March 26, 20242 yr On 2024/03/13 at 2:43 PM, Joerg said: I have less than 100 until now. Another file with the datapoints I am actually polling (I don't need many of the other points so I left them out) Sunsynk 8k LG01 modbus register in use.xlsx 13.79 kB · 7 downloads To whom it may concern: I solved most of my problems reading registers recently with a Firmware update...
March 28, 20242 yr On 2024/03/26 at 1:17 PM, Gambit said: Did Sunsynk support provide any register documentation for their batteries? No they didn't but to be fair I didn't ask for it as I don't have their batteries.
April 16, 20242 yr Hello @kellerza, Not sure if this helps. I have tried a few things. This is on the EDGE branch with 50kw HV Sunsynk. The addon would crash after around 5 to 10 minutes of running, changing the sheduling to the solarman example appears to have helped stabilise the addon. What I do notice now that I understand the inverter setup better is that the battery data is not reading correctly. There are actually two battery inputs and so the battery_power and battery_current are meant to be the summed values from battery_1_power + battery_2_power and battery_1_current + battery_2_current respectively. The battery_voltage and battery_power are both reporting a value 10x below what would be expected. Here is some of the debug log showing some errors. 2024-04-16 10:12:22,286 DEBUG pymodbus.logging Getting Frame - 0x3 0x2 0xfe 0x4a 2024-04-16 10:12:22,286 DEBUG pymodbus.logging Factory Response[ReadHoldingRegistersResponse': 3] 2024-04-16 10:12:22,286 DEBUG pymodbus.logging Frame advanced, resetting header!! 2024-04-16 10:12:22,286 DEBUG pymodbus.logging Getting transaction 1 2024-04-16 10:12:22,286 DEBUG pymodbus.logging Unrequested message: ReadHoldingRegistersResponse (1) 2024-04-16 10:12:22,286 DEBUG pymodbus.logging Frame - not ready 2024-04-16 10:12:22,287 DEBUG sunsynk.sunsynk Time taken to fetch 4 registers starting at 616 : 6.07s 2024-04-16 10:12:22,287 WARNING sunsynk.sunsynk Did not complete read, only read 8/4 2024-04-16 10:12:22,287 DEBUG sunsynk.sunsynk Request registers: [616, 617, 618, 619] glen=4. Response [100, 500, 900, 1500, 1700, 2100, 4000, 4000] len=8. regs={616: 100, 617: 500, 618: 900, 619: 1500, 620: 1700, 621: 2100, 622: 4000, 623: 4000} 2024-04-16 10:12:22,288 DEBUG pymodbus.logging Adding transaction 1 2024-04-16 10:12:22,288 DEBUG pymodbus.logging send: 0x1 0x3 0x2 0x6e 0x0 0x4 0x24 0x6c 2024-04-16 10:12:22,323 DEBUG pymodbus.logging recv: 0x1 0x3 0x8 old_data: addr=None 2024-04-16 10:12:22,323 DEBUG pymodbus.logging Processing: 0x1 0x3 0x8 2024-04-16 10:12:22,323 DEBUG pymodbus.logging Frame - not ready 2024-04-16 10:12:22,339 DEBUG pymodbus.logging recv: 0xff 0xe4 0xff 0xe2 0x0 0x4d 0x0 0x13 0x43 0x1e old_data: addr=None 2024-04-16 10:12:22,339 DEBUG pymodbus.logging Processing: 0xff 0xe4 0xff 0xe2 0x0 0x4d 0x0 0x13 0x43 0x1e 2024-04-16 10:12:22,339 DEBUG pymodbus.logging Frame - not ready 2024-04-16 10:12:25,291 DEBUG pymodbus.logging Adding transaction 1 2024-04-16 10:12:25,291 DEBUG pymodbus.logging send: 0x1 0x3 0x2 0x6e 0x0 0x4 0x24 0x6c 2024-04-16 10:12:25,330 DEBUG pymodbus.logging recv: 0x1 0x3 0x8 0xff old_data: addr=None 2024-04-16 10:12:25,330 DEBUG pymodbus.logging Processing: 0x1 0x3 0x8 0xff 2024-04-16 10:12:25,330 DEBUG pymodbus.logging Frame - not ready 2024-04-16 10:12:28,294 DEBUG pymodbus.logging Adding transaction 1 2024-04-16 10:12:28,294 DEBUG pymodbus.logging send: 0x1 0x3 0x2 0x6e 0x0 0x4 0x24 0x6c 2024-04-16 10:12:28,337 DEBUG pymodbus.logging recv: 0x1 0x3 0x8 0xff 0xe2 0xff old_data: addr=None 2024-04-16 10:12:28,337 DEBUG pymodbus.logging Processing: 0x1 0x3 0x8 0xff 0xe2 0xff 2024-04-16 10:12:28,337 DEBUG pymodbus.logging Frame - not ready 2024-04-16 10:12:28,353 DEBUG pymodbus.logging recv: 0xe1 0x0 0x4c 0x0 0xf 0x31 0x17 old_data: addr=None 2024-04-16 10:12:28,353 DEBUG pymodbus.logging Processing: 0xe1 0x0 0x4c 0x0 0xf 0x31 0x17 2024-04-16 10:12:28,353 DEBUG pymodbus.logging Frame - not ready Please let me know if there is something I can do to try and get the addon improved.
