Axpert MKS II 5kW Error 08
On 2020/04/12 at 3:31 PM, charlez said:
@Coulomb thanks for this info. But as you said earlier they may provide a setting later using SOC. What software are you using to manage your inverters? This is what I can get out of my Narada batteries. Just passing a couple of fields to emoncms and not being used. Using the voltage to switch and not ideal.
temp::[31.0, 32.0, 31.0, 31.0] C
soh::100.0 %
status::[[], [], [], [('Charging', True)]] flag
packvolts::53.61 volts
soc::100.0 %
capacity::112.76 ah
addr::[1] BID
current::2.44 amps
cell_volts::(53.61300000000001, [3.554, 3.564, 3.567, 3.558, 3.549, 3.561, 3.564, 3.551, 3.567, 3.609, 3.613, 3.601, 3.587, 3.586, 3.582]) volts
cycles::330 cycles
Hi Charlez/ Everyone,
First off I want to thank each and everyone here for this create post and contribution to the community. I also started to get this 08 error and this has help me tremendously. @Charlez is it possible to give me more info regarding how you got the info from your Narada BMS? Did you use specific command protocol or does this automatically send for example every few seconds? Did you use RS485 or RS232? I tried searching all over the internet and could not get any info on this or command protocols. I could get for polyntech but nothing for Narada. Thanks in advance.
Quintin
  • Replies 241
  • Views 111.2k
  • @charlez - I don't think the suppliers are even aware of this issue with the inverter! Here is the circuit The heart of the isolater, is the LD03-16B12 (AC/DC Converter Vin = 90-528VAC
  • @charlez has pointed me to this information from the official Axpert MKS II manual: 14. WARNING: Because this inverter is non-isolated, only three types of PV modules are acceptable: single cryst
  • I did put up a fuss with Voltronic themselves regardings this issue.  At first they gave me a lame answer as follows : "Per your information below, it means error 08 was caused by the surge from
On 2020/11/17 at 10:35 AM, HermanD said:
Enable an AC charge current of only 2A and switch the inverter charge priority to "Solar First"
Very interested in this potential solution Herman.
Are you referring to setting 11 - Maximum utility charging current to be set to 2A and setting 16 - Charge source priority to be set to CSO instead of OSO?
With OSO only solar can charge batteries but with CSO, utility can also charge if there is no solar
On 2020/11/17 at 1:35 PM, HermanD said:
I had the same issue with the Error8 when my inverter(s) are in bypass mode, no solar input from panels and rain in the air.  My approach to solve (hide) this is to not add any additional hardware to the setup.  Enable an AC charge current of only 2A and switch the inverter charge priority to "Solar First".  The MKSII inverter can only charge from AC when in bypass mode, thus it will not use the AC charging when there is still battery available.  AC charging will not be used in bypass mode with solar availability.  The 2A AC charge setting is only enough to bias the inverter and do not really charge the batteries over the night period (My batteries SOC will go up with 1% maximum after about 10 hours on bypass).  After enabling these settings on my inverters I have not experience Error8 again for the entire winter (lots of rain and bypass mode incidents).  I hope this helps a few of you.
Thats a good solution too if one has batteries
Hi Smirresa,
Yes, setting 11 set to 2A and setting 16 set to CSO.  In CSO the inverter will only charge from utility in bypass mode when there no solar.  If you are in bypass mode, but there is solar (cloudy day with batteries low), then the AC charge will not occur.  If you are running from batteries and no solar (at night time) then the AC charge will not occur.  AC charging will only work when you are in bypass mode and no solar.
Regards
On 2020/12/15 at 10:55 AM, HermanD said:
Hi Smirresa,
Regards
Thanks Herman
Implemented this solution on two separate systems in two different parts of the country on the 1st of December, when I first saw the post.
No error 08 messages on either of the systems since then, despite intermittent cloudy and wet weather.
Seems like a lasting solution. If anything changes I will give feedback
Hi, wondered if there was any new feedback on this? Similar issue on Growatt, but mostly 11:00 morning starts to trip- not load related, and not only during rainy days. Did have utility charge set high (40amp) especially during latest loadshed again to not be caught out, have dropped it to 10A.
