Sunsynk 8kW

Featured Replies

9 minutes ago, Achmat said:

Brilliant. 

 

You can also manually turn the smart load on or off by long pressing the AC load icon on the main scream on the inverter. 

 

Some spelling mistakes on the Pdf but nothing that would impact reading it. 

Speaking of spelling mistakes, you've got a screamer going on there 😉

  • Replies 375
  • Views 93.2k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • There are 3 connections on the inverter.  Grid connection. This is the grid input connection but is also an output if the grid is available. If there are loads after the municipal meter but befor

  • The guy doing my install said why they don't use the thin dc strand for AC is because there is lots of little sparks between the inner part of the cable. The solid core is to limit the sparks between

  • Hi  Attached is a link to youtube for a good explanation of how a RCD works.    

Posted Images

13 minutes ago, Tariq said:

@Achmatcouldn’t find the ac load icon you are referring to, can you post a screenshot and highlight it 

The top right square that shows current loads. 

It will turn on for 2 hours but it seems the long press doesn't work anymore. Must have been removed with the newest firmware. 

Finally getting to test my SMART LOAD function, set the solar load at 2200 watts ( 2 kw geyser and average 200 watt household loads ), the day started out as partly cloudy and the SMART LOAD switched on and off as the sun moved in and out from behind the clouds, then the sky became totally cloudy/drizzly, I switched the ON ALWAYS ON GRID function ( grid is available ), inverter draws power from solar and battery, NOT from grid, as I originally thought, AND did not stop at the preset cut off percentage on the AUX screen, I had to untick TIME OF USE, then only did the inverter draw from solar and the balance from the grid.

This experiment was conducted with grid available

Thanks for all trhe interesting info. I am wanting to install 8KW Deye/Sunsynk hybrid in OFF-GRID system, and would like to use the generator port for smart loads (water heater). However, I would also like to install more solar with a suitable micro-inverter (ie has freq shift and derating). Can this be adone? In other words, can one use the generator port for smart load AND at the same time also AC couple additional microinverters either to generator port or battery out/UPS port? 

2 minutes ago, proteapermaculture said:

Thanks for all trhe interesting info. I am wanting to install 8KW Deye/Sunsynk hybrid in OFF-GRID system, and would like to use the generator port for smart loads (water heater). However, I would also like to install more solar with a suitable micro-inverter (ie has freq shift and derating). Can this be adone? In other words, can one use the generator port for smart load AND at the same time also AC couple additional microinverters either to generator port or battery out/UPS port? 

It can only be used in one way. Either generator or micro inverter but not both. 

If it's off grid with no incoming Eskom supply then you can use the grid input as a generator input and the aux for micro inverter.

4 minutes ago, proteapermaculture said:

OK. So generator power source and micro-inverter possible.....

BUT it seems that Smart load (uses generator port on Sunsynk ) and micro-inverter not possible? Is that correct

 

Correct. Smart load will only work on the aux port. 

Thanks Achmat for confirming its not possible to do both! Looking at info I still dont understand why the genertor port (aux port as you better call it) cant be used for the Smart load function and the AC coupling of microinverter connected on the battery UPS output (since its bi-directional inverter I believe). Looks like you cant have both as shown in the manual diagrams of settings, but is this a software or hardware limitation?

That makes sense...but:

The generator port is not only an input- thats why its called auxillary (aux). Aux port can be used for smart loads (loads only on when battery full or at specific percentage).

Then I also noted that AC coupling to the batttery ouput/UPS is possible so this port is also not only and output!. However, using the UPS output as input for microinverter  somehow disdables use of the aux port.

Hence my confusion!...

Edited by proteapermaculture

Thanks very much as it now makes sense when you said: "its the same port. You EITHER use it as a generator input OR microinverter input OR smart load which is an output. " To an unexperience eye the circuit diagrams does not seem like load and gen is the same port. (Sunsynk 8k manual)image.png.616734e0b17ca931d3d74a5f9c9a6de3.png

Edited by proteapermaculture

So I have a friend that could not wait to get his Axpert replaced with a Deye unit.

Now after a week he calls me in to help. Unit switches off when grid fails.

So I went a had a look. Man, what a ballsup...

So the "sparky" decided to wire the two Neutral terminal together, thus saving 2m of black wire.

When mains fails, the unit still stays on and shows 230V on the output, but measuring shows Zero volts.
I suspect the relay card failed?

Would this be expensive to replace?

On 2021/03/11 at 11:36 AM, proteapermaculture said:

Thanks very much as it now makes sense when you said: "its the same port. You EITHER use it as a generator input OR microinverter input OR smart load which is an output. " To an unexperience eye the circuit diagrams does not seem like load and gen is the same port. (Sunsynk 8k manual)image.png.616734e0b17ca931d3d74a5f9c9a6de3.png

Load and gen aren't the same port. Aux and gen are the same port. 