June 3, 20242 yr Hi everybody! So I've been running my ESPHome + Sunsynk 12kva for many months now without issue. Then a few days ago it started showing weird stats like 40,000% battery charge and 60k kw solar. It would record these readings intermittently, so if I looked at my history graphs there'd be insane spikes that would last minutes to hours. I figured it was loose connections as I never soldered the wires and that's caused issues before, no dice. Now, after fiddling with the wires, its not even reporting data. I reinstalled ESPHome with my .yaml onto the ESP32, no dice. Ran the log and found this (see screenshots) Has sunsynk changed some modbus addresses or is my EPS32 just cooked? I checked my .yaml and there are no duplicates.
June 4, 20242 yr BEWARE OF GENERIC ESP32 BOARDS VOLTAGE SUPPLY SUPPLY ON VS Good day all. I have discovered that the power of ESP dev board is problematic. If you test the power on the bottom Left of the board you only get 1.8-2,4 Volt. This causes a brownout as soon as you connect the TTL-Rs485 Converter. What I have done to get it right is to take the GND on the right hand side and the VIN on the Left side. Just a not if someone comes across this. Thanks al for all the great info and code !!!!!!! Happy Tinkering Edited June 4, 20242 yr by JAndy
June 7, 20242 yr Hello everyone. I wonder if there is a chance to control the "Smart Load" output from Home Assistant. I would like to automate it so that when the water in the hot water tank is heated to a set temperature, the "smart load" output is turned off. Edited June 7, 20242 yr by sarzyk
June 7, 20242 yr Author Hi @sarzyk There are Modbus addresses for Smart Loads, have no experience with them though and I don't think that they are in the default Slipx's code. I think that it might be easier to just put in a smart switch with power monitoring (ewelink) preferably as they are easier to link to HA.
June 7, 20242 yr Author On 2024/06/04 at 12:33 AM, BobTheDinosaur said: Hi everybody! So I've been running my ESPHome + Sunsynk 12kva for many months now without issue. Then a few days ago it started showing weird stats like 40,000% battery charge and 60k kw solar. It would record these readings intermittently, so if I looked at my history graphs there'd be insane spikes that would last minutes to hours. I figured it was loose connections as I never soldered the wires and that's caused issues before, no dice. Now, after fiddling with the wires, its not even reporting data. I reinstalled ESPHome with my .yaml onto the ESP32, no dice. Ran the log and found this (see screenshots) Has sunsynk changed some modbus addresses or is my EPS32 just cooked? I checked my .yaml and there are no duplicates. Lets see the code, looks like you might have multiple modbus controllers as it talks about Modbuscontroller:136 & 043? Maybe something with one of the ESPHome updates
June 7, 20242 yr Author On 2024/06/04 at 1:22 PM, JAndy said: BEWARE OF GENERIC ESP32 BOARDS VOLTAGE SUPPLY SUPPLY ON VS Good day all. I have discovered that the power of ESP dev board is problematic. If you test the power on the bottom Left of the board you only get 1.8-2,4 Volt. This causes a brownout as soon as you connect the TTL-Rs485 Converter. What I have done to get it right is to take the GND on the right hand side and the VIN on the Left side. Just a not if someone comes across this. Thanks al for all the great info and code !!!!!!! Happy Tinkering Best RS485 controller is the one from @iiznh at smarthomeintegrations.co.za as it includes the power supply and a 3.3v RS485 interface, most of the separate boards have 5V RS485 and seem to be rather problematic.
June 10, 20242 yr On 2024/06/07 at 7:44 AM, Sc00bs said: Best RS485 controller is the one from @iiznh at smarthomeintegrations.co.za as it includes the power supply and a 3.3v RS485 interface, most of the separate boards have 5V RS485 and seem to be rather problematic. I agree. Smarthomeintegrations.co.za is the best, this observation was before I had a board. Just putting it out there for reference if someone used the "old" method.