In this case it is 2x 5kW in parallel- and mostly one of the two that always error 8.
On 2021/03/20 at 8:17 PM, Igubu said:
any new feedback
The solution Herman proposed definitely solved the 08 (and 04) errors/problems on the Axpert inverters. Not a single error or trip since making the changes in Dec 2020. Not familiar with the Growatt inverters
I had the problem on two systems. One with 2 x 5kVA in parallel and the other with a single 5kVA unit.
As far as I remember, for the dual system, the 08 error mostly occurred on the master inverter
The Growatt has the same axpert designed mainboard- many similarities:)
on the positive side the friend with the same issue has not seen it since the same change was done approx 7 weeks ago! So I reckon this is a design fault in the board- but will Growatt refund because of it? Difficult to prove, but I’m of the opinion grid charge is a feature that has to work as designed.
  • 3 months later...
On 2019/06/12 at 11:47 AM, Esau said:
Hi there everyone, i  hoping you can help. tonight on utility at 1 am my axpert 5 kva went into error 08.  i switch it over to municipal for now as my inverter will not switch off.
it went on and off twice before it would not restore.
this has happened multiple times since install. my installer keeps tellib me it is due to buying a cheap make and only changing the inverter will fix my issues. yet my original one, which now instead of running everything, just runs my lights and geyser. the new one runs justy plugs.
my old inverter is still running on lead acids. where my new one is running on a hubble lithium.
the company who sold me the battery said by putting two batteries in series it would solve my tripping issues.
The installer keeps saying the voltage of something is too high for the inverter to handle. which i dont understand.
So the  basically i am sitting with 2 issues. it use to trip randomly like today in middle of the night. and the  when for eg i put a lawnmower on .it would then continue tripping until i switched the switch from inverter to municipal. help
Hi Rochelle,
2 Possible scenarios I think  - the first is the " usual error 08" .. comments about that first.
Error 8 are notorious with all " Axpert"  mainboards..these include, Axpert, Kodac, RCT, Growatt etc etc..they all use the same mainboard. The only thing that helped (proven by a lot of users) was to set utility charge very low - Think it's setting 11 - set it to 2A (Amps). This means it will only grid charge at a low value- if you can live without grid charging, set it to 0A if possible.
From " HermanD"'s solution earlier:
" Yes, setting 11 set to 2A and setting 16 set to CSO.  In CSO the inverter will only charge from utility in bypass mode when there no solar.  If you are in bypass mode, but there is solar (cloudy day with batteries low), then the AC charge will not occur.  If you are running from batteries and no solar (at night time) then the AC charge will not occur.  AC charging will only work when you are in bypass mode and no solar" .
Second scenario is the usual troubleshooting steps:
What are you settings, are there any errors logged? You mention plugs only - but " plugs only"  can definitely trip something. The inverter and Hubble have max charge/discharge current settings - what are yours set at? Another thought perhaps - are the Hubbles the models with CAN interface, as well as the Axpert - or are they configured without comms, and just set using "AGM/Lead" Volt values?
Assuming the installer here is professional and knows his stuff?
Getting a better hybrid inverter like a Sunsynk "could" solve some of your issues, but it's not necessary unless all steps to resolve has been tried. Only valid reason would be if you require a larger inverter to carry all the loads for example. There are many other reasons for it, but in your case, not required right now to just make your system work.
Interesting that you now have 2x inverters, and 2x separate battery banks - hopefully these are not connected in any way on the same DB.
Connecting batteries in series will increase Voltage - so if you had 2x 12V batteries - in series they will be 24V.  Not sure how increasing V will solve anything if the installer is already saying the "V is too high" ..The V has to match what your inverter is - so perhaps lets start there.
To assist a bit here, lets get the basics first:
Which Model of Axpert do you have? There should be something on a sticker to show the exact model.
Which Model lithium hubbles do you have and how many of them? Are they connected in Parallel (so double amp hours, but same V - assuming 12V or 48V)
Once we know that, we can pull the axpert manual up and check compare your settings..
