August 17, 20205 yr 21 minutes ago, Johann1982 said: @AchmatSo while I was waiting for tech support to reply to my emails I decided to change the frequencies on my grid input.. I gave it a 0.5hz higher and 0.5hz lower tollerance... So far my aux load hasn't dropped again. So what are your settings now?
August 17, 20205 yr Author Grid V High 265.0V Grid V Low 185.0V Grid Hz High 52.00Hz Grid Hz Low 46.50Hz
August 17, 20205 yr 1 hour ago, Johann1982 said: @AchmatSo while I was waiting for tech support to reply to my emails I decided to change the frequencies on my grid input.. I gave it a 0.5hz higher and 0.5hz lower tollerance... So far my aux load hasn't dropped again. So Eskom could be the cause die to their fluctuating frequency and voltage? Any restarts yet? I can't test as I've already moved my aux loads over to the main load output of the inverter.
August 17, 20205 yr Brilliant. It would be difficult for me to monitor restarts as I only had a Geyserwise and two aircons connected so will not know of any restarts unless I am home at the time it happens. With your mining rigs on the aux output would be fairly easy for you to monitor the status of your aux output even if you are not home.
August 17, 20205 yr Author Yeah, I open the windows system logs then I can check for unscheduled restarts. None so far. I leave team viewer open on my work pc so that I can check if it goes down.
August 18, 20205 yr Author Ok, so had 3 restarts in a 24 hour period. I adjusted the Hz to max high and max low to further troubleshoot.
August 18, 20205 yr Author Ok, so just spoke to one of the better informed people at Sunsynk. Aux and Input binds internally when grid connection is available, so it exports grid to aux. When the mains goes off it disconnects and reconnects via DC bus. That is why there is a 5 second delay. So whenever the grid connection drops out of sync with mains the aux reboots. So it is either a sensitivity setting or the grid is too unstable.
August 18, 20205 yr Good investigation which brings us back to the Eskom supply being the issue more so than the inverter aux settings even though they could make some improvements to it.
August 18, 20205 yr Author @AchmatDefinitely. I am busy trying to get them to make the line input more tolerant to Eskom's unstable network. Will keep you posted.
August 18, 20205 yr 2 hours ago, Achmat said: Good investigation which brings us back to the Eskom supply being the issue more so than the inverter aux settings even though they could make some improvements to it. Where are you situated that Escom is fluctuating so badly?
August 18, 20205 yr Author @FixAMessI'm in Hermanus. Eskom isn't as bad, I just think the inverter is set too sensitive. Or a sudden change in frequency is too much for the inverter then it stops the feed to Aux.
August 18, 20205 yr 40 minutes ago, FixAMess said: Where are you situated that Escom is fluctuating so badly? I'm in Somerset West 1 minute ago, Johann1982 said: @FixAMessI'm in Hermanus. Eskom isn't as bad, I just think the inverter is set too sensitive. Or a sudden change in frequency is too much for the inverter then it stops the feed to Aux. No too far from me and agreed that the inverter might just be too sensitive to any sudden frequency changes to the grid.
August 18, 20205 yr 1 hour ago, Achmat said: I'm in Somerset West Weird... so am I, and I don't really see any issues. I think it does depend on your neighbourhood though. When I lived down in Somerset Ridge, I had a much more stable voltage than I do now. Difference between a house built in 2004 and one built in 1975 🙂
August 20, 20205 yr On 2020/08/16 at 7:52 AM, Johann1982 said: @AchmatNo, didn't do earth bond as I have tested it as is and even in off-grid mode my ELU's work. I think it does an internal bond also, the relay with the earth bond is just an extra precaution. Hi Johan, do a voltage check between load neutral and earth when AC grid is off. One of the Sunsynk manuals specifically states you will read 110v with a floating neutral unless resolved with a relay. My load output neutral earth measured +- 50V when in island mode but this was resolved when I installed a relay. The 50V gave me a little bite when touched. Surprisingly my E/L did trip when you press the test button without relay installed but I was told that is not a reliable test for safe functioning. The Sunsynk definitely does not have an internal relay doing the bonding job like a Victron. I bought a R100 40A NO relay from ACDC. It is so small I fixed it with cable ties inside the inverter. As you know there is a lot of space inside once you open the front cover.
August 20, 20205 yr On 2020/08/14 at 8:43 AM, Johann1982 said: Does anyone know of realtime monitoring software for these inverters? The portal is dodgey most of the time and slow. Can't wait 5 minutes every time for the logger to upload, would like to be able to see stats real time. Hi Johan, in passing the other Johan from Centurion Solar mentioned to me he was trying to retrieve the communication protocol from Sunsynk. I suppose Centurionsolar is thinking about running the Sunsynk on the ICC solar software. This should enable real time view and control like it can on the Mecer/Axeprts, however I do not see any reason Sunsynk cant hook up a better solution themselves.
