September 4, 20232 yr 4 hours ago, lun123 said: no the sensor does not show up there. No template sensors are shown, only the original "Master" and "Slave" entities Is there something i can do to show these sensors? Try adding: state_class: total_increasing to your template sensor i.e. # sensor.sunsynk_total_pv_energy sunsynk_total_pv_energy: friendly_name: Sunsynk Total PV Energy value_template: "{{ states('sensor.master_master_total_pv_energy') | float + states('sensor.sunsynk1_slave_total_pv_energy') | float }}" unit_of_measurement: "kWh" device_class: energy_storage state_class: total_increasing
September 5, 20232 yr Hi, I'm not sure if any of you have already checked this but I'm interested in the difference between the consumption displayed by the app (solarmann) and EspHome (# 084 Day Load Energy). Example from yesterday : # 084 Day Load Energy Solarmann application: Example from today: Solarmann application: A small update to this topic. I managed to solve the problem and I have the same results as in the orginal application. I added the code to ESPHOME: ############################################### Day Energy Consumption TOTAL ########################################### - platform: template # Sum of Day Load Energy and Day Grid Import and Day Battery Discharge to get total Day Energy Consumption name: "${friendly_name} Day Energy Consumption" unit_of_measurement: "kWh" accuracy_decimals: 2 device_class: energy state_class: total_increasing lambda: |- return (id(sunsynk_esphome_day_load_energy).state + id(sunsynk_esphome_day_grid_import).state + id(sunsynk_esphome_day_battery_discharge).state); update_interval: 5s Edited September 8, 20232 yr by Dariusz UPDATE
September 6, 20232 yr On 2023/09/01 at 9:01 PM, lun123 said: It has been running like this for days now and there is no if shown on the solar. , The issue I have with the template sensor created for "sensor.sunsynk_total_day pv" is that it does not read the state. State is shown as undefined. the other sensors read correctly, however this is info taken either form the master or the slave inverter. As soon as I create ethe combines sensor template, I get the same result. Hi, Did you manage to solve this problem? I don't know where the problem is but some sensors are not displayed correctly. Problem solved. As someone mentioned earlier it should be added: state_class: total_increasing Edited September 8, 20232 yr by Dariusz
September 12, 20232 yr The 8 and 5 use the same registers. https://github.com/slipx06/Sunsynk-Home-Assistant-Dash/blob/main/ESPHome-8K-Sunsynk.yaml Hi @slipx I have a three phase hybrid inverter Deye SUN-10K-SG04LP3 with battery pack. Will your yaml work with my inverter?
September 12, 20232 yr Hi @slipx I have a three phase hybrid inverter Deye SUN-10K-SG04LP3 with battery pack. Will your yaml work with my inverter? Hi. The registers for the 3 phase are different so it wont work without some modification. There is an example to get you started on the github but I have not tested this https://github.com/slipx06/Sunsynk-Home-Assistant-Dash/blob/main/DEY12k-modbus.yaml
September 12, 20232 yr Author Hi @slipx I have a three phase hybrid inverter Deye SUN-10K-SG04LP3 with battery pack. Will your yaml work with my inverter? If you use the 3-phase Yaml file you should be pretty good. They both use the same Modbus Registry document with the difference between the single phase and 3-phase inverters being when it comes to the values ones concerning the 3-phases of incoming and outgoing power. Otherwise the registers are pretty much the same. Attached is the Modbus Registry file I have sunsynk_modbus - no chinese (1).pdf
September 12, 20232 yr If you use the 3-phase Yaml file you should be pretty good. They both use the same Modbus Registry document with the difference between the single phase and 3-phase inverters being when it comes to the values ones concerning the 3-phases of incoming and outgoing power. Otherwise the registers are pretty much the same. Attached is the Modbus Registry file I have sunsynk_modbus - no chinese (1).pdf 309.74 kB · @Sc00bs I'll check soon. Thx
September 14, 20232 yr Does anyone know how to convert the Modbus register values for the MCU and COMM firmware to the actual values? These are registers 13 and 14 and my results when reading these are: MCU/13 6.0.2.4 Register Value: 24612 COMM/14 E.4.2.6 Register Value: -7130 The register document does not seem to give any indication of how to do this. Thanks Mark Edited September 14, 20232 yr by MarkvG
September 14, 20232 yr Does anyone know how to convert the Modbus register values for the MCU and COMM firmware to the actual values? These are registers 13 and 14 and my results when reading these are: MCU/13 6.0.2.4 Register Value: 24612 COMM/14 E.4.2.6 Register Value: -7130 The resister document doe snot seem to give any indication of how to do this. Thanks Mark Hex is your friend...
