September 25, 20214 yr Hi, thank you for the fruitful information shared. I was looking for Firmware F2809_GW500.07_20191227_B. for updating of my system (SPF 5000TL HVM-WPV) but unfortunately I could not find this in the site. would you guys please guide me where I can find this Firmware.
September 25, 20214 yr On 2021/08/29 at 11:42 AM, Rooney Hat said: I'm pretty sure the firmware for the TL and ES are very different as they are totally different types. TL can be found here: https://drive.google.com/drive/folders/12ttv9oCoC2rowUPDdsjfs0P4fz9DuSVt Good advice indeed, I have my 3 x 4.8kWh LiFePo4 batteries with the TL low voltage inverter. During the day my bats get fully charge at around 14h00 and the solar is no longer used but the bats until say about 80% and then charge again till there is no sun and the the bats are at 90%. Is this normal or my inverter settings are wrong? I need to set it such that when the bats are full it can direct the solar power to the household appliances and they average 300Wh. Please assist with the correct settings to achieve this.
October 1, 20214 yr On 2021/09/25 at 12:52 PM, Augyman said: Good advice indeed, I have my 3 x 4.8kWh LiFePo4 batteries with the TL low voltage inverter. During the day my bats get fully charge at around 14h00 and the solar is no longer used but the bats until say about 80% and then charge again till there is no sun and the the bats are at 90%. Is this normal or my inverter settings are wrong? I need to set it such that when the bats are full it can direct the solar power to the household appliances and they average 300Wh. Please assist with the correct settings to achieve this. I think you might be running into a similar issue that I have. I'm using Pylontech LI Batteries with BMS enabled, and it will fully charge to 100% then turn off solar completely and discharge batteries till 94% then charge again. This has been reported as the normal for the TL model, I think it's damn stupid. As a work around, once this happens, I have a ugly method to get it working properly, but it's manual process currently: 1) When batteries hit 100% and the solar turns off, I let it drop to 99%, then I set the inverter from SBU to Utility, then switch it back to SBU again a few seconds later... This enables the solar again. 2) As I have PylonTech and can connect to them via console, Enable admin mode and disable charging for both my batteries. This keeps the solar incoming to power the house but does not charge the batteries anymore. Then once the sun is down, I enable charging again on my batteries. It's really an ugly way of doing it, but until I get a new inverter or they release a firmware that fixes it, that's how it goes.
October 1, 20214 yr 32 minutes ago, Rooney Hat said: I think you might be running into a similar issue that I have. I'm using Pylontech LI Batteries with BMS enabled, and it will fully charge to 100% then turn off solar completely and discharge batteries till 94% then charge again. This has been reported as the normal for the TL model, I think it's damn stupid. As a work around, once this happens, I have a ugly method to get it working properly, but it's manual process currently: 1) When batteries hit 100% and the solar turns off, I let it drop to 99%, then I set the inverter from SBU to Utility, then switch it back to SBU again a few seconds later... This enables the solar again. 2) As I have PylonTech and can connect to them via console, Enable admin mode and disable charging for both my batteries. This keeps the solar incoming to power the house but does not charge the batteries anymore. Then once the sun is down, I enable charging again on my batteries. It's really an ugly way of doing it, but until I get a new inverter or they release a firmware that fixes it, that's how it goes. My ES does this as well. Doesn't seem to just be a TL thing. I'm using March 2021 firmware for my ES.
October 1, 20214 yr Maybe if we keep bugging Growatt support with these issue of PV switching off when batteries are at 100%, they will come up with a fix for that. They need to understand that this can not be normal 😁 Edited January 18, 20233 yr by hoohloc gramma
October 1, 20214 yr 27 minutes ago, hoohloc said: Maybe if we keep bugging Growatt support with this issue of PV switching off when lithium batteries are at 100%, they will come up with a fix for that. They need to understand that this can not be normal 😁 Slight correction
October 1, 20214 yr 39 minutes ago, hoohloc said: Maybe if we keep bugging Growatt support with this issue of PV switching off when batteries are at 100%, they will come up with a fix for that. They need to understand that this can not be normal 😁 It also doesn't seem to matter how it's being charged. I don't even have PV; Eskom recharge only, and batteries are cycled to 94% every time.
October 1, 20214 yr My es only switches off pv in SUB mode. It works normally in SOL(sbu). The battery was full early pv went down to support the base load before I put the aircons on on the screen shot. Firmware version 041 00 328 which as far as I'm aware came with the inverter.