August 20, 20205 yr 15 minutes ago, Halcyon said: Johan from Centurion Solar mentioned to me he was trying to retrieve the communication protocol from Sunsynk They did not mention anything about this being proprietary, so I assume it is OK to post here. sunsynk_modbus.docx
August 20, 20205 yr Author 5 hours ago, Halcyon said: Hi Johan, do a voltage check between load neutral and earth when AC grid is off. One of the Sunsynk manuals specifically states you will read 110v with a floating neutral unless resolved with a relay. My load output neutral earth measured +- 50V when in island mode but this was resolved when I installed a relay. The 50V gave me a little bite when touched. Surprisingly my E/L did trip when you press the test button without relay installed but I was told that is not a reliable test for safe functioning. The Sunsynk definitely does not have an internal relay doing the bonding job like a Victron. I bought a R100 40A NO relay from ACDC. It is so small I fixed it with cable ties inside the inverter. As you know there is a lot of space inside once you open the front cover. @HalcyonOk, sounds like a plan. mind attaching a photo of your relay setup please?
August 20, 20205 yr 4 hours ago, JustinSchoeman said: They did not mention anything about this being proprietary, so I assume it is OK to post here. sunsynk_modbus.docx 185.4 kB · 13 downloads How would I go about using this info? I have no knowledge of home automation or setting up a pi. Would be interested in a plug and play solution though.
August 20, 20205 yr 2 hours ago, Johann1982 said: @HalcyonOk, sounds like a plan. mind attaching a photo of your relay setup please? Sure I’ll open it up when I get a chance and send a pic. In the mean time here is a link to their latest manual. Refer page 15 and 17. Mine was wired like the diagram. https://6a0f9a11-bc20-45f8-b815-9b3f4c5ed335.filesusr.com/ugd/50e58b_26a9a8b1b3ee486f808a5ad94bb042fc.pdf I used a 40A Normally open power relay with 230v ac coil from AC/DC. Live neutral wire powering coil into 240V ATS port on inverter. Earth wire bridging load E and N into the Common and NO port on relay. Make sure to tick is-landing mode signal check box setting in battery section of setup menu and Voila.
August 20, 20205 yr Author @HalcyonWould I have to bind earth and neutral on my smart load as well or are they connected internally to the load output and one relay on the output would be enough?
August 20, 20205 yr Good question. I think one would be enough but to be honest I am not sure. Check the manual page 9, they have a circuit block diagram showing how the AC and DC bus are set up. Including the grid, Gen, load outputs with relays diagrams.
August 21, 20205 yr 9 hours ago, Halcyon said: Sure I’ll open it up when I get a chance and send a pic. In the mean time here is a link to their latest manual. Refer page 15 and 17. Mine was wired like the diagram. https://6a0f9a11-bc20-45f8-b815-9b3f4c5ed335.filesusr.com/ugd/50e58b_26a9a8b1b3ee486f808a5ad94bb042fc.pdf I used a 40A Normally open power relay with 230v ac coil from AC/DC. Live neutral wire powering coil into 240V ATS port on inverter. Earth wire bridging load E and N into the Common and NO port on relay. Make sure to tick is-landing mode signal check box setting in battery section of setup menu and Voila. Halcyon, thanks for your info. Have the 8kw inverter and all working well. When connected to grid the voltage between earth and neutral is fine. When grid falls away the voltage difference is bad. So in island mode does this solve this problem? My thinking was to install relay onto grid, if grid falls away then connect neutral to earth through the relay. thanks for your comment.
August 21, 20205 yr 6 hours ago, Werner67 said: Halcyon, thanks for your info. Have the 8kw inverter and all working well. When connected to grid the voltage between earth and neutral is fine. When grid falls away the voltage difference is bad. So in island mode does this solve this problem? My thinking was to install relay onto grid, if grid falls away then connect neutral to earth through the relay. thanks for your comment. Hi Werner, the only way to solve the problem is with a power relay linking load output neutral and earth when grid falls away and vice versa. The inverter emits a voltage signal to switch the relay on and off. To use this signal you have to have the latest firmware installed on the machine and check the box in settings for island mode signal. Refer to the latest Sunsynk manual. It shows how to wire and setup correctly.
August 21, 20205 yr On 2020/08/20 at 8:55 PM, Halcyon said: Sure I’ll open it up when I get a chance and send a pic. In the mean time here is a link to their latest manual. Refer page 15 and 17. Mine was wired like the diagram. https://6a0f9a11-bc20-45f8-b815-9b3f4c5ed335.filesusr.com/ugd/50e58b_26a9a8b1b3ee486f808a5ad94bb042fc.pdf I used a 40A Normally open power relay with 230v ac coil from AC/DC. Live neutral wire powering coil into 240V ATS port on inverter. Earth wire bridging load E and N into the Common and NO port on relay. Make sure to tick is-landing mode signal check box setting in battery section of setup menu and Voila. Can you post a picture of your relay connection up close? The diagram on the manual isn't clear.