October 5, 20232 yr On 2023/08/13 at 6:25 PM, slipx said: The 8 and 5 use the same registers. https://github.com/slipx06/Sunsynk-Home-Assistant-Dash/blob/main/ESPHome-8K-Sunsynk.yaml Hi, slipx. Thanks a mill for all your work on ESPHome. I got set up pretty easily with an ESP32 and following this forum thread and scoobs' youtube vids. Got data pulling through but it was all jumbled, figured out that it's because I have the Sunsynk 12kva 3ph and the register is different. My question is: On your github page there's a yaml for the 8kw inverters that is complete (and is what I got started with) and another yaml file for the 12kw inverters. The 12kw file appears incomplete? How do I go about replacing the relevant parts of the 8kw file? I've tried just copy pasting everything from the 12kw yaml to the 8kw yaml after the BINARY SENSORS line but it breaks the yaml code. After some fiddling I found that the issue that I thought was spacing or something was actually the ${modbus_controller_id} term that was causing trouble. I replaced all instances with "sunsynk". Also, there appears to be a lot more sensors in the 8kw file than in the 12kw file, is that correct or do I need to pick each sensor code section out one by one from the 12kw file and replace em in the 8kw file? Thanks again!
October 6, 20232 yr Hi. I haven't really looked at the 12kW three phase inverters. That config was copied from another repo just for reference and has not been tested. If I have some time I'll create a proper version.
October 7, 20232 yr On 2023/10/06 at 12:33 PM, slipx said: Hi. I haven't really looked at the 12kW three phase inverters. That config was copied from another repo just for reference and has not been tested. If I have some time I'll create a proper version. OK that makes sense this. I'll do some work on it and if it works I'll post it on here.
October 7, 20232 yr On 2023/01/08 at 10:43 PM, Klatremis said: I only made this user to share this 🤣 Thanks all for the inspiration. Exactly as BrettC suggest, I made this in the weekend for my deye I have shared it with some hundreds other danish deye owners and waiting for more feedback. The adresses i use is matching my 12kW 3 phase, low voltage hybrid deye inverter. I seems for me that the modbus adresses does not match your sunsync inverters(deye inverters). github.com/klatremis/esphome-for-deye I'd like to power my ESP32 from the Sunsynk's board as well. Do you know the voltage on the CN2 7&8 pins? Would this USB power supply work? https://make.net.za/product/usb-fast-charge-module-ip6505-single-usb/
October 7, 20232 yr 8 hours ago, BobTheDinosaur said: OK that makes sense this. I'll do some work on it and if it works I'll post it on here. I've created a version based on my 8K and kellerza 3P definitions. I have not tested this so please be careful with writing to registers. https://github.com/slipx06/Sunsynk-Home-Assistant-Dash/blob/main/ESPHome-3P-12K-Sunsynk.yaml
October 8, 20232 yr On 2022/09/14 at 2:28 PM, Sc00bs said: @sjlouw I am doing something wrong and I can't figure out what cause I can't get my ESP32 to work! I have tried 2 different boards and two different RS485 connectors (same models as you specified) but no joy Have tried different ethernet cables etc, I am using a T568B cable so using the orange/orange&white cables (pin 1&2) These are the errors I am getting, any idea? Settings on the inverter are as specified. I am also getting this issue. Did you manage to solve it?
October 8, 20232 yr Has anyone tried this on a 5kW Deye? I am struggling to get data from the inverter. Here is my yaml code: and here is the logs from ESPHome: I have checked and rechecked wiring and soldering. It's as if no data is coming through.
October 9, 20232 yr @kellerza, so I adjusted the polling rates according to the link provided. It then still crash. I then increased to 20 seconds and it still crashed. here is some of my config. Maybe there is something wrong with the sensors. SENSOR_DEFINITIONS: single-phase SENSORS: - energy_management - power_flow_card - pv2_voltage - pv2_power - pv2_current - battery_temperature - dc_transformer_temperature - radiator_temperature - total_load_energy - settings - load_limit SENSORS_FIRST_INVERTER: - settings MANUFACTURER: Sunsynk READ_ALLOW_GAP: 2 READ_SENSORS_BATCH_SIZE: 20 SCHEDULES: - KEY: W READ_EVERY: 20 REPORT_EVERY: 60 CHANGE_BY: 80 - KEY: RW READ_EVERY: 20 REPORT_EVERY: 60 CHANGE_ANY: true - KEY: any_unit READ_EVERY: 30 REPORT_EVERY: 60 CHANGE_BY: 80
October 10, 20232 yr @kellerza, do you know if anyone has tried your integration with the 50kW three phase?