June 11, 20242 yr On 2024/06/07 at 7:41 AM, Sc00bs said: Lets see the code, looks like you might have multiple modbus controllers as it talks about Modbuscontroller:136 & 043? Maybe something with one of the ESPHome updates So I've found that the read error is only when my batteries are at minimum, which is 15% (then it reports 44,474% almost constantly), or when SunSynk Day PV is at zero then it reports 6,483.1 kWh every hour or so, and SunSynk Day Grid Import just randomly reports 1,333kWh Here comes the code: ##########################WARNING HAS NOT BEEN TESTED USE AT YOUR OWN RISK ######################################## # Based on https://github.com/kellerza/sunsynk/blob/main/src/sunsynk/definitions3ph.py # substitutions: settings_skipped_updates: "10" devicename: sunsynk device_description: "Sunsynk RS485 Logger" friendly_name: "SunSynk" esphome: name: $devicename comment: '${device_description}' esp32: board: nodemcu-32s framework: type: arduino # Enable logging logger: baud_rate: 0 # Enable Home Assistant API api: encryption: key: "" ota: password: "" wifi: ssid: password # Enable fallback hotspot (captive portal) in case wifi connection fails ap: ssid: '${devicename}' password: fallback_password fast_connect: true power_save_mode: none captive_portal: # Enable time component to reset energy at midnight # https://esphome.io/components/time.html#home-assistant-time-source time: - platform: homeassistant id: homeassistant_time uart: id: mod_bus tx_pin: GPIO17 rx_pin: GPIO16 baud_rate: 9600 stop_bits: 1 modbus: id: sunsynk_modbus flow_control_pin: GPIO4 modbus_controller: - id: sunsynk address: 0x01 modbus_id: sunsynk_modbus setup_priority: -10 update_interval: "15s" command_throttle: "50ms" ############################################### BINARY SENSORS ######################################## binary_sensor: - platform: modbus_controller # 552 Grid Connected Status modbus_controller_id: sunsynk name: "${friendly_name} Grid Connected Status" id: sunsynk_esphome_grid_connected_status register_type: holding address: 552 # SENSORS # ####################################################################################################### ############################################### BATTERY ############################################### sensor: - platform: modbus_controller modbus_controller_id: sunsynk name: '${friendly_name} Battery Temperature' id: sunsynk_esphome_battery_temperature register_type: holding address: 586 unit_of_measurement: °C accuracy_decimals: 1 device_class: temperature state_class: measurement value_type: U_WORD filters: - offset: -1000 - multiply: 0.1 - platform: modbus_controller # 587 Battery Voltage modbus_controller_id: sunsynk name: "${friendly_name} Battery Voltage" id: sunsynk_esphome_battery_voltage register_type: holding address: 587 unit_of_measurement: "V" accuracy_decimals: 1 device_class: voltage state_class: measurement filters: - multiply: 0.01 value_type: U_WORD - platform: modbus_controller # 588 Battery SOC modbus_controller_id: sunsynk name: "${friendly_name} Battery SOC" id: sunsynk_esphome_battery_soc register_type: holding address: 588 unit_of_measurement: "%" accuracy_decimals: 0 device_class: battery value_type: U_WORD - platform: modbus_controller # 590 Battery Power modbus_controller_id: sunsynk name: "${friendly_name} Battery Power" id: sunsynk_esphome_battery_power register_type: holding address: 590 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power value_type: S_WORD - platform: modbus_controller # 591 Battery Current modbus_controller_id: sunsynk name: "${friendly_name} Battery Current" id: sunsynk_esphome_battery_current register_type: holding address: 591 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement value_type: S_WORD filters: - multiply: 0.01 - platform: modbus_controller # 115 Battery Capacity Shutdown modbus_controller_id: sunsynk name: "${friendly_name} Battery Capacity Shutdown" id: sunsynk_esphome_battery_capacity_shutdown register_type: holding address: 115 unit_of_measurement: "%" accuracy_decimals: 0 device_class: battery ############################################### INVERTER ############################################## - platform: modbus_controller # 636 Inverter Power modbus_controller_id: sunsynk name: "${friendly_name} Inverter Power" id: sunsynk_esphome_inverter_power register_type: holding address: 636 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power value_type: S_WORD - platform: modbus_controller # 633 Inverter L1 Power modbus_controller_id: sunsynk name: "${friendly_name} Inverter L1 Power" id: sunsynk_esphome_inverter_L1_power register_type: holding address: 633 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power value_type: S_WORD - platform: modbus_controller # 634 Inverter L2 Power modbus_controller_id: sunsynk name: "${friendly_name} Inverter L2 Power" id: sunsynk_esphome_inverter_L2_power register_type: holding address: 634 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power value_type: S_WORD - platform: modbus_controller # 635 Inverter L3 Power modbus_controller_id: sunsynk name: "${friendly_name} Inverter L3 Power" id: sunsynk_esphome_inverter_L3_power register_type: holding address: 635 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power value_type: S_WORD - platform: modbus_controller # 627 Inverter Voltage modbus_controller_id: sunsynk name: "${friendly_name} Inverter Voltage" id: sunsynk_esphome_inverter_voltage register_type: holding address: 627 unit_of_measurement: "V" accuracy_decimals: 1 device_class: voltage state_class: measurement filters: - multiply: 0.1 value_type: U_WORD - platform: modbus_controller # 638 Inverter Frequency modbus_controller_id: sunsynk name: "${friendly_name} Inverter Frequency" id: sunsynk_esphome_inverter_frequency register_type: holding address: 638 unit_of_measurement: "Hz" accuracy_decimals: 2 filters: - multiply: 0.01 value_type: U_WORD state_class: measurement ############################################### GRID ################################################## - platform: modbus_controller # 609 Grid Frequency modbus_controller_id: sunsynk name: "${friendly_name} Grid Frequency" id: sunsynk_esphome_grid_frequency register_type: holding address: 609 unit_of_measurement: "Hz" accuracy_decimals: 2 filters: - multiply: 0.01 value_type: U_WORD state_class: measurement - platform: modbus_controller # 625 Grid Power modbus_controller_id: sunsynk name: "${friendly_name} Grid Power" id: sunsynk_esphome_grid_power register_type: holding