On 2021/08/13 at 12:45 PM, TonyH said:

Here is a diagram that has passed COC422772407_InverterwiringsplitNeutralandEarthBarAsBuild.thumb.jpg.1babdb495f67b8bcc845eb42d90d16b0.jpg

Hi Tony, 

I am having Main E/L Tripping issues every time it rains, this is since my electrician installed an eath on my PV panels to an earth spike. 

Did you earth your PV panels ? 

My Sunsynk is currently Grid connected after the Mains E/L, not sure if this would be creating an issue. 

I have checked my pannels for leakage to earth, and there is none.

Link to comment
Share on other sites

Hi Colin, the panels must be earthed to protect against lightning and a faulty panel. My panels are earthed. The Inverter input should be after the feeding EL from your main panel as yours is. For the EL to trip because of rain, water has to connect the earth to the live or neutral. That is unlikely due to the earth spike. Is your earth spike linked to the earth of your common earth for the inverter and house earth (Grid earth)? The earth spike should also be connected to the output of the ATS 240 relay to pull the Inverter output neutral to earth when the Inverter is on Island mode. This prevents a floating voltage on your neutral which can be 80VAC or more.

Link to comment
Share on other sites

Thanks Tony, 

I came across this recommendation on the forum, and seems similar to your setup with the Inverter Grid connected before the Main E/L, so I'm going to give this a go. 

My house is old, and only has a combination OL-EL breaker wich is a 20 mA, so I will replace this with a 60 Amp OL Breaker, and a separate EL. 

Thanks for your response. 

image.png.5c721d8140ac1df6e8b71be024a7c882.png

Link to comment
Share on other sites

  • 2 weeks later...

Hi Colin

I see a possible change needed to this diagram ...

The 2 25A MCBs on the lines to the 2 SPDs should not be there. The aim of the SPD is to protect the inverter from surges on the Escom and/or load lines. these 25A breakers will trip before the 35A ones in the inverter line, thus only disconnecting the SPDs from the system, the 35A MCBs should be the ones to trip in the event there is a voltage surge, to isolate the inverter as fast as possible.

I trust that makes sense, and if I am wrong, will someone please correct me ... thanks

CharlieD

Link to comment
Share on other sites

  • 1 month later...
On 2022/03/13 at 7:28 AM, CharlesDavis said:

Hi Colin

I see a possible change needed to this diagram ...

The 2 25A MCBs on the lines to the 2 SPDs should not be there. The aim of the SPD is to protect the inverter from surges on the Escom and/or load lines. these 25A breakers will trip before the 35A ones in the inverter line, thus only disconnecting the SPDs from the system, the 35A MCBs should be the ones to trip in the event there is a voltage surge, to isolate the inverter as fast as possible.

I trust that makes sense, and if I am wrong, will someone please correct me ... thanks

CharlieD

Any confirmation on this ?

Link to comment
Share on other sites

Hey all

 

so I installed an 5kw sunsync last night with a hubble am2. I saw that i have a floting n-e volt of about 110V.Im scared that this might danage alpliances ect. Already popped the surge protection plug.

 

Im gonna install the relay tonight but my question is can i bridge straight to the Earth from the grid or do i definitely need to install an earth spike on the outside?

Link to comment
Share on other sites

2 hours ago, Be4dawn said:

Hey all

 

so I installed an 5kw sunsync last night with a hubble am2. I saw that i have a floting n-e volt of about 110V.Im scared that this might danage alpliances ect. Already popped the surge protection plug.

 

Im gonna install the relay tonight but my question is can i bridge straight to the Earth from the grid or do i definitely need to install an earth spike on the outside?

As far as I know, the earth can be bridged but the neutrals have to be separated. 

Link to comment
Share on other sites

On 2022/03/13 at 7:28 AM, CharlesDavis said:

Hi Colin

I see a possible change needed to this diagram ...