October 10, 20232 yr On 2023/10/07 at 4:19 PM, BobTheDinosaur said: I'd like to power my ESP32 from the Sunsynk's board as well. Do you know the voltage on the CN2 7&8 pins? Would this USB power supply work? Depending on your inverter (Think the 3phase is 7&8), yes it will work, Make sure you double check positive and negative. Reversing the polarity leads to fubar micro-controllers. Also make sure you insulate it, you do not want positive to short to ground in the inverter case. On 2023/10/08 at 4:28 PM, ZippyZappy said: I have checked and rechecked wiring and soldering. It's as if no data is coming through. I have a purposefully designed circuit for Deye/Sunsynk/Sol-Ark inverters called the SmartDeyeDongle with custom written firmware (for home assistant) where I actually fixed the quirks in the opensource software. (You can order from me, I ship to all cities/towns in South Africa) smarthomeintegrations(dot)co(dot)za Considering your time is probably worth more than R250-500p/h most people struggle for days. If you aim is to learn low level electronics, let me not stand in your way. Welcome to the magic realm where the smoke means you lost a life, de-solder, reorder and try again. If your aim is to get your inverter automated and saving on eskom consumption then getting a ready-made module is probably the way to go. Chances are that you will recoup the cost very quickly in a month or two. So I am just going to mention this here. Lots of people are trying to build RS485 circuits designed for 5V that was meant to be used on an Arduino platform. The whole arduino platform is 5V. The ESP32/8266 on the other hand is 3.3V. yrmv
October 16, 20232 yr On 2023/08/16 at 5:01 PM, XAB said: Glad I could help @XianZA. I have now connected both cables on the BMS 485/CAN of my SUNSYNK 5.5KW(newer model) with the below RJ45 Duplicator (Important to get one that does not split the pairs but rather "mirrors" it). I connected Orange to A+ - Orange/WHT to B- and Green/WHT to ground on my USB to RS485. Now I can update settings via HASSIO finally. Important to note that the RX / TX works on pins 1(Orange/WHT) and 2(Orange) and your battery on pins 4(Blue) and 5 ( Blue/WHT). I tested this first when getting the RJ45 splitter/duplicator. Prior to this I could receive data via the RS485 port next to the CAN port(left of it) but had to use Blue/WHT(A+) & Blue (B-) from the cable to receive data via the USB to RS485. But could not update as the RS485 port only allowed to receive data. Image of RJ45 Duplicator into BMS 485/CAN Image of USB to RS485 I think I've connected my sunsynk 8.8kw via the same method however getting a few errors, anyone have any ideas what I can try to get it working? MQQT shows this in the logs Sunsynk Multi shows these in the logs: Appreciate any help getting this working as I'm close to giving up at this stage but feel i'm sooooo close...
October 17, 20232 yr 12 hours ago, chessmaster said: I think I've connected my sunsynk 8.8kw via the same method however getting a few errors, anyone have any ideas what I can try to get it working? MQQT shows this in the logs Sunsynk Multi shows these in the logs: Appreciate any help getting this working as I'm close to giving up at this stage but feel i'm sooooo close... Small update, looks like MQTT is looking healthier after installing this https://github.com/SharkyRawr/hass-mqtt-fix However I'm still getting these errors in the sunsynk multi logs:
October 22, 20232 yr Has anyone had this working on a new SunSynk 5.5 Ecco inverter in the UK? Here are the ports on the UK 5.5 Ecco. I've tried the BMS \ CAN connector and RS485 connectors, I am begining to think that the UK versions do not have the correct pin outs on the BMS \ CAN bus and the RS485 port on the inverter may have a different pin out compared to the BMS \ CAN. Edited October 22, 20232 yr by Ivan Endicott
October 22, 20232 yr On 2023/10/17 at 9:35 AM, chessmaster said: However I'm still getting these errors in the sunsynk multi logs: I assume the USB-RS485 dongle is on another machine with mbusd running? then your problem sounds/seems like a cable problem, between the dongle and the inverter, could even be a broken conductor in the cable making no contact on either of the 2 needed conductors...
October 25, 20232 yr Thanks all the contributors here, certainly a massive help! I'm doing this slightly differently, and for another use case, using a microchip ATMEGA4809 and common line driver circuitry similar to what most are referencing, all at 5 volts. To the point: The Deye machine I'm developing off. MODEL NO: SUN-5K-SG01LP1-EU MAIN: Ver 0-3381-1515 HMI: Ver 0000-C35D What I've found: T568B BMS 485/CAN: B-/Pin 1(orange/white), A+/Pin 2(orange), Pin3/Gnd(green/white). METER/METER: B-/Pin 4(blue), A+/Pin 5(blue/white), Pin3/Gnd(green/white). Hopefully helps, I doubt this is the latest firmware, so you might have to split out with the battery. Edited October 25, 20232 yr by Reuf clarification
October 29, 20232 yr Guys, can you help, I see others get this error. 21:51:58][W][modbus_controller:136]: Duplicate modbus command found: type=0x3 address=150 count=1 [21:51:58][W][modbus_controller:136]: Duplicate modbus command found: type=0x3 address=154 count=1 [21:51:58][W][modbus_controller:136]: Duplicate modbus command found: type=0x3 address=160 count=1 [21:51:58][W][modbus_controller:136]: Duplicate modbus command found: type=0x3 address=164 count=1 [21:51:58][W][modbus_controller:136]: Duplicate modbus command found: type=0x3 address=166 count=4 [21:51:58][W][modbus_controller:136]: Duplicate modbus command found: type=0x3 address=172 count=1 [21:51:58][W][modbus_controller:136]: Duplicate modbus command found: type=0x3 address=175 count=4 Also, my sensors is unknown How did you resolve this error, duplicated Modbus ?
