Hi I installed a Axper King inverter with 12 x JAP72S09-340/SC 340W panels in a 2S-6P configuration. The MPPT controller blew 2 weeks ago after 6 months of operation and I sent it back for a warranty claim. The supplier responded with "We need to change your Solar Charge Controller that got damaged due to the wrong connection of the solar panel configuration. Incorrect input Voltage and Current. The ---5KING inverter should be 3 in series with a maximum of 4 strings in parallel of +- 330w – 360w solar panels." I responded with the manufacturer spec stating a 60-115v PV voltage with 4000w limit. My panels are 37.74v max power and with 2S at 75.48V. Well within…
- 30 replies
- 9.6k views
-
Sorry if this is in the wrong place since I have installed my inverter on Sunday I am unable to read my pre paid meter. it shows error -30- I have tried all the plugs in my house, inverter side and grid side but nothing seems to work. If I go to my gate motor in the front of my property and plug it into a socket then the meter reads just fine, if I run to my house before the meter battery goes flat it will sit on a reading without changing and then eventually go into error -30- I have tried unplugging the ct coil from the inverter to see if that helps, but it doesn’t. because I don’t have solar I am testing the work mode out so I can cycle my ba…
- 50 replies
- 12k views
- 2 followers
-
I have set up in SunSynk battery setup the following:- Lithium Battery Capacity 144AH Charge Amps 100A Discharge Amps 100A (activate ticked) When I check the LI-BMS on the panel I get a communication error. How do I make the communication work.
-
- 1 reply
- 1.5k views
-
-
Hi , I am looking for a push notification subsystem that will allow me to push inverter and battery events to my smart phone . Such events will naturally include ac grid disturbance / recovery , battery SOC thresholds , inverter / battery faults , energy usage thresholds etc. I have now experienced that such a subsystem is not nice to have , it is critical in the lifecycle of home solar system. I have a embedded Linux based controller similar to raspberry pi , and my own logging service app exposes full metrics from my Axpert inverter and battery . I have evaluated an app called gotify which I installed on my cloud server , but have experienced reliability issues et…
- 11 replies
- 1.4k views
-
Hi, Anyone with Growatt SPF5000-ES knowledge tell me if its normal for the Fans to spin all the time (or Turbines by the sound of it.) Just installed a new Inverter in my house but with the Fan's blowing all the time means more money to move it. No Errors, everything works lekker. Just Turbines are annoying Thanks all
- 7 replies
- 11.1k views
-
thought i would give you guys a heads up.... Over the last 3 weeks, i have had 6 Imeon installs fail. 4 of the units have been fan failures, 1 has been charger circuit board and this weeks one has just been internal failure. The way that the manufacturer is handling the issues and the time factor leaves a fair bit to be desired. Firstly not stock in S.A for spares initially, then a delay of between a week to 3 weeks for repair. I must admit two were swapped out with a fight. Their tends to be a pattern, between 4 to 6 months of usage you will start getting a red led error with the center icon flashing, once you reset the unit it will work again for 15min up to a da…
- 26 replies
- 13.3k views
-
Hi all, What cable is needed to let the inverter and battery talk to each other? Thanks
- 14 replies
- 2.9k views
-
I'm Eskom fed and I've found that my analogue "wheel" only turns back if I export 3kw or less. When it rises to 10kw or more, the wheel stops. Is there a way I can limit the solar export power on my Sunsync 16kw inverter?
- 7 replies
- 2.7k views
-
Hi. Anyone with experience in using the Smart Load function on the Deye / SunSynk inverters? I have 5KWp PV but using on average under 2KW at any time during the day, so want to connect one geyser to the inverter using the Smart Load feature. System is grid tied and works very well, but want to optimise the use of the 5KWp panels and 8Kw inverter! Recommendations on any energy efficient geyer elements that I can use?
-
- 18 replies
- 27.4k views
-
-
Hi, We have an MECER Axpert MKS Hybrid off-grid inverter 5kVA/5kW with Pylontech 3000. At the end of load shedding, when the power is restored, the inverter begins charging. Right at the end of its charging cycle, the power drops for a brief period and causes all computers in the office to switch off. Any idea on what setting on the inverter needs to be adjusted to prevent this brief cut off from happening? Thanks Jim
-
- 3 replies
- 1k views
-
-
Hey guys Been struggling with new inverter(RCT-AXPERT MX2 11K 48v) setup on Pylontech 2x UP5000.I cant seem to get the inverter and batteries communicating when setting program 5 to pyl i get error 61 and no flashing battery to confirm the two are communicating. I have tried multiple cables for the pin layout to no avail. Anyone have a confirmed working pin lay out for the BMS cable or a maybe a firmware update for the inverter?
- 2 replies
- 901 views
-
Excuse my ignoramxe here. We are busy building a new.small house and would like to have my mecer 1kw run our lights (all. Led) and all plugs in the two bedrooms as these will only. Be used for very light loads (cellphones, laptop etc) How does one do this? Do I tell the electrician to connect the inverter to the lights and plugs breakers? How does one do This? We want the inverter to supplement eskom, meaning the inverter support the loads then automatically switch to eskom when battery or sun finish.