address: 625 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 622 Grid L1 Power modbus_controller_id: sunsynk name: "${friendly_name} Grid L1 Power" id: sunsynk_esphome_grid_power_L1 register_type: holding address: 622 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 623 Grid L2 Power modbus_controller_id: sunsynk name: "${friendly_name} Grid L2 Power" id: sunsynk_esphome_grid_power_L2 register_type: holding address: 623 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 624 Grid L3 Power modbus_controller_id: sunsynk name: "${friendly_name} Grid L3 Power" id: sunsynk_esphome_grid_power_L3 register_type: holding address: 624 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 600 Grid Voltage modbus_controller_id: sunsynk name: "${friendly_name} Grid Voltage" id: sunsynk_esphome_grid_voltage register_type: holding address: 600 unit_of_measurement: "V" accuracy_decimals: 1 device_class: voltage state_class: measurement filters: - multiply: 0.1 value_type: U_WORD - platform: modbus_controller # 610 Grid L1 Current modbus_controller_id: sunsynk name: "${friendly_name} Grid L1 Current" id: sunsynk_esphome_grid_current_L1 register_type: holding address: 610 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement value_type: S_WORD filters: - multiply: 0.01 - platform: modbus_controller # 611 Grid L2 Current modbus_controller_id: sunsynk name: "${friendly_name} Grid L2 Current" id: sunsynk_esphome_grid_current_L2 register_type: holding address: 160 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement value_type: S_WORD filters: - multiply: 0.01 - platform: modbus_controller # 612 Grid L3 Current modbus_controller_id: sunsynk name: "${friendly_name} Grid L3 Current" id: sunsynk_esphome_grid_current_L3 register_type: holding address: 160 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement value_type: S_WORD filters: - multiply: 0.01 - platform: modbus_controller # 619 Grid CT Power modbus_controller_id: sunsynk name: "${friendly_name} Grid CT Power" id: sunsynk_esphome_grid_ct_power register_type: holding address: 619 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD ############################################### LOAD ################################################ - platform: modbus_controller # 653 Load Power modbus_controller_id: sunsynk name: "${friendly_name} Load Power" id: sunsynk_esphome_load_power register_type: holding address: 653 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 650 Load L1 Power modbus_controller_id: sunsynk name: "${friendly_name} Load L1 Power" id: sunsynk_esphome_load_l1_power register_type: holding address: 650 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 651 Load L2 Power modbus_controller_id: sunsynk name: "${friendly_name} Load L2 Power" id: sunsynk_esphome_load_l2_power register_type: holding address: 651 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 651 Load L3 Power modbus_controller_id: sunsynk name: "${friendly_name} Load L3 Power" id: sunsynk_esphome_load_l3_power register_type: holding address: 652 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD ############################################### SOLAR PV1 ############################################# - platform: modbus_controller # 672 PV1 Power modbus_controller_id: sunsynk name: "${friendly_name} PV1 Power" id: sunsynk_esphome_pv1_power register_type: holding address: 672 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: U_WORD - platform: modbus_controller # 676 PV1 Voltage modbus_controller_id: sunsynk name: "${friendly_name} PV1 Voltage" id: sunsynk_esphome_pv1_voltage register_type: holding address: 676 unit_of_measurement: "V" device_class: voltage state_class: measurement accuracy_decimals: 1 filters: - multiply: 0.1 value_type: U_WORD - platform: modbus_controller # 677 PV1 Current modbus_controller_id: sunsynk name: "${friendly_name} PV1 Current" id: sunsynk_esphome_pv1_current register_type: holding address: 677 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement filters: - multiply: 0.1 value_type: U_WORD ############################################### SOLAR PV2 ############################################# - platform: modbus_controller # 673 PV2 Power modbus_controller_id: sunsynk name: "${friendly_name} PV2 Power" id: sunsynk_esphome_pv2_power register_type: holding address: 673 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: U_WORD - platform: modbus_controller # 678 PV2 Voltage modbus_controller_id: sunsynk name: "${friendly_name} PV2 Voltage" id: sunsynk_esphome_pv2_voltage register_type: holding address: 678 unit_of_measurement: "V" accuracy_decimals: 1 filters: - multiply: 0.1 device_class: voltage state_class: measurement value_type: U_WORD - platform: modbus_controller # 679 PV2 Current modbus_controller_id: sunsynk name: "${friendly_name} PV2 Current" id: sunsynk_esphome_pv2_current register_type: holding address: 679 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement filters: - multiply: 0.1 value_type: U_WORD ############################################### SOLAR PV3 ############################################# - platform: modbus_controller # 674 PV3 Power modbus_controller_id: sunsynk name: "${friendly_name} PV3 Power" id: sunsynk_esphome_pv3_power register_type: holding address: 674 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: U_WORD - platform: modbus_controller # 680 PV3 Voltage modbus_controller_id: sunsynk name: "${friendly_name} PV3 Voltage" id: sunsynk_esphome_pv3_voltage register_type: holding address: 680 unit_of_measurement: "V" accuracy_decimals: 1 filters: - multiply: 0.1 device_class: voltage state_class: measurement value_type: U_WORD - platform: modbus_controller # 681 PV3 Current modbus_controller_id: sunsynk name: "${friendly_name} PV3 Current" id: sunsynk_esphome_pv3_current register_type: holding address: 681 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement filters: - multiply: 0.1 value_type: U_WORD ############################################### SOLAR PV4 ############################################# - platform: modbus_controller # 675 PV4 Power modbus_controller_id: sunsynk name: "${friendly_name} PV4 Power" id: sunsynk_esphome_pv4_power register_type: holding address: 675 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: U_WORD - platform: modbus_controller # 682 PV4 Voltage modbus_controller_id: sunsynk name: "${friendly_name} PV4 Voltage" id: sunsynk_esphome_pv4_voltage register_type: holding address: 682 unit_of_measurement: "V" accuracy_decimals: 1 filters: - multiply: 