Batteries

Batteries, battery monitors, chargers, accessories & battery care

  1. Started by Bobster.,

    Here's an illustration. I don't know if this is usual/acceptable or not. But I believe that numbers don't lie, so this is what it is. With a return to the office and thus an early morning commute imminent, I want to run my heat pump earlier in the morning. I used to do this. It was the situation when my system was installed in mid 2019. Here's what happened 23rd July 2019 SOC at midnight was 82%. Pump turns on at 4:30 with SOC 75%. The thermostat turns the pump off at 6:10 with SOC now 41%. Here's what the portal shows me for 25th Jan 2020 70% SOC at midnight. Heat pump kicks in at 4:30. SOC when the heat pump turns on is 58%. A…

  2. Started by Tinbum,

    Would anyone have a copy of the latest firmware for the Sofar ME3000SP?

  3. Has anyone had a successful experience connecting Pylontech UP5000's to Sunny Island Series 6-11 battery inverters and if so did the install also successfully include the connection of the COMMS cable? According to the SMA SI-LiIon-TI-en-45 doc connecting Pylontechs are approved but I am not sure on the COMMS cable wiring required. The other alternative I have been considering is the BYD BATTERRY BOX LV FLEX LITE units but the above SMA battery doc says not to use for off grid, maybe somebody can also pass on there experience with these models please.

  4. Started by chrisc,

    Friend bought a house in 2020 with an existing inverter and a 6kw 48 volt lithium-ion battery, plus 8 x PV panels The inverter is a 8KVA unit and was recognised as a PIP-5048 unit. It was noticed that despite there being 8 PV panels, the maximum power generated power from the panels was only 135 watts The display on the panel shows that the load presented to the inverter is 8% (TV, fridge, some lights, computer) SetSolar in Epping replaced the MPP charger board and now you can see 350 watts during the day. The inverter is set to provide a float charge of 54V Prior to having the inverter repaired, at random (twice a month) the circuit-breaker on the …

  5. Hello again. I am considering changing my second PV system batteries to PylonTech UP 5000 batteries in due course. On my other I use PylonTech US3000C with no problems. I was wondering if a comparison chart between these two different battery sizes exist, and where would I be able to find it? Thanks a lot

  6. Started by Venom,

    Anyone know these batteries and if you do post some specs please https://solartradesales.co.za/product/7-2-kwh-125ah-lithium-ion-batteries-10-years-warranty-guaranteed/

  7. I am trying to configure 4 x 100Ah SOSolar Gel batteries to be used with my Sunsynk 5.5Kwh Inverter. Can anyone help with the settings required as per the settings picture below?

  8. Started by Morne SBR,

    Is anyone else having issues with hubble am2 not holding Soc ?

  9. Started by JohanG,

    Can one incorporate a 24v lithium battery into a 48v setup.😕

  10. Started by MdF,

    Morning All, Would just like to confirm DIP switch settings for using 2 x LBSA 51.2V 105Ah LiFePO4 batteries in parallel. According to the spec sheet as bellow it should be as follows: Master 1 2 3 and 4 = Off, 5 = On, 6 7 & 8 = Off Slave 1 = On, 2 3 4 5 6 7 & 8 = Off Thanks MdF

  11. Started by CobusK,

    Good morning I am running a Dyness B3 3.6KW battery on a Deye/Sunsynk 8KW inverter. All systems operate normal, but the battery indicator on the LCD of the Deye began to show 3 red exclamation marks when SOC is 100%. The red exclamation marks disappear as soon as a discharge period occurs. This only started about 3 weeks after commissioning of the system. Various inquiries led me to Rectron, the distributor of Dyness. I had a good service experience with Anzej Lozovski and Werner Bezuidenhoudt and received an email from them informing me that the manufacturer confirmed that this is normal. Their response: Below is the suppliers response to the ERROR men…

  12. Started by CapeTown,

    This is a stupid question, but rather safe than sorry, so am asking. Hubble's manual / paperwork / etc online isn't fantastic already, and I looked at every single install pic I could find on here, but none show the terminals. I labelled the pic below 1 to 4. Which of the terminals do I connect my cables to? My connector under my battery is red and black though, but not sure if I use 1 & 3 or 2 & 4, or it doesn't matter. At the moment I have a single battery only with a SunSynk 5.5 inverter. And on the DIP switches just the 1 up, the other three down? Thanks.