Last thought - you mention lawnmower for example trips it - that sounds to me like too much load on the inverter/battery/combination of both. You don't mention solar panels - assuming none?
The reason it works in municipal mode is you are essentially in bypass  - so the inverter wont trip, as it's literally just letting the power flow through from the grid.
Edited by Igubu
*Added
Here some basic settings below - you can reply with your values here - again - you don't mention solar, so a lot of these depends on solar panels, charging from them etc..
Here from the manual for the 48V Axpert-MKSII_5KVA - Manual V1.2 -but you might have a different model. Error 08 can also be internal, so incorrect installation.. but lets check model of inverter and batteries first and then your settings.
01 - SBU/Uti - Utility First
02 - 10A
03 - APL
04 - SdS
05 - AGM/USE?
06 - Lfr
07 - trd
08 - 230v
09 - 50Hz
11 - 2A
12 - these will only have values if setting 01 =  SBU or SOL - if set to SBU - what are your settings here?
13 - Your values?
16 - Your values
18 - bOn
19 - ESP
20 - LON
22 - AON
23 - bYd
25 - FEN
26 - Your Values
27 - Your Values
29 - Your Values
31 - SbE
32 - Depends on setting 05 - USE or ont
33 - EdS
34 - 37  - should be blank as 33 must be disabled.
38 - Neutral bonding depends how it's installed by your installer, and physically bonding the correct wires
39 - NA (33 disabled)
Edited by Igubu
thank you for commenting. Can you post a picture of it after already done?
Some other engineering solutions were also offered, but my opinion is it’s a design issue from factory, so Axpert/Kodak/Growatt etc who all use the mainboard should recall and fix it themselves while these units are still new and under warranty.
I have the same fault 08 "Inverter bus voltage too high" popping up on my Must Power PV18-5048VHM inverter with the setup below:
  • No PV panels installed
  • 1 x Pylontech 3000C battery without comms cable
  • Inverter wired into the DB as a UPS for my lights and plugs
  • Battery earth and inverter earth are connected to the DB earth
  • No other faults or issues
  • Mounted in garage
In both cases the fault occurred at night after load shedding when the battery was recharging. After resetting the inverter it operated normally until next night. Recently I had an issue with my earth at the Eskom box causing the prepaid meter to disconnect leaving me without power until Eskom fixed the earth connection on the neutral cable outside.
The second possible cause/contribution was that this was the first time in ages that I had parked my car in the garage after driving in a rain storm. The garage at at 10pm was very humid (almost steam sauna). Both faults also occurred very early in the morning when the garage cools down and there is possible condensing from the humidity.
The last issue could be that I had changed the battery charging rate down from 25A to 10A and I'm experimenting with higher charging rates to see if there is any pattern
The issue has been described a few times- you have to drop utility charging to minimum (2A?) and the problem should go away.
It's an inherent design problem, unless you solder resistors on, changing Util charging to 2A is the only workaround that helps. It has nothing to do with panels, grounding etc.
It does make it almost unusable - as 2A charging is very low - but at least better than it tripping.
to
  • Mounted in garage
After 6 rounds of testing I haven't been able to recreate error 08. The only condition missing is the rain with the wet car parked in the garage next to the inverter. My theory is that on my inverter error 08 is triggered by condensation and/or very high relative humidity
Sure it’s not just no loadshedding last week or so? It’s the discharge/charge from util that triggers it when adding loads.
Yes, I simulate load shedding by disconnecting Eskom for 3 hours while at home using my appliances normally. This discharges 1/3 to 1/2 of the pylontech 300C's capacity. I also bumped up the charging rate to 20A
On 2021/09/13 at 7:49 PM, Igubu said:
Hi Rochelle,
Hi there, apologies only seeing your response now.
we initially bonly had 1 x axpert 5kw 48v inverter , connected to 8 x 105ah lead acid batteries. and 12 x 380 w canadia solar panels  Never had issue with this system. Had whole house except geyser , oven and large ac connected.
Decided to split house to be able to run ac in summer. db board was split up by electrician.
Bought new axpert 5kw 48v mksII.
So now old inverter is just running lights on lead acids. plan was to parralel
inverters when the lead acids gave up ghost.