The 2 25A MCBs on the lines to the 2 SPDs should not be there. The aim of the SPD is to protect the inverter from surges on the Escom and/or load lines. these 25A breakers will trip before the 35A ones in the inverter line, thus only disconnecting the SPDs from the system, the 35A MCBs should be the ones to trip in the event there is a voltage surge, to isolate the inverter as fast as possible.

I trust that makes sense, and if I am wrong, will someone please correct me ... thanks

CharlieD

Thanks, agreed. 

I have not installed the SPD's on my install as the Sunsynk already has internal SPD's.  

The relay for the eath bond is a must though to het rid of the floating neutral when in island mode. 

Link to comment
Share on other sites

On 2022/04/21 at 3:54 PM, PowerUser said:

As far as I know, the earth can be bridged but the neutrals have to be separated. 

You cannot bridge the municipal Neutral and Earth even if it's to a separate Earth Spike, this will cause an earth trip on your Mains. 

Neutrals on the inverter input and output are bonded internally in the Sunsynk in "Normal" operating mode, so you cannot put a permanent earth bond on the inverter output Neutral. You need to use a relay so the Inverter output Neutral is only bonded to earth in when in Island mode. 

Hop this makes sense. 

Link to comment
Share on other sites

7 hours ago, Colin B said:

You cannot bridge the municipal Neutral and Earth even if it's to a separate Earth Spike, this will cause an earth trip on your Mains. 

Neutrals on the inverter input and output are bonded internally in the Sunsynk in "Normal" operating mode, so you cannot put a permanent earth bond on the inverter output Neutral. You need to use a relay so the Inverter output Neutral is only bonded to earth in when in Island mode. 

Hop this makes sense. 

I think, you misunderstood the question. @Be4dawn was asking, if he can bridge the municipal earth with the inverter earth. Even in your diagram, those appear to be bridged.

Edited by PowerUser
Link to comment
Share on other sites

  • 2 months later...
  • 2 months later...
On 2021/08/07 at 4:34 PM, abeetude said:

Step 1 -  Ensure "Islanding Mode" is selected on the Inverter

Step 2 - Remove the BLACK NEUTRAL wire which is currently screwed into the NC (Normally Closed) terminal

image.png.08ce1e998f97bd5adffd08201e1454fc.png

 

Step 2 - Connect the removed  BLACK NEUTRAL wire and connect it to the NO (Normally Open) terminal

image.png.91d232a03bf9f5d27cc5d3c80e883081.png

 

Step 3 - Connect from the Inverter ATS240V a cable to the relay pins 14 & 13

image.png.efa46472751a00341ecca7d08584d4f9.png

image.png.341e2e5dbd29ae59abf9210a44493335.png

image.png.af16e72f680ba138e6865844d1bb35c2.png

Step 4 - Connect N from the connector block to N on the Inverter LOAD and E to Earth on the Inverter

image.png.96dc2c30fa265b83bda107c435ec65e7.png

Hope that helps.

@Leshen Helped me figure it out a while ago so kudo's to him...

 

 

image.png

This worked perfectly for me too. The instructions received from Segen Solar for their unit is entirely incorrect regarding numbering of the terminals and how to connect it.

 

 

Link to comment
Share on other sites

  • 3 weeks later...

So when I do my install I must have the grid neutral and the inverter load neutral separated in my DB? 

So there will be 2 separate neutral bars? 

And then ofcourse install a relay. 

Does the relay earth have to go to a ground spike or can it go to the earth from the inverter/municipal DB earth? 

Edited by Chris_S
Link to comment
Share on other sites

  • 3 weeks later...
  • 1 month later...

I'm an electronics engineer not a power engineer, so the following may or may not be relevant, but I've worked in several places around the world and this definitely happens.