  13. Started by JacquesVDM,

    Hi everyone. Does anyone have the comms protocol of the Hubble AM-2 batteries? (RS232 preferred) I want to design a controller to activate relays at certain SOC levels. Thanks Jacques

  14. Started by Ayesha,

    I have a 5kva growatt inverter running well for the 16 months. for the last 2 weeks we were getting an error 56 on the inverter when we reset (power down and power up) the inverter the error clears and everything works again. Today we got the error 56 code again i reset the inverter and it started working but i have a flashing warning light on setting 19. The inverter is using the grid and solar at the moment it is not even picking up the battery. I checked on the shinephone app and it looks like the battery depleted as according to the App it is sitting at 10%. Is there a way to check the battery and what percentage charge it has left and how do we get the battery rechar…

    • 0 replies
    • 1.6k views
  15. Started by John Nguyen,

    Hi everybody ! I need help with my UPS, currently the UPS is giving an error of Inverter output voltage abnormal and cannot get it online, I have checked the wires connected to the thermostat and the measurement is 0.5V, now it is still running bypass . hope someone can give me the answer, thanks for the help

  16. Evening I am new to this forum and first time posting. I am definitely not a fundi when it comes to electronics. I have an issue where I keep having an F08 error and everything turns off. Rubicon gave a loan inverter which ran for 2 weeks then the same thing is happening. The technician seems to think it is the battery so switched the slave and master around. Worked fine for 7 hours and poof F08 error all the lights turnef off again. Load is 8% so not very high at all. Trouble is it turns off at random times. I cannot seem to get answers and I am tempted for them to take the wholes system back. Not what I was expecting. Any advice would be appreciated. Thanks

    • 3 replies
    • 1.3k views
  17. Started by Blackwidow,

    Hi All, I have a 8KW Sunsynk with 2 5.5 100Ah Hubble batteries connected in parallel. My question is with the charging and discharging can I up the Ah from round about 100Ah to 200Ah due to 2 batteries running or should I never dis\charge them more than what they are rated for as a single unit at 100Ah? As sometimes I have enough battery reserve but in spikes it shuts down the system as batteries are limited on the lower Ah

  18. Started by Lightyear,

    Good day. I bought a pylontech battery US3000 and I took some time without charging it and now its showing a red ALM light and the light is not turning off and the battery is not charging My inverter is Kodak 0GX 5.48 Is there any way to make the light turn off? Thank you for your support

    • 4 replies
    • 4.2k views
  19. Hi all, I currently have some lead acid deep cycle batteries, 8 x 102Ah, with sets of 2 in series, 4 parallel strings, for a total of 408Ah @ 24V. I paid around R 16 000 the batteries and am now looking at replacing them as they seem to get quite low overnight and don't even charge fully. I have a Mecer (Axpert) 3kVA 24V inverter, charging the batteries of 1.5kw solar, and at most drain the batteries 40-50Ah @ 24V overnight running fridge/freezer, security camera system, lights and usb chargers etc. I see some Lithium Ion / Phosphate batteries that promise thousands of cycles when they are drained up to 80% of their charge (DoD). I'm only wanting to s…

  20. Cost aside, a 400ah Sealed led Acid/Gel battery bank at 50% Depth of Discharge would give me 200ah, ideally or lets be kind and say 150ah on a 24v system. Why then would suppliers recommend getting a 24v 100ah lithium battery, on the same system and on the same loads? This is a Pv/Grid coupled system by the way, with 12 x 250w panels with an MPPSolar Chinese Inverter. Please help.

    • 4 replies
    • 2.3k views
  21. Started by Jo-Jo,

    Good afternoon. We have just installed a 5Kw sunsynk inverter with a pylontech up5000 battery, this is new to me the up5000 has an audible alarm every 5sec. The battery is fully charged. Please assist. BR

    • 5 replies
    • 2.3k views
  22. Started by Antonio de Sa,

    The response from the OEM technical staff I quote : First mail The best would be to get the battery to us in order for us to investigate the problem. Second mail after I told them I'm running without BMS Please note that you should not run without a BMS as this would damage the cells and has voided your warranty on the cells. Is this a fact? this is the answer I received from my battery OEM, however, I don't see anything regarding this subject on they operating manual. I have a cell on my battery that it's voltage is running lower than the other 15 cells. Typically they customer service in my point of view is equal to Zero, nada, niks…

  23. I have 2 x Shoto SDA10 4.8's (15S version) that are approximately 6 months old. Am I likely to have problems if I add another brand new one to this setup? Tx.

  24. I had 2 x 3000Pylontech batteries working well with my 5 KVa Mercer inveter. I have added 2 more 3000c batteries. I now have an Error 4 issue each time I switch to USB or SOL in program 1 even though all four batteries are fully charged. Can anyone suggest a solution

    • 3 replies
    • 917 views
  25. I’ve got 3 x 4.8kwh LifeP04 batteries rated at 80% DOD over 6000 cycles - that is over 16 years of cycles and my warranty period is only 10 years. When they were installed, my installer set up the inverter to drain down to 30% DOD overnight before switching to grid and leave 10% in the batteries to cover for load shedding and power outages in the middle of the night. Now nobody likes paying for insurance and I suggest nobody likes leaving 10% of battery on the table every day for the odd occasion that Eskom goes boom while the sun is not shining. So here is my idea. For the odd occasion that I need the extra battery, I’m comfortable draining the battery to 9…

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.