October 12, 20214 yr Hi All Has anyone experienced this my Sunsynk has been working fine of recently its occasionally trip thee earth leakage on its grid side feed that it the feed that coming from grid to the inverter. So u have a direct feed from grid main CB to Inverter main CB see below picture your feedback is appreciated. Edited October 12, 20214 yr by John2 Additional information
October 12, 20214 yr Author Tests that has been done Neutral to earth 0v live and earth 230v. I don't have and earth to neutral bond have tested sockets all fine without bond both when grid is available and when no grid.Below is my main db with no issues I have 2 EL one for non essential and one for essential.
October 12, 20214 yr Author @Leshen I know you have installed quite a few of them have you came across anything like this. So the grid connection to the inverter is from the Main grid CB 63amp to Inverter grid 63amp to EL63amp then to SP63 to inverter.
October 12, 20214 yr Check that you dont have the inverter grid side feed after the earth leakage. It should be before the earth leakage(of non essentials) or it will cause an imbalance and trip the EL.
October 12, 20214 yr 27 minutes ago, John2 said: @Leshen I know you have installed quite a few of them have you came across anything like this. So the grid connection to the inverter is from the Main grid CB 63amp to Inverter grid 63amp to EL63amp then to SP63 to inverter. Hi John. Did you supply the inverter with grid power before or after the EL?
October 12, 20214 yr Author 4 minutes ago, Leshen said: Hi John. Did you supply the inverter with grid power before or after the EL? @Leshen after the EL
October 12, 20214 yr Author 3 hours ago, 87 Dream said: Looks like you have found the culprit... 87 @87 Dream yes Leshen has thanks @Leshen appreciated
October 12, 20214 yr Author 1 minute ago, 87 Dream said: The Power of the Forum 😅😅🤣🤣. Glad you found the needle in the hay stack @John2 guys like @Leshen are walking encyclopedias & we are richer for their membership on this group. 87 @87 Dream true and they willing to share that info 😅
October 12, 20214 yr 18 minutes ago, 87 Dream said: The Power of the Forum 😅😅🤣🤣. Glad you found the needle in the hay stack @John2 guys like @Leshen are walking encyclopedias & we are richer for their membership on this group. 87 You are too kind 87
October 13, 20214 yr Thanks Gents, I enjoy also the information! @Leshenon a different but related topic : I know of 2 Sunsynk 8kW installations where the Earth Leakage (home DB) trips after loadshedding. They do not have an earth - neutral bond relay installed, so my quess is when the Eskom / Munic Neutral and Earth return, there is an unbalanced leakage (?). Any inputs or discussions around this that you are aware of? Kind Regards, Jaco
October 16, 20214 yr Can anyone please supply me with the information regarding the earth neutral bond relay they’ve installed. Also where you’ve sourced it from We had a millisecond municipal trip tonight which caused my 8kw Sunsynk to trip the earth leakage. I need to do this mod asap as I am going to the KNP in 3 weeks time.
October 17, 20214 yr 10 hours ago, Johandup said: Can anyone please supply me with the information regarding the earth neutral bond relay they’ve installed. Also where you’ve sourced it from I just installed a normal dinrail mounted 230V relay that you could buy at most electrical suppliers, there are other brands like Hager, ownesto, ABB. The Sunsynk manual does not mention a specific type or brand.
October 17, 20214 yr On 2021/10/13 at 4:07 PM, Jaco P Bloem said: Thanks Gents, I enjoy also the information! @Leshenon a different but related topic : I know of 2 Sunsynk 8kW installations where the Earth Leakage (home DB) trips after loadshedding. They do not have an earth - neutral bond relay installed, so my quess is when the Eskom / Munic Neutral and Earth return, there is an unbalanced leakage (?). Any inputs or discussions around this that you are aware of? Kind Regards, Jaco A neighbour of mine's earth leakage tripped every time the grid came back after load shedding. It's a normal home installation, she does not have an inverter. My electrician took a look and determined that her earth leakage was too sensitive, he replaced it and there have been no problems since for over 1 year now.
October 17, 20214 yr 1 minute ago, YellowTapemeasure said: A neighbour of mine's earth leakage tripped every time the grid came back after load shedding. It's a normal home installation, she does not have an inverter. My electrician took a look and determined that her earth leakage was too sensitive, he replaced it and there have been no problems since for over 1 year now. Have tested mine and it is within spec. But it a gray area.
October 17, 20214 yr 35 minutes ago, Johandup said: Did you install it inside the inverter? Hi Johan, yes I installed it inside the inverter as there is some space inside the inverter behind the string isolator and I used cable ties to strap it a bit so that it cannot move around freely. The space was a bit tight but it done the trick. Sorry I don’t have a photo but with all the wiring in that box it is kind of hidden away behind all the wires, but see empty box and position.
October 17, 20214 yr On 2021/10/13 at 6:07 PM, Jaco P Bloem said: Thanks Gents, I enjoy also the information! @Leshenon a different but related topic : I know of 2 Sunsynk 8kW installations where the Earth Leakage (home DB) trips after loadshedding. They do not have an earth - neutral bond relay installed, so my quess is when the Eskom / Munic Neutral and Earth return, there is an unbalanced leakage (?). Any inputs or discussions around this that you are aware of? Kind Regards, Jaco Hi Jaco. It could be many issues. One being that the EL is too sensitive. If the inverter is being fed through the EL, it will trip. The E/N bondind is only required on the LOAD/Essential side of the inverter when the grid fails. So when the grid is down, you need to bond Earth and the LOAD neutral. If this isn’t done then there will be approx 110V between Earth and Neutral on the LOAD side which isn’t legal.
October 17, 20214 yr 33 minutes ago, Gerrie said: Hi Johan, yes I installed it inside the inverter as there is some space inside the inverter behind the string isolator and I used cable ties to strap it a bit so that it cannot move around freely. The space was a bit tight but it done the trick. Sorry I don’t have a photo but with all the wiring in that box it is kind of hidden away behind all the wires, but see empty box and position. Tx for the reply. Much appreciated.
July 24, 20232 yr On 2021/10/12 at 9:27 AM, Leshen said: Hi John. Did you supply the inverter with grid power before or after the EL? Shouldn't the supply from the mains to the inverter be protected by an EL? If something goes wrong with the cable or inverter no EL will trip.
July 24, 20232 yr 23 minutes ago, MPAD said: Shouldn't the supply from the mains to the inverter be protected by an EL? If something goes wrong with the cable or inverter no EL will trip. No because you will get a lot of nuisance tripping.
July 24, 20232 yr 52 minutes ago, Leshen said: No because you will get a lot of nuisance tripping. I've self installed my Sunsynk and have a 15m 10mm house wire cable between mains and the feed in for inverter. Am concerned that it is not safe due to not having an E/L between the two. What if something goes wrong with the inverter? From my reading Sunsynk recommends a RCD before the inverter? Should I try and get 100ma RCD or not waste my time. Edited July 24, 20232 yr by MPAD correction to rcd
July 24, 20232 yr 2 hours ago, MPAD said: If something goes wrong with the cable or inverter no EL will trip. Do not put a RCD on the input of the inverter you will have endless tripping issues. The current MCB feeding the input of the inverter is the protection for the cable and inverter.40/50 amp MCB for 10mm² wire. Edited July 24, 20232 yr by TaliaB