April 6, 20215 yr 51 minutes ago, Luminous said: AC travels on the outer part of a conductor was also going to comment on this, yes the skin effect exists, but at less than 100kHz, its hardly worthwhile mentioning, at 50Hz, its around 9mm for copper... so a 18mm round copper conductor would be penetrated 100% by AC mains. In fact the skin effect, we really only take note of or take into consideration, in RF applications...
April 6, 20215 yr On 2021/03/10 at 11:24 PM, Vassen said: its the same port. You EITHER use it as a generator input OR microinverter input OR smart load which is an output. The generator input is meant to start up a generator and charge the batteries when the batteries fall to a certain SOC. The micro inverter input is used to add an ac coupled inverter to give you additional solar production. A note, that the micro inverter zero export function does not really work as intended. I have had to disable to zero export when my batteries are below 90% and enable it again once batteries are over 90% otherwise it tends to export the micro inverter power to the grid. The smart load function is used to dump excess power to loads during excess solar production and batteries are over a certain SOC. If batteries fall below the configured SOC, the smart load is turned off. I suggest you watch some of the sunsynk / deye training videos which explain the operation of the inverter. I have been looking at putting up a wind turbine. Would it be possible you think to connect the turbine to the AUX input. Both My MPPT are being used at the moment. I have the 8.8kv inverter
April 9, 20215 yr With regard to the sound of the 8kw inverter. Within 6m you still here it clearly. It switches on and off so no even noice. I will not install it close to me. Spend a little and put it in the garage.
April 10, 20215 yr On 2021/04/01 at 6:31 PM, Vassen said: I have heard that the new models have 22A @Vassen how would you know if you’ve bought the newer model? Where can I check? Week before last I bought an 8kW SunSynk at a great price and it came with the WIFI dongle.
April 10, 20215 yr 5 hours ago, Trev said: @Vassen how would you know if you’ve bought the newer model? Where can I check? Week before last I bought an 8kW SunSynk at a great price and it came with the WIFI dongle. The specs on the sticker will say if it is an 18A or 22A version
April 11, 20215 yr On 2021/04/10 at 4:08 PM, Speedster said: The specs on the sticker will say if it is an 18A or 22A version 🙈 of course... Thanks!
May 13, 20215 yr What are the differences between Solarman Home, Smart and Pro and which is recommended? I am using SM Home on my Sunsynk inverter and the battery info is not correctly displayed. For instance, my comms between the batteries and inverter is correct and its controlled as expected but on the solarman app i only see 1 battery (i have 2) and the temp shows 100C which is definately not the case...
May 13, 20215 yr 1 hour ago, Induna said: What are the differences between Solarman Home, Smart and Pro and which is recommended? I am using SM Home on my Sunsynk inverter and the battery info is not correctly displayed. For instance, my comms between the batteries and inverter is correct and its controlled as expected but on the solarman app i only see 1 battery (i have 2) and the temp shows 100C which is definately not the case... What battery do you have? I have 4 pylontechs and it doesn't read the individual batteries but the data from the BMS. First pic is from Solarman Business and second one from Solarman Smart. I alternate between these two and even though I have pro and home versions I don't use them.
May 14, 20215 yr 7 hours ago, Achmat said: What battery do you have? I have 4 pylontechs and it doesn't read the individual batteries but the data from the BMS. First pic is from Solarman Business and second one from Solarman Smart. I alternate between these two and even though I have pro and home versions I don't use them. Thanks. I have 2 Lithium Batteries SA 5.2kW batteries. So far they are performing great and the price/kWh was also very good.
May 20, 20215 yr Hi everybody, I am new to solar and had a 8kw SunSynk installed with 14 x 415w Canadian panels and 3 x 3.6kw Pylontech's as a starting point. So far my batteries is functioning in "Backup Mode", still looking at my usage to see if my battery capacity will be enough to start using the timer for night time. One question I have is regarding exporting power to the grid. Is their a way you can limit the amount of power I can export to the grid instead of everything that is not used by consumption? This is my current settings: Edited May 20, 20215 yr by JimmyB
May 20, 20215 yr 2 minutes ago, JimmyB said: Hi everybody, I am new to solar and had a 8kw SunSynk installed with 14 x 415w Canadian panels and 3 x 3.6kw Pylontech's as a starting point. So far my batteries is functioning in "Backup Mode", still looking at my usage to see if my battery capacity will be enough to start using the timer for night time. One question I have is regarding exporting power to the grid. Is their a way you can limit the amount of power I can export to the grid instead of everything that is not used by consumption? How do you have it set up and connected? Do you have loads before the inverter (aka non-essential loads) and CT coil correctly installed?
May 20, 20215 yr 12 minutes ago, YellowTapemeasure said: How do you have it set up and connected? Do you have loads before the inverter (aka non-essential loads) and CT coil correctly installed? I have only my oven as non-essential, the rest of the house is essential loads. CT Coil I am not sure, will have to go and check. I have one of the very old analog disc power meters so i can push power back to the grid. Edited May 20, 20215 yr by JimmyB
May 20, 20215 yr 1 minute ago, JimmyB said: I have only my Stove as non-essential, the rest of the house is essential loads. CT Coil I am not sure, will have to go and check. I have one of the very old analog disc power meters so i can push power back to the grid. Your settings are correct if you don't to export. If the inverter is still exporting and your your meter is spinning backwards, then the ct sensor is either not installed or installed incorrectly. You can tick limit to load to only power the essential loads and nothing will go back to the grid or for the stove if it's on.