October 31, 20232 yr Guys on the Sunsynk 8KVA what must your MODBUS SN number be to use the ESP32Dev board & RS485 ? Must it be left as 1 or changed to 0 ? I struggle to get data from the inverter Everything was working fine for months, did ESPhome updates and Slipx updates and now receiving no data. Re-flashed etc a number of times etc. No luck Thanks
November 2, 20232 yr On 2023/10/31 at 11:18 PM, Vaughanza said: Guys on the Sunsynk 8KVA what must your MODBUS SN number be to use the ESP32Dev board & RS485 ? Must it be left as 1 or changed to 0 ? I struggle to get data from the inverter Everything was working fine for months, did ESPhome updates and Slipx updates and now receiving no data. Re-flashed etc a number of times etc. No luck Thanks I am struggling with the same issue. I am now trying to figure out what changed, will let you know. Using a 5kW though. Perhaps @slipx, do you have any ideas for us, please?
November 2, 20232 yr On 2023/10/31 at 11:18 PM, Vaughanza said: Guys on the Sunsynk 8KVA what must your MODBUS SN number be to use the ESP32Dev board & RS485 ? Must it be left as 1 or changed to 0 ? I struggle to get data from the inverter Everything was working fine for months, did ESPhome updates and Slipx updates and now receiving no data. Re-flashed etc a number of times etc. No luck Thanks I got mine sorted. I updated ESPHome and HomeAssistant, then played around with the config for ESPHome: substitutions: settings_skipped_updates: "30" devicename: sunsynk device_description: "Sunsynk RS485 Logger" friendly_name: "SunSynk" esphome: name: $devicename comment: '${device_description}' esp32: board: esp32dev framework: type: arduino # Enable logging logger: baud_rate: 0 # Enable Home Assistant API api: encryption: key: !secret api_encryption_key ota: password: !secret ota_password_sunsynk wifi: ssid: !secret wifi_ssid password: !secret wifi_password # Enable fallback hotspot (captive portal) in case wifi connection fails ap: ssid: '${devicename}' password: !secret fallback_password fast_connect: true power_save_mode: none captive_portal: # Enable time component to reset energy at midnight # https://esphome.io/components/time.html#home-assistant-time-source time: - platform: sntp id: sntp_time timezone: Africa/Johannesburg servers: - pool.ntp.org uart: id: mod_bus tx_pin: 17 rx_pin: 16 baud_rate: 9600 stop_bits: 1 modbus: id: sunsynk_modbus flow_control_pin: 4 modbus_controller: - id: sunsynk address: 0x01 modbus_id: sunsynk_modbus setup_priority: -10 update_interval: "5s" command_throttle: "50ms" ############################################### BINARY SENSORS ######################################## binary_sensor: - platform: modbus_controller # 194 Grid Connected Status modbus_controller_id: sunsynk name: "${friendly_name} Grid Connected Status" id: sunsynk_esphome_grid_connected_status register_type: holding address: 194 - platform: modbus_controller # 280 Gen Peak Shaving Status modbus_controller_id: sunsynk name: "${friendly_name} Gen Peak Shaving Status" id: sunsynk_esphome_gen_peak_shaving_status register_type: holding address: 280 bitmask: 0x10 - platform: modbus_controller # 280 Grid Peak Shaving Status modbus_controller_id: sunsynk name: "${friendly_name} Grid Peak Shaving Status" id: sunsynk_esphome_grid_peak_shaving_status register_type: holding address: 280 bitmask: 0x100 # SENSORS # ####################################################################################################### ############################################### BATTERY ############################################### sensor: - platform: modbus_controller # 182 Battery Temperature modbus_controller_id: sunsynk name: "${friendly_name} Battery Temperature" id: sunsynk_esphome_battery_temperature register_type: holding address: 182 unit_of_measurement: "°C" accuracy_decimals: 1 device_class: temperature state_class: measurement value_type: U_WORD filters: - offset: -1000 - multiply: 0.1 - platform: modbus_controller # 183 Battery Voltage modbus_controller_id: sunsynk name: "${friendly_name} Battery Voltage" id: sunsynk_esphome_battery_voltage register_type: holding address: 183 unit_of_measurement: "V" accuracy_decimals: 1 device_class: voltage state_class: measurement filters: - multiply: 0.01 value_type: U_WORD - platform: modbus_controller # 184 Battery SOC modbus_controller_id: sunsynk name: "${friendly_name} Battery SOC" id: sunsynk_esphome_battery_soc register_type: holding address: 184 unit_of_measurement: "%" accuracy_decimals: 0 device_class: battery value_type: U_WORD - platform: modbus_controller # 190 Battery Power modbus_controller_id: sunsynk name: "${friendly_name} Battery Power" id: sunsynk_esphome_battery_power register_type: holding address: 190 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power value_type: S_WORD - platform: modbus_controller # 191 Battery Current modbus_controller_id: sunsynk name: "${friendly_name} Battery Current" id: sunsynk_esphome_battery_current register_type: holding address: 191 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement value_type: S_WORD filters: - multiply: 0.01 - platform: modbus_controller # 217 Battery Capacity Shutdown modbus_controller_id: sunsynk name: "${friendly_name} Battery Capacity Shutdown" id: sunsynk_esphome_battery_capacity_shutdown register_type: holding address: 217 unit_of_measurement: "%" accuracy_decimals: 0 device_class: battery ############################################### INVERTER ############################################## - platform: modbus_controller # 175 Inverter Power modbus_controller_id: sunsynk name: "${friendly_name} Inverter Power" id: sunsynk_esphome_inverter_power register_type: holding address: 175 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power value_type: S_WORD - platform: modbus_controller # 154 Inverter Voltage modbus_controller_id: sunsynk name: "${friendly_name} Inverter Voltage" id: sunsynk_esphome_inverter_voltage register_type: holding address: 154 unit_of_measurement: "V" accuracy_decimals: 1 device_class: voltage state_class: measurement filters: - multiply: 0.1 value_type: U_WORD - platform: modbus_controller # 164 Inverter Current modbus_controller_id: sunsynk name: "${friendly_name} Inverter Current" id: sunsynk_esphome_inverter_current register_type: holding address: 164 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement value_type: S_WORD filters: - multiply: 0.01 - platform: modbus_controller # 193 Inverter Frequency modbus_controller_id: sunsynk name: "${friendly_name} Inverter Frequency" id: sunsynk_esphome_inverter_frequency register_type: holding address: 193 unit_of_measurement: "Hz" accuracy_decimals: 2 filters: - multiply: 0.01 value_type: U_WORD state_class: measurement ############################################### GRID ################################################## - platform: modbus_controller # 079 Grid Frequency modbus_controller_id: sunsynk name: "${friendly_name} Grid Frequency" id: sunsynk_esphome_grid_frequency register_type: holding address: 79 unit_of_measurement: "Hz" accuracy_decimals: 2 filters: - multiply: 0.01 value_type: U_WORD state_class: measurement - platform: modbus_controller # 169 Grid Power modbus_controller_id: sunsynk name: "${friendly_name} Grid Power" id: sunsynk_esphome_grid_power_169 register_type: holding address: 169 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 167 Grid LD Power modbus_controller_id: sunsynk name: "${friendly_name} Grid LD Power 167" id: sunsynk_esphome_grid_power_167 register_type: holding address: 167 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 168 Grid L2 Power modbus_controller_id: sunsynk name: "${friendly_name} Grid L2 Power 168" id: sunsynk_esphome_grid_power_168 register_type: holding address: 168 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 150 Grid Voltage modbus_controller_id: sunsynk name: "${friendly_name} Grid Voltage" id: sunsynk_esphome_grid_voltage register_type: holding address: 150 unit_of_measurement: "V" accuracy_decimals: 1 device_class: voltage state_class: measurement filters: - multiply: 0.1 value_type: U_WORD - platform: modbus_controller # 160 Grid Current modbus_controller_id: sunsynk name: "${friendly_name} Grid Current" id: sunsynk_esphome_grid_current register_type: holding address: 160 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement value_type: S_WORD filters: - multiply: 0.01 - platform: modbus_controller # 172 Grid CT Power modbus_controller_id: sunsynk name: "${friendly_name} Grid CT Power" id: sunsynk_esphome_grid_ct_power register_type: holding address: 172 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD ############################################### LOAD ################################################ - platform: modbus_controller # 178 Load Power modbus_controller_id: sunsynk name: "${friendly_name} Load Power" id: sunsynk_esphome_load_power register_type: holding address: 178 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 176 Load L1 Power modbus_controller_id: sunsynk name: "${friendly_name} Load L1 Power" id: sunsynk_esphome_load_l1_power register_type: holding address: 176 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 177 Load L2 Power modbus_controller_id: sunsynk name: "${friendly_name} Load L2 Power" id: sunsynk_esphome_load_l2_power register_type: holding address: 177 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: modbus_controller # 192 Load Frequency modbus_controller_id: sunsynk name: "${friendly_name} Load Frequency" id: sunsynk_esphome_load_frequency register_type: holding address: 192 unit_of_measurement: "Hz" accuracy_decimals: 2 filters: - multiply: 0.01 value_type: U_WORD state_class: measurement ############################################### SOLAR PV1 ############################################# - platform: modbus_controller # 186 PV1 Power modbus_controller_id: sunsynk name: "${friendly_name} PV1 Power" id: sunsynk_esphome_pv1_power register_type: holding address: 186 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: U_WORD - platform: modbus_controller # 109 PV1 Voltage modbus_controller_id: sunsynk name: "${friendly_name} PV1 Voltage" id: sunsynk_esphome_pv1_voltage register_type: holding address: 109 unit_of_measurement: "V" device_class: voltage state_class: measurement accuracy_decimals: 1 filters: - multiply: 0.1 value_type: U_WORD - platform: modbus_controller # 110 PV1 Current modbus_controller_id: sunsynk name: "${friendly_name} PV1 Current" id: sunsynk_esphome_pv1_current register_type: holding address: 110 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement filters: - multiply: 0.1 value_type: U_WORD ############################################### SOLAR PV2 ############################################# - platform: modbus_controller # 187 PV2 Power modbus_controller_id: sunsynk name: "${friendly_name} PV2 Power" id: sunsynk_esphome_pv2_power register_type: holding address: 187 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: U_WORD - platform: modbus_controller # 111 PV2 Voltage modbus_controller_id: sunsynk name: "${friendly_name} PV2 Voltage" id: sunsynk_esphome_pv2_voltage register_type: holding address: 111 unit_of_measurement: "V" accuracy_decimals: 1 filters: - multiply: 0.1 device_class: voltage state_class: measurement value_type: U_WORD - platform: modbus_controller # 112 PV2 Current modbus_controller_id: sunsynk name: "${friendly_name} PV2 Current" id: sunsynk_esphome_pv2_current register_type: holding address: 112 unit_of_measurement: "A" accuracy_decimals: 1 device_class: current state_class: measurement filters: - multiply: 0.1 value_type: U_WORD ############################################### SOLAR TOTAL ########################################### - platform: template # Sum of PV1 and PV2 to get total PV Power name: "${friendly_name} Solar Power" unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement lambda: |- return (id(sunsynk_esphome_pv1_power).state + id(sunsynk_esphome_pv2_power).state); update_interval: 5s ############################################### OUTPUTS ############################################### - platform: modbus_controller # 166 Aux Power modbus_controller_id: sunsynk name: "${friendly_name} AUX Power" id: sunsynk_esphome_aux_power register_type: holding address: 166 unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement value_type: S_WORD - platform: template # Essential Power based on register 175 + 167 - 166 name: "${friendly_name} Essential Power" unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement lambda: |- return (id(sunsynk_esphome_inverter_power).state + id(sunsynk_esphome_grid_power_167).state - id(sunsynk_esphome_aux_power).state); update_interval: 5s - platform: template # Essential Power1 based on register 175 + 169 - 166 name: "${friendly_name} Essential Power 1" unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement lambda: |- return (id(sunsynk_esphome_inverter_power).state + id(sunsynk_esphome_grid_power_169).state - id(sunsynk_esphome_aux_power).state); update_interval: 5s - platform: template # Nonessential Power 172 - 167 name: "${friendly_name} Nonessential Power" unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement lambda: |- return (id(sunsynk_esphome_grid_ct_power).state - id(sunsynk_esphome_grid_power_167).state); update_interval: 5s - platform: template # Nonessential Power1 172 - 169 name: "${friendly_name} Nonessential Power 1" unit_of_measurement: "W" accuracy_decimals: 0 device_class: power state_class: measurement lambda: |- return (id(sunsynk_esphome_grid_ct_power).state - id(sunsynk_esphome_grid_power_169).state); update_interval: 5s ############################################### ENERGY ################################################ - platform: modbus_controller # 070 Day Battery Charge modbus_controller_id: sunsynk name: "${friendly_name} Day Battery Charge" id: sunsynk_esphome_day_battery_charge register_type: holding address: 70 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 071 Day Battery Discharge modbus_controller_id: sunsynk name: "${friendly_name} Day Battery Discharge" id: sunsynk_esphome_day_battery_discharge register_type: holding address: 71 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 072 Total Battery Charge modbus_controller_id: sunsynk name: "${friendly_name} Total Battery Charge" id: sunsynk_esphome_total_battery_charge register_type: holding address: 72 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing value_type: U_DWORD_R filters: - multiply: 0.1 - platform: modbus_controller # 074 Total Battery Discharge modbus_controller_id: sunsynk name: "${friendly_name} Total Battery Discharge" id: sunsynk_esphome_total_battery_discharge register_type: holding address: 74 unit_of_measurement: "kWh" accuracy_decimals: 0 device_class: energy state_class: total_increasing value_type: U_DWORD_R filters: - multiply: 0.1 - platform: modbus_controller # 076 Day Grid Import modbus_controller_id: sunsynk name: "${friendly_name} Day Grid Import" id: sunsynk_esphome_day_grid_import register_type: holding address: 76 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 077 Day Grid Export modbus_controller_id: sunsynk name: "${friendly_name} Day Grid Export" id: sunsynk_esphome_day_grid_export register_type: holding address: 77 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 078 Total Grid Import modbus_controller_id: sunsynk name: "${friendly_name} Total Grid Import" id: sunsynk_esphome_total_grid_import register_type: holding address: 78 unit_of_measurement: "kWh" accuracy_decimals: 2 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 081 Total Grid Export modbus_controller_id: sunsynk name: "${friendly_name} Total Grid Export" id: sunsynk_esphome_total_grid_export register_type: holding address: 81 unit_of_measurement: "kWh" accuracy_decimals: 2 device_class: energy state_class: total_increasing value_type: U_WORD filters: - multiply: 0.1 - platform: modbus_controller # 084 Day Load Energy modbus_controller_id: sunsynk name: "${friendly_name} Day Load Energy" id: sunsynk_esphome_day_load_energy register_type: holding address: 84 unit_of_measurement: "kWh" accuracy_decimals: 2 device_class: energy state_class: total_increasing filters: - multiply: 0.1 value_type: U_WORD - platform: modbus_controller # 085 Total Load Energy modbus_controller_id: sunsynk name: "${friendly_name} Total Load Energy" id: sunsynk_esphome_total_load_energy register_type: holding address: 85 unit_of_measurement: "kWh" accuracy_decimals: 2 device_class: energy state_class: total_increasing value_type: U_DWORD_R filters: - multiply: 0.1 - platform: modbus_controller # 096 Total PV Energy modbus_controller_id: sunsynk name: "${friendly_name} Total PV Energy" id: sunsynk_esphome_total_pv_energy register_type: holding address: 96 unit_of_measurement: "kWh" accuracy_decimals: 2 device_class: energy state_class: total_increasing filters: - multiply: 0.1 value_type: U_DWORD_R - platform: modbus_controller # 108 Day PV Energy modbus_controller_id: sunsynk name: "${friendly_name} Day PV Energy" id: sunsynk_esphome_day_pv_energy register_type: holding address: 108 unit_of_measurement: "kWh" accuracy_decimals: 1 device_class: energy state_class: total_increasing filters: - multiply: 0.1 value_type: U_WORD ############################################### TEMPERATURE ################################################ - platform: modbus_controller # 