the one I have? Last question, I promise, if the unit is faulty/irrepairable do I go for another Axpert or are there other suggestions? Ok,ok I am a novice.
September 15, 20205 yr 12 hours ago, Rolf said: I have just bought a PylonTech 3.5Kw battery which I wanted to connect to my Axpert 5Kw/4Kv hybrid inverter A single Pylontech is rated for only 37 A continuous, 74 A peak. That's about 1.7 kW continuous or 3.4 kW peak. Perhaps your loads are higher than this? The Pylontech BMS may be disconnecting due to overload, and this could be confusing the inverter, certainly causing the relays to click on and off.
September 21, 20205 yr Author Anybody here that have the latest firmware for the 3.5 Pylontechs. Bought a second battery about a year after the first one. After doing all the equalizing etc I can still see on ICC the one working harder than the other. I tried to contact the importer but they have not even replied to my mail. I was also promised the latest firmware from another person, but still did not receive anything. Thanks
September 23, 20205 yr On 2020/09/21 at 9:14 AM, kobus joubert said: After doing all the equalizing etc I can still see on ICC the one working harder than the other. For how long has your new battery in the system? New batteries take a few weeks to be 'run in' And how is your cabling done? Cables to inverter from Plus on your first battery and minus on your last battery? Otherwise that could also explain what you are experiencing
September 30, 20205 yr 44 minutes ago, kobus joubert said: Batteries more than 8 months together. Yes wiring etc all done correct Hmm - ok, then it cannot be the battery having to settle in anymore What is the current difference between the batteries that you are seeing? And difference in SOC?
October 2, 20205 yr Good Day I have 3 pylon tech batteries and two inverters setup in PAL mode with 18 panels split into 9 and 9 to the inverters. What should the charging settings be on both the inverters to charge the batteries. Currently my batteries keep charging to 101% SOC on all three of them and settings is as above of Chris Hobson , setting 2 is set as 50A on each Inverter. Should it be set less, let say 30 -35A per inverter? Thanks Jacques
October 2, 20205 yr 9 hours ago, vwykj said: Should it be set less, let say 30 -35A per inverter? If you have 3x US3000, then your stack can combined take up to 111A for charging (3x 37A). I would hence say that your 50A setting on each inverter is spot on. No need to reduce that
October 4, 20205 yr On 2020/10/03 at 3:41 AM, wolfandy said: your 50A setting on each inverter is spot on. No need to reduce that In fact you could increase the maximum charge current on one inverter to 60 A, so you have 50 + 60 = 110 A available. What voltage settings are you using (settings 26 and 27 mainly)? There has been a lot of adjustment of the recommended settings over time. Here are my latest corrections to the original Pylontech suggested settings, as Chris Hobson may have posted:
October 4, 20205 yr Thanks for reply guys. Much appriciated it. Just another thing. My ICC software keeps showing my batteries SOC ehen charged as 101% charged. I cant seem to get it to stop only at 100% or Full. Must I be concern about the exstra 1%. Please find below my settings getting it from my inverters. Setting 26 = 52V Setting 27 (floating) = 51V Thanks Jacques Edited October 4, 20205 yr by vwykj
October 4, 20205 yr No need to be concerned. It is purely a calculation issue. ICC calculates the SoC utilizing the SoH (State of Health).
October 4, 20205 yr @Coulomb@Bloubul7@wolfandyThanks for your assistance. Much appriciated. Is I had a problem where both inverters faild at same time. The master inverter MB failed and Slave the PV card. So was not sure if it was maybe a setting on the mercer axpert 5k inverters.
October 4, 20205 yr 6 hours ago, vwykj said: Please find below my settings getting it from my inverters. Do you have the Pylon comms cable for ICC to receive data from the Pylon BMS? If yes, then I would change the 'Back to Grid Voltage' and 'Back to Discharge Voltage' to make sure that the Axpert's settings do not interfere with ICC switching modes (assuming that you are then also using 'Using SOC for Control' on the battery tab) 5 hours ago, vwykj said: Is I had a problem where both inverters faild at same time. The master inverter MB failed and Slave the PV card. So was not sure if it was maybe a setting on the mercer axpert 5k inverters. Sorry to hear I will leave it to our resident expert @Coulomb to answer, but I doubt that it can be caused by any of the settings. What I can see in your screenshots above is in line with what I am running in my own system What panels do you have and how are they connected?
October 5, 20205 yr 12 hours ago, vwykj said: Is I had a problem where both inverters faild at same time. The master inverter MB failed and Slave the PV card. Was this some time ago, replaced and working now, and you just want to be sure it won't happen again as a result of bad settings? Or has this just recently occurred?