- 6 replies
- 1.8k views
- 2 followers
-
Hi; I have a Sunsynk 8kw and 2x5kw Greenrich batteries. I was wondering is there a way that one can see the Cycle count on the Sunsynk itself or the web app perhaps by using the remote debug feature. Thanks
-
- 3 replies
- 2.7k views
-
-
Good day all I have searched but it seems that not many have used the Solis 6kw hybrid inverter. For those who have, may I please pick your brain a bit. I have taken the plunge to install 4x535W panels with the Solis 6kw hybrid inverter in a grid tied configuration (with a conlog bec23 prepaid meter). I also have 2 x 4,8kWh pylontech up5000 batteries connected. Thanks to the guys at conlog I have successfully deactivated the load line reversal trip with the token they gave me. My question is on the running program/mode of the inverter. I am currently running on "self use" mode as I want to charge the batteries with the surplus power not used and then cycle…
- 23 replies
- 10.7k views
- 1 follower
-
HI All I been have an issue with above inverter, I have 6 X 480w PV installed (2 panels in series 3strings) with Hubble AM2 5.5kw battery, I run the inverter in SUB mode ( as I dont want to cycle the battery). I have the system for about 2 months, I have noticed after a month sometimes it will drop PV output to 16w with around 92volts but zero amps for 20-30mins even under load and than starts working again, over the last week , it gotten worse like in picture one for about 1.5 hours no amps so PV output is about 16w but I am getting 92v approx during this time. now since last Friday (see pic2) every morning once sun us out , there is no amps with around 92v and on…
- 6 replies
- 1.2k views
-
Hello Forum Colleagues, Long story short, this has happened/has been happening to me for a while now, with two different inverter models, from two different producers --> hybrid MPP Solar PIP6048MT 6kW, the one that I have now installed in my PV system, and the previous hybrid inverter from Powland 5kW (exact model does not matter now), that I have replaced. In the morning (between 8AM - 10 AM), the inverter does not see the real & correct PV panels voltage & wattage and keeps on pulling energy from battery to power the loads, even if the battery is 100% charged (PYLONTECH US3000C - 1 unit) from the utility during the night, and I know for sure that the pane…
-
- 1 reply
- 1.1k views
-
-
Hey guys, has anyone noticed the strange values in the growatt server dashboard? They dont seem to add up all that well to me and I'm wondering if its the dashboard itself that's wrong or something on my end. Basically below you'll see that I've generated 10.0kWh from Solar, imported 4.6kWh from the grid, Discharged 0.1kWh from Batteries and Charged 10.0kWh, with a total consumption of 9.6kWh today. But I think its reporting wrongly between the Solar today & Charge today. Since I've been running SBU today with SOL-only charge, there's no grid going into my batteries & I'm able to run all day just on Solar while charging as well with the occasiona…
- 12 replies
- 2.7k views
-
Hello, I want to change the date on my inverter display with is wrong... But can't seem to find how. I have tried to do that using the watchpower app but I couldn't. Ps the date on the app is correct... On the one on the display of the inverter is wrong. If anyone knows how to fix it please help
-
- 0 replies
- 560 views
-
-
hello brothers i need axpert vm 3kva 50 PWM scc frimware
-
- 0 replies
- 512 views
-
-
Good day all, I am looking at a 10kva Victron system with 14.3kw Solar MD battery and 16 x 540w panels in Durbanville - Cape Town. Any reason to rather go with the 10kva instead of 2 x 5kva Multiplus II? Apparently I don't need the Zeihl anti islanding relay with the 5kva units, but do need it with the 10kva MP II. Also only see the 3 and 5kva units on the City of Cape Towns approved inverter list and not the 10? Would d be much appreciated if someone can give me advice and more info. Regards,
-
- 0 replies
- 1k views
-
-
Hi folks, My system uses 3 Growatt 5000es inverters in three phase mode with 9 Pylontech US3000C batteries. The inverter works in SBU mode (Solar->Battery->Utility). In the mornings all solar power charges the battery and the house uses the grid (instead of using solar for the house and the remaining power for the battery charge). This is clearly a firmware bug, as if I turn off the grid input, the inverters stars working as it should (using solar for the house loads and charging the battery with remaining power). Here is clearly shown: And after switching off the grid for 5 seconds and then turning it back on, it works as it should: Ano…
- 15 replies
- 15.1k views
- 1 follower
-
I have an Axpert/VM-3000 inverter, panels, lifepo4. As soon as it starts getting light in the mornings, about 1.5 hours before the panels can produce usable energy my inverter switches over to solar/battery, same in the afternoon, the last 1.5 hours of daylight does not produce much energy. I don't want the inverter to use battery power. It must use solar when enough is available to power the load, and switch to Utility when PV input falls below what's needed. I don't want it to use battery power as it adds cycles on the batteries. Where do I go from here: Add a timer switch on the PV input wires, and only connect the panels to the inverter during th…
- 5 replies
- 1.6k views
- 1 follower
-
Anybody have the Voltronic Axpert RCT MX2 Hybrid off-grid inverter 8KW installed with Hubble AM2 battery that can share the settings perhaps.
-
- 0 replies
- 503 views
-
-
Hi I am hoping someone can assist me here. I am having a couple issues on the my sun synk 8kW inverter. My setup is completely off grid and running 10kW of LI batteries but they do not have compatible BMS. I have been advised that for full off grid state the system should not the work mode timer engaged however it seems that even if I turn it off it re-enables itself after a minute or so. I am having the following issues and I am not sure if its related to the work mode timer but the device is inconsistent about how it works. 1. Battery levels will indicate as low and then when they start charging they spike to 100% (I am installing thicker battery cables in…
-
- 26 replies
- 4.8k views
-
-
Any recommendations on a decent 3000w inverter. Was hoping for the sunsynk 5kw but can't afford it. Many thanks
- 24 replies
- 7k views
- 2 followers