090 DC Transformer Temperature modbus_controller_id: sunsynk name: "${friendly_name} DC Transformer Temperature" id: sunsynk_esphome_dc_transformer_temperature register_type: holding address: 090 unit_of_measurement: "°C" accuracy_decimals: 1 device_class: temperature state_class: measurement value_type: S_WORD filters: - offset: -1000 - multiply: 0.1 - platform: modbus_controller # 091 Radiator Temperature modbus_controller_id: sunsynk name: "${friendly_name} Radiator Temperature" id: sunsynk_esphome_radiator_temperature register_type: holding address: 091 unit_of_measurement: "°C" accuracy_decimals: 1 device_class: temperature state_class: measurement value_type: S_WORD filters: - offset: -1000 - multiply: 0.1 ################################################ READ SETTINGS ############################################# - platform: modbus_controller # 250 System Mode Time 1 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time1" id: sunsynk_esphome_system_mode_time1 register_type: holding skip_updates: ${settings_skipped_updates} address: 250 icon: "mdi:clock" - platform: modbus_controller # 251 System Mode Time 2 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time2" id: sunsynk_esphome_system_mode_time2 register_type: holding skip_updates: ${settings_skipped_updates} address: 251 icon: "mdi:clock" - platform: modbus_controller # 252 System Mode Time 3 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time3" id: sunsynk_esphome_system_mode_time3 register_type: holding skip_updates: ${settings_skipped_updates} address: 252 icon: "mdi:clock" - platform: modbus_controller # 253 System Mode Time 4 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time4" id: sunsynk_esphome_system_mode_time4 register_type: holding skip_updates: ${settings_skipped_updates} address: 253 icon: "mdi:clock" - platform: modbus_controller # 254 System Mode Time 5 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time5" id: sunsynk_esphome_system_mode_time5 register_type: holding skip_updates: ${settings_skipped_updates} address: 254 icon: "mdi:clock" - platform: modbus_controller # 255 System Mode Time 6 modbus_controller_id: sunsynk name: "${friendly_name} System Mode Time6" id: sunsynk_esphome_system_mode_time6 register_type: holding skip_updates: ${settings_skipped_updates} address: 255 icon: "mdi:clock" - platform: modbus_controller # 255 Grid Peak Shaving raw register value modbus_controller_id: sunsynk id: grid_peak_shaving_raw register_type: holding address: 280 value_type: U_WORD ################################################ WRITE SETTINGS ############################################ switch: - platform: modbus_controller # 326 Toggle Force Generator use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} Toggle Force Generator" id: sunsynk_esphome_toggle_force_generator register_type: holding address: 326 bitmask: 8192 # 2^13 to target bit 13 icon: "mdi:toggle-switch" - platform: modbus_controller # 247 Toggle Solar Sell use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} Toggle Solar sell" id: sunsynk_esphome_toggle_solar_sell register_type: holding address: 247 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 248 Toggle System Timer use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} Toggle System Timer" id: sunsynk_esphome_toggle_Time_of_Use register_type: holding address: 248 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 243 Priority Load use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} Toggle Priority Load" id: sunsynk_esphome_toggle_priority_load register_type: holding address: 243 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 274 System Mode Grid Charge Time 1 use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} System Mode Grid Charge Time1" id: sunsynk_esphome_toggle_grid_charge_time1 register_type: holding address: 274 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 275 System Mode Grid Charge Time 2 modbus_controller_id: sunsynk use_write_multiple: true name: "${friendly_name} System Mode Grid Charge Time2" id: sunsynk_esphome_toggle_grid_charge_time2 register_type: holding address: 275 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 276 System Mode Grid Charge Time 3 modbus_controller_id: sunsynk use_write_multiple: true name: "${friendly_name} System Mode Grid Charge Time3" id: sunsynk_esphome_toggle_grid_charge_time3 register_type: holding address: 276 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 277 System Mode Grid Charge Time 4 modbus_controller_id: sunsynk use_write_multiple: true name: "${friendly_name} System Mode Grid Charge Time4" id: sunsynk_esphome_toggle_grid_charge_time4 register_type: holding address: 277 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 278 System Mode Grid Charge Time 5 modbus_controller_id: sunsynk use_write_multiple: true name: "${friendly_name} System Mode Grid Charge Time5" id: sunsynk_esphome_toggle_grid_charge_time5 register_type: holding address: 278 bitmask: 1 icon: "mdi:toggle-switch" - platform: modbus_controller # 279 System Mode Grid Charge Time 6 modbus_controller_id: sunsynk use_write_multiple: true name: "${friendly_name} System Mode Grid Charge Time6" id: sunsynk_esphome_toggle_grid_charge_time6 register_type: holding address: 279 bitmask: 1 icon: "mdi:toggle-switch" number: - platform: modbus_controller # 268 System Mode SoC Time 1 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time1 name: "${friendly_name} System Mode SoC Time1" unit_of_measurement: "%" address: 268 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 269 System Mode SoC Time 2 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time2 name: "${friendly_name} System Mode SoC Time2" unit_of_measurement: "%" address: 269 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 270 System Mode SoC Time 