May 20, 20215 yr 19 minutes ago, JimmyB said: I have only my oven as non-essential, the rest of the house is essential loads. CT Coil I am not sure, will have to go and check. I have one of the very old analog disc power meters so i can push power back to the grid. As @Achmat has stated, if the CT is installed correctly and you tick "limit to loads" it should not export to grid. Ticking Sol Exp Batt Full will only export to grid once batteries have been charged.
May 20, 20215 yr 1 hour ago, YellowTapemeasure said: As @Achmat has stated, if the CT is installed correctly and you tick "limit to loads" it should not export to grid. Ticking Sol Exp Batt Full will only export to grid once batteries have been charged. Did check CT Coil is not installed. I do want to export to grid but I want to limit the amount that are being exported. Is that possible?
May 20, 20215 yr 13 minutes ago, JimmyB said: Did check CT Coil is not installed. I do want to export to grid but I want to limit the amount that are being exported. Is that possible? Not that I am aware of, the only way that you could limit it is by using your oven 😀
May 20, 20215 yr 28 minutes ago, JimmyB said: Did check CT Coil is not installed. I do want to export to grid but I want to limit the amount that are being exported. Is that possible? You can then tick limit to load but then if you have any excess pv it will not go to the stove when it's being used. Edit. Limit to load will only supply the essential loads even without a CT installed. If you have non essentials then the only way to limit export to only these loads would be to connect the CT sensor. Edited May 20, 20215 yr by Achmat
May 20, 20215 yr 19 minutes ago, YellowTapemeasure said: Not that I am aware of, the only way that you could limit it is by using your oven 😀 Use my oven as a big useless heater 🤣
May 21, 20215 yr Hi guys, great thread. I just had my solar system installed. 3.35kwp of solar and a 5kwh lithium battery. The whole house is on load except for geyser on aux and underfloor heating on grid. I have a few questions regarding how these inverters work.(installer didn't have much experience with these fancy inverters) 1. I switched off the inverter when grid was available and the appliances on load were disconnected. Is this how it should work? 2. I see a lot of posts about neutral earth bonding. Unfortunately I don't understand much about mains electricity. Is there a simple test that I can do with my multimeter to see if I have a problem or whether I will need a relay. 3. My battery is powering the non essential loads on the grid. I have use timer ticked in systems page I don't want this to happen. Is there a way of controlling this without using the aux port? Thanks in advance Edited May 21, 20215 yr by phidz
May 21, 20215 yr 34 minutes ago, phidz said: Hi guys, great thread. I just had my solar system installed. 3.35kwp of solar and a 5kwh lithium battery. The whole house is on load except for geyser on aux and underfloor heating on grid. I have a few questions regarding how these inverters work.(installer didn't have much experience with these fancy inverters) 1. I switched off the inverter when grid was available and the appliances on load were disconnected. Is this how it should work? 2. I see a lot of posts about neutral earth bonding. Unfortunately I don't understand much about mains electricity. Is there a simple test that I can do with my multimeter to see if I have a problem or whether I will need a relay. 3. My battery is powering the non essential loads on the grid. I have use timer ticked in systems page I don't want this to happen. Is there a way of controlling this without using the aux port? Thanks in advance Welcome to the sunsynk club. I've had the same experience where installers are only familiar with the axpert type inverters installed as a load shedding solution. 1. If the inverter is switched off, the loads will be disconnected. You should have a transfer switch before the inverter so that you can switch the loads back to grid if you need to switch the inverter off for maintenance and repairs. 2. I don't have the neutral bond on mine installed and have not had any issues so can't comment on how to test if you need to have this done or not. 3. Can you share your system mode screen. If you tick limit to load then the batteries will only be used for the loads and not go to the grid side.
May 21, 20215 yr 19 minutes ago, Achmat said: Welcome to the sunsynk club. I've had the same experience where installers are only familiar with the axpert type inverters installed as a load shedding solution. 1. If the inverter is switched off, the loads will be disconnected. You should have a transfer switch before the inverter so that you can switch the loads back to grid if you need to switch the inverter off for maintenance and repairs. 2. I don't have the neutral bond on mine installed and have not had any issues so can't comment on how to test if you need to have this done or not. 3. Can you share your system mode screen. If you tick limit to load then the batteries will only be used for the loads and not go to the grid side. Thank you, so far I'm very much impressed by this inverter. I have attached the system settings I have. Thanks I will tick the limit to load option and monitor. Another question is regarding solar input, I can't seem to reach anywhere close to pv size, it looks like the current is being restricted to around 10amps. The spec sheet on the inverter says 11 + 11. Edited May 21, 20215 yr by phidz
May 21, 20215 yr 8 minutes ago, phidz said: Thank you, so far I'm very much impressed by this inverter. I have attached the system settings I have. Thanks I will tick the limit to load option and monitor. Another question is regarding solar input, I can't seem to reach anywhere close to pv size, it looks like the current is being restricted to around 10amps. The spec sheet on the inverter says 11 + 11. In winter the panels will struggle to reach the full amps. On the Solarman app you can check the MPPT current and if it's clipping it will have a flat peak. Pic below is from my array which in summer it gets up to 18A but in winter it barely gets to 10A. I have the 8kw inverter. I know there were some issues which were resolved with a software update. What is the software version and have you requested an update since the installation.
May 21, 20215 yr 14 minutes ago, Achmat said: In winter the panels will struggle to reach the full amps. On the Solarman app you can check the MPPT current and if it's clipping it will have a flat peak. Pic below is from my array which in summer it gets up to 18A but in winter it barely gets to 10A. I have the 8kw inverter. I know there were some issues which were resolved with a software update. What is the software version and have you requested an update since the installation. Thanks a lot. I guess I just have to be patient till summer. It says COMM:e416 and MCU:3161 I have a 5kw inverter