October 15, 20214 yr On 2020/02/17 at 10:54 PM, SiliconKid said: I've recently purchased and installed the following: 1 x Growatt SPF 5000TL HVM 5kVA/5kW Hybrid Inverter. 2 x Pylontech US3000 batteries. 1 x Pylontech cable kit with RJ45 BMS comms cable included. I've just spent 5 days communicating with Growatt in China to figure out why I could not get the inverter to communicate with the BMS on the master battery properly. After many, many emails back and forward, and far too many hours of research online, I finally got it right today and I think it is worth sharing this information here, in case anybody else needs it, because I couldn't find the right information anywhere on the internet, all in one place, explained properly. It turns out that the Growatt SPF5000 has to be connected to the Pylontech batteries differently to the way Axpert inverters are connected to Pylontech batteries. Everything I was reading online was saying that you need to plug the RJ45 comms cable into the CAN port on the master battery and then into the BMS port on the inverter, and then you need to set the battery type to Li (setting 05 on Axpert and Growatt inverters) and then choose Li profile L02 (also apparently the same for Axpert and Growatt inverters). It turns out, the Growatt does NOT communicate via the CAN port. It communicates via the RS485 port that is positioned below the CAN port on the master battery. And in addition to that, it requires a 9600 baud rate, which you can set using the 4 small white dipswitches on the master battery. For the Growatt you must set those dipswitches to: 1 0 0 0 (ON OFF OFF OFF) When connected to the CAN port and put into Li (L02) mode, the Growatt inverter faults and gives an error 20 and an error 04 constantly. When connected to the RS485 port with the dipswitches set to 1000, comms is immediately established and it works as intended. I also installed 2 firmware updates on the inverter, that were sent to me by Growatt in China (who were very helpful through this entire process despite not actually giving me the information I actually needed to solve this), but in retrospect I actually wonder if those firmware updates even made a difference because I was able to put the inverter into Li (L02) mode before applying those firmware updates anyway, I just didn't know about the RS485 port and the dipswitches. Recommended configuration process 1. Turn inverter on but run off battery only. Disable A/C input and A/C output (use isolator switches if you have them). 2. Go to setting 5 and select battery type = Li. Then select profile L02 (This is specifically for Pylontech batteries). Push ESC to return to home screen. Go back to setting 5 and verify that it was saved as Li. 3. Now shutdown the inverter and batteries completely. Turn the batteries off using the on/off flip switch, not just the red button on the master battery. 4. Now make sure that the end of the comms cable on the battery side (it will probably have a little sticker on it that says BAT) is plugged into the RJ45 port labelled RS485 that is below the CAN port. And also make sure that the other end is plugged into the RJ45 port labelled BMS on the inverter and NOT into the other RJ45 port that is labelled RS485 (Yes, I know, it's weird, just go with it). 5. Now set the 4 little white dipswitches to: ON OFF OFF OFF (1000). 6. Now turn the batteries back on and then turn the inverter back on. You should no longer see any fault codes or the red fault light. How to tell that the inverter really is communicating with the BMS properly 1. You should now see a little Li symbol next to the battery icon on the home screen of the inverter, and that Li symbol should NOT be flashing. When it's not flashing and is solid it means comms is working. 2. If you go and look at most of the battery values on the status screens or in settings related to battery level (SOC) you should now see percentage values where there were voltage values before. Setting 21 is a good example of that. I hope this helps somebody else because the information available online with regards to the Growatt routers is of no help in this regard and most of the information available relates to Axpert inverters, which appear to be very similar to the Growatt at face value, but communicate with the Pylontech batteries differently from what I can see. Hello there. I have the SpF 5000 ES and your advice did not work for me. I was about to create my own cable because I noticed that on Pylontech side the Can/RS485 socket has the Pin 7/8 for communication but the Growatt has the pins 1and2. But my brilliant wife came with the idea of using Can port on batteries and to select L052 instead of Loo2 from menu 36. Result=> IT WORKS!!!
October 16, 20214 yr 15 hours ago, Vali said: Hello there. I have the SpF 5000 ES and your advice did not work for me. I was about to create my own cable because I noticed that on Pylontech side the Can/RS485 socket has the Pin 7/8 for communication but the Growatt has the pins 1and2. But my brilliant wife came with the idea of using Can port on batteries and to select L052 instead of Loo2 from menu 36. Result=> IT WORKS!!! That's exactly what you're supposed to do for the 5000ES. Glad it works now.