September 14, 20232 yr Hex is your friend... Thank you. I had tried that, but still not getting to expected result. Any further hints would be appreciated. Thanks
September 14, 20232 yr Thank you. I had tried that, but still not getting to expected result. Any further hints would be appreciated. Thanks Use the raw register values and not the twos-complement. So not the negative number. Since 24612 is a smaller number it's pretty straight forward. 0x6024
September 14, 20232 yr Thanks for the continued development and improvement, Johan @kellerza! This might be nothing, but I'm getting the following in my log. Any thoughts on why the "Unknown sensor specified" messages appear? Prolly a noob question, so apologies in advance! s6-rc: info: service s6rc-oneshot-runner: starting s6-rc: info: service s6rc-oneshot-runner successfully started s6-rc: info: service fix-attrs: starting s6-rc: info: service fix-attrs successfully started s6-rc: info: service legacy-cont-init: starting s6-rc: info: service legacy-cont-init successfully started s6-rc: info: service legacy-services: starting services-up: info: copying legacy longrun sunsynk (no readiness notification) s6-rc: info: service legacy-services successfully started 17:48:06 INFO Loading configuration: /data/options.json 17:48:06 INFO sunsynk library version: 0.6.4 17:48:06 INFO Schedules: +-----------+-----+------+--------+-----------+----------+------------+ | Key | src | Read | Report | Change by | Change % | Change any | +-----------+-----+------+--------+-----------+----------+------------+ | date_time | | 60 | 60 | | | True | | rw | | 5 | 300 | | | True | | w | * | 15 | 60 | 80 | | | | kwh | | 300 | 300 | | | | | any_unit | | 15 | 300 | | | | | no_unit | | 15 | 300 | | | True | +-----------+-----+------+--------+-----------+----------+------------+ 17:48:06 INFO Using three phase sensor definitions. 17:48:06 ERROR Unknown sensor specified: aux_power 17:48:06 ERROR Unknown sensor specified: essential_power 17:48:06 ERROR Unknown sensor specified: grid_connected 17:48:06 ERROR Unknown sensor specified: inverter_current 17:48:06 ERROR Unknown sensor specified: load_frequency 17:48:06 ERROR Unknown sensor specified: non_essential_power
September 14, 20232 yr @kellerza My log with Deye 10k, three phase: s6-rc: info: service s6rc-oneshot-runner: starting s6-rc: info: service s6rc-oneshot-runner successfully started s6-rc: info: service fix-attrs: starting s6-rc: info: service fix-attrs successfully started s6-rc: info: service legacy-cont-init: starting s6-rc: info: service legacy-cont-init successfully started s6-rc: info: service legacy-services: starting services-up: info: copying legacy longrun sunsynk (no readiness notification) s6-rc: info: service legacy-services successfully started 18:01:55 INFO Loading configuration: /data/options.json 18:01:55 INFO sunsynk library version: 0.6.4 18:01:55 INFO Schedules: +-----------+-----+------+--------+-----------+----------+------------+ | Key | src | Read | Report | Change by | Change % | Change any | +-----------+-----+------+--------+-----------+----------+------------+ | date_time | | 60 | 60 | | | True | | rw | | 5 | 300 | | | True | | w | * | 5 | 60 | 80 | | | | kwh | | 300 | 300 | | | | | any_unit | | 15 | 300 | | | | | no_unit | | 15 | 300 | | | True | +-----------+-----+------+--------+-----------+----------+------------+ 18:01:55 INFO Using three phase sensor definitions. 18:01:55 ERROR Unknown sensor specified: aux_power 18:01:55 ERROR Unknown sensor specified: essential_power 18:01:55 ERROR Unknown sensor specified: grid_connected 18:01:55 ERROR Unknown sensor specified: inverter_current 18:01:55 ERROR Unknown sensor specified: load_frequency 18:01:55 ERROR Unknown sensor specified: non_essential_power 18:01:55 INFO Added hidden sensors as other sensors depend on it: Rated power, Serial 18:01:55 INFO Connecting to tcp://192.168.1.167:8899 18:01:56 INFO Reading startup sensors Prog1 Time, Prog6 Time, Battery Low Capacity, Prog2 Time, Prog3 Time, Prog5 Time, Serial, Prog4 Time, Rated power 18:01:57 INFO ############################################################ 18:01:57 INFO Inverter serial number '****6152' 18:01:57 INFO ############################################################ 18:01:57 INFO MQTT: Connecting to homeassistant@core-mosquitto:1883 18:01:57 INFO MQTT: Connection successful 18:01:58 INFO Read every (inverter 1) +-----+----------------------------------------------------------------------------------+ | s | Sensors | +-----+----------------------------------------------------------------------------------+ | 5 | prog1_capacity, prog1_charge, prog5_charge, prog6_time, use_timer, grid_power, | | | prog3_capacity, grid_ct_power, prog2_charge, prog4_time, pv1_power, | | | prog4_charge, prog1_time, battery_low_capacity, prog2_time, prog6_capacity, | | | battery_power, prog3_power, prog6_charge, pv2_power, prog2_capacity, | | | prog1_power, prog5_power, prog2_power, priority_load, prog3_time, prog3_charge, | | | prog5_capacity, prog5_time, prog4_capacity, prog6_power, prog4_power, | | | load_limit, inverter_power | | 15 | battery_current, grid_frequency, overall_state, pv1_current, grid_voltage, | | | battery_voltage, pv1_voltage, battery_soc | | 300 | day_load_energy, day_grid_export, day_grid_import, day_battery_charge, | | | day_pv_energy, total_grid_export, total_battery_discharge, total_battery_charge, | | | total_pv_energy, total_grid_import, day_battery_discharge | +-----+----------------------------------------------------------------------------------+ 18:01:58 INFO Report every (inverter 1) +-----+---------------------------------------------------------------------------------+ | s | Sensors | +-----+---------------------------------------------------------------------------------+ | 60 | battery_power, grid_power, pv2_power, grid_ct_power, pv1_power, inverter_power | | 300 | day_grid_export, pv1_current, prog1_capacity, prog1_charge, prog5_charge, | | | prog6_time, battery_current, day_grid_import, use_timer, total_grid_export, | | | prog3_capacity, total_battery_charge, grid_voltage, prog2_charge, prog4_time, | | | pv1_voltage, battery_soc, day_battery_discharge, prog4_charge, day_load_energy, | | | prog1_time, grid_frequency, overall_state, prog2_time, prog6_capacity, | | | day_pv_energy, battery_low_capacity, prog3_power, prog6_charge, prog2_capacity, | | | total_pv_energy, prog1_power, prog5_power, battery_voltage, prog2_power, | | | priority_load, prog3_time, prog3_charge, prog5_capacity, day_battery_charge, | | | prog5_time, prog4_capacity, total_battery_discharge, prog4_power, prog6_power, | | | total_grid_import, load_limit | +-----+---------------------------------------------------------------------------------+ 18:02:10 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number 18:02:12 INFO Frame error retry attempt(1): V5 frame contains invalid sequence number 18:02:40 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number 18:03:10 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number 18:03:12 INFO Frame error retry attempt(1): V5 frame contains invalid sequence number 18:03:40 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number 18:04:10 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number 18:04:12 INFO Frame error retry attempt(1): V5 frame contains invalid sequence number
September 14, 20232 yr I also get the frame errors: 17:55:59 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number 17:56:01 ERROR OSError in read_deye: timeout reading 1 registers from 117 poll_need_to_read 18:01:58 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number 18:07:12 ERROR OSError in read_deye: timeout reading 1 registers from 117; timeout reading 37 registers from 141 poll_need_to_read 18:07:13 ERROR Error retry attempt(0): Connection already closed 18:14:05 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number 18:15:00 ERROR (1 in 5 min) OSError in read_deye: timeout reading 1 registers from 117 poll_need_to_read 18:15:01 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number
September 15, 20232 yr Thanks for the continued development and improvement, Johan @kellerza! Thanks, glad you find it useful! 17:48:06 INFO Using three phase sensor definitions. 17:48:06 ERROR Unknown sensor specified: aux_power 17:48:06 ERROR Unknown sensor specified: essential_power 17:48:06 ERROR Unknown sensor specified: grid_connected 17:48:06 ERROR Unknown sensor specified: inverter_current 17:48:06 ERROR Unknown sensor specified: load_frequency 17:48:06 ERROR Unknown sensor specified: non_essential_power Since you use sensor groups in your config (power_flow_card) https://kellerza.github.io/sunsynk/reference/definitions#power-flow-card-power-flow-card it includes several sensors. It seems like the names of the three-phase sensors do not match exactly, or these are not present in the three-phase inverter definition. Single phase defs: https://github.com/kellerza/sunsynk/blob/main/src/sunsynk/definitions.py Three phase defs: https://github.com/kellerza/sunsynk/blob/main/src/sunsynk/definitions3ph.py 18:04:12 INFO Frame error retry attempt(1): V5 frame contains invalid sequence number I also get the frame errors: 17:55:59 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number 17:56:01 ERROR OSError in read_deye: timeout reading 1 registers from 117 poll_need_to_read 18:01:58 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number 18:07:12 ERROR OSError in read_deye: timeout reading 1 registers from 117; timeout reading 37 registers from 141 poll_need_to_read 18:07:13 ERROR Error retry attempt(0): Connection already closed 18:14:05 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number 18:15:00 ERROR (1 in 5 min) OSError in read_deye: timeout reading 1 registers from 117 poll_need_to_read 18:15:01 INFO Frame error retry attempt(0): V5 frame contains invalid sequence number Apparently the solarman dongle is quite temperamental. There is some improvement (using native errors correction) in the edge addon. I've also asked the pysolman authors what they recommend to make this more reliable. Probably best to open an issue, as its easier to track on Github than in a forum.
