  1. Hi, I see the Axpert Inverter Manual is not clear on the Maximum AC Input current that the Axpert range of inverters can handle, thus I am wondering what the different opinions on this will be. What would you guys say is the ideal DB board AC input Dual Pole Circuit breakers to use on single inverter installations: 1.5kVA Axpert 3kVA Axpert 5kVA Axpert

  2. HI experts im curious whats the max number of strings and panels per string (72cell panels) you guys have installed successfully on Axpert PF1 (5kva)? would it manage 5 strings of 3 panels (Voc around = 46V and Isc=9.3A). seems safe to have a string voltage of 138V with 46.5A for 5 strings (ignoring cable losses). Im concerned that the total PVin exceeds 6kw. Thanks in advance

  3. dont use this circuit breaker on solar system ! very dangerous

  4. Started by JTK,

    SO I started today configuring my setup 1. VenuxGS - connected - updated - sorted 2. MPPT - Connected - updated - sorted 3. 2xPulontech US3000's - Connected - sorted - have one issue. power LED of one unit does not come on. all seems to operate as intended. VE.Cam Cable made up and working 4. Multiplus II - Conencted - Can see as device through Venus. MK3 - installed. VE Config picks up Usb-Mk3 but does not see the Multi. Am I missing something? Normal UTP cable right? Thanks!

    • 2 replies
    • 1.5k views
  5. Hi all can i clone firmware from Inverex inverter ? if yes so pleas tell me how to download firmware from inverter

    • 2 replies
    • 1.4k views
  6. Started by Mistral,

    What is the difference between the Multiplus and the Multiplus II specs wise? I think the II is cheaper? I did hear talk that the II complies with Cape Town regulations? The only Victron I can find on the Cape Town list is the Grid which is no longer made!

  7. Started by Frodo,

    Hi, Which repair centres in and around Pretoria/Gauteng would you guys advise? A balance between price and service needs would be optimal.

  8. Me again... Ok, so everything hooked up, powered on and running well - installed WatchPower from the CD, hooked up the Axpert (green/black 5000VA/5000W model with parallel card - I initially thought it was the 4000W model...) via USB to my laptop, but could not change any settings via the software. After reviewing the settings and making the changes via the inverter control panel functions, the Pylons are charging - went with the following settings (no PV yet, so utility only): (26) CV Bulk Charging @ 53.8v (27) Floati Charge @ 53.2v Max Charge Current @ 30A all round So, after fiddling with the login password, I finally got in as the administ…

  9. Started by Dean,

    Hi I am trying to get stock of some inverters and batteries, however it seems with the load shedding rush no one has any stock. Does anyone know where I can get some GoodWe Inverters, Omni Power 240AMP/H Batteries etc ? Thanks

    • 5 replies
    • 1.8k views
  10. Started by admiral,

    I am trying to determine the best location for having a Victron Multiplus II installed. Unfortunately my garage has quite a few cupboards / shelves etc. already installed, and I am not keen on moving them around. There is space below one of the cupboards, but I am not sure if there are any regulations around how high an inverter should be installed from the floor? There may be a bit of space next to a tumble dryer, but that is hardly a friendly environment - unless I put e.g. some "fire board" next to the tumble dryer? (Fire board is the stuff used inside wood stoves and so on to keep the fire from burning directly against the metal.

  11. Started by jasonvanwyk,

    Hi all. My system is as follows: 1. 2 x Axpert 5kva 5kw inverters 2. 4 x 2.4Kwh pylontech batteries 3. 28 x 280w panels (7840w total) 4. ICC software. Using the ICC software, I've set the system to use SOC% to control how the batteries are charged. I've set them to charge only using solar power. I've set the system to switch over to grid when my batteries reach 25% SOC and then switch back to Solar/Battery power once the batteries have reached 35% SOC. This all works very well. However something strange I've noticed is that, when the batteries have reached below 25% SOC and have started charging between the 25-35% SOC parameters, the grid wattag…

    • 7 replies
    • 2.6k views
  12. Started by Farmer,

    Ek,wil net weet of daar al 72 v invertsers in gebruik is en wat sou die voordele en nadele van so,inverter wees? Toe ek begin het is gese dat die 48v meer effektief is as bv 24 v.....is 72v dan nog beter?...;die een ter sprake is n 3 fase ..5kva per fase.

    • 3 replies
    • 1.6k views
  13. Good day All, I am unfortunately in Cape Town and hence CoCT are being outright (insert profanity here) about their NRS "approved" Inverters. I have (form many years of work) this manic need for redundancy and hence am looking at getting 2x 3kVA MKS-3K-Plus Axperts and parallel them so in the event I loose one I at least still have half load capability or have the ability to increase full load by adding additional units at a later stage. The price point is then similar to say a MLT Oasis 8.0H with no redundancy and then I still need to add a MPPT to the mix as well. Are there any other inverters that can be paralleled other than the Voltronic Axpert that …

    • 7 replies
    • 2.3k views
  14. Started by Frodo,

    Hi. I noticed SolarPower does not allow me to change the “Allow AC charger times” from “01:00 - 04:00” (default?) to “00:00 - 00:00” (for always on). When trying to apply the settings, it says “Setting False!” This is on a Super 4k model Infinisolar. I am still using SolarPower 1.09. The battery voltages drops from 54v down to 51.7v as soon as the PV is unavailable. Why does this happen? Sometimes, the inverter also switches off in the early morning hours, while the grid is available. The “AC on/off” timer is set to “00:00 / 00:00” in other words it is disabled. Any ideas? Thanks.