October 5, 20205 yr @Coulomb This happens two weeks ago, and I had a concern it could have been the settings. The installer said it was a eskom surge but I was not 100% convinced. It is fixed now, The MB was replaced and the PV card was replaced. I have changed all the settings to your recommendations above in the post. I have also changed the program 2 back to 50A on both the Master and the Slave Inverters. @wolfandy Thanks for your feedback as well. My setup is as follows: Two Inverters setup in PAL mode 18 x 330V Canadian panels setup as 9 to Master inverter and 9 to the Slave Inverter. 3 x Pylon US3000B Plus 3.5 KWh Li-Ion Battery connected in a stack Yes my Raspberry with the ICC software do have a pylontech communication cable connected to the batteries console port to read the battery information. So that is why my other concern is the ICC software shows the batteries charge to 101% and not sure if I must be worried about it as @Bloubul7 indicated it is a calculation issue. Thanks for everyone`s feedback much appreciated. I`m not a expert just a user and I trying to do some research on it and getting your experts input to understand everything Thanks Jacques
October 5, 20205 yr 7 hours ago, vwykj said: 18 x 330V Canadian panels setup as 9 to Master inverter and 9 to the Slave Inverter. How many cells per panel? 60 or 72? And how are they wired? How many in series and how many in parallel? And what is the MPPT voltage rating of your Axpert? 145V? 8 hours ago, vwykj said: Yes my Raspberry with the ICC software do have a pylontech communication cable connected to the batteries console port to read the battery information. Great. But then I would recommend the following to ensure that ICC is switching between modes based on the SOC from the Pylon BMS instead of the Axpert based on voltage readings: Set 'Back to Grid Voltage' to 47V Set 'Back to Discharge Voltage' to 58V Enable 'Using SOC for Control' on the battery tab and set your desired SOC values (keeping in mind that if your batteries will not fully carry you throughout the night the Axpert's self-consumption will still be drawn from the Pylons even while running on utility) 8 hours ago, vwykj said: So that is why my other concern is the ICC software shows the batteries charge to 101% and not sure if I must be worried about it As mentioned by @Bloubul7, this is a calculation 'error' and not something to worry about. I get the same
October 11, 20205 yr Good Day I have another question please. I see my 3 pylontech cycles differ. Is it ok. My primary battery is at 207, the rest is at 203 and 202. I can say the two lower ones do pick up on cycles. Or must I change the batteries around abit? Thanks Edited October 11, 20205 yr by vwykj
October 11, 20205 yr @wolfandy Good Day I have another question please. I see my 3 pylontech cycles differ. Is it ok. My primary battery is at 207, the rest is at 203 and 202. I can say the two lower ones do pick up on cycles. Or must I change the batteries around abit? Thanks
January 12, 20215 yr Hi guys i need help, just bought 3 US3000 batteries. What does the ADD switches do exactly? And how should they be set properly for 3 parrallel batteries? Thanks
November 29, 20214 yr On 2020/10/04 at 3:57 AM, Coulomb said: In fact you could increase the maximum charge current on one inverter to 60 A, so you have 50 + 60 = 110 A available. What voltage settings are you using (settings 26 and 27 mainly)? There has been a lot of adjustment of the recommended settings over time. Here are my latest corrections to the original Pylontech suggested settings, as Chris Hobson may have posted: Hi, i have a axpert inverter with a pylon US3000C and I'm using SMH via raspberry pi, will these setting work?
November 30, 20214 yr On 2020/10/11 at 8:31 PM, vwykj said: @wolfandy Good Day I have another question please. I see my 3 pylontech cycles differ. Is it ok. My primary battery is at 207, the rest is at 203 and 202. I can say the two lower ones do pick up on cycles. Or must I change the batteries around abit? Thanks You are very lucky to have them so close together! My first two packs (LEOCH) came with some 26 cycles difference. I added another pack some months later and the fourth one year later. The actual cycle counts are: 429, 403, 320, 65. So what? Yes, they have some little differences in behavior that show up at low SOC, but at full charge they equalize themselves. An advantage might be that they will not reach end of live all together at the same time. LEOCH claims the guaranteed number of cycles with 100% discharge be 3500. Design live span 20 years.
November 30, 20214 yr 23 hours ago, JohanH said: i have a axpert inverter with a pylon US3000C and I'm using SMH via raspberry pi, will these setting work? My understanding is that with that sort of set-up (which I'm not familiar with), the Pi will send commands to the inverters to over-ride any battery related settings you make. I have no idea if it will optimise the maximum current by setting one inverter to a different current limit than the others. In the general case with n inverters and m battery modules, that could be rather tricky. So maybe it just sets all the inverters to use the same maximum charge current. So basically: I don't think you have to worry about it.