New inverter has 12 x canadian solar 450w panels . and 1 x Hubble 5.5kw 100ah lithium battery. it was running plugs, which is tvs  and 1 x fridge and 1 x freezer. Switched to gas stove and geyser
Kept getting voltage too high. Got told that some items are drawing more ah than my battery can provide  .
so installed 2nd 5.5kw 100ah battery. Voltage issue sorted.
But error 08 persisted .
Have received new firmware upgrade that I received from supplier to install . It seemed to work for a period of 2 weeks. or so we thought, we just had not had any rain.
So now I am contemplating putting all back onto my old inverter and sending the new one back. but doing that is going to cost me approximate 5 k just to switch and remove.
Current setting is 2a charge, and sbu. Never charges from grid only bypas when no solar and batteries arent enough.
I am going to try the settings as prescribed and cross my fingers.
thank you for the time you took to respond.
Edited by rochelle
Hi Rochelle,
Seems it’s been a journey! My first solar system 9 years ago was 2x old axperts and 4x 200ah gels - worked well for a few years - inverters anyways… somewhere in the last 2-3 years axpert changed design, possibly outsourced something to get it made cheaper.. and they started supplying numerous other companies with the same flawed design.. (kodak,mecer,rct,growatt the list goes on….)
I’ll give you the correct advise,  but not what you probably want to hear. The error 8 will not go away, firmware will not help.
Loadshed etc is going to be a thing for many years- nobody wants to struggle. The rest of your components are very good (hubble has CAN as well)- get rid of the cheap axperts- return the one if you can, sell the other one to somebody for a few grand, and buy a proper hybrid inverter.
With a little management , maybe not even, a single 8kW sunsynk will make all your problems go away. You will be able to get at least 20% more usable capacity out of your 10kW battery bank because of CAN,  and the mppt’s themselves will probably generate 10-20% more power from the same panels - they really are that much more efficient than axperts!
Yes the 8kW is around  R34k, yes somebody (preferably a master installer - sunsynk has a list of them in SA) will charge you again to install- but probably the same as just changing things back. Simplify things, no more split db  boards, EVERYTHING on one inverter via 1 main DB.
Dont stress about it- solar is a journey, we all learn as we go, but believe
me it’s not worth struggling with Axperts.
Happy to explain anything around additional benefits and options around Sunsynks ( Have one myself)- but many others will also recommend them as the only worthwhile option.
* just read the old Post from a while back… see I repeated a few things :).. btw your SBU has to be on CSO, but read the old post on what that means. Also forgot to mention your sunsynk has 2x mppt inputs, split into 4x string inputs- so you can use both your pv arrays with one inverter, installer just needs to check string sizing-wiring, which will be different compared to Axperts..
Edited by Igubu
7 minutes ago, Igubu said:
Hi Rochelle,
Thanks, i have changed the settings for now, the axpertis unfortunately still under warranty, but i know what will happen. they will "fix" it and send it back .
I asked if they can take it back and i can pay in on a sunskyn.
Nope it has to be unused  and in the original box (facepalm) like really!
I have changed the setting to 2a and cso. though it started charging my batteries. i will set it to 0 a tomorrow. and see if it trips again during the rainy night tonight.
Thanks. Just so infuriating that teo of the same inverters can give such different service.
  • 6 months later...
Hi guys, any luck with this issue? I have an inverter on my test bench with only batteries(4 old Flooded)and mains connected. If i connect battery and switch on inverter it runs perfect with bus voltage at +-375v no load connected. If i turn the inverter to standby mode the bus-voltage climbs to 640v and if i then try to power it up i get error 08. Scenario 2 if i run in battery mode and turn mains on (ut1) in 2 min the inverter goes to error 08 bus-voltage of 640v.
what it looks like the dc-dc overshoots with no load.
Hi Stormpie,
It’s not a fixable issue, inherent design issue. Only work around is to set grid charge to min, think 2 amp or something, or disable charge from grid in CSO if possible.
Mine seems to have gone away. It may have had something to do with very high humidity or reducing the charging amps down to 20A on the pylontech.