    • 0 replies
    • 1.2k views
  15. Started by MartinCoetzee,

    is anyone else having this, i have tried to isolate why but no luck. Getting error 17 for a multiple of reasons, overload when there is no overload. Its 2 x 5kva invertors in parallel with 24 x 350 rec panels on 2 x 150/100 regulators. I have a few more clients wanting the same system but i dont feel confident doing it anymore. Batteries have been doubled in size to 880 ah.

  16. Started by Namverter,

    Hi all I need some help. Which Firmware U1 and U2 should I use in order to connect 2 Voltronic Power MKS 5000VA/4000W 48VDC inverters in parallel?

  17. Started by Bluefronted,

    Hi Guys, I was told by a dealer that one has to use a Victron accredited installer to hook up a Victron system to your DB , etc or else the warranty will be void. Is this true ? Suggestions on any Victron re-sellers , looking for a Quattro or Multiplus 2 5000 thanks

    • 2 replies
    • 1.4k views
  18. Hi, I am trying to understand the parallel connection of these two types of inverters. Is it possible to maybe upload some photos of the actual installations you guys have done on parallel configurations, showing the AC and DC wiring and also communications connections between the inverters and DB’s etc? Thanks.

  19. Started by Clivevan,

    I am new - hallo all. A few simple questions but I cannot get an answer anywhere. Intended load shedding setup: Mains plus 5000 watt axpert inverter and 4x200 AH Vision AGM batteries (a few panels maybe later). What happens if I should EXCEED 5000 watt usage? Does the inverter simply trip out? What is the effect on the batteries (while mains is switched on) if I consistently run close to 5 000 watts? Ie does the current simply pass through leaving the batteries alone as if they are being trickle charged just to preserve them for long term storage? Or does that current have a life shortening effect on the batteries? If so, then surely the inverte…

    • 15 replies
    • 4.4k views
  20. Started by Mr.A,

    Hi All, I recently bought a Mecer 5KV inverter. It states I must use 8 gauge wire for AC IN/OUT. Went to Builders they did know what I was talking about. They gave me stove installation wire. Will this work? Does anyone have gauge conversion to mm used in SA please?

  21. Started by Energy-Jason,

    Hi Guys. Hope all is well. I was wondering if the Venus GX was compatible with the Victron Multi 48/1200/13-16 1000W Inverter/Charger . We would like it to talk to the Pylon US3000B. The loads in our Fiber -WIFI hut is only 250W. We require long backup times with limited space. I am opting for the small multi as it has 13A charger and is the smallest I could find. Just need the Multi to speak to the Pylon. Hope you can help. Thanks so much all! Sincerely Jason

  22. Started by malek94,

    Hello everyone yesterday I have decided to parallel my MKS 5KW together and I had factory firmware V72.61. unfortunately, this firmware downgrades my unit to 4000W instead of 5000W. so now I want to roll back the firmware and bring my unit back to 5000W. beside my other unit with factory firmware 74.10 without a change in its firmware. here is a photo of my MKS 5KW. I have tried to ask Voltronic to send the original firmware but they answer that V72.61 is correct firmware and I would change control board! I still believe that there is a dummy firmware or any other version can let us upgrade the firmware to 74.10 or compatible firmware with this …

    • 2 replies
    • 2.5k views
  23. Started by Gellies,

    Hi I have 4 x 3.6kW Pylontechs coupled to an Axpert 5 mkii with 10 x 350W panels in two strings of 5 each. In every daily cycle I get a code 04 warning (battery low). I seldom get to the full charge at 53.2V. It ussually stops around 52V at the end of the day. As soon as PV charge stops I get code 04 at say around 49 - 51V battery power. It takes the whole night to get to say 48.5V when the PVs kick in again. Is this normal for Lithium Ferrous batteries. It seems that their band of operation is fairly narrow at 48V to 53.2V. Regards

  24. Started by Mr.A,

    Hi all, I am new so please forgive the ignorance where applicable 😂 After installing the inverter, switched power on....nothing no light no sound nothing. Must mention no battery nor PV connected only eskom at AC IN. Is this normal as I did not want to use until I have the rest but just wanted to see if it would turn on. Please advise.

  25. Started by Kiran,

    I have a RCT inverter charger model RCT- AXPERT 5K 5000VA/4000W , I NEED TO KNOW IF I CAN USE THE PYLONTECH US3000 LITHIUM BATTRIES,DO I HAVE TO UPGRADE MY FIRMWARE ON THE INVERTER , PLEASE CAN ANY ONE ADVICE

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.