0.1 device_class: voltage state_class: measurement value_type: U_WORD - platform: modbus_controller # 683 PV4 Current modbus_controller_id: sunsynk name: "${friendly_name} PV4 Current" id: sunsynk_esphome_pv4_current register_type: holding address: 683 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement filters: - multiply: 0.1 value_type: U_WORD ############################################### SOLAR TOTAL ########################################### - platform: template # Sum of PV1 and PV2 to get total PV Power name: "${friendly_name} Solar Power" unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement lambda: |- return (id(sunsynk_esphome_pv1_power).state + id(sunsynk_esphome_pv2_power).state + id(sunsynk_esphome_pv3_power).state + id(sunsynk_esphome_pv4_power).state); update_interval: 5s ############################################### OUTPUTS ############################################### - platform: modbus_controller # 667 Gen Power modbus_controller_id: sunsynk name: "${friendly_name} Gen Power" id: sunsynk_esphome_gen_power register_type: holding address: 667 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 664 Gen L1 Power modbus_controller_id: sunsynk name: "${friendly_name} Gen L1 Power" id: sunsynk_esphome_gen_l1_power register_type: holding address: 664 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 665 Gen L2 Power modbus_controller_id: sunsynk name: "${friendly_name} Gen L2 Power" id: sunsynk_esphome_gen_l2_power register_type: holding address: 665 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 666 Gen L3 Power modbus_controller_id: sunsynk name: "${friendly_name} Gen L3 Power" id: sunsynk_esphome_gen_L3_power register_type: holding address: 666 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD ############################################### ENERGY ################################################ - platform: modbus_controller # 514 Day Battery Charge modbus_controller_id: sunsynk name: "${friendly_name} Day Battery Charge" id: sunsynk_esphome_day_battery_charge register_type: holding address: 514 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 515 Day Battery Discharge modbus_controller_id: sunsynk name: "${friendly_name} Day Battery Discharge" id: sunsynk_esphome_day_battery_discharge register_type: holding address: 515 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 516 Total Battery Charge modbus_controller_id: sunsynk name: "${friendly_name} Total Battery Charge" id: sunsynk_esphome_total_battery_charge register_type: holding address: 516 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing value_type: U_DWORD_R filters: - multiply: 0.1 - platform: modbus_controller # 518 Total Battery Discharge modbus_controller_id: sunsynk name: "${friendly_name} Total Battery Discharge" id: sunsynk_esphome_total_battery_discharge register_type: holding address: 518 unit_of_measurement: "kWh" accuracy_decimals: 0 device_class: energy state_class: total_increasing value_type: U_DWORD_R filters: - multiply: 0.1 - platform: modbus_controller # 520 Day Grid Import modbus_controller_id: sunsynk name: "${friendly_name} Day Grid Import" id: sunsynk_esphome_day_grid_import register_type: holding address: 520 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 521 Day Grid Export modbus_controller_id: sunsynk name: "${friendly_name} Day Grid Export" id: sunsynk_esphome_day_grid_export register_type: holding address: 521 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 522 Total Grid Import modbus_controller_id: sunsynk name: "${friendly_name} Total Grid Import" id: sunsynk_esphome_total_grid_import register_type: holding address: 522 unit_of_measurement: "kWh" accuracy_decimals: 2 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 524 Total Grid Export modbus_controller_id: sunsynk name: "${friendly_name} Total Grid Export" id: sunsynk_esphome_total_grid_export register_type: holding address: 524 unit_of_measurement: "kWh" accuracy_decimals: 2 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 526 Day Load Energy modbus_controller_id: sunsynk name: "${friendly_name} Day Load Energy" id: sunsynk_esphome_day_load_energy register_type: holding address: 526 unit_of_measurement: "kWh" accuracy_decimals: 2 device_class: energy state_class: total_increasing filters: - multiply: 0.1 value_type: U_WORD - platform: modbus_controller # 527 Total Load Energy modbus_controller_id: sunsynk name: "${friendly_name} Total Load Energy" id: sunsynk_esphome_total_load_energy register_type: holding address: 527 unit_of_measurement: "kWh" accuracy_decimals: 2 device_class: energy state_class: total_increasing value_type: U_DWORD_R filters: - multiply: 0.1 - platform: modbus_controller # 534 Total PV Energy modbus_controller_id: sunsynk name: "${friendly_name} Total PV Energy" id: sunsynk_esphome_total_pv_energy register_type: holding address: 534 unit_of_measurement: "kWh" accuracy_decimals: 2 device_class: energy state_class: total_increasing filters: - multiply: 0.1 value_type: U_DWORD_R - platform: modbus_controller # 529 Day PV Energy modbus_controller_id: sunsynk name: "${friendly_name} Day PV Energy" id: sunsynk_esphome_day_pv_energy register_type: holding address: 529 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing filters: - multiply: 0.1 value_type: U_WORD ############################################### TEMPERATURE ################################################ - platform: modbus_controller # 540 DC Transformer Temperature modbus_controller_id: sunsynk name: "${friendly_name} DC Transformer Temperature" id: sunsynk_esphome_dc_transformer_temperature register_type: holding address: 540 unit_of_measurement: "°C" accuracy_decimals: 1 device_class: temperature state_class: measurement value_type: S_WORD filters: - offset: -1000 - multiply: 0.1 - platform: modbus_controller # 541 Radiator Temperature modbus_controller_id: sunsynk name: "${friendly_name} Radiator Temperature" id: sunsynk_esphome_radiator_temperature register_type: holding address: 541 unit_of_measurement: "°C" accuracy_decimals: 1 device_class: temperature state_class: measurement value_type: S_WORD filters: - offset: -1000 - multiply: 0.1 ################################################ READ SETTINGS ############################################# - platform: modbus_controller # 148 System Mode Time 1 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time1" id: sunsynk_esphome_system_mode_time1 register_type: holding skip_updates: ${settings_skipped_updates} address: 148 icon: "mdi:clock" - platform: modbus_controller # 149 System Mode Time 2 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time2" id: sunsynk_esphome_system_mode_time2 register_type: holding skip_updates: ${settings_skipped_updates} address: 149 icon: "mdi:clock" - platform: modbus_controller # 150 System Mode Time 3 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time3" id: sunsynk_esphome_system_mode_time3 register_type: holding skip_updates: ${settings_skipped_updates} address: 150 icon: "mdi:clock" - platform: modbus_controller # 151 System Mode Time 4 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time4" id: sunsynk_esphome_system_mode_time4 register_type: holding skip_updates: ${settings_skipped_updates} address: 151 icon: "mdi:clock" - platform: modbus_controller # 152 System Mode Time 5 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time5" id: sunsynk_esphome_system_mode_time5 register_type: holding skip_updates: ${settings_skipped_updates} address: 152 icon: "mdi:clock" - platform: modbus_controller # 153 System Mode Time 6 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time6" id: sunsynk_esphome_system_mode_time6 register_type: holding skip_updates: ${settings_skipped_updates} address: 153 icon: "mdi:clock" ################################################ WRITE SETTINGS ############################################ switch: - platform: modbus_controller # 145 Toggle Solar Sell use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} Toggle Solar sell" id: sunsynk_esphome_toggle_solar_sell register_type: holding address: 145 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 146 Toggle System Timer use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} Toggle System Timer" id: sunsynk_esphome_toggle_Time_of_Use register_type: holding address: 146 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 141 Priority Load use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} Toggle Priority Load" id: sunsynk_esphome_toggle_priority_load register_type: holding address: 141 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 172 System Mode Grid Charge Time 1 use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} System Mode Grid Charge Time1" id: sunsynk_esphome_toggle_grid_charge_time1 register_type: holding address: 172 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 173 System Mode Grid Charge Time 2 modbus_controller_id: sunsynk use_write_multiple: true name: "${friendly_name} System Mode Grid Charge Time2" id: sunsynk_esphome_toggle_grid_charge_time2 register_type: holding address: 173 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 174 System Mode Grid Charge Time 3 modbus_controller_id: sunsynk use_write_multiple: true name: "${friendly_name} System Mode Grid Charge Time3" id: sunsynk_esphome_toggle_grid_charge_time3 register_type: holding address: 174 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 175 System Mode Grid Charge Time 4 modbus_controller_id: sunsynk use_write_multiple: true name: "${friendly_name} System Mode Grid Charge Time4" id: sunsynk_esphome_toggle_grid_charge_time4 register_type: holding address: 175 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 176 System Mode Grid Charge Time 5 modbus_controller_id: sunsynk use_write_multiple: true name: "${friendly_name} System Mode Grid Charge Time5" id: sunsynk_esphome_toggle_grid_charge_time5 register_type: holding address: 176 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 177 System Mode Grid Charge Time 6 modbus_controller_id: sunsynk use_write_multiple: true name: "${friendly_name} System Mode Grid Charge Time6" id: sunsynk_esphome_toggle_grid_charge_time6 register_type: holding address: 177 bitmask: 1 icon: "mdi:toggle-switch" number: - platform: modbus_controller # 166 System Mode SoC Time 1 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time1 name: "${friendly_name} System Mode SoC Time1" unit_of_measurement: "%" address: 166 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 167 System Mode SoC Time 2 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time2 name: "${friendly_name} System Mode SoC Time2" unit_of_measurement: "%" address: 167 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 168 System Mode SoC Time 3 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time3 name: "${friendly_name} System Mode SoC Time3" unit_of_measurement: "%" address: 168 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 169 System Mode SoC Time 4 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time4 name: "${friendly_name} System Mode SoC Time4" unit_of_measurement: "%" address: 169 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 170 System Mode SoC Time 5 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time5 name: "${friendly_name} System Mode SoC Time5" unit_of_measurement: "%" address: 170 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 171 System Mode SoC Time 6 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time6 name: "${friendly_name} System Mode SoC Time6" unit_of_measurement: "%" address: 171 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 154 System Mode Power Time 1 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time1 name: "${friendly_name} System Mode Power Time1" unit_of_measurement: "W" address: 154 min_value: 0 max_value: 12000 step: 100 value_type: U_WORD - platform: modbus_controller # 155 System Mode Power Time 2 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time2 name: "${friendly_name} System Mode Power Time2" unit_of_measurement: "W" address: 155 min_value: 0 max_value: 12000 step: 100 value_type: U_WORD - platform: modbus_controller # 156 System Mode Power Time 3 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time3 name: "${friendly_name} System Mode Power Time3" unit_of_measurement: "W" address: 156 min_value: 0 max_value: 12000 step: 100 value_type: U_WORD - platform: modbus_controller # 157 System Mode Power Time 4 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time4 name: "${friendly_name} System Mode Power Time4" unit_of_measurement: "W" address: 157 min_value: 0 max_value: 12000 step: 100 value_type: U_WORD - platform: modbus_controller # 158 System Mode Power Time 5 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time5 name: "${friendly_name} System Mode Power Time5" unit_of_measurement: "W" address: 158 min_value: 0 max_value: 12000 step: 100 value_type: U_WORD - platform: modbus_controller # 159 System Mode Power Time 6 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time6 name: "${friendly_name} System Mode Power Time6" unit_of_measurement: "W" address: 159 min_value: 0 max_value: 12000 step: 100 value_type: U_WORD - platform: modbus_controller # 128 Grid Charge Battery current use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_grid_charge_bat_current name: "${friendly_name} Grid Charge Battery current" unit_of_measurement: "A" address: 128 min_value: 0 max_value: 185 step: 5 value_type: U_WORD - platform: modbus_controller # 108 Battery Max Charge current use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_bat_max_charge_current name: "${friendly_name} Battery Max Charge current" unit_of_measurement: "A" address: 108 min_value: 0 max_value: 185 step: 5 value_type: U_WORD - platform: modbus_controller # 109 Battery Max Discharge current use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_bat_max_discharge_current name: "${friendly_name} Battery Max Discharge current" unit_of_measurement: "A" address: 109 min_value: 0 max_value: 185 step: 5 value_type: U_WORD - platform: modbus_controller # 143 Max Sell Power use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} Max Sell power" id: sunsynk_max_sell_power address: 143 unit_of_measurement: "W" min_value: 0 max_value: 12000 step: 500 value_type: U_WORD ################################################ TEXT SENSORS ################################################## text_sensor: - platform: modbus_controller # 500 Overall State modbus_controller_id: sunsynk name: "${friendly_name} Overall State" id: sunsynk_esphome_overall_state register_type: holding skip_updates: ${settings_skipped_updates} raw_encode: HEXBYTES address: 500 lambda: |- uint16_t value = modbus_controller::word_from_hex_str(x, 0); switch (value) { case 0: return std::string("standby"); case 1: return std::string("selftest"); case 2: return std::string("normal"); case 3: return std::string("alarm"); case 4: return std::string("fault"); default: return std::string("unknown"); } - platform: template name: "${friendly_name} Time Slot 1" id: sunsynk_esphome_time_slot_1 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time1).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time1).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time1).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); - platform: template name: "${friendly_name} Time Slot 2" id: sunsynk_esphome_time_slot_2 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time2).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time2).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time2).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); - platform: template name: "${friendly_name} Time Slot 3" id: sunsynk_esphome_time_slot_3 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time3).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time3).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time3).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); - platform: template name: "${friendly_name} Time Slot 4" id: sunsynk_esphome_time_slot_4 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time4).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time4).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time4).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); - platform: template name: "${friendly_name} Time Slot 5" id: sunsynk_esphome_time_slot_5 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time5).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time5).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time5).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); - platform: template name: "${friendly_name} Time Slot 6" id: sunsynk_esphome_time_slot_6 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time6).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time6).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time6).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); ################################################ SELECT SENSORS ################################################ select: - platform: modbus_controller #141 Select Energy Patern use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_select_energy_pattern name: "${friendly_name} Energy Pattern" address: 141 value_type: U_WORD optionsmap: "Battery first": 0 "Load first": 1 - platform: modbus_controller #142 Select Work Mode use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_select_work_mode name: "${friendly_name} Work Mode" address: 142 value_type: U_WORD optionsmap: "Selling First": 0 "Zero Export + Limit to Load Only": 1 "Limited to Home": 2
June 12, 20242 yr Author All looks good @BobTheDinosaur , I suspect that it has something to do with your ESP32/RS485
July 6, 20241 yr On 2024/06/12 at 8:17 AM, Sc00bs said: All looks good @BobTheDinosaur , I suspect that it has something to do with your ESP32/RS485 So i've replaced both my RS485 and ESP32 (matching voltages now) and got ESPHOME set up and running again, all sensors are working but my problem remains. I have regular, intermittent absurdly high readings on a few sensors. @slipx have you got any ideas? I found this post which seems to have the same problem as I do, at least when looking at his debug info for his battery SOC. https://community.home-assistant.io/t/modbus-errors-on-sunsynk/604063
July 6, 20241 yr Author 5 hours ago, BobTheDinosaur said: So i've replaced both my RS485 and ESP32 (matching voltages now) and got ESPHOME set up and running again, all sensors are working but my problem remains. I have regular, intermittent absurdly high readings on a few sensors. @slipx have you got any ideas? I found this post which seems to have the same problem as I do, at least when looking at his debug info for his battery SOC. https://community.home-assistant.io/t/modbus-errors-on-sunsynk/604063 What did you replace the RS485 with @BobTheDinosaur? The MAX485 boards are often problematic and I think it may have something to do with their RS485 running at 5V and the inverters running at 3.3V
July 6, 20241 yr 3 hours ago, Sc00bs said: What did you replace the RS485 with @BobTheDinosaur? The MAX485 boards are often problematic and I think it may have something to do with their RS485 running at 5V and the inverters running at 3.3V I changed to a 3.3V RS485. I think i found it on this thread, but it's this one. https://www.communica.co.za/products/wvs-rs485-3-3v-breakout-module?variant=44563441254700 To me it's looking like a code issued. Something to do with the modbus comms. Which is why I'm hoping Slipx has some ideas.