HI

I had a Synsynk 8 for about 15 months and then got a direct lightning hit on the lamp pole outside the house which took it out. I was absolutely satisfied with the old one and it did everything as expected.

Got a new one now and things are funny.  I have split the loads into essential and non essential.  Essential on the UPS side and non essential on the grid side.

The problem is that the power does not add up.  Often the sun would provide say 3kw.  The essential would take 1 kw and the battery is full so 2kw is available to non essential and the flow diagram shows the 2 kw flowing to non-essential.

The problem is when all non essential loads are disconnected, it still shows the 2kw flowing to them. So where is this power going.  I have clicked to the zero export, so nothing is suppose to flow to the grid.

The end results is that during the day all the available power is used and my usage curve follows the production curve exactly.

The exact same setup worked perfectly with my previous unit.

I  have not done the ground/neutral bond.

 

Regards

Attie

 

 

 

7 minutes ago, Attie Jonker said:

HI

I had a Synsynk 8 for about 15 months and then got a direct lightning hit on the lamp pole outside the house which took it out. I was absolutely satisfied with the old one and it did everything as expected.

Got a new one now and things are funny.  I have split the loads into essential and non essential.  Essential on the UPS side and non essential on the grid side.

The problem is that the power does not add up.  Often the sun would provide say 3kw.  The essential would take 1 kw and the battery is full so 2kw is available to non essential and the flow diagram shows the 2 kw flowing to non-essential.

The problem is when all non essential loads are disconnected, it still shows the 2kw flowing to them. So where is this power going.  I have clicked to the zero export, so nothing is suppose to flow to the grid.

The end results is that during the day all the available power is used and my usage curve follows the production curve exactly.

The exact same setup worked perfectly with my previous unit.

I  have not done the ground/neutral bond.

 

Regards

Attie

 

 

 

Have you checked that the CT coil is installed correctly? 

1 hour ago, Attie Jonker said:

Yes, I inverted the wires and then the ct value went negative.  The CT value however now stays zero the whole time and I cant remember if this is correct.

What points are the wires connected on the inverter? It might be in the wrong points. 

11 minutes ago, Wetkit said:

Should the CT not show Zero if everything is working correctly?

Perhaps disconnect the battery and the PV and then see what the power flow looks like?

Technically yes but the CT could even be on the wrong wire. 

 

4 hours ago, Attie Jonker said:

Yes, I inverted the wires and then the ct value went negative.  The CT value however now stays zero the whole time and I cant remember if this is correct.

What municipal meter do you have? If the inverter is pushing back to the meter it would trip if its a prepaid meter or worse, charge you for sending power back. 

Reading your post again and I think your CT is on the wrong wire. It should be on the live incoming line immediately after the municipal meter. 

5 hours ago, Attie Jonker said:

Yes, I inverted the wires and then the ct value went negative.  The CT value however now stays zero the whole time and I cant remember if this is correct.

This what my inverter shows. 

Screenshot_20210317-182901_Gallery.jpg

HI Guys 

Thanks for all the replies.

So yes my non essentials are on the grid side.  So if I switch off the Eskom incoming, then it recognizes no grid and only supply the essentials.  So this correct.  I only have 2 geyser and the stove on the grid side. So if I switch those breakers off, it means there is now no grid side load.  The inverter then still shows on the flow diagram power flowing to the little house next to the power lines.

I changed nothing when the new inverter was installed, did not move the CT coil or nothing.  Just installed the new inverter, so the only possibility for error regarding the CT coil is wires wrong way round.

I have a prepaid meter and it does not complain or anything when I export to the grid.

With the old inverter, you could clearly see that the grid side loads absorbing power or not as the trip switches to those loads were opened and closed.  Here I see nothing.

Regards

Attie

5 minutes ago, Attie Jonker said:

HI Guys 

Thanks for all the replies.

So yes my non essentials are on the grid side.  So if I switch off the Eskom incoming, then it recognizes no grid and only supply the essentials.  So this correct.  I only have 2 geyser and the stove on the grid side. So if I switch those breakers off, it means there is now no grid side load.  The inverter then still shows on the flow diagram power flowing to the little house next to the power lines.

I changed nothing when the new inverter was installed, did not move the CT coil or nothing.  Just installed the new inverter, so the only possibility for error regarding the CT coil is wires wrong way round.

I have a prepaid meter and it does not complain or anything when I export to the grid.

With the old inverter, you could clearly see that the grid side loads absorbing power or not as the trip switches to those loads were opened and closed.  Here I see nothing.

Regards

Attie

If the grid is down and it still shows electricity going to the non essential side then your CT is located on the wrong wire. 

Even though you do say nothing was changed since the new installation I do think the CT was moved in this process. I would physically go and make sure that the CT is installed at the right location. 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.