3 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time3 name: "${friendly_name} System Mode SoC Time3" unit_of_measurement: "%" address: 270 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 271 System Mode SoC Time 4 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time4 name: "${friendly_name} System Mode SoC Time4" unit_of_measurement: "%" address: 271 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 272 System Mode SoC Time 5 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time5 name: "${friendly_name} System Mode SoC Time5" unit_of_measurement: "%" address: 272 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 273 System Mode SoC Time 6 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_soc_time6 name: "${friendly_name} System Mode SoC Time6" unit_of_measurement: "%" address: 273 min_value: 0 max_value: 100 step: 5 value_type: U_WORD - platform: modbus_controller # 256 System Mode Power Time 1 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time1 name: "${friendly_name} System Mode Power Time1" unit_of_measurement: "W" address: 256 min_value: 0 max_value: 8000 step: 100 value_type: U_WORD - platform: modbus_controller # 257 System Mode Power Time 2 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time2 name: "${friendly_name} System Mode Power Time2" unit_of_measurement: "W" address: 257 min_value: 0 max_value: 8000 step: 100 value_type: U_WORD - platform: modbus_controller # 258 System Mode Power Time 3 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time3 name: "${friendly_name} System Mode Power Time3" unit_of_measurement: "W" address: 258 min_value: 0 max_value: 8000 step: 100 value_type: U_WORD - platform: modbus_controller # 259 System Mode Power Time 4 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time4 name: "${friendly_name} System Mode Power Time4" unit_of_measurement: "W" address: 259 min_value: 0 max_value: 8000 step: 100 value_type: U_WORD - platform: modbus_controller # 260 System Mode Power Time 5 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time5 name: "${friendly_name} System Mode Power Time5" unit_of_measurement: "W" address: 260 min_value: 0 max_value: 8000 step: 100 value_type: U_WORD - platform: modbus_controller # 261 System Mode Power Time 6 use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_set_power_time6 name: "${friendly_name} System Mode Power Time6" unit_of_measurement: "W" address: 261 min_value: 0 max_value: 8000 step: 100 value_type: U_WORD - platform: modbus_controller # 230 Grid Charge Battery current use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_grid_charge_bat_current name: "${friendly_name} Grid Charge Battery current" unit_of_measurement: "A" address: 230 min_value: 0 max_value: 185 step: 5 value_type: U_WORD - platform: modbus_controller # 210 Battery Max Charge current use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_bat_max_charge_current name: "${friendly_name} Battery Max Charge current" unit_of_measurement: "A" address: 210 min_value: 0 max_value: 185 step: 5 value_type: U_WORD - platform: modbus_controller # 211 Battery Max Discharge current use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_bat_max_discharge_current name: "${friendly_name} Battery Max Discharge current" unit_of_measurement: "A" address: 211 min_value: 0 max_value: 185 step: 5 value_type: U_WORD - platform: modbus_controller # 293 Grid Peak Shaving Power use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} Grid Peak shaving power" id: sunsynk_grid_peak_shaving_power address: 293 unit_of_measurement: "W" min_value: 0 max_value: 8000 step: 500 value_type: U_WORD - platform: modbus_controller # 245 Max Sell Power use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} Max Sell power" id: sunsynk_max_sell_power address: 245 unit_of_measurement: "W" min_value: 0 max_value: 8000 step: 500 value_type: U_WORD ################################################ TEXT SENSORS ################################################## text_sensor: - platform: modbus_controller # 059 Overall State modbus_controller_id: sunsynk name: "${friendly_name} Overall State" id: sunsynk_esphome_overall_state register_type: holding skip_updates: ${settings_skipped_updates} raw_encode: HEXBYTES address: 59 lambda: |- uint16_t value = modbus_controller::word_from_hex_str(x, 0); switch (value) { case 0: return std::string("standby"); case 1: return std::string("selftest"); case 2: return std::string("normal"); case 3: return std::string("alarm"); case 4: return std::string("fault"); default: return std::string("unknown"); } - platform: template name: "${friendly_name} Time Slot 1" id: sunsynk_esphome_time_slot_1 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time1).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time1).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time1).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); - platform: template name: "${friendly_name} Time Slot 2" id: sunsynk_esphome_time_slot_2 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time2).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time2).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time2).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); - platform: template name: "${friendly_name} Time Slot 3" id: sunsynk_esphome_time_slot_3 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time3).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time3).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time3).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); - platform: template name: "${friendly_name} Time Slot 4" id: sunsynk_esphome_time_slot_4 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time4).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time4).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time4).