September 21, 20232 yr Posted 17 hours ago Does anyone have a solution to this weird problem? We have a SOLARMAN app running for a few years without any issues. Now it reports the daily energy use, but the curves disappear the next day. So only shows the current day curves. The data is being collected and stored and I can download it to Excel. But we can’t see the history on the main page. We have tried everything. Deleting the account, reloading. Etc. The other 250 SOLARMAN apps we have installed work fine. In desperation, about to change to Sunsynk dongles and app for this client. Thanks,
September 22, 20232 yr Author Posted 17 hours ago Does anyone have a solution to this weird problem? We have a SOLARMAN app running for a few years without any issues. Now it reports the daily energy use, but the curves disappear the next day. So only shows the current day curves. The data is being collected and stored and I can download it to Excel. But we can’t see the history on the main page. We have tried everything. Deleting the account, reloading. Etc. The other 250 SOLARMAN apps we have installed work fine. In desperation, about to change to Sunsynk dongles and app for this client. Thanks, Have you tried contacting the guys at Solarman?
October 1, 20232 yr @kellerza, I figured it out.... Here is the addon added to @slipx .yaml file in order for the Force Generator functionality to be managed by HA. Adding it here in case it can help someone else in future... Wow, this is exactly what Im looking for... Can i trigger this as a script?
October 3, 20232 yr I just want to add, after numerous failed attempts and frustrating hours, I finally got my 5kw Sunsynk in HomeAssistant via a ESP32.
October 5, 20232 yr I just want to add, after numerous failed attempts and frustrating hours, I finally got my 5kw Sunsynk in HomeAssistant via a ESP32. Ditto from my side for an 8.8kW Sunsynk Thanks to all the bright folk on this channel who posted all the info/tips/code/photos etc. Also to the Solar Intergrations YouTube channel.
October 5, 20232 yr Author I just want to add, after numerous failed attempts and frustrating hours, I finally got my 5kw Sunsynk in HomeAssistant via a ESP32. Glad to hear you got sorted out @McGuywer
October 5, 20232 yr @kellerza Is there something in the configuration that could be causing my SolarMan dongle to freeze and become inaccessible?
October 5, 20232 yr Author @kellerza Is there something in the configuration that could be causing my SolarMan dongle to freeze and become inaccessible? If you have the refresh's set too often then it will overload the dongle and can interfere with the uploading of data to the cloud. Just increase the time between refreshes in the settings.
October 5, 20232 yr If you have the refresh's set too often then it will overload the dongle and can interfere with the uploading of data to the cloud. Just increase the time between refreshes in the settings. @kellerza Is there something in the configuration that could be causing my SolarMan dongle to freeze and become inaccessible? Try https://kellerza.github.io/sunsynk/reference/schedules#proposed-schedule-overrides-for-solarman Try those. YMMV depending on the amount of sensors you read. In this case less is better, else the dongle resets and disappears for a while Edited October 5, 20232 yr by kellerza
October 5, 20232 yr Try https://kellerza.github.io/sunsynk/reference/schedules#proposed-schedule-overrides-for-solarman Try those. YMMV depending on the amount of sensors you read. In this case less is better, else the dongle resets and disappears for a while Thank you.