October 30, 20214 yr Finally received a new firmware. I am seeing the battery go into standby mode see screenshots. Solar is still providing to the load.
October 31, 20214 yr 15 hours ago, Iss said: Finally received a new firmware. I am seeing the battery go into standby mode see screenshots. Solar is still providing to the load. Can you perhaps share that firmware?
October 31, 20214 yr 16 hours ago, Iss said: Finally received a new firmware. I am seeing the battery go into standby mode see screenshots. Solar is still providing to the load. Now this is interesting Edited October 31, 20214 yr by hoohloc
October 31, 20214 yr 6 minutes ago, hoohloc said: Now this is interesting Indeed. I thought 500.09 was the latest and greatest. Maybe this latest version 'fixes' the issue with lithium batteries
October 31, 20214 yr 3 minutes ago, JoeyhZA said: Indeed. I thought 500.09 was the latest and greatest. Maybe this latest version 'fixes' the issue with lithium batteries it looks like that. 🥳
October 31, 20214 yr 37 minutes ago, hoohloc said: Hi Bro Can you send me the the firm you have and the procedure to do the update? want to give it a try. Are you using Pylontech batteries or which batteries are you using? Everytime my batteries are full, my inverter switches off the PV and draws from the batteries but the same does not happen at night. When the batteries are full at night, the inverter just keeps them on idle and keeps drawing form the grid, which is perfect. Just can't get the same to happen during the day with PV or grid and if this firmware fixes this issue, then it will be a blessing 😄 1 hour ago, JoeyhZA said: Can you perhaps share that firmware? https://drive.google.com/file/d/1XFeZBEfKaXHCVBjgOuDSKhve3fnwJald/view?usp=drivesdk
October 31, 20214 yr 52 minutes ago, hoohloc said: it looks like that. 🥳 Will wait for you to give it a go and see if it solves it all then I'll get some lithiums
October 31, 20214 yr Just now, JoeyhZA said: Will wait for you to give it a go and see if it solves it all then I'll get some lithiums 😂 Maybe I should wait a bit and get more details from @Iss . Not sure if he is using BMS, he said his setting on setting 05 is USE
October 31, 20214 yr 18 hours ago, Iss said: Finally received a new firmware. I am seeing the battery go into standby mode see screenshots. Solar is still providing to the load. Here is the firmware : https://drive.google.com/file/d/1XFeZBEfKaXHCVBjgOuDSKhve3fnwJald/view?usp=drivesdk
October 31, 20214 yr 33 minutes ago, hoohloc said: 😂 Maybe I should wait a bit and get more details from @Iss . Not sure if he is using BMS, he said his setting on setting 05 is USE Using BMS on PylonTech US3000B&C batteries
November 1, 20214 yr Can someone assist me with access to download this firmware. I read that the process of uploading the firmware is a bit of a challenge. If there is a post on the forum that guides how to go about uploading the firmware please also assist me with it. Thanks a lot.
November 1, 20214 yr 23 minutes ago, Augyman said: Can someone assist me with access to download this firmware. I read that the process of uploading the firmware is a bit of a challenge. If there is a post on the forum that guides how to go about uploading the firmware please also assist me with it. Thanks a lot. Hoping to upgrade to fix an issue you're currently experiencing? If not ,applying the whole if it ain't broke leave it methodology might be an idea.
November 5, 20214 yr On 2021/10/30 at 4:06 PM, Iss said: Finally received a new firmware. I am seeing the battery go into standby mode see screenshots. Solar is still providing to the load. Excellent news! Any further feedback on this so far? Also still seeing the issue where data is lost for some time or has this also been resolved? Any other updates like BMS/Comms Board updates applied? Other than this main FW update? (500.12)
November 6, 20214 yr 22 hours ago, Tsa said: Excellent news! Any further feedback on this so far? Also still seeing the issue where data is lost for some time or has this also been resolved? Any other updates like BMS/Comms Board updates applied? Other than this main FW update? (500.12) The only issue I have is the total values from the comm card is in minus values. Other than that I’m happy with the update. I scheduled a meeting with Amos to has a look at the issue. At this time I’m leaning towards a DB or software bug.
November 6, 20214 yr On 2021/11/01 at 1:05 PM, Augyman said: Can someone assist me with access to download this firmware. I read that the process of uploading the firmware is a bit of a challenge. If there is a post on the forum that guides how to go about uploading the firmware please also assist me with it. Thanks a lot. Note that firmware on that post was 500.09. The procedure to flash remains the same.