"Earth" is not the same everywhere, and it's not necessarily the same in any one place all the time. You can often measure a distinct E-E voltage between two earth spikes depending on their distance apart and the conductivity of the soil, especially between wet and dry. So quite where one binds earth and neutral in a distributed (eg farm) environment like mine always bothers me We have an earth spike at every DB (Eskom in, houses, shed, pumphouse etc) with EL units protecting everything. The one thing I haven't yet done on my new installation is install the E-N link relay, because frankly it bothers me. Not connecting netralsin a small system I get, but I've had some fairly serious tickles in my pump house because of untied neutrals, especially when drawing fairly large power across fairly long distances. Also, floating neutral voltages are a major potential source of RF interference (that used to be my field), upsetting TVs, radios, walkie talkies etc.

Link to comment
Share on other sites

  • 2 months later...
On 2022/09/28 at 12:09 AM, Chris_S said:

So when I do my install I must have the grid neutral and the inverter load neutral separated in my DB? 

So there will be 2 separate neutral bars? 

And then ofcourse install a relay. 

Does the relay earth have to go to a ground spike or can it go to the earth from the inverter/municipal DB earth? 

I have the same situation and would just like to confirm:

I understand that the neutrals need to be separate and that the N/E bonding needs to happen when there is no grid (via relay/contactor), but my house has a N/E bond where the cables come into the house, so bonding Neutral to Earth when there is no grid connection will indirectly connect the inverter Neutral to the Grid neutral as they are bonded.

Would this be an issue?

Link to comment
Share on other sites

  • 7 months later...
 

Hi there, would this contactor not make this easier and simplify installation? Link below.

MC1-20 Onesto Contactor 2Pole 20A 230V (12937)

 

 

 

 

 

Step 1 -  Ensure "Islanding Mode" is selected on the Inverter

Step 2 - Remove the BLACK NEUTRAL wire which is currently screwed into the NC (Normally Closed) terminal

image.png.08ce1e998f97bd5adffd08201e1454fc.png

 

Step 2 - Connect the removed  BLACK NEUTRAL wire and connect it to the NO (Normally Open) terminal

image.png.91d232a03bf9f5d27cc5d3c80e883081.png

 

Step 3 - Connect from the Inverter ATS240V a cable to the relay pins 14 & 13

image.png.efa46472751a00341ecca7d08584d4f9.png

image.png.341e2e5dbd29ae59abf9210a44493335.png

image.png.af16e72f680ba138e6865844d1bb35c2.png

Step 4 - Connect N from the connector block to N on the Inverter LOAD and E to Earth on the Inverter

image.png.96dc2c30fa265b83bda107c435ec65e7.png

Hope that helps.

@Leshen Helped me figure it out a while ago so kudo's to him...

 

 

image.png

 

Link to comment
Share on other sites

  • 2 weeks later...

Good Day All

I have purchased a Sunsync inverter and am about to have it installed but I need to ensure that i have all the components on hand for when it's being installed. While this thread is quite detailed, I have been hearing mixed information about a relay and whether it is still required for a 5kva Sunsync inverter which has an ATS240.

1. Is the Sunsync inverters sold in 2023, still require the relay if it has an ATS240? Seems Growatt's has it built in.

2. Is there a way to wire the inverter so that the relay is not required?

3. Which relay exactly is required? Please provide a link

Link to comment
Share on other sites

 

Good Day All

I have purchased a Sunsync inverter and am about to have it installed but I need to ensure that i have all the components on hand for when it's being installed. While this thread is quite detailed, I have been hearing mixed information about a relay and whether it is still required for a 5kva Sunsync inverter which has an ATS240.

1. Is the Sunsync inverters sold in 2023, still require the relay if it has an ATS240? Seems Growatt's has it built in.

2. Is there a way to wire the inverter so that the relay is not required?

3. Which relay exactly is required? Please provide a link

1. Yes. Growatt is a off grid inverter unlike the Sunsynk

2. No

3.  Any 10A or higher relay or even a small contactor. 220V AC coil with 2 N/C contacts. 

Edited by Scorp007
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...