July 6, 20241 yr Author 7 hours ago, BobTheDinosaur said: I changed to a 3.3V RS485. I think i found it on this thread, but it's this one. https://www.communica.co.za/products/wvs-rs485-3-3v-breakout-module?variant=44563441254700 To me it's looking like a code issued. Something to do with the modbus comms. Which is why I'm hoping Slipx has some ideas. Nice board @BobTheDinosaur, I haven't see that one before
July 6, 20241 yr On 2024/06/12 at 12:49 AM, BobTheDinosaur said: So I've found that the read error is only when my batteries are at minimum, which is 15% (then it reports 44,474% almost constantly), or when SunSynk Day PV is at zero then it reports 6,483.1 kWh every hour or so, and SunSynk Day Grid Import just randomly reports 1,333kWh Hi. Which are the specific registers that are giving you incorrect readings.
July 7, 20241 yr 6 hours ago, slipx said: Hi. Which are the specific registers that are giving you incorrect readings. 588 Battery SOC 520 Day grid import 529 Day PV energy 672+673 PV1+PV2 Power Those are the ones I noticed on my dash. According to a developer friend who's had a look there are a few more but that was just mentioned in passing, will hopefully be able to look at it with him again tomorrow. To reiterate - nothing changed on the ESP32, it just started doing this by itself maybe 1-2 months ago. It also only seems to report these spikes when the values for these registers are at their lowest point. So for battery SOC it only spikes when SOC hits 15% which is the lowest it'll go. Day PV energy only spikes when it stops increasing i.e. PV has gone to zero. Day grid import spikes randomly from what I can tell.
July 7, 20241 yr 8 hours ago, BobTheDinosaur said: 588 Battery SOC 520 Day grid import 529 Day PV energy 672+673 PV1+PV2 Power Those are the ones I noticed on my dash. According to a developer friend who's had a look there are a few more but that was just mentioned in passing, will hopefully be able to look at it with him again tomorrow. To reiterate - nothing changed on the ESP32, it just started doing this by itself maybe 1-2 months ago. It also only seems to report these spikes when the values for these registers are at their lowest point. So for battery SOC it only spikes when SOC hits 15% which is the lowest it'll go. Day PV energy only spikes when it stops increasing i.e. PV has gone to zero. Day grid import spikes randomly from what I can tell. @BobTheDinosaur have you tried turning off your inverter for a couple of minutes and turning it back on again?
July 7, 20241 yr 9 hours ago, slipx said: Do you see the same behavior on the Sunsynk portal? How are you powering the ESP32? No, the SS portal looks fine. Edited July 7, 20241 yr by BobTheDinosaur
July 7, 20241 yr 7 hours ago, Gambit said: @BobTheDinosaur have you tried turning off your inverter for a couple of minutes and turning it back on again? Yup. did that full power down. didn't change a thing
July 7, 20241 yr @slipx,@kellerza, @Sc00bs Update and some progress, hoping Kellerza has some insight into this. My ESP32 has always been plugged into the inverter's Modbus port ("Modebus") and worked great for months. I read on a thread here that solarassistant advises using the 485 meter port. So I switched today. https://powerforum.co.za/topic/8451-sunsynk-inverter-monitoring/page/24/ While on the Modbus port the esphome logs were showing lots of chunks CRC errors, when switching to the 485 meter port those CRC errors reduced drastically in number and frequency. The problem still hasn't gone away with the registers I mentioned in my post above. Though my dev buddy has helped by applying a filter with two options to the Battery SOC register: filters: - filter_out: 44474 # - clamp: # min_value: 0 # max_value: 100 # ignore_out_of_range: true As the error was a consistently intermittent 44,474 kWh the first filter did the job. I found some related posts here: https://github.com/kellerza/sunsynk/issues/63 Now this begs the question, should I be on the BMS port using a splitter? Or should I factory reset my inverter and see what happens?
July 7, 20241 yr Author 9 hours ago, Gambit said: @BobTheDinosaur have you tried turning off your inverter for a couple of minutes and turning it back on again? Turning it off and then on again sorted out my RS485 issues when I was having a problem. I would definitely try it if you haven't done it already.