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); - platform: template name: "${friendly_name} Time Slot 5" id: sunsynk_esphome_time_slot_5 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time5).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time5).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time5).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); - platform: template name: "${friendly_name} Time Slot 6" id: sunsynk_esphome_time_slot_6 icon: "mdi:clock" lambda: |- int minutes, hours; if (id(sunsynk_esphome_system_mode_time6).state) { minutes = static_cast<int>(id(sunsynk_esphome_system_mode_time6).state) % 100; hours = static_cast<int>(id(sunsynk_esphome_system_mode_time6).state) / 100; } else { minutes = 0; hours = 0; } char formatted_time[6]; snprintf(formatted_time, sizeof(formatted_time), "%02d:%02d", hours, minutes); return esphome::optional<std::string>(formatted_time); ################################################ SELECT SENSORS ################################################ select: - platform: modbus_controller #243 Select Energy Patern use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_select_energy_pattern name: "${friendly_name} Energy Pattern" address: 243 value_type: U_WORD optionsmap: "Battery first": 0 "Load first": 1 - platform: modbus_controller #244 Select Work Mode use_write_multiple: true modbus_controller_id: sunsynk id: sunsynk_esphome_select_work_mode name: "${friendly_name} Work Mode" address: 244 value_type: U_WORD optionsmap: "Selling First": 0 "Zero Export + Limit to Load Only": 1 "Limited to Home": 2 - platform: modbus_controller #280 Select Grid Peak Shaving use_write_multiple: true modbus_controller_id: sunsynk name: "${friendly_name} Grid Peak Shaving" id: sunsynk_esphome_select_grid_peak_shaving address: 280 value_type: U_WORD optionsmap: "Disabled": 0 "Enabled": 256 lambda: |- // we are only interested in the 8th bit binary 0001 0000 0000 need to map the options 0, 256 in select //ESP_LOGE("main","Modbus Number incoming value = %d",x); //ESP_LOGE("main","Modbus eval value = %d",(x & 0x0100)); if ((x & 0x0100) == 0) return std::string("Disabled"); if ((x & 0x0100) == 256) return std::string("Enabled"); return {}; write_lambda: |- //ESP_LOGE("main","Modbus write gets = %d",value); uint16_t unmodified = id(grid_peak_shaving_raw).state; //ESP_LOGE("main","Modbus write unmodified = %d", unmodified); // optionsmap should only return 2 values... 0 , 256 so bitmask with complement 0x0100 to ensure we keep the original values in register. Then appply OR with the value that was chosen uint16_t modified = ((unmodified & ~0x0100) | value); //ESP_LOGE("main","Modbus write to write = %d", modified); return modified;
November 2, 20232 yr Guys eventually got my Esp32 & RS485 working again. The problem was the RS485 board not sure what happened to it. Added a new board and all data started coming through. Something things I learned. 1. Don't need two pairs of wires coming from the your RS45. Only need the orange ( goes to A on RS485 ) and the orange/white (goes to B on the RS485) 2. If you get this error " 21:51:58][W][modbus_controller:136]: Duplicate modbus command found: type=0x3 address=150 count=1 " I was told to increase your Modbus_controller update_interval. When I increased this the error went away. 3. I read that don't add power to the RS485 from the ESP32 only connect the ground and not the 5v. Hope this all correct but it seems to be working fine now. What I am concerned about is that I read that you should power the ESP32 Dev board with 3v and not 5v ? I am using a phone charger and usb cable to power the ESp32 dev board, is this going to cause a problem ? Thanks
November 2, 20232 yr Well done @McGuywer, excellent. Also got min sorted today by adding a new RS485 board. For some reason the board got damaged even though the RED led lights up. I thought the problem was because of all the updates on Esphome and Dashboard updates. So now I bought extra boards. What do you power your ESP32 board with ?
November 2, 20232 yr The ESP32 board runs off 3.3v but the simplest way is to power it using the usb port. It has an internal voltage regulator so you will be fine.
November 3, 20232 yr Author Hi @Vaughanza Heinz from Smarthomeintegrations imports a very nice ESP32Shield that includes a power supply and 3.3V RS485/Canbus interface that he uses in his SmartHomeDongle. If you have an 8, 12 or 16kw Sunsynk/Deye inverter (not sure about the 5kw) you can then power the unit from the 12V power supply inside the inverter which is very neat. I did a review of the whole package on my Youtube channel and he did say that he would sell them without his firmware for the DIYers if someone wants. Is a very neat solution and gets rid of all of the soldering and most of the wiring issues that seem to plague people's ESP32 installs.
November 4, 20232 yr On 2023/11/03 at 8:18 AM, Sc00bs said: Hi @Vaughanza Heinz from Smarthomeintegrations imports a very nice ESP32Shield that includes a power supply and 3.3V RS485/Canbus interface that he uses in his SmartHomeDongle. If you have an 8, 12 or 16kw Sunsynk/Deye inverter (not sure about the 5kw) you can then power the unit from the 12V power supply inside the inverter which is very neat. I did a review of the whole package on my Youtube channel and he did say that he would sell them without his firmware for the DIYers if someone wants. Is a very neat solution and gets rid of all of the soldering and most of the wiring issues that seem to plague people's ESP32 installs. Thanks @Sc00bs appreciate it. Was thinking that when I watched your video earlier.
November 4, 20232 yr Author He was also talking about selling the shields separately with an ESP32 if you still want to do